YAKY 4x16 Cable Load Capacity for 63A Pre-metering in a Single-Family House

michcio 32697 6
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 14843668
    michcio
    Electrician specialist
    Hello
    There is a building (single-family house)
    The power line is made by YAKY 4x16 cable. The length of the PE is about 15m.
    The cable is run in a pipe Arot 50mm under the floor of the basement (basically already in the ground) and for a section of about 3m in a furrow in a solid brick wall, also in a pipe.

    I have doubts about the long-term load capacity of this cable, and specifically whether 63A pre-metering is not too much for it.
    Assuming these 40kW peak voltage drop is
  • ADVERTISEMENT
  • #2 14843707
    opornik7
    Electrician specialist
    michcio wrote:
    Well, I have a dilemma - will it be suitable or not?
    I yes and no. On contact depending on the method of counting.
    I would change because in a while the Recipient will get the idea of increasing the power and du..... strangle in the bushes.
    A good rule of thumb for design is to oversize by at least one degree and I do it without telling anyone why ;) .
  • ADVERTISEMENT
  • #3 14843784
    michcio
    Electrician specialist
    In this case, perhaps it is enough to replace YAKY with YAKXS without changing the cross-sectional area?
    In the switchgear a little small space, it will be difficult to maneuver 25 mm2 under the disconnector, in addition, sector conductors will have to be pressed (at 16 mm2 are still round).
    For XLPE insulation comes out 77-84A in the air and 92-98A in the ground (I give forks because different manufacturers specify differently).
  • ADVERTISEMENT
  • #4 14843814
    opornik7
    Electrician specialist
    michcio wrote:
    In that case, maybe replacing YAKY with YAKXS without changing the cross section is enough?

    Do what you want, end see. My late Dad used to say.
  • ADVERTISEMENT
  • #5 14848226
    kubai
    Level 14  
    michcio wrote:
    In the PN-IEC gives barely 52A for the cable in the ground and yet I have the impression that the load capacities given in the PN are in relation to the manufacturers' data often much lower...

    Well, I have a dilemma - will it be suitable or not?

    How old is the building? In my opinion, the colleague can not follow the data for cables currently manufactured, but at most those that were given by the cable manufacturer at the time. As for the long-lasting load capacity, here the manufacturer rather knows more about it than the data in the standard, which is often already a few years old on the neck - the crown example is cables for inverters: 2YSLCY when converted to 2XSLCY allows you to reduce the cable by one cross-section down.
    michcio wrote:
    The floor will be ripped so there will be a chance for replacement - only is there a need for it?
    Electricity demand is growing every year and there is no indication that it will start to decrease. I would say that oversizing the PE by one section is currently a good practice rather than an exaggeration, especially since we are talking about 15mb.
  • #6 14848331
    Akrzy74
    Rest in Peace
    I would consider XLPE insulated cable.
  • #7 14848722
    michcio
    Electrician specialist
    The current cable is several years old so I think you can successfully apply to it the parameters of modern products.

    I just decided to replace it with YAKXS (XLPE insulation). The price compared to PVC is basically identical.

Topic summary

The discussion revolves around the load capacity of a YAKY 4x16 cable used in a single-family house, specifically concerning its suitability for a 63A pre-metering setup. Participants express concerns about the long-term load capacity of the cable, suggesting that oversizing the cable is prudent due to increasing electricity demands. Recommendations include considering a switch to YAKXS cable with XLPE insulation, which offers higher current ratings (77-84A in air and 92-98A in ground) compared to the current PVC-insulated cable. The age of the existing cable is noted, with suggestions that modern parameters can be applied to it. The consensus leans towards replacing the cable to ensure safety and reliability.