Fault loop impedance. Is there a formula to calculate the impedance?

rysiu.e 101887 18
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 5265220
    rysiu.e
    Level 12  
    Hello all. I have read a bit about the short circuit loop impedance and I know that it can be measured with a meter. Is there a formula to calculate this impedance?
  • ADVERTISEMENT
  • #2 5265477
    stomat
    Level 38  
    Are you going to measure or calculate impedance? There are formulas for calculating impedance. Varies depending on the data you have.
  • #3 5265597
    rysiu.e
    Level 12  
    I would like to calculate but I found nothing concrete. How can you Stomat give the formulas I would be really grateful.
  • ADVERTISEMENT
  • #4 5265679
    sq9jjh
    Electrician specialist
    Hello. Root of the sum of the squares of R and X. Google it and you will find it. Greetings.
  • ADVERTISEMENT
  • #5 5265783
    Łukasz-O
    Admin of electroenergetics
    rysiu.e wrote:
    I would like to calculate but I found nothing concrete. How can you Stomat give the formulas I would be really grateful.


    Understands that you have measured short circuit loops and want to calculate allowable impedance? That's what you mean?

    Zdop = Uf / k * Ibezp

    where:
    Zdop - admissible impedance
    Uf - phase voltage
    k - correction factor
    I - nominal fuse current


    greetings
  • #6 5265903
    rysiu.e
    Level 12  
    I do not have such a measure and I would like to calculate it from the formula.
  • #7 5266300
    Łukasz-O
    Admin of electroenergetics
    rysiu.e wrote:
    I do not have such a measure and I would like to calculate it from the formula.


    If you want to evaluate the protection against electric shock, unfortunately, you will not be able to do without a meter. You can, of course, theorize.

    If you have an ordinary voltmeter and ammeter, you can try to approximate calculations - rather just for fun:

    Zs = Uo-U / I

    Ik = Uo / Zs

    where:
    Zs - fault loop impedance
    Uo - idle phase voltage
    U - phase voltage under load
    I - load current
    Ik - short-circuit current

    I also recommend google and Wikipedia, just like my colleague sq9jjh there you will learn about basic formulas. Unfortunately, complex numbers will also be needed. I wish you perseverance :|
    Greetings.
  • ADVERTISEMENT
  • #8 5266307
    rysiu.e
    Level 12  
    Thanks for your interest helped.
  • #9 5266464
    sq9jjh
    Electrician specialist
    In the past, it was all "on foot", but nowadays there are a lot of computational support programs. If someone wants to, he can download the demo version of the "obl 2002" program from the net. I have and know this program for pain, and it's pretty decent. The full version is paid, of course, but in my opinion it is the best I have ever found for TN and TT networks.
    Greetings.
  • #10 5266638
    Łukasz-O
    Admin of electroenergetics
    Calculate it, but you must have data :D
  • #11 5266665
    sq9jjh
    Electrician specialist
    Sure he will. He knows the cross-section and length, he will find formulas, he will also find tables with data, it is not easy to want to be able to do so. Best regards to my colleague Łukasz-O.
  • #12 5271539
    pawelo220v
    Level 12  
    And if you have a friend of an electrician who has a short circuit loop impedance meter, let him tell you or measure it himself as a friend (because it normally costs a few zlotys. :)
  • #13 5273525
    lukaszu6
    Level 16  
    Tell me what is the acceptable short circuit loop impedance?
    As I measured with the meter recently, it was 0.58 ohm.
    It's good or bad
  • #14 5273707
    modlinp
    Level 15  
    It is very difficult to give a correct answer to this question. The impedance value should be small, i.e. single ohms and less (in your case the value is correct, but you can find a case where this value could still be too high :D ). Is the value correct, it is necessary to check the effectiveness of the automatic power off (and this depends on the used protection and network system)
  • #15 5273724
    sq9jjh
    Electrician specialist
    Łukasz6 wrote:
    tell me what is the acceptable short circuit loop impedance?
    As I measured with the meter recently, it was 0.58 ohm.
    It's good or bad

    Hello. Good questions! If you asked in practice why we measure the short circuit loop impedance, you would not have such dilemmas now. Greetings.
  • #16 18691125
    Spiced91
    Level 5  
    Hello,
    I would like to check the effectiveness of the applied protections in the LV switchgear (measuring junction) during a short-circuit. The circuit from the junction is routed through a cable line in the ground, approx. 100 m, then enters the pole and then runs along the overhead line for approx. 150 meters to the RSA type longitudinal switch disconnector.
    I want to check the effectiveness of the automatic power cut-off in 5 seconds. and the question is whether to check it for a circuit whose entire length is 250m? Is this the worst case? Or should I also check for a shorter circuit, e.g. when the cable enters a pole? I would like to ask for your support.
  • #17 18691695
    CYRUS2
    Level 43  
    sq9jjh wrote:
    Sure he will. He knows the cross-section and length, he will find formulas, he will also find tables with data, it is not easy to want to be able to do so. Best regards to my colleague Łukasz-O.
    Not true.
    IPZ cannot be calculated.
    Because the IPZ covers everything - right down to the way.
    What colleague Łukasz wrote in post # 7 is IPZ measurement using the technical method.
  • #18 18691709
    stonefree
    Level 27  
    CYRUS2 wrote:
    IPZ cannot be calculated.
    And yet the designers calculate the performance conditions using the SWZ, and this even coincides with the measurements.
  • #19 18691712
    CYRUS2
    Level 43  
    Spiced91 wrote:
    I want to check the effectiveness of the automatic power cut-off in 5 seconds. Is this the worst case? Or should I also check for a shorter circuit, e.g. when the cable enters a pole?
    The power supply cable to the building is protected by a fuse in the connection - not in the switchgear.
    stonefree wrote:
    And yet the designers calculate the performance conditions using the SWZ, and this even coincides with the measurements.
    Because they have measured input data.
    This calculation can only be used to make a project.
    It cannot substitute for a control measurement.

Topic summary

The discussion revolves around calculating fault loop impedance (Zs) and the formulas associated with it. Participants clarify that while impedance can be measured with a meter, there are also formulas for calculation. Key formulas mentioned include Zs = (Uo - U) / I for fault loop impedance and Zdop = Uf / (k * Ibezp) for admissible impedance. The importance of having accurate data for calculations is emphasized, and the necessity of measuring impedance for assessing protection against electric shock is noted. Additionally, the conversation touches on the use of software tools for calculations and the significance of understanding the effectiveness of automatic power cut-off systems in electrical installations.