    Hello electricians. I have a question.
    What is the maximum power that can be drawn through a 5x10mm ground cable in 3 phases (three-phase motors)?

    When there was no plant yet, I had a power allocation of 12kW, after starting the company, I increased the power allocation to 22kW and a year later to 32kW. Now I am thinking about an allocation of 50kW, because it is known that there are more and more machines and the plant is expanding.

    Now the question is, will a 5x10mm earth cable withstand 50kW (3 phase motors)? What is the maximum safe continuous power for such a cable?

    I know that I have 3x63A / 400v protection in the meter box.
  • ADVERTISEMENT
  • #2 10124911
    Oksy
    Level 20  
    Hello.
    What is the length of this cable?
  • ADVERTISEMENT
  • #3 10125006
    arek59
    Level 29  
    The cable length is approximately 30m, measured in steps. The cable is copper.
  • ADVERTISEMENT
  • ADVERTISEMENT
  • #5 10125911
    jarecki 86
    Electrician specialist
    GBW wrote:
    35kW max.

    In short, NOT TRUE .
    Long-term current-carrying capacity is not the only criterion for selecting the cable cross-section, and in this case the power limit is 28KW - please refer to the PN-IEC 60364-5-523 standard.

    In addition, one must not forget about the selection of the cross-section due to the permissible voltage drop.
    Here, in turn, according to the SEP-E-002 standard, the voltage drop in the receiving circuits from the electricity meter to the receiver connection point should not exceed 3%, while the total voltage drop from the electrical installation connector to the terminals of any receiver should not exceed 4%. and the voltage drops in the internal supply line should not exceed 0.5% in this case.
    For the current power allocation (32KW), the decrease in WLZ is 1.05%, which is 2 times the permissible value.
  • #6 10607835
    arek59
    Level 29  
    With a power allocation of 32kW, the 5x10mm cable so far withstands and does not heat up, or it only gets lukewarm with all machines running. I will not be up to anything for now. I consider the topic closed.