lukaszlanga wrote: while searching, I found very divergent values from 35A to 59A
And this was probably due to the insulation material: PVC, XLPE, EPR
YKY is the old Polish designation and defines PVC insulation, and for this you should choose the long-term load capacity, preferably from the tables of standard 60364-5-523. Long-term current carrying capacity of cables or a newer edition of this standard.
So from memory it will be about 40A for the cable laid completely in the ground, and the protection for this cable is 32A. If the cable is routed in a different environment (even partially), then its load capacity should be reduced, due to the higher environmental temperature (20 degrees C for the ground, 30 degrees C in the air). In the standard, everything is served as if on a tray.