Human Fault Loop Impedance: Understanding IPZ, IEC 60364-4-41, and Effects on 230V Systems

topikpl 152969 14
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 10674507
    topikpl
    Level 10  
    Hello,

    at the beginning, I note that I do not have an electrical education and I am interested in the issue of the above-mentioned impedance (ipz for short) purely hobbyist.

    Well, I heard that for an installation in a flat ip 0.4 ohms is "good", but 1 ohms is "bad". Wanting to explain to myself what can mean "good" and "bad" mean, I searched the Internet and found PN-IEC 60364-4-41, which says that the ipz should be selected so that in 230V systems, the tripping time of the switching device was 0.4s.

    A suitable formula is Zs x Ia
  • ADVERTISEMENT
  • #2 10674518
    retrofood
    VIP Meritorious for electroda.pl
    3.1.13. (10.9, 15) It is forbidden to publish entries that violate the spelling rules of the Polish language, which are careless and incomprehensible.

    3.1.17. (10.9, 16) It is forbidden to publish entries lowering the general level of discussion, resulting from laziness or containing the demanding nature of statements.
  • #3 10674723
    Łukasz-O
    Admin of electroenergetics
    At the request of the topic, however, it does not release the author from correcting the spelling of the units, reading the content of the section, etc. This is a technical forum, we require a minimum of knowledge and a lot of details.
  • ADVERTISEMENT
  • Helpful post
    #4 10674754
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #5 10674856
    HeSz
    Electrician specialist
    topikpl wrote:

    Well, I heard that for an installation in an apartment ip with 0.4 Ohm is "good", but 1 Ohm is "bad". Wanting to explain to myself what can mean "good" and "bad" mean, I searched the Internet and found PN-IEC 60364-4-41, which says that the ipz should be selected so that in 230V systems, the tripping time of the switching device was 0.4s.

    A suitable formula is Zs x Ia
  • #6 10674981
    topikpl
    Level 10  
    Thank you for bringing the topic back and for the answers.

    I improved Ohm to Om, because that's what the moderator meant - I'm not quite sure. I can see that the electrician community is sensitive and likes to be enigmatic :-)

    @ 15kVmaciej: ok, I think I understand, but what causes "too" high impedance in practice? Probably the cross-section and length of the cable (for which the wrong protection was selected), and for a circuit with a correctly selected fuse? Circuit damage?

    @HeSz: ok, I will read it again, but this later, in the morning I won't make it.

    I remind everyone of the basic electric units:
    wat [W] - we write "watts"
    kilowatt [kW] - we write "kilowatts"
    ampere [A] - we write "amperes"
    volts [V] - we write "volts" (not "volts")
    kilowatt hour [kWh]
    ohm [?] - ohms (not "ohms", not "ohms", not "ohms")
    [retrofood]
  • #7 10675140
    MrMazi
    Level 16  
    Hi
    Ia is the trip current Ia = k * In [A]

    k is the coefficient which is determined from the fuse characteristics.
    It is assumed that for the circuit breakers it is:
    characteristic B; k = 5
    characteristic C; k = 10
    characteristic D; k = 20

    So with the S301 B16 protection, the current causing it to trip at the right time is 16 x 5 = 80A.
    The permissible fault loop impedance is then 230/80 = 2.87 ?.
    As you can see, assuming 0.4 is good and 1 is bad is bad reasoning.
  • #8 10675156
    retrofood
    VIP Meritorious for electroda.pl
    MrMazi wrote:

    The permissible fault loop impedance is then 230/80 = 2.87 ?.


    And where is the coefficient taking into account measurement errors?
  • Helpful post
    #9 10675325
    MrMazi
    Level 16  
    retrofood wrote:
    MrMazi wrote:

    The permissible fault loop impedance is then 230/80 = 2.87 ?.


    And where is the coefficient taking into account measurement errors?


    Does this coefficient depend on the control and measurement equipment used?
    Therefore, it cannot be administered with theoretical consideration of the prolem.

    Well, unless my colleague was about another measurement error?
  • ADVERTISEMENT
  • #10 10675466
    topikpl
    Level 10  
    Thank you for your answers and for drawing attention to the units. I will definitely not write more Ohm or Om in my life :wink:

    My understanding is that after accounting for the error of the measuring device, the impedance value will be somewhere in the range of 0.5-2 ohms. So whether it is "good" or "bad", in practice it depends on the device with which the measurements are made.
  • #11 10675479
    MrMazi
    Level 16  
    Maybe another way. To understand me well.
    If the measured impedance is 2 ? and the meter error is 1%, then the actual value of the fault loop impedance can be from 1.98 to 2.02 ?.
    We take the worst value, i.e. 2.02 ?.
    It does not change the fact that 2.87 ? is allowed.

    It doesn't depend on the device!
    Installation parameters (including fault loop impedance) do not depend on what they are measured.
    This is not the case in any area of life.
  • #12 10675894
    topikpl
    Level 10  
    MrMazi wrote:
    It doesn't depend on the device!
    Installation parameters (including fault loop impedance) do not depend on what they are measured.
    This is not the case in any area of life.

    I expressed myself wrong. Naturally, reality does not depend on measurement (although there is a theory about this ;-) ). My point is that different meters give different ranges, if you measure with a big error you can get a range that goes "wrong", even though measuring with an accurate device would show "good".
  • #13 10676022
    MrMazi
    Level 16  
    When measuring standard S301 B16 protected socket circuits, the value of this allowable impedance is 2.87 ?.
    Let the meter readings be about 1? (which is already a big result).
    You do not have to worry then that the meter is lowering so much that you may be above the maximum allowable impedance.
    There are no such measures whose error would be 300%.
    It's worse when the result is 2.5 ?. Then the risk of being above the requirements is much greater
  • #14 10676407
    Miniax
    Electrician specialist
    Whether the IPZ is satisfactory (ie "day or bad") depends on the equipment used in the installation. In general, if the condition of the automatic shutdown of the power supply is met, then the impedance can be considered satisfactory (at least in terms of protection in the right time). In addition, the layout of the grid is essential - whether it is TN or TT. Of course, in average home installations, it can be assumed in advance what a relatively satisfactory value will be. However, it does not change the fact that each installation should be approached individually and it is not possible to clearly define what values of fault loop impedance are satisfactory.
  • #15 10678769
    Anonymous
    Level 1  

Topic summary

The discussion revolves around the concept of fault loop impedance (IPZ) in electrical installations, particularly in 230V systems, as outlined in the PN-IEC 60364-4-41 standard. Participants clarify that a low impedance value (0.4 ohms) is considered "good," while a higher value (1 ohm) is deemed "bad." The importance of IPZ lies in its role in ensuring that circuit protection devices trip within a specified time (0.4 seconds) during faults. The formula Zs x Ia is used to determine the permissible fault loop impedance, where Ia is the trip current influenced by the characteristics of the circuit breaker. The conversation highlights that acceptable impedance values can vary based on installation specifics, including the type of circuit (TN or TT) and the characteristics of the protective devices used. Measurement errors and their impact on perceived impedance values are also discussed, emphasizing the need for accurate measurement tools to ensure safety and compliance.