Is 4x2.5 mm Cable Sufficient for an 11 kW Motor?

kiecio 59838 35
Best answers

Is 4x2.5 mm² cable enough for an 11 kW motor, or what cable size should be used?

4x2.5 mm² is usually too small for an 11 kW motor; the thread’s main recommendation is 4x4 mm², with 6 mm² suggested for extra margin. For a motor in a simple three-phase + PE setup, one reply says 4x2.5 mm² may only be acceptable for short runs laid on a wall or floor, up to about 50 m, while in conduit 4x4 mm² was suggested and up to about 90 m [#5380129] Another reply notes that an 11 kW motor has a rated current of about 23 A, so 4 mm² may warm up under full load, and recommends 6 mm² because starting current is much higher [#5387486] A later reply also says that in most cases 4x4 is enough for an 11 kW motor [#5388241] If the motor uses star-delta starting, more conductors are needed than a 4-core cable provides [#5380129]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 5380021
    kiecio
    Level 11  
    Posts: 25
    Rate: 13
    Hello
    What will be the appropriate cable for an 11 kW motor, or will 4x2.5 mm be enough?
  • ADVERTISEMENT
  • #2 5380062
    piorun7890
    Level 18  
    Posts: 388
    Help: 12
    Rate: 269
    A 4x2.5 cable should be enough for this engine.
  • #3 5380091
    Kobra
    Level 18  
    Posts: 238
    Help: 14
    Rate: 50
    Hello
    Well, I would disagree with the previous statement
    First of all, the cable should have five wires
    Secondly, what about the starting current!
    Personally, I would use at least 5 x 6 mm2
    Regards
  • #4 5380099
    kiecio
    Level 11  
    Posts: 25
    Rate: 13
    I`m not really an expert in this topic :/ that`s why my question: what is the 5th wire for and what is the starting current?
  • ADVERTISEMENT
  • #5 5380129
    Luklukowaty
    Level 19  
    Posts: 394
    Help: 29
    Rate: 42
    Specific and to the point answer:

    I assume that the motor works in a star, we do not use N, we connect PE, i.e.:

    4x4mm2 for electrical installation pipe, maximum cable length is about 90 meters.
    For cables laid directly on the wall or on the floor, 4x2.5mm2 is enough, but the maximum length is about 50 meters.

    If the motor has a delta-star start, unfortunately it will have more veins. If you want to keep the engine, you have to give it a larger cross-section...

    There should be a 6mm2 cable in the switchboard.

    The cross-section and length of the cables will guarantee (if the protection devices are selected correctly) the correct operation of the engine and protection devices.
  • #6 5380249
    Kobra
    Level 18  
    Posts: 238
    Help: 14
    Rate: 50
    Quote:

    I assume that the motor works in a star, we do not use N, we connect PE,

    Hmmm This is probably a new theory
    I always thought that the N cable was not needed for the triangle
    Quote:

    so my question: what is the 5th wire for and what is the starting current?

    The fifth wire I wrote about is protection, or grounding
    The starting current occurs when the engine starts. Its value may reach several amperes. The operating time of the starting current depends on the time when the engine accelerates to the nominal speed.
    Correct me if I`m wrong
    Regards
  • #7 5380263
    Luklukowaty
    Level 19  
    Posts: 394
    Help: 29
    Rate: 42
    Quote:
    Hmmm This is probably a new theory
    I always thought that the N cable was not needed for the triangle


    And did I write differently? I pointed out that we do not use N, so I don`t know why you need five veins - you suggested marking the matter this way, because I understood this:

    U, V, W, N, PE, so there are your five wires and I indicated that N is redundant... so there are four wires left...

    Apart from that... finally a three or a star, because you write about a triangle, I write about a star... ;)
  • #8 5380268
    marian_em
    Level 25  
    Posts: 843
    Help: 60
    Rate: 182
    Kobra wrote:
    First of all, the cable should have five wires
    There is no need for this, the motor itself only needs three phase wires to work, the fourth is PE.
  • #9 5380284
    Kobra
    Level 18  
    Posts: 238
    Help: 14
    Rate: 50
    Quote:

    And did I write differently?

    Yes, yes

    I think you`ve mixed up some concepts
    The star (you wrote about) requires a five-wire power supply
    A triangle of just four
    Either way, protection is required and unfortunately people forget about it
  • #10 5380323
    Madrik
    VIP Meritorious for electroda.pl
    Posts: 12459
    Help: 622
    Rate: 1163
    kiecio wrote:
    Hello
    What will be the appropriate cable for an 11 kW motor, or will 4x2.5 mm be enough?


    The fairies went on vacation. Maybe some data from the tablet? E.g. In? Un?
    The starting current may be as high as 10xIn (often it is several hundred amperes, not a dozen or so). In case of heavy (long boot) this is a serious load on the network.
    I wouldn`t recommend less than 4mm2. I once saw an 11kW motor connected to the test with 1.5mm2 wires, which boiled the insulation after two minutes.
  • #11 5380406
    marian_em
    Level 25  
    Posts: 843
    Help: 60
    Rate: 182
    Kobra wrote:
    The star (you wrote about) requires a five-wire power supply
    It requires three phases and PE (or PEN), just like a triangle.
  • #12 5387486
    SZYMKA10
    Level 11  
    Posts: 13
    Rate: 11
    if it is 11 kW, it has a rated current of approximately 23 amperes, on average it is assumed to be 5-6 amps per mm2, so 4 mm2 may get warm when the engine is fully loaded
    I recommend 6mm2
    the motor should probably be connected in a delta via a star-delta switch, so there is no contactor for control and the 5th wire of the cable (blue) is not needed
    a 6mm2 cable will easily withstand the starting current on the star (but after acceleration, you need to switch to the triangle because on the star it has 1/3 of the power)
    but three phases and grounding yes
  • #14 5387760
    kiecio
    Level 11  
    Posts: 25
    Rate: 13
    SZYMKA10 wrote:

    the motor should probably be connected in delta via a star-delta switch


    so I can connect it to T/G even if I have the markings 290/500v?
  • #15 5387930
    JK60
    Level 14  
    Posts: 65
    Help: 5
    Rate: 27
    As above
    Madrik wrote:

    The fairies went on vacation. Maybe some data from the tablet? ...

    The engine does not always require G/T switching, what is it for, is it hard to start, what is the power supply.
    When determining the cross-section, it is also important how the cable is routed and how the motor is protected... (in most cases, a 4x4 is enough for an 11kW motor).
  • #16 5388134
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #17 5388241
    JK60
    Level 14  
    Posts: 65
    Help: 5
    Rate: 27
    I have several 11kW units with direct start and it is not a problem at all.
    Moreover, I have the impression that some people treat this forum as for clairvoyants and unnecessary discussions begin.
    You just need to ask the question well. I have an engine of ... power ... etc., located at a distance ... from the switchboard, starting ... (e.g. light), the cables will be laid ... (e.g. in a gutter), etc.
    To answer the question - when it comes to current carrying capacity - a 4x2.5 cable is insufficient in some cases, it is better to use a 4x4 cable.
  • #18 5388688
    HeSz
    Electrician specialist
    Posts: 1186
    Help: 97
    Rate: 198
    Gentlemen, please note that this is a 500 V motor, so the rated current is approximately 17 A.
    A cable with three loaded conductors, laid in air at a design temperature of 30°C, with a cross-section of 2.5 mm^2 conductors, has a long-term load capacity of 25 A and a permissible short-circuit density of 1 second is 143A/mm^2. (PN EN 60364-5-523:2001 and Telefonica catalogue)
    Regards.
  • #19 5389002
    Akrzy74
    Rest in Peace
    Posts: 7910
    Help: 363
    Rate: 1497
    JK60 -
    Quote:
    I have several 11kW units with direct start and it is not a problem at all.
    At "home" - I guess it means in the company where you work... / your own transformer station / and not connected to the public network. As for the cable for this 11KW, definitely 4x4, even if it is 500V. The norm is the norm, and life and common sense have their own... By the way... recently I saw an engine /11KW, 400V/ drawing almost 40A from the network during operation... of course, the "expert" had previously set the thermal limiter to max-42A. The light was dimming... but he kept walking... until, of course, he burned out...
  • ADVERTISEMENT
  • #20 5389227
    HeSz
    Electrician specialist
    Posts: 1186
    Help: 97
    Rate: 198
    Akrzy74 wrote:
    JK60 -
    Quote:
    I have several 11kW units with direct start and it is not a problem.
    At "home" - I guess it means in the company where you work... / your own transformer station / and not connected to the public network. As for the cable for this 11KW, definitely 4x4, even if it is 500V. The norm is the norm, and life and common sense have their own... By the way... recently I saw an engine /11KW, 400V/ drawing almost 40A from the network during operation... of course, the "expert" had previously set the thermal limiter to max-42A. The light was dimming... but he kept walking... until, of course, he burned out...

    My posts are about electricians, not idiots who set thermal protection "so that it doesn`t go off".
  • #21 5389477
    Akrzy74
    Rest in Peace
    Posts: 7910
    Help: 363
    Rate: 1497
    But how can you tell a patsy/gardener apart? :D /, from a veteran electrician - such a new profession: electrical gardener... :D .Such reasoning "so as not to knock out" can often be found in mines... :cry: - someone else will come, diagnose and repair...
  • #22 5390567
    marian_em
    Level 25  
    Posts: 843
    Help: 60
    Rate: 182
    How long should this cable be? 4x2.5mm² may not be too much, but I recommend 4x4mm², it will have a slight margin.
  • #23 5390855
    JK60
    Level 14  
    Posts: 65
    Help: 5
    Rate: 27
    Akrzy74 wrote:
    At "home" - I guess it means in the company where you work... / your own transformer station / and not connected to the public network.

    Of course it is, and this 11kW engine is supposed to work in the kitchen of a residential building as a fan. I wrote earlier, there was little data (if I were a clairvoyant, I would receive about 37 bubbles today), and the answer to this question has already been given many times.
  • #24 5395913
    kiecio
    Level 11  
    Posts: 25
    Rate: 13
    Since the engine is quite old, it is difficult to read anything from the nameplate, but it provides some detailed data:
    TYPE S1-160-L-3
    IP-44
    290/500V 50 ?
    0.80 ? 311/18.1 ?
    960 rpm B-3
    I couldn`t read where there was a question mark :/
    The engine will drive 2 circular saws with a diameter of 630 cm
    I don`t know what type of current, I can only say that it will work in a private household on a cable about 50-60 m long.
    Currently, half of the section has a cable of probably 4x1.5mm (aluminium) and the other half has a cable of 4x2.5mm (copper) (the 5.5kW motor runs without any problems), now it is being replaced with an 11kW one and hence these questions:
    -what cable
    -what security
    - how many amperes of the switch and whether the connection is G or T or G/T
    Well, I guess now this data is enough and I also have fuses... I have B25 in front of the meter and C25 behind it
    And now they`re asking for some feedback
  • #25 5396691
    JK60
    Level 14  
    Posts: 65
    Help: 5
    Rate: 27
    You won`t be able to fight much with these safeguards.
    500V motor in a 400V network, for now try it without major investments and see how it will work. Maybe someone has already tried it and will comment.

    From what I found out, it won`t work without rewinding, a new 11kW with these speeds costs about PLN 2,000

    [I am adding for clarity] With a new or rebuilt engine:

    First, replace the protection in front of the counter with C25. In the long run, you need to increase the power allocation because you will not be able to use other devices during startup.
    G/T switch, 4x2.5 Cu cable but from the contactors to the motor 7x (for peace of mind I would use 4x4)
  • #26 5400623
    kiecio
    Level 11  
    Posts: 25
    Rate: 13
    How many amperes is the switch and is it really G/T?
  • #27 5401281
    Daj
    Level 14  
    Posts: 85
    Help: 3
    Rate: 34
    So this will be the data from the table
    TYPE S1-160-L-3
    IP-44
    290/500V 50Hz
    cos φ 0.80 31.1/18.1 A
    960 rpm B-3

    it looks like a mine engine, I haven`t dealt with anything like that before, but from what I remember from school, this engine will spin when powered from the 230/400V network, but it will be weaker, i.e. it will have less than 11kW

    I don`t agree with the suggestion JK60 replacing the fuse behind the meter with a slow-blowing C25 fuse because there is such a thing as gradation of protections and why do you need two C25s one after the other and you never know which one will work first.

    As for rewinding, the cost with shipping and replacement of bearings would be around PLN 1,500 or less
  • #28 5401660
    kiecio
    Level 11  
    Posts: 25
    Rate: 13
    So a 25A switch will be enough for this engine, because the seller in the electrical store offered me a 63A for this engine for PLN 160 :D :D and the 25A one costs PLN 80, so I`d be pretty pumped :/
    The engine is quite old and from what I can see, it is star-bridged and apparently it used to work that way, so according to @Daj`s opinion, can I use the Star/Triangle switch without any worries?
    As for the B25 protection that I have in front of the meter, when I turn on the 5.5 kW engine, something sizzles in it :/
  • #29 5401681
    MARIUSZ R
    Level 28  
    Posts: 1055
    Help: 94
    Rate: 278
    To calculate protection and cable cross-section, I recommend the Suwak3 program. From 0.06 to 355 kW.
  • #30 5401880
    Daj
    Level 14  
    Posts: 85
    Help: 3
    Rate: 34
    Sorry, I was a bit hasty, the plate states that the motor operates at a voltage of 290/500V, i.e. the phase band has a calculated rated voltage of 290 V, and when using the Y/Δ switch and powered from the 3x400 V network, each phase of the motor will receive a voltage of 400 when connected in Δ. So V probably won`t stand it and will burn

    This means that the Y/Δ switch cannot be used in this engine

Topic summary

✨ The discussion centers around the suitability of a 4x2.5 mm cable for powering an 11 kW motor. Responses indicate that while a 4x2.5 mm cable may suffice for short distances (up to 50 meters), a larger cross-section, such as 4x4 mm or 5x6 mm, is recommended to accommodate starting currents and ensure safe operation. The necessity of a fifth wire for grounding (PE) is debated, with some asserting that only three phase wires and a ground are needed. Concerns about voltage drop and the motor's operational characteristics when connected in star or delta configurations are also highlighted. The importance of proper cable sizing based on distance, load, and installation conditions is emphasized, with suggestions for using protective devices and ensuring adequate current ratings.
Generated by the language model.

FAQ

TL;DR: For an 11 kW three-phase motor (~23 A rated) [Elektroda, SZYMKA10, post #5387486], “4 × 2.5 mm² works only up to 50 m” [Elektroda, Luklukowaty, post #5380129]; most installers choose 4 × 4 mm² copper in star with PE. Use correct protection and match nameplate voltage.

Why it matters: Correct sizing prevents stalled starts, nuisance trips, and burnt windings for workshop or farm machinery.

Quick Facts

• Rated current: 17–23 A depending on 500 V or 400 V supply [Elektroda, HeSz, #5388688; SZYMKA10, #5387486] • Long-term ampacity: 2.5 mm² Cu, 25 A in free air at 30 °C [Elektroda, HeSz, post #5388688] • Typical cable pick: 4 × 4 mm² Cu ≤ 60 m run [Elektroda, Marian_em, post #5390567] • Starting current: up to 10 × In (≈230 A) [Elektroda, Madrik, post #5380323] • Rewind or derate 290/500 V motors on 400 V grids [Elektroda, Daj, post #5401880]

What cable cross-section is best for an 11 kW motor under 60 m?

Use 4 × 4 mm² copper. It carries 23 A with margin, keeps voltage drop reasonable, and meets installers’ experience [Elektroda, JK60, #5388241; Marian_em, #5390567].

Do I need a neutral wire for three-phase motors?

No. The motor needs three phases plus PE. Neutral (N) is unused unless ancillary 230 V loads share the cable [Elektroda, marian_em, post #5380268]

Why did my motor stall on light timber even though fuses stayed intact?

Thin mixed wiring (20 m of 4 × 1.5 Al + 30 m of 4 × 2.5 Cu) caused voltage drop, cutting torque. Flux drops with voltage, so torque falls (M = Ψ·I) [Elektroda, kiecio, #5407966; 00marian00, #5417606].

Should I use a star-delta (Y/Δ) starter on a 290/500 V nameplate?

No. The motor is designed for 500 V in star; switching to delta on 400 V would over-voltage the windings (400 V per phase) and burn them [Elektroda, Daj, post #5401880]

What happens if I undersize the cable further, say 1.5 mm²?

Insulation may overheat in minutes; one test boiled 1.5 mm² insulation after two minutes on 11 kW load [Elektroda, Madrik, post #5380323]

Three-step checklist to size cable and protection quickly?

  1. Read nameplate voltage and full-load current.
  2. Select cable with ampacity ≥ 1.25 × In and ≤ 3 % voltage drop for run length.
  3. Choose breaker: C-curve at 1.1–1.25 × In and ensure upstream selectivity. Tools like Moeller Suwak PKZ automate this [Elektroda, JK60, post #5387686]

What standard tables back these numbers?

PN-EN 60364-5-523 gives ampacity and short-circuit density; example: 2.5 mm² Cu, 25 A, 143 A·s/mm² [Elektroda, HeSz, post #5388688]

Edge case: private transformer vs public grid—does it matter?

A private substation tolerates direct starts better because voltage sag stays local. Public networks may flicker lights or trip upstream fuses [Elektroda, Akrzy74, post #5389002]