Why is the IT network layout not widely used?
Dzonzi 37320 50
Why is the IT earthing system not widely used in general electrical installations?
IT systems are not widely used because they are expensive to build and even more expensive to operate, and they require continuous monitoring of insulation/leakage so the first fault can be found and repaired quickly [#16152604][#16152666] Their main advantage is that the first earth fault does not immediately disconnect the supply, which is useful where continuity matters, such as operating rooms and other critical industrial installations [#16152666][#16153015] But that advantage only holds if the system is supervised and faults are removed promptly; otherwise a second earth fault can create a dangerous current path and the system stops being effectively safe [#16152726][#19677659] So IT is used mainly in special places like hospitals, mines, power plants, water treatment plants, and some industrial equipment, not as a general-purpose distribution system [#16153015][#19529392]
  • Is impedance monitoring the main limitation of IT networks?
    #1 16152578
    Dzonzi
    Rate: 59
    Hi.
    Why is the IT network not widely used, since it is much safer than others? I found in google that it is used only where high security is required, e.g. hospitals, and the main disadvantage of this network is the need to constantly monitor the impedance of the system.
    Why?
    Is it only because of this disadvantage that this network is so rarely used?
    The IT network system is constantly used in specific solutions, where it is necessary to ensure a high level of protection and ensure its reliability. Most often you can meet him in hospitals, where operating rooms are supplied in this way. This system is characterized by the fact that there is no direct connection to the ground potential from the supply side (the connection is made by high impedance), so there is no path for the short-circuit current. Even if the insulation of the receiving device is damaged, there is no risk of an electric shock. This can only cause a second short-circuit of the next device. The disadvantage of this solution is the necessity to constantly monitor the impedance of the system.
  • Higher construction and operating costs limit IT networks
    #2 16152604
    retrofood
    Help: 1140
    Rate: 4800
    Dzonzi wrote:
    Hi.
    Why?
    Yes, that is due to the high construction costs and even higher operating costs.
  • #3 16152608
    Strumien swiadomosci swia
    Help: 1405
    Rate: 6430
    But reliability compensates for these inconveniences.
  • #4 16152637
    zdzisiek1979
    Help: 563
    Rate: 1256
    Reliability?
    TN networks are also reliable, only users fail.
    If IT networks existed on a daily basis, repairs would only take place after the second earth fault. The electrician would see how it would not be possible to activate the security.
    Where they are subject to supervision, therefore they work as they should.
  • #5 16152642
    Dzonzi
    Rate: 59
    So what's the deal with impedance control?
  • #6 16152658
  • IT network maintains operation after the first earth fault
    #7 16152666
    zdzisiek1979
    Help: 563
    Rate: 1256
    The point is to keep it running smoothly.
    Originally the network is isolated from "earth". The first earth fault does not matter for her work, it is an advantage. Thanks to this, for example, the respirator works because the fuse has not tripped, but the second earth fault may result in immediate disconnection and the network does not work.
    That is why the automation systems control the leakage current and provide timely alarms, thanks to which the first earth fault can be repaired and the network fully operational.
    In addition, the network is safe in terms of protection against electric shock, but loses it after the first earth fault. Perhaps I will misuse the term that the network acts like a TN after the first earth fault. Therefore, during the tests, a forced ground fault is performed and the network is tested as TN. Only this earth fault is done with the head so that it would not be a hate.
  • #8 16152688
    Dzonzi
    Rate: 59
    WojcikW wrote:
    Dzonzi wrote:
    Why is the IT network not widely used, since it is much safer than others? ...
    It is not safer.
    Well, how is not safer, since
    IT network safety depends on continuous fault monitoring and maintenance
    #9 16152726
    retrofood
    Help: 1140
    Rate: 4800
    Buddy, because it all depends on one short word. And it is "if."
    If the grid is constantly monitored, if the first earth fault is removed immediately (electricians would not be available in the country), if the control devices did not fail (and they are quite complex), if ... if ... if. And finally, the most important thing. If no asshole pushes his fingers into it, which in our country, where there are more misfit electricians than all the inhabitants, is impossible to fulfill. That's the whole problem.
  • Second earth fault turns isolated IT network dangerous
    #10 16152792
    zdzisiek1979
    Help: 563
    Rate: 1256
    Oh, someone's nerves are gone :D
    Because the network is isolated! And the first damage is a misuse of the word safe yet, but each subsequent one is a threat.
    Since the network is galvanically isolated from the ground, the only way for electricity is very high resistances and the phenomenon of capacitance.
    But with the second earth fault, these resistances can drop to a few k? or several hundred ? and here the path for the shock current is ideal.
    I ignore the fact of complicated damage.
    This is what the control system is watching to detect.
    Yes, we consider damage that is convenient for us, which is one thing. There may be more of them at the same time.
    You can also consider grounding the same active conductor in several places at the same time.
    Therefore, equalization connections are also important in these networks, but this is a different story.
    Consider the operating room.
    The surgeon takes the electric saw that is damaged. Saw damaged. The saw is on the table. The earthquake closes the floor table ... now the earthquake is handled is closed by the surgeon but still nothing. But if another fault occurs, the short-circuit path will close between one fault and the other, i.e. the surgeon will be the conductor for the current that will flow between one fault and the other.
  • IT networks preserve operation after the first insulation fault
    #11 16153015
    Help: 1405
    Rate: 6430
    There is an operating room, water treatment plants, power plants, individual devices in industrial installations, there are even special inverters for IT networks.
    Just so that the device does not fall out of work if something breaks in it.
    This is not the case for ordinary clickers and Peciks, which would surely be killed because the first failure would never be removed for various reasons, mainly laziness and dullness.
  • IT networks used in mines with layered insulation protection
    #12 16153172
    Hajna
    Help: 69
    Rate: 145
    IT networks are used in coal mines at the bottom with voltages of 500 and 1000 VAC, security measures used UKSI (insulation control device) withdrawn, CZU (central leakage protection) no longer used, RRgzx 0.5 10 central-blocking protection. The first two protections, after lowering the insulation resistance, controlled the network in the voltage state, and RRgzx also controls the network in the de-energized state.
    • PL_RRgx_A05.pdf (191.82 KB) You must be logged in to download this attachment.
  • IT networks are not inherently safer than TN
    #13 16153203
  • Insulation monitoring handles first faults better than RCDs
    #14 16153340
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    This is what I read and I think that we have a cross-section of IT networks from mining, through hospitals, to Norway, I will add a marine. And yet the assumptions for installing IT networks in these places are quite different. In mining, we use it to avoid the dangers related to the environment, which is often explosive. And hospitals for the acceptance of the first earth fault. In Norway, they use and will be used in wooden houses, which are a phobia of Norwegians, not to burn from the installation. It is known that the return of these installations for houses in Europe is no longer planned, but today's insulation monitoring devices do a great job of dealing with the first earth fault. They disconnect the network at values unmatched by RCDs and do it with much greater certainty.
  • #15 16153360
  • #16 16153433
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    WojcikW wrote:
    New distribution IT is not being built in Norway,
    In the city or in remote villages where these houses are built.
  • #17 16153742
  • #18 16153814
    Krzysztof Kamienski
    Help: 2033
    Rate: 5167
    I, in turn, am an admirer of my TT. Four wires, not five, EBS (Power Plant) ordered the obligatory use of RCDs, so Chinese electrical traders are rubbing their hands - protection (expensive) and earth rods (even more expensive). :D But it's strange - the tropics, when mass electrification entered Paramaribo (1930s) and all the buildings then wooden, and the Old Indians say that such a network layout is from the beginning. Probably because the greedy and mean Dutch colonizers were saving on knitting. :D
  • #19 16153828
  • #20 16156089
    rafal_rx
    Help: 56
    Rate: 108
    WojcikW wrote:
    I wonder how the TN system sets fire to wooden houses?
    Phase short-circuit to ground or even to N that does not trip by overcurrent. Theoretically possible.
  • #21 16156107
    retrofood
    Help: 1140
    Rate: 4800
    It is enough to use the so-called RCD. fire, i.e. with I? = 300 or even 500 mA.
  • #22 16156221
    Help: 1405
    Rate: 6430
    Maybe the legions of Electricians will stop polemics with lamers because it brings nothing but pointless posts.
    There are topics that the Users will never understand, such a world.
    IT is space for them.
  • #23 16156394
  • IT network suits mines and hospitals, not homes
    #24 19529392
    DawidBudny
    Depends on requirements. The IT network in the mine is not used to ensure the reliability of the power supply, because at each first earth fault, the power supply is immediately turned off. The most important thing is the low value of the earth leakage current, which in the case of other network systems would be a threat. It is about the so-called fading currents. Let us imagine a mine tunnel which is water-insulated and blasting works are carried out in it, suddenly an earth fault with a high current value may result in the firing of fuses. And also effective shutdown of the power supply as a result of mechanical damage to cables, which is a very common case thanks to the shielded cable, the so-called individual screens for each core and a common screen. When the insulation resistance drops as a result of a fault, the power is immediately disconnected. On the other hand, in hospitals, the most important thing is to ensure the reliability of power supply to operating theaters, and with such small cable capacities, the first earth fault current is 0, so it is not dangerous for humans, which in the case of mines and large capacities of cables from the transformer to the receiver would result in death for humans. In my opinion, it would be the safest at home. With the 400v inter-phase voltage and low operating currents and small cable capacities, the first earth fault would be completely harmless to humans, but due to the cost of the network such as installation and maintenance it is completely unprofitable economically, therefore it is not taken into account at all. Regards
  • IT network suits hospitals, not mines, due to fault current risks
    #25 19529416
    tyqva
    Level 37  
    Help: 335
    Rate: 1173
    thanks to the shielded cable, the so-called individual screens for each core and a common screen. When the insulation resistance drops as a result of a fault, the power is immediately disconnected. On the other hand, in hospitals, the most important thing is to ensure the reliability of power supply to operating theaters, and with such small cable capacities, the first earth fault current is 0, so it is not dangerous for humans, which in the case of mines and large capacities of cables from the transformer to the receiver would result in death for humans. Regards
    It would be good if you were still writing in Polish ...
  • Historical shift from IT to TT and TN systems
    #26 19529549
    Tomasz Lew
    Help: 57
    Rate: 190
    IT requires special supervision, otherwise it can be dangerous when multiple loads are powered and two of them will break. IT was common in Poland at the beginning of the 20th century, then it was replaced by a safer TT, probably than the French, and during World War II, the Germans began to introduce the TN system in Poland as the safest variant for transmission networks, which did not require such low earth resistance as in TT and at the less susceptible to atmospheric surges due to the multiple earthing points
  • IT networks need supervision and fault monitoring
    #27 19530141
  • Forum discussion should stay open to all users
    #28 19554775
    AdamKurek
    I have learned a lot if someone thinks they know everything or is so haughty that for him the curiosities and basics are nonsense is their problem. Moreover, thanks to the existence of this type of discussion, the search engine advertises the forum, which was not supposed to be a circle of mutual adoration of an important circle of "insiders", but a public value for the exchange of information, help and education.
    Such limiting the discussion and throwing negative beliefs stomp, claims that "someone will never understand something" contradicts the idea of a forum, that is communication and education.
    It is worth thinking wider than the tip of your nose, coming out of a bubble of limited and negative beliefs about people and the world. Because it HARMs others, poorer the world and life.
    Apart from slander, there is probably nothing worse than denying others the right to share their learning, which is like censorship!
    If someone does not like the level of the discussion or the questions, let them enter what interests them without spoiling them or impoverishing the interests of others (because it is like vandalism).
    As for the topic, I will have the opportunity to help in the implementation of this type of installation at my neighbor and see in practice ew as a passionate doing something similar at home. Because, as I can see in the YT videos, it happens that hobbyists make additional installations themselves, e.g. off-grid, where the electricity does not kick at all, because there is no connection to the ground. Although I am just beginning to implement the topic and I don't know much yet ...
    ..but everyone has the right to know , in a free world, to learn, to develop. Dividing people and forbidding, limiting them, saying in advance that it is not worth that they will not understand anything is something like a mental terror . Denying people what is most important in civilization that is, access to science, to knowledge!
  • #29 19554841
    retrofood
    Help: 1140
    Rate: 4800
    You are already trying to set up others, although this is your first post on the forum. It's polite, yes? Do you have a mirror at home? Take a look. Are you wandering into someone else's yard and doing your cleanup?
  • Standards and books are available for lay readers
    #30 19554861
    CYRUS2
    Help: 1241
    Rate: 3536
    AdamKurek wrote:
    I learned a lot.
    As for the subject, I will have the opportunity to help in the implementation of this type of installation at my neighbor and see for myself in practice
    From this it follows that it makes no sense to explain to laymen.
    The stream of consciousness was right.
    AdamKurek wrote:
    Denying people what is most important in civilization, i.e. access to science, to knowledge!
    Don't be fairy.
    Bookstores are open. Books can be bought.
    PKN is also selling willing standards.
The discussion centers around the limited use of IT (Isolated Terra) network layouts despite their perceived safety advantages, particularly in high-security environments like hospitals and mines. Key points include the high construction and operational costs associated with IT networks, the necessity for constant monitoring of insulation resistance, and the potential risks following the first earth fault. Participants debate the reliability of IT networks compared to TN (Terra Neutral) systems, emphasizing that while IT networks can maintain operation after a first fault, they become less safe after subsequent faults. The conversation also touches on the specific applications of IT networks in various industries, including healthcare and mining, and the historical context of their use in Norway. Ultimately, the consensus suggests that the complexity and maintenance requirements of IT networks limit their widespread adoption.
TL;DR: An IT earthing system lets power keep running after a first fault, yet adding insulation monitoring can raise installation cost by 30 % [Schneider, 2019]. “It is not safer if the second fault appears” [Elektroda, retrofood, post #16152726]
Why it matters: Designers must weigh uninterrupted service against higher cost and strict maintenance demands.
• First-fault touch voltage stays below 25 V when network capacitance ≤1 µF [IEC 60364-4-41]. • Insulation monitoring devices (IMD) alarm at ≤50 kΩ resistance for ≤1 kV systems [IEC 61557-8]. • Extra hardware adds approx. 25-40 % to switchgear price [Schneider, 2019]. • IMD test current ≤1 mA to avoid nuisance trips [Bender, 2020]. • Norway still has ~70 % rural LV feeders in legacy IT, but all new builds adopt TN [NVE, 2015].
What exactly is an IT earthing system?
IT (Isolé-Terre) keeps the supply side isolated from earth; the transformer neutral is either not connected or connected through high impedance. All exposed conductive parts are earthed, creating a separate PE network [IEC 60364-1].
Where is the IT layout still preferred?
Hospitals, mines, ships, water-treatment works and some legacy Norwegian rural grids use IT to keep critical loads alive during a first earth fault [Elektroda, Hajna, #16153172; #16153015; Strumien …, #16153015].
Why is IT uncommon in homes and offices?
Extra isolation transformers, insulation monitoring devices and fault alarms increase capital cost by roughly one-third and require 24/7 supervision, making TN–S or TT cheaper for large public networks [Elektroda, retrofood, #16152604; Schneider, 2019].
Is IT inherently safer than TN or TT?
IT eliminates dangerous touch voltage only until the first fault is fixed. A second fault on another conductor creates a phase-to-phase short and typical fault currents >400 A in LV systems, equal to TN hazards [Elektroda, zdzisiek1979, post #16152666]
What happens during the first earth fault?
Fault current is limited to the network’s capacitive leakage—usually <0.5 mA in hospital circuits—so protective devices stay closed and equipment keeps running [IEC 60364-4-41]. The IMD issues audible and visual alarms [Elektroda, zdzisiek1979, post #16152666]
Why must insulation be continuously monitored?
Because the very feature that keeps equipment alive also hides faults. IMDs track resistance and capacitance; if it falls below 50 kΩ or leakage rises, staff must intervene before a second fault occurs [IEC 61557-8; Elektrode, Anonymous, #16153742].
What is the risk at the second earth fault?
If a different phase contacts PE, the system behaves like TN with a bolted phase-to-phase short. Prospective touch voltage can exceed 230 V and trip fuses, stopping life-support or mine ventilation [Elektroda, kkas12, post #19677659]
How do I locate a first earth fault in an IT circuit?
  1. Press the IMD’s locator button to inject a 2.5 Hz tracing signal. 2. Use a clamp meter to scan outgoing feeders for maximum current. 3. Isolate branches until the alarm clears [Bender, 2020].
Which standards govern design and testing?
Key documents: IEC 60364-4-41 (protection against shock), IEC 61557-8 (IMD performance), IEC 60364-6 (verification), and EN 50110 (operation of electrical installations).
Can I retrofit my house to IT?
Possible but rarely economical. You would need a dedicated isolation transformer, IMD, PE network upgrade and separate RCDs on socket groups. Expect material cost >€1 000 for a 10 kVA system [Approx. market data, 2023].
Does IT reduce fire risk in wooden buildings?
Legacy Norwegian IT grids were kept partly to avoid earth-fault currents in rocky soil, yet statistical studies show no lower dwelling-fire rate versus TN areas [NVE, 2015].
What edge cases limit IT use?
Long cables raise capacitance; above 1 µF the first-fault current can exceed 5 mA, forcing immediate disconnection and negating IT’s advantage [IEC 60364-4-41].