Low Voltage in Sockets: Impact on Meter Readings, 180V-200V Range, 600 Revolutions 1kWh Counter
GT2x 24357 12
Will low socket voltage (about 180–200 V) increase an ordinary 1 kWh meter’s readings, and how does the meter measure consumption?
No—low voltage by itself will not make the meter overstate your bill; the meter should be checked, but the real problem is the cause of the low voltage [#15164301] The voltage you measured, 180–200 V, is below the permissible 230 V ±10% range (207–253 V), so it should be investigated [#15164301] The fault can be in the power network or in your installation, so first have an electrician diagnose the internal wiring and then, if needed, ask the power utility to check their side of the boundary [#15164440][#15165923] If all sockets show the same low voltage and the lights flicker, a poor PEN connection before the meter is one possible cause [#15165923]
  • #1 15164171
    GT2x
    Rate: 24
    Hello, I wanted to ask if the low voltage in the sockets will not increase the meter readings?
    How do they work?
    1) current x voltage (constant 230V)
    2) current x instantaneous voltage
    Ordinary counter 600 revolutions 1 kWh
    The voltage ranges from 180V to 200V.
  • #2 15164289
    2ab92
    Help: 6
    Rate: 31
    First, find the cause of such a voltage and do not worry about the meter.
    Because the consequences of such a state can be more severe a few pennies more on the bill.
    This voltage is below the limit value.
    Jar-Woj
    Help: 98
    Rate: 314
    Don't worry, voltage drops can't cause meter readings to overstate.
    Are you sure about the correctness of the meter readings?
    Have you checked multiple outlets to see if they all have the same voltage fluctuations?
    If fluctuations occur only in a part of the installation, it should be checked by a specialist.
    If, on the other hand, the voltage is the same in all sockets, then the fault is most likely with the power grid.
    Either way, you should notify the power industry, such voltage drops should not take place and may indicate a fault.
    According to the PN-IEC 60038 standard, the permissible voltage deviations from the nominal 230V are +/-10%, i.e. from 207V to 253V.
  • #4 15164303
    slawekjang
    Rate: 21
    So low voltage is present in your friend's whole apartment? The standard says 230 +/- 10%, which is a bit low ;)
    Regards
    zbich70
    Help: 1171
    Rate: 6666
    The fault may be in the network or in the receiving installation.
    Socket outlets are not a power supply point.
    You need to call an electrician who will first diagnose the installation.
  • #6 15165882
    GT2x
    Rate: 24
    There is such a low voltage in all sockets. To measure the voltage, I use:
    Instructions for posting photos and pictures on the forum https://www.elektroda.pl/rtvforum/topic2053101.html [retrofood]
    It works fine because in another house it shows 225V.
    Renovation was recently and all cables replaced, but it's good that it doesn't inflate the bills :D
    Thanks for the replies
    .Jack
    Electrician specialist
    Help: 361
    Rate: 427
    GT2x wrote:
    All sockets are so low voltage.
    Does your friend have noticeable flickering lights?
    Low voltage in all sockets and flickering light may be caused by poor contact of the PEN cable already in the connector before the meter.
    Troubleshooting: Have your electricity supplier check on their side of the property boundary first.
  • #8 15166071
    GT2x
    Rate: 24
    It blinks quite often, I thought the bulbs needed to be replaced :D
  • #9 15166274
    zbich70
    Help: 1171
    Rate: 6666
    I think it's better to check first own and make sure the sell is in someone else's . Only then question others.
    But colleagues proposing the opposite way of acting are right - after all, DSO does not charge for unfounded calls.
    So let's even call for a blown bulb and a "non-contacting switch".
    And let's also call the water supply company for a leaking tap and a clogged toilet... :D
  • #10 15167043
    2ab92
    Help: 6
    Rate: 31
    If it blinks, it means something is burning somewhere.
    If you have a multimeter, you can do a primitive measurement of the short-circuit loop impedance.
    Voltage drop / current drawn by some device of known power. You can find the current from the formula for power. This may lead to the failure site.
    But the best solution is to call an electrician with professional measuring equipment to locate the faulty circuit. This is no joke, it can end up in shock.
    Network failure - unlikely in my opinion, the neighbors would certainly notice.
  • #11 15167409
    AreckiSzef
    and (depending on various other factors) saying goodbye to home electronics...
  • #12 15167982
    GT2x
    Rate: 24
    It's messed up ... I'm checking with a meter if there is a short circuit and amperes drawn at the fuses and the socket. :D
  • #13 15168122
    pol102
    Help: 163
    Rate: 369
    Just so you're aware that when you check the amperage before the fuse, you can blow the fuse in the meter or even the meter itself.
The discussion revolves around the impact of low voltage (180V-200V) on electricity meter readings, specifically concerning a standard meter with 600 revolutions per kWh. Participants clarify that low voltage does not lead to inflated meter readings, as the meter operates based on the actual current and instantaneous voltage. They emphasize the importance of diagnosing the cause of the low voltage, which could stem from issues in the electrical network or the installation itself. Recommendations include checking multiple outlets, consulting an electrician for proper diagnostics, and notifying the power supplier about the voltage drops. Flickering lights may indicate poor connections or faults in the wiring. Participants advise caution when measuring electrical parameters to avoid damaging equipment.