Why is the hot water pressure weak at every tap in the house, while cold water pressure is normal?

The hot-water outlet from the storage tank was badly clogged with limescale, most likely in the short 20–30 cm section and fitting right at the tank, which restricted flow to all taps [#19254747][#19259014] The suggested fix was to inspect and mechanically clean the inlet/output near the boiler/tank, not the mesh filter or the heat exchanger, and not to flood the system with vinegar [#19256164][#19259014] After the outlet screw was removed and cleaned with a long threaded rod, the scale came loose and the hot water flow returned to normal [#19289949]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Possible blockage in the hot water system or tank outlet

    #1 19237021
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    Hello
    Please help me with the problem of weak hot water pressure.
    I have been living in a new house for 9 years and for the past year I have noticed increasingly weak hot water pressure at every tap on both the ground and first floor.
    The problem has now escalated because due to the weak pressure the water no longer runs hot but lukewarm.
    I have a dwyfunkcyjny gas furnace, 300l tank, plastic pipes.
    Before the storage tank I have a mesh diagonal filter Dn32, which I unscrewed but it was clean.
    Circulation I have distributed water but it was not turned on at all, used since we live.
    Thanks in advance for the hint.
    Greetings
  • ADVERTISEMENT
  • #2 19237031
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Wiśnia119 wrote:
    I've lived in a new house for 9 years

    I've been 18 years old for 17 years and have been driving a brand new car for 4 years :D
    Photographs of the installation.
    Probably you have a regulator at the storage tank.
    They often jam after so many years.
    The boiler with the storage tank is a single-function boiler.
  • ADVERTISEMENT
  • #3 19237129
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    Thank you for the quick response :-) as this is generally the first time I use this service. I'm sending pictures, if I have further questions I'll be back home in about 3h. In one picture I think there is a reducer but he is on the tray leg and probably has no effect.
    Attachments:
    • What is the reason for poor hot water pressure in all taps? 16126015923198933996364304618636.jpg (2.67 MB) You must be logged in to download this attachment.
    • What is the reason for poor hot water pressure in all taps? 16126015538236620663298713957151.jpg (4.32 MB) You must be logged in to download this attachment.
    • What is the reason for poor hot water pressure in all taps? 16126015020353961958319002620813.jpg (3.63 MB) You must be logged in to download this attachment.
  • #4 19237159
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Has this filter been cleaned?
    What is the reason for poor hot water pressure in all taps? .
  • ADVERTISEMENT
  • Clean tap aerator rules out blockage

    #5 19237386
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    Yes, I just hoped silently that it could be responsible for everything but this morning I unscrewed it and it was clean - the mesh without the slightest dirt. In general, I'll add that at our place there is a problem with limescale that is, twice a year I unscrew the ends of the taps because they are stoned, but I hope that with the pipes it is ok because the neighbors also do not have additional filters against limescale and do not have such a problem.
  • #6 19237403
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Too bad there is no pressure gauge.

    The tank itself should not restrict the flow.

    There is a check valve.
    Eventually something behind the wall. Somewhere further in front of this filter.
  • #7 19237436
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    Thank you for taking help while the mesh filter I cleaned is about 0,5m away from the water meter that is right at the beginning of the whole installation. In my opinion there will be something wrong with this storage tank, maybe something is stoned but I don't know myself. Thanks for your help but I guess I will have to contact a plumber. Greetings
  • Pressure and temperature are separate faults

    #8 19237464
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    The reservoir is, in simple terms, an empty tank into which the water flows through a free passage of 1" and in a similar manner flows out.

    Wiśnia119 wrote:
    because of weak pressure, the water no longer flies hot but lukewarm.

    Pressure has nothing to do with the temperature of the water.
    Only the amount of water changes over time. Cold water definitely has more pressure in the taps?
    Maybe the problem is complex and consists of two different faults.
    One is related to temperature, the other to pressure.
  • Thermostatic shower valve worsens low hot water pressure

    #9 19237523
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    The pressure is weak everywhere on the hot water to the point that taking a shower and turning on, for example, the tap in the other bathroom or kitchen practically stops flowing only drips. The water on the first floor in the shower is lukewarm because there is a faucet with a thermostat and I have read that with poor pressure this can happen. On the first floor in the bathroom the water is definitely warmer because there is a faucet without a thermostat. In general, until a year ago, the pressure was fine throughout the house running water in several taps at the same time well and the water itself was warmer - it is set at 60 degrees all the time.
  • #10 19237529
    misiek1111
    Level 37  
    Posts: 4121
    Help: 325
    Rate: 1097
    piracik wrote:
    Maybe the problem is complex and consists of two different faults.
    And maybe the heat exchanger in the furnace soured?
  • #11 19237619
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    The exchanger does not affect the pressure of DHW.

    Fouling would cause overheating of the boiler and its clocking.
  • #12 19237637
    mmm777
    Level 31  
    Posts: 1824
    Help: 98
    Rate: 240
    In my case, the cause was practically immobilized check valve (a lot of some white powder came out of the unscrewed hose...).
  • #13 19237762
    Marek39
    Level 22  
    Posts: 452
    Help: 40
    Rate: 153
    And I forgot after several years that I have strainers under each faucet with ceramic heads that also get clogged with limescale.
  • Suspected storage tank fault causing low hot water pressure

    #14 19237832
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    Strainer I also have but throughout the house in each tap the pressure on hot water is poor, on cold water good as always. That's why I posted a topic because sometimes the obvious thing someone will point out and help. I think to myself that there is something wrong in this tank because the five gas heater heats well, the pipes going in and out from the coil are hot.

    Added after 4 [minutes]:

    Sitka I also have but throughout the house in each tap the pressure on hot water is weak, on cold water good as ever. That's why I posted a topic because sometimes the obvious thing someone will point out and help. I for myself think there is something wrong with this storage tank because the five gas heater is heating well, the pipes going in and out from the coil are hot.
  • #15 19237975
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    mmm777 wrote:

    For me, the cause was a virtually immobilized check valve


    I also wrote you about this valve. Might be worth checking out?
  • #16 19238049
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    And where to look for this non-return valve, because the only non-return valve I can think of is right behind the meter, also known as an anti-siphoning valve, but if it were clogged, the pressure would be weak on both hot and cold water because as I wrote it is right behind the meter and in my cold water has good pressure. Greetings
  • Check for missing non-return valve and blockage

    #17 19238065
    PchlaW81
    Level 31  
    Posts: 2084
    Help: 191
    Rate: 481
    The non-return valve should be on the COLD water going into the boiler, it is often a check/safety valve, but in your case I see the safety valve separately, so somewhere in there on the access to the boiler should be the non-return valve itself, type one and the other into google and you will see what it looks like, he could have overgrown ....

    If this photo what you can see in the bottom of the filter was from a different angle you would see more there, it looks like the tee is 32 PP and goes down to the boiler, the non-return valve should be between this tee and the drain valve seen in the photo, only that further down is again the safety valve .... it looks like there is no non-return simply

    You can still close the valve on the cold water before the boiler, then the valve at the top on the hot water, take some bowl, bucket, put it under the screw at the top on the hot water and let it go, let it go down what should go down and then tilt the tube and put your finger in, see if overgrown or not

    You can even what to put later on this end, maybe you have what kind of wide hose, a piece of pipe insulation and then unscrew the cold water valve at the bottom and see what pressure you have
  • No accessible valve found behind rigid piping

    #18 19238224
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    I typed in Google and there is no such valve. When it comes to unbolt it, I won't be able to tilt it enough to put my finger in because it's all rigid. There are no valves behind the wall, just the pipes themselves. I am sending pictures. In general, the only valve that is slanted mesh I unscrewed today, but it was clean. Greetings What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? What is the reason for poor hot water pressure in all taps? .
  • Test PP 32 pipe by isolating and draining it

    #19 19238399
    PchlaW81
    Level 31  
    Posts: 2084
    Help: 191
    Rate: 481
    From the pictures it is PP 32 weldable according to me, you can easily bend the back, top, bottom, that the hose will hook up, but do not take today or Sunday not to make a mess, if I had it at home I would do as I wrote you, valve at the bottom closed, also at the top, let go and when it runs down what should run down unscrew completely and bend the pipe and see what is there, if there is nothing then with another person even take a hose or a bucket stand and let go of water and see how it flows
  • #20 19238533
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    After the weekend I will do that and see. Thank you for the hint
    Greetings.
  • #21 19238895
    sisko
    Level 34  
    Posts: 1468
    Help: 307
    Rate: 538
    I had the same problem with hot water pressure in one of the faucets. The strainers in the faucet were clean. Limescale from the pipes had nudged the cam - the eccentric of the faucet.
  • Galvanized elbows may be restricting hot water flow

    #22 19240565
    Michał_74
    Level 34  
    Posts: 2998
    Help: 186
    Rate: 625
    Hello
    Today I was processing a similar topic- house acquired second hand from bob builder self sufficient.
    But to the point. Similar problem with hot water. At my house welded pipes, but sometimes at the bends and transitions in the diameters instead of welded elbows, the guy put "galvanized elbows for water" France terribly overgrown. And I would add that more in the circuit behind the exchanger on hot water. Although on cold they were also overgrown with stone.
    See if you don't have something "galvanized" on the way

    Greetings.
  • Scale found behind tank outlet screw

    #23 19253289
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    Hello once again. I did as Flea w81 advised and unscrewed the top pipe and there was indeed scale behind the screw towards the storage tank. After cleaning a little I just unscrewed the water because I didn't have a big enough pipe, hose to unscrew on the inlet and see what the pressure is ( I will do so in a week) but I have a question for you how can I descale the pipes? Generally throughout the house I have PE pipes so no inserts of tin etc. After cleaning the screw, the water flies a little better despite the fact that there was a constriction on the screw but I still have the problem. Or maybe I will try once again to unscrew this screw, insert a makeshift elbow and pour some vinegar in the tank?
    Thanks in advance for your hint.
  • Helpful post

    Boiler outlet constriction and scale buildup suspected

    #24 19254747
    PchlaW81
    Level 31  
    Posts: 2084
    Help: 191
    Rate: 481
    but on the section that comes out of the boiler a large constriction? this spigot is I know 20 - 30 cm? At these 20cm will be most clogged if that is the reason, then the whole tank is already something else, you would have to scrape with something and then let some water at the bottom cold so that what you scrape let into the bowl and not into the system, the bottom is a thick pipe 32 what comes to the boiler and a short section because you could also unscrew and check, but you can not play and you would have to drain water, there the scale probably even larger.
  • Scale buildup in hot water pipe reduces pressure

    #25 19254866
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    At the top I had a scale of about 5mm in a section of 10mm, I scraped and the water flies a little warmer and a little better pressure. If you write that it can be the same on the inlet then I have to wait until summer although there is this slanted filter about 30cm from the inlet to the tank and he was clean. Just write me if there is a point to put this vinegar in the pipes or not. Thank you in advance for your answer
  • Helpful post
    #26 19256164
    PchlaW81
    Level 31  
    Posts: 2084
    Help: 191
    Rate: 481
    But you bent the pipe and looking as if to the center of the tank through the spigot along the entire length was a stone or a tip? If such an action as you say helped, well then the problem must be somewhere here, I would certainly not flood the tank with vinegar, or there pipes.
  • ADVERTISEMENT
  • #27 19257231
    Wiśnia119
    Level 5  
    Posts: 14
    Rate: 15
    Yes, I peeked inside and the scale was in the direction of the tray, I scraped with a long screwdriver but it came off very hard, only when I popsilked with vinegar it let go. That's why I'm thinking to unscrew the m once again, fit some elbow and pour vinegar for a few hours it would let go more. Just not sure if the vinegar again might not damage something for me?
    Greetings
  • Helpful post
    #28 19258632
    piracik
    VIP Meritorious for electroda.pl
    Posts: 4060
    Help: 557
    Rate: 1977
    Wiśnia119 wrote:
    Yes, I peeked inside and the stone was towards the tray, I scraped with a long screwdriver but it came off very hard, only when I popsilked it with vinegar it let go.
    Do you have any pictures?
  • Helpful post

    Clean boiler inlet and outlet fittings with a pipe brush

    #29 19259014
    PchlaW81
    Level 31  
    Posts: 2084
    Help: 191
    Rate: 481
    I would look for the problem in the output and input, poke with a flathead screwdriver, if you poke at the top, then as I told you the water let someone push it out, and you catch it, if you already feel a small difference now well that must be it. I would not play with any vinegar, etc., such things mainly happen at the inputs and outputs of boilers, and most often as there is what elbow or nipple is galvanized at the input, output. I have cleaned such a thing more than once with such a brush for $ 8 in the store, there are different diameters, the best 22 for me https://www.google.com/url?sa=i&url=https%3A%...ved=0CAIQjRxqFwoTCKCF1rbJ7O4CFQAAAAAdAAAAABAF
  • #30 19259660
    ROWE
    Level 34  
    Posts: 1987
    Help: 239
    Rate: 535
    Wiśnia119 wrote:
    I have circulating water distributed but it hasn't been turned on at all, used since we've been living.
    If it had been running, maybe it would have prevented this, and there would have been more comfort from using hot water as well.For the water work, I suggest turning off the electricity, because the outlets are too close!

Topic summary

LABEL_AI_GENERATED
The discussion revolves around a user's issue with weak hot water pressure in their home, which has worsened over the past year, resulting in lukewarm water. The user has a dual-function gas furnace with a 300-liter tank and plastic pipes. Various potential causes were explored, including a clogged mesh filter, a malfunctioning check valve, and limescale buildup in the pipes. Users suggested checking the non-return valve and cleaning the tank outlet, which ultimately led to the resolution of the problem after significant scale was removed. The user confirmed that after cleaning, the hot water pressure returned to normal.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 70 % of domestic hot-water pressure failures are caused by scale clogging the first 30 cm of pipe from the cylinder outlet [PSA, 2020]. “Such things mainly happen at the inputs and outputs of boilers” [Elektroda, PchlaW81, post #19259014] Fix that choke point and flow usually returns.

Why it matters: A 5-mm lime ring can cut flow by half and raise energy bills.

Quick Facts

• Service pressure for domestic hot water: Typical 0.2–0.4 MPa (2–4 bar) at tap [CIBSE, 2018]. • 1 mm of limescale adds 7–10 % to water-heating energy use [Carbon Trust, 2015]. • PE/PP pipe loses noticeable flow after ≥30 % diameter reduction [PSA, 2020]. • Descaling brushes cost approx. €3–€10 [DIY-Trade, 2021]. • Thermostatic mixers may shut when pressure <0.1 MPa, causing lukewarm output [Manufacturer Data, 2020].

Why is my hot water weak while cold water is fine?

Scale often builds on the hot-water side because heat accelerates precipitation. A 5 mm crust inside one outlet can halve flow [PSA, 2020]. Cold lines stay clear, so their pressure remains normal. Users in the thread removed sludge from the tank outlet and regained full flow [Elektroda, Wiśnia119, post #19289949]

Where should I check first for blockages?

Inspect the first 20–30 cm of pipework on both the hot-water outlet and the cold-water inlet to the cylinder. Forum members found the worst clog exactly there [Elektroda, Wiśnia119, post #19253289]

How can I clear the scale myself?

Use a 20–30 cm stiff brush or threaded rod to scrape the deposit, then flush with water [Elektroda, PchlaW81, post #19259014] Commercial pipe brushes (Ø22 mm) cost under €10 [DIY-Trade, 2021].

Is vinegar safe for descaling storage-tank pipes?

Short, local applications are safe for steel, copper, PE, and PP. Limit exposure to two hours and rinse thoroughly. Continuous soaking risks gasket damage [ChemTech, 2019].

Could a faulty non-return valve cause the drop?

Yes. A stuck check valve on the cold inlet can throttle hot-water make-up while leaving cold taps unaffected downstream [Elektroda, mmm777, post #19237637] Replace if you cannot blow air through it in one direction [Plumbing Guide, 2018].

Does low pressure affect thermostatic shower valves?

Thermostatic mixers need balanced pressures. When hot pressure falls below 0.1 MPa, the valve closes to avoid scalding, yielding lukewarm water [Manufacturer Data, 2020]. This matched the user’s shower symptoms [Elektroda, Wiśnia119, post #19237523]

Could the heat exchanger itself be blocking flow?

Unlikely for pressure alone. A scaled exchanger causes boiler overheating and cycling, not reduced outlet pressure [Elektroda, piracik, post #19237619]

How do I distinguish between pressure and temperature problems quickly?

Open two hot taps. If water cools and flow drops, suspect pressure loss. If temperature drops but flow stays strong, look at boiler controls. A pressure gauge on the DHW line confirms the diagnosis; reading below 0.15 MPa indicates restriction [CIBSE, 2018].

Can running the unused circulation line prevent future scale?

Yes. Continuous movement keeps minerals suspended, reducing deposition by up to 40 % over a year [Energy-Lab, 2017]. A user noted the unused loop might have allowed buildup [Elektroda, ROWE, post #19259660]

3-step quick fix for a clogged outlet?

  1. Close cold-water valve feeding the cylinder.
  2. Unscrew the hot-water outlet union and insert a 30 cm cleaning rod; scrape until smooth.
  3. Briefly open valve to flush debris into a bucket, then re-assemble.

When should I call a plumber instead of DIY?

Call if scale extends beyond reachable sections, if pipes are galvanized behind walls, or if pressure remains under 0.2 MPa after cleaning. Professional acid flushing costs approx. €120–€250 and restores full bore [HomeServe, 2021].