[Solved] Types of Cables/Wires for Switchgear Connections: 5x10mm² Cable, Devices, Brands, Models

dam234 28533 22
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17754568
    dam234
    Level 10  
    Hello.
    I would like to know what cables/wires to use to connect devices in the switchgear
    The switchgear comes with a 5x10mm^2 cable
    I mean exactly those cables/wires that you can see in the picture.
    Types of Cables/Wires for Switchgear Connections: 5x10mm² Cable, Devices, Brands, Models
  • ADVERTISEMENT
  • Helpful post
    #2 17754631
    osiniak75
    Level 35  
    6mm? is enough to string this switchgear.
  • ADVERTISEMENT
  • #3 17754643
    dam234
    Level 10  
    Rope or wire?
  • ADVERTISEMENT
  • Helpful post
    #4 17754649
    kkas12
    Level 43  
    Of course the link.
    Sleeves necessary.
  • #5 17754652
    osiniak75
    Level 35  
    Link, conveniently and aesthetically.
  • #6 17754660
    dam234
    Level 10  
    So using a 4mm line, it's better not to connect, but to give 6mm?
  • #7 17754699
    osiniak75
    Level 35  
    What is the protection against the meter? Me, as I like to sleep peacefully, I would give 6mm? especially on N. I have also seen such switchboards on 4mm?.
  • #8 17754715
    dam234
    Level 10  
    As for the pre-meter protection, I do not know, because only a 5x10mm cable protrudes from the wall.
    The switchboard is to be located in the beauty salon.
  • Helpful post
    #9 17754727
    kkas12
    Level 43  
    Do it with the same cross-section, i.e. 10mm2.
  • Helpful post
    #10 17754729
    elpapiotr
    Electrician specialist
    A drastic descent from 10 mm? to 4 mm? is not recommended.
  • #11 17754781
    dam234
    Level 10  
    So, gentlemen, is it better to give 6mm? or is it better to give 10mm??
    Will 10mm? easily fit into the cameras?
  • #12 17754795
    elpapiotr
    Electrician specialist
    These are short sections, and if the preceding protection does not exceed the load capacity of this "six", it is enough.
  • #13 17754830
    dam234
    Level 10  
    I'll find out tomorrow what the pre-meter protection is and let you know.
    Thank you very much for your help, it cleared things up for me.
  • #14 17764088
    mawerix123
    Level 39  
    kedziorq1 wrote:
    The terminals on the modular electrical devices allow for connecting the cable cross-section to 25mm2 and not to 35mm2.


    35mm2 is max, although there are exceptions, such as Schneider, where it has two terminals, but even 25mm2 cannot be connected.

    BTW: I'm curious about this 3-phase light in post #1 what's up :?:
  • ADVERTISEMENT
  • #15 17764179
    emigrant
    Level 29  
    kkas12 wrote:
    Of course the link.

    Because? Since when are household switchboards subject to movement, vibration, etc? People don't want to use wire, because fingers hurt... With this "of course" it's something you see.
  • #16 17764220
    kkas12
    Level 43  
    The whole world uses a rope to sew boards and switchboards.
    And in the name of what should I torture myself by using wire for this purpose?
    In addition, there is such a thing as electrodynamic forces.

    I suggest to meet what my colleague suggests in tables where a cross-section exceeding 10mm2 is required to be sewn.
    It happens that sometimes it is much more than that.
  • #17 17764411
    Łukasz-O
    Admin of electroenergetics
    mawerix123 wrote:


    BTW: I'm curious about this 3-phase light in post #1 what's up :?:


    Form over substance, nothing more. Someone watched the tutorials on YT ;)
    One lamp indicates that the voltage is applied to the FR, the other indicates that the FR is switched on, and the third informs about the voltage behind the RCD.
  • #18 17764688
    mawerix123
    Level 39  
    Łukasz-O wrote:
    One lamp indicates that the voltage is applied to the FR, the other indicates that the FR is switched on, and the third informs about the voltage behind the RCD.


    Oh yeah, I had a cursory look at it earlier, which is something like this... all clicks up and the Christmas tree is lit ;)
  • #19 17764817
    Łukasz-O
    Admin of electroenergetics
    mawerix123 wrote:
    (...) all clicks up and the Christmas tree is lit ;)

    Exactly so ?
  • #20 17766177
    masonry
    Level 30  
    emigrant wrote:
    With this "of course" it's something you see.

    This is not a whim, but good practice advice.
    Stranded wires are used not only in the situations you mentioned.
    As for the cross-section, I would not go below 6mm, and how to it will be big, you need to give 10mm.
  • #21 17766208
    kkas12
    Level 43  
    Because that's writing to write, buddy.

    The cable also has the advantage that you can press two wires (even with different cross-sections) with one end. Then the clamp still "sees" only one wire, even though there are actually two wires in the terminal.
    However, in the case of wire, it is not only practically impossible, but we also have an almost certain guarantee of an unreliable contact in the cage clamp of the apparatus.
    And in the case of two conductors with different cross-sections, a "bad" contact is 100% reliable.
    And it will come out sooner or later.
    And the higher the currents, the faster we have a failure resulting in damage to the device and possibly a fire.
  • #22 17775812
    dam234
    Level 10  
    mawerix123 wrote:
    BTW: I'm curious about this 3-phase light in post #1 what's up

    As for the 3 phase indicator, I don't know what it is for. The photo is not mine, just taken from the internet.
  • #23 17794904
    dam234
    Level 10  
    Use of 6mm wires

Topic summary

The discussion revolves around the appropriate cables and wires for connecting devices in switchgear, specifically focusing on a 5x10mm² cable. Participants debate the sufficiency of using 6mm² versus 10mm² cables, with recommendations leaning towards maintaining the same cross-section of 10mm² for safety and reliability. Concerns are raised about the risks of using lower gauge wires, particularly in relation to load capacity and potential electrical failures. The conversation also touches on the use of stranded wires versus solid wires, emphasizing the advantages of stranded wires in terms of flexibility and connection reliability. The need for proper pre-meter protection is mentioned, with a consensus that a minimum of 6mm² is advisable, especially for high-current applications.
Summary generated by the language model.