What will be the appropriate cable for an 11 kW motor, or will 4x2.5 mm be enough?
What will be the appropriate cable for an 11 kW motor, or will 4x2.5 mm be enough?
Czy wolisz polską wersję strony elektroda?
Nie, dziękuję Przekieruj mnie tamQuote:
I assume that the motor works in a star, we do not use N, we connect PE,
Quote:
so my question: what is the 5th wire for and what is the starting current?
Quote:Hmmm This is probably a new theory
I always thought that the N cable was not needed for the triangle
Quote:
And did I write differently?
kiecio wrote:Hello
What will be the appropriate cable for an 11 kW motor, or will 4x2.5 mm be enough?
Madrik wrote:
The fairies went on vacation. Maybe some data from the tablet? ...
Kobra wrote:
The star (you wrote about) requires a five-wire power supply
JK60 wrote:
The engine does not always require G/T switching, what is it for, is it hard to start, what is the power supply.
When determining the cross-section, it is also important how the cable is routed and how the motor is protected... (in most cases, a 4x4 is enough for an 11kW motor).
Quote:At "home" - I guess it means in the company where you work... / your own transformer station / and not connected to the public network. As for the cable for this 11KW, definitely 4x4, even if it is 500V. The norm is the norm, and life and common sense have their own... By the way... recently I saw an engine /11KW, 400V/ drawing almost 40A from the network during operation... of course, the "expert" had previously set the thermal limiter to max-42A. The light was dimming... but he kept walking... until, of course, he burned out...I have several 11kW units with direct start and it is not a problem at all.
Akrzy74 wrote:JK60 -Quote:At "home" - I guess it means in the company where you work... / your own transformer station / and not connected to the public network. As for the cable for this 11KW, definitely 4x4, even if it is 500V. The norm is the norm, and life and common sense have their own... By the way... recently I saw an engine /11KW, 400V/ drawing almost 40A from the network during operation... of course, the "expert" had previously set the thermal limiter to max-42A. The light was dimming... but he kept walking... until, of course, he burned out...I have several 11kW units with direct start and it is not a problem.
Akrzy74 wrote:At "home" - I guess it means in the company where you work... / your own transformer station / and not connected to the public network.
TL;DR: For an 11 kW three-phase motor (~23 A rated) [Elektroda, SZYMKA10, post #5387486], “4 × 2.5 mm² works only up to 50 m” [Elektroda, Luklukowaty, post #5380129]; most installers choose 4 × 4 mm² copper in star with PE. Use correct protection and match nameplate voltage.
Why it matters: Correct sizing prevents stalled starts, nuisance trips, and burnt windings for workshop or farm machinery.
• Rated current: 17–23 A depending on 500 V or 400 V supply [Elektroda, HeSz, #5388688; SZYMKA10, #5387486] • Long-term ampacity: 2.5 mm² Cu, 25 A in free air at 30 °C [Elektroda, HeSz, post #5388688] • Typical cable pick: 4 × 4 mm² Cu ≤ 60 m run [Elektroda, Marian_em, post #5390567] • Starting current: up to 10 × In (≈230 A) [Elektroda, Madrik, post #5380323] • Rewind or derate 290/500 V motors on 400 V grids [Elektroda, Daj, post #5401880]