Hello.
First...
I read the forum and I wonder why the theorists are probably mainly against the use of RCDs in TN-C installations.
I do not want to discuss normal and regulations because I know what they are, but also everyone knows what they used to be in the past.
Suppose we have an old building, the power is supplied by two wires (TN-C standard) phase and PEN earthed by power plants.
In this old house we have old sockets without a grounding "pin", and, for example, several with a pin connected to the PEN conductor. (Two wires everywhere).
I understand that the regulations and standards say that the RCD in such an installation is evil, but for a common sense, it seems to me that the RCD does more good than evil here.
When we connect a device of the first class of protection to a socket without a grounding "pin" (I know you must not, but explain it to older people, for them this socket and this socket), without an RCD, we do not have any protection in the event of a breakdown on the housing, and after assembly Although the RCD has minimal protection, in the event of current leakage to the chassis and the human RCD should turn off the power.
I understand the regulations, but it is probably better to be protected by an RCD in this way than to be protected only by a 16A fuse. :-)
I am writing this because I see that the forum is followed by people who have used RCDs in the TN-C installation.
After all, the RCD does not pose a direct threat to life in such an installation, it can give a slightly illusory sense of security, but it increases it anyway in relation to the lack of an RCD.
A question for those who know, is there any reason why RCDs should not be used in TN-C and this reason is directly life-threatening?
Can you confirm that the RCD in TN-C gives no advantages?
I myself have seen systems where half of the old building (you can say factory) was in the TNC system and there were RCDs and these switches actually worked in practice, and the other half were only renovated to TN-S.
Next....
I read a few topics where people asked about minor things, a small renovation of the installation in the OLD house and the "specialists" came to them for not having separate over-current switches for each socket.
Don't you think it's a bit sick?
I understand the implementation of standards in new construction, but if someone does a SMALL renovation and tries to slightly improve the installations, he will probably not get help in this forum, because they tell him to replace everything and everywhere :-)
There are hundreds of thousands of houses in Poland where 20 sockets work on one phase with the old "plug" and there are no problems with it, and if someone wants to improve something, it would be appropriate to help him as much as possible, and not to criticize "no because no", the standard says ...
First...
I read the forum and I wonder why the theorists are probably mainly against the use of RCDs in TN-C installations.
I do not want to discuss normal and regulations because I know what they are, but also everyone knows what they used to be in the past.
Suppose we have an old building, the power is supplied by two wires (TN-C standard) phase and PEN earthed by power plants.
In this old house we have old sockets without a grounding "pin", and, for example, several with a pin connected to the PEN conductor. (Two wires everywhere).
I understand that the regulations and standards say that the RCD in such an installation is evil, but for a common sense, it seems to me that the RCD does more good than evil here.
When we connect a device of the first class of protection to a socket without a grounding "pin" (I know you must not, but explain it to older people, for them this socket and this socket), without an RCD, we do not have any protection in the event of a breakdown on the housing, and after assembly Although the RCD has minimal protection, in the event of current leakage to the chassis and the human RCD should turn off the power.
I understand the regulations, but it is probably better to be protected by an RCD in this way than to be protected only by a 16A fuse. :-)
I am writing this because I see that the forum is followed by people who have used RCDs in the TN-C installation.
After all, the RCD does not pose a direct threat to life in such an installation, it can give a slightly illusory sense of security, but it increases it anyway in relation to the lack of an RCD.
A question for those who know, is there any reason why RCDs should not be used in TN-C and this reason is directly life-threatening?
Can you confirm that the RCD in TN-C gives no advantages?
I myself have seen systems where half of the old building (you can say factory) was in the TNC system and there were RCDs and these switches actually worked in practice, and the other half were only renovated to TN-S.
Next....
I read a few topics where people asked about minor things, a small renovation of the installation in the OLD house and the "specialists" came to them for not having separate over-current switches for each socket.
Don't you think it's a bit sick?
I understand the implementation of standards in new construction, but if someone does a SMALL renovation and tries to slightly improve the installations, he will probably not get help in this forum, because they tell him to replace everything and everywhere :-)
There are hundreds of thousands of houses in Poland where 20 sockets work on one phase with the old "plug" and there are no problems with it, and if someone wants to improve something, it would be appropriate to help him as much as possible, and not to criticize "no because no", the standard says ...