Cross-Section Wire Selection in Switchgear: Guidelines for Overcurrent Circuit Breakers
wtct 25713 8
  • #1 11750342
    wtct
    I would like to make sure that the cross-sections of wires in the switchgear before the overcurrent circuit breakers are selected in the same way as for the installation behind the circuit breakers?
    Thanks in advance for the information!
  • #2 11750375
    zbich70
    Help: 1171
    Rate: 6666
    And are there any other protections besides those in the transformer station??? ;)
  • #3 11750380
    bartekfigura
    Level 30  
    Help: 112
    Rate: 524
    Cross-sections are selected due to:
    - long-term load capacity
    - voltage drops
    -mechanical strength
    - overload capacity
    - short-circuit conditions
    - and fire protection
  • #4 11750423
    Rzuuf
    Help: 1355
    Rate: 1700
    ... And if the conditions mentioned above by a colleague bartekfigure are the SAME before and after the circuit-breaker, then the entire section of the installation is made with the SAME cross-section.
    Especially since the current before the circuit breaker is the same as after the circuit breaker.
    TWK
    Electrician specialist
    Help: 220
    Rate: 510
    In normal working condition yes. But not in an emergency.
    lordpakernik wrote:
    Same.
    The same (in the sense of methodology), but the protection against the conductor in question should be taken into account! I do not know any new regulations in this matter (if anyone knows, please complete), but according to PN-57/E-05022, the following conditions had to be taken into account in the use of protection at branches:
    - cross-section of the branching cable (i.e. "behind the circuit-breaker" in the example described) not smaller than 3 consecutive standardized cross-sections from that supplying the switchgear,
    - wires from the branch to the protective device must be protected against mechanical damage (in my opinion, the cover is the switchgear housing),
    - the cable cannot pass through a room with an explosion hazard (here the switchgear is rather not built in such a room),
    - the length of the section in non-industrial facilities cannot exceed 1m (in a small switchgear it is not a problem, in a large one not necessarily).
    So to sum up, with a small switchgear in an apartment/house it is important to take into account the condition with cross-sections. If a 10 mm² wire enters the switchgear, you cannot use less than 2.5 mm² in front of "eSami" (subsequent cross-sections (6, 4 and 2.5), even if it is a lighting circuit, then 1.5 mm².
    This cross-section must be converted to the same material for different cable materials). Of course, it may be that the previous protection is suitable for the section from which the branch is made - this must be checked when making the switchgear.
  • #7 11750805
    bartekfigura
    Level 30  
    Help: 112
    Rate: 524
    The emergency operating state, i.e. short-circuit conditions, may be different.
  • #8 11750859
  • #9 11750961
    wtct
    There is an RCD in front of the overcurrent circuit breakers and a 20 A overcurrent circuit breaker in front of the meter.
The discussion centers on the selection of wire cross-sections in switchgear before overcurrent circuit breakers, emphasizing that the same criteria apply as for installations behind the circuit breakers. Key factors for wire selection include long-term load capacity, voltage drops, mechanical strength, overload capacity, short-circuit conditions, and fire protection. It is noted that if the conditions are identical before and after the circuit breaker, the wire cross-sections should also be the same. However, considerations for emergency conditions, such as short-circuit scenarios, may necessitate different approaches. Regulations, such as PN-57/E-05022, stipulate that the cross-section of branching cables should not be smaller than three standardized sizes from the supplying switchgear, and additional protections against mechanical damage and environmental hazards must be considered.