Quote: As for the rest - according to N SEP E 002 there should be a separate circuit, but there is little chance that the resourceful housewife will not turn on these devices elsewhere.
It should be, and what will be if it is not a dedicated circuit?
There are no dangers with proper installation. Do not add demagogy to the 2W circuit - "non-allocated". 2.5mm2 circuit protected by 16A.
You can pull 16A - 3680W and the fuse will not blow out. Neither installation - also the circuit will not hurt. 3680W is not a "pharmacy", it is not a cutoff value.
16A fuse will blow out after some time at 20A current. Theoretically 1.45 In. No dedicated circuit, it's just a lack of comfort in operation - and nothing else. Because as in the kitchen in the oven circuit 3600W
there is also a socket for a kettle, it's a kettle + oven and the fuse blows out.
Each circuit with sockets must be protected with a 16A fuse - and no more, because this is the permissible -16A - current of each socket in the circuit.