Maximum kW Load Capacity for YAKY 4x120 Aluminum Cable Over 80m Distance

PAWPIO1 60780 10
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 8038852
    PAWPIO1
    Level 2  
    Hello.
    I am asking for information on how much kW a 4x120 alu cable for continuous single-shift operation can pull, I have designed such a cable and I am wondering if I should give it a bit more if I need to increase power in the future, I will add that the cable is about 80m long. Thank you in advance for your response.
  • ADVERTISEMENT
  • #2 8038896
    sq9jjh
    Electrician specialist
    PAWPIO1 wrote:
    Hello.
    I am asking for information on how much kW the 4x120 alu cable can pull for continuous single-shift operation,

    It depends on the arrangement and a few other details, but roughly for 400V, it is from 130 to 160kW.
  • ADVERTISEMENT
  • #3 8038927
    michuszcze
    Level 17  
    When laid in the ground, it is a long-term current carrying capacity of 188 A, i.e. about 108 kW.
  • #4 8039018
    PAWPIO1
    Level 2  
    michuszcze wrote:
    When laid in the ground, it is a long-term current carrying capacity of 188 A, i.e. about 108 kW.

    Thank you very much for your answer .
    Are these 108 kW or is this the maximum load??
    What will happen when the electricity consumption is 130 kW???
  • #5 8039284
    MrMazi
    Level 16  
    These 188 A is the maximum allowable current for long-term operation. If more flows, the temperature of the conductor will start to increase relative to the overload of the cable.
  • ADVERTISEMENT
  • #6 8039341
    michuszcze
    Level 17  
    Buddy, the tables give different current carrying capacity, these 130 kW will also transfer as a colleague wrote in probably the second post.
  • #7 8039366
    PAWPIO1
    Level 2  
    Thank you very much for the answers, I think that for peace of mind I will arrange 4 x150 and I will have a supply for the future.
  • #8 8039397
    michuszcze
    Level 17  
    Oh buddy, it's not a cable as you write, but a YAKY cable.
    Regards
  • #9 8040271
    Akrzy74
    Rest in Peace
    One colleague wrote:
    Quote:
    Buddy, the tables indicate the current carrying capacity differently; When laid in the ground, it is a long-term current carrying capacity of 188 A


    Maybe I'll add something from myself to verify the answers :)

    Maximum kW Load Capacity for YAKY 4x120 Aluminum Cable Over 80m Distance

    Maximum kW Load Capacity for YAKY 4x120 Aluminum Cable Over 80m Distance

    Ps. Do not forget about the correction factors and the use of appropriate tables - mine comes from the Institute of Power Engineering :wink:
  • ADVERTISEMENT
  • #10 8044858
    Miwhoo
    Electric installations specialist
    The "Guidelines for Measurements in the Power Sector" confirm the truth of my colleague Akrzy :)
    For 3-4-core cables laid permanently in the ground, the long-term load capacity of cables with paper, rubber and PVC insulation:

    vein cross-section | current
    --------------------------
    50mm2 | 165A
    70mm2 | 205A
    95mm2 | 240A
    120mm2 | 275A
    150mm2 | 315A
    185mm2 | 355A
  • #11 8044931
    elpapiotr
    Electrician specialist
    Hello.

    The same is stated by Prof. Henryk Markiewicz in his book "Electrical installations" ed. II changed.

Topic summary

The discussion revolves around the load capacity of a YAKY 4x120 aluminum cable for continuous single-shift operation over a length of approximately 80 meters. Responses indicate that the cable can handle a long-term current carrying capacity of about 188 A, translating to approximately 108 kW. However, some sources suggest that it can also support loads up to 130 kW, depending on the arrangement and installation conditions. It is emphasized that exceeding the maximum allowable current can lead to increased conductor temperatures, potentially causing damage. The original poster considers upgrading to a 4x150 cable for future power needs. Additional references to guidelines and tables for cable load capacities are provided.