Watt (W) vs Volt-Ampere (VA): What’s the Difference in AC Circuits?
mateusz885 55898 10
What is the difference between watts (W) and volt-amperes (VA) in AC circuits, and when are they equal?
W is active power and VA is apparent power; they are equal only for an ideal resistive load, where P = U × I with no phase shift, but in general AC circuits active power is not simply the RMS voltage times RMS current [#3982276] [#18244522] If the current is phase-shifted relative to the voltage, or the load is nonlinear, the apparent power in VA can be greater than the real power in W [#3983516] For transformer selection, a 500W rating usually assumes a resistive load, so a 500W and 500VA label are not always interchangeable [#3983696] For amplifier supplies, one reply notes that a class AB amp may draw about 1.7–2 times its audio output power from the supply, and for a 400W home audio amplifier a 400VA transformer can be enough, though 500VA–600VA provides more margin [#18245003]
  • #1 3982224
    mateusz885
    Help: 9
    Rate: 67
    This topic could be raised more than once ... but I did not find anything specific (because there were no specific answers)
    W - watt - active power unit. For the voltage U in volts (V) and the current I in amperes (A) the power P is obtained in watts (W).
    VA - volt-ampere - a unit of apparent power in alternating current circuits. 1 VA is the apparent power of a current with an effective amperage of 1 ampere and an effective voltage of 1 volt
    ALEEE always The power (in other words, work done per unit of time) consumed by any device (e.g. a resistor) is equal to: P = U * I
    So 1W = 1VA
    I hope I'm thinking well, if not, please correct me and stick the topic in order to avoid the next posts of this type.
    the information in this post is taken from:
    www.edw.com.pl
    www.portalwiedzy.onet.pl
    www.wikipedia.org
  • #2 3982276
    krzyjak
    Help: 110
    Rate: 137
    P = U * I = S only holds for an ideal resistor. It can be said that the active power (unit W) across the resistor is equal to the apparent power (unit VA). I don't know what exactly you mean. Make your statement more specific. greetings
    In general, active power is not the product of the RMS current and voltage, this only occurs for an ideal resistor.
  • #3 3983297
    mateusz885
    Help: 9
    Rate: 67
    it is a transformer to drive 2x 200W 4r mosfets (such with 0.5 kW but usually in stores the power is given in VA)
    @Edit
    however, the amplifier is not a perfect resistor and will not consume electricity like a welder ... but most sources say that you should mount a transformer a little more power than the sum of the power of all channels at a given loudspeaker load
    @Edit
    in my case it is 4 ohms
    I don't know anyway, I don't know anything about it - that's why I'm asking
  • #4 3983516
    k4be
    Help: 102
    Rate: 333
    if the current is phase-shifted in relation to the voltage (cos phi) or is non-linearly dependent on it, the number VA will be greater than the number W.
    gregor10
    Help: 41
    Rate: 27
    K4BE - YOU WERE RIGHT, the luck will not be equal, and if you look at VA and W, then if you have a choice of 500VA and 500W transformers, take 500W.
    k4be
    Help: 102
    Rate: 333
    Rather, they will be the same, but a manufacturer writing 500W will assume that the resistive load will be powered.
    avatar
    Level 36  
    Help: 159
    Rate: 415
    So 1W = 1VA
    There is a mistake in this reasoning. No COS Fi
    because 1VA can sometimes equal 0.3W and sometimes 0.82W
    If you have an audio amplifier that is able to give 400 watts to the speakers and is in class AB, then you have to assume that the luck must be with an adequate margin
    I would look for 620VA luck
  • #8 4001486
    mateusz885
    Help: 9
    Rate: 67
    I don't have to look around because for 99% of the order; pi will probably be 600 or 650 VA 2x 40V (after straightening it will give 2x 57V) - 50V is recommended and 65 is the max; p
    I think you should be ok and you? (I will find out how much the transformer will cost, because 600VA 2x 35V is 157 PLN gross - toroidy.pl)
  • #9 18244209
    gruniu
    Rate: 178
    I did not know for a long time what Ampere is. Only when I was about to buy a power supply and calculated how much Watt the LEDs would consume, I found out how many Amps the power supply must have.
    Now I ask someone to explain to me what VA is in a simple way.
    If my plant's transformer says 30MVA, does it mean that devices or machines can draw 30MW of electricity in an instant?
  • #10 18244522
    krzysssztof
    Help: 52
    Rate: 54
    Not.
    Search for "power triangle", "active power", "reactive power", "apparent power".
    "W" is a unit of active power, and "VA" is apparent power.
  • #11 18245003
The discussion centers on the distinction between watts (W) and volt-amperes (VA) in electrical systems. Watts represent active power, while volt-amperes denote apparent power, particularly in AC circuits. The relationship between the two is clarified: for ideal resistive loads, 1 W equals 1 VA, but this equivalence does not hold for non-resistive loads where phase shifts occur, leading to VA being greater than W. Users emphasize the importance of selecting transformers with adequate VA ratings to match the power requirements of devices, particularly amplifiers, which may not operate as perfect resistors. The conversation also touches on the concept of power factor (cos φ) and its impact on the relationship between W and VA.