240V 3-phase mains – is 200/215V within acceptable standards?
aksel_pl 130497 102
Are 200–215 V phase voltages at the meter output acceptable on a 230 V supply, and could they explain dimming lights and failing electronics?
Yes—according to the thread, a 230 V low-voltage supply may vary by +10%/−15%, and the weekly 10-minute averages must stay within the standard limits, so 200–215 V is generally within the permitted range, though 205 V is close to the lower edge [#13261838][#13329265] Still, several replies say that dimming lamps and damaged electronics warrant inspection by a qualified person because the cause could be a loose PEN/N connection or another fault either in your installation or in the supplier’s network [#13261941][#13263032] The advice is to verify the installation from the ownership boundary and, if you want proof, request a network analyzer or recorder rather than relying on an ordinary multimeter [#13263032][#13262926][#13284987] Brief spikes are easy to miss with a normal meter; an oscilloscope can show them, but without logging/memory it is not a good tool for hunting intermittent events [#13262267][#13261983] One reply also notes that if the load changes, the voltage can move within the normal range and the distributor may see nothing actionable if the phases are otherwise fairly even [#13264541]
  • #1 13261398
    aksel_pl
    Help: 8
    Rate: 76
    I think the thread has already been here, but I can't find it.
    For about a month, I have been noticing the dimming of lamps, microwave fans, LED lighting, etc.
    Today I decided to take measurements with the Sanwa PC5000a meter - I think it is sufficient for reliable measurements.
    Finally, I measured 3 phases just at the output of the meter in the main distribution box and it turned out that at the time of measuring the voltage they were respectively 200, 215 and 215v
    My question is, is this acceptable?
    Because an employee at 911 said that 10-15% is acceptable, which means that this fluctuation would be within the norm.
    I would like to add that the whole problem began when the construction of a large housing estate was completed several meters away.
    I have heard that they have to put up a transformer and so far they cannot connect the housing estate (they cannot connect it to the main street line, but they have to draw electricity from another ...
    But I see that some residents somehow have electricity in their apartments.
    Recently, I have lost quite expensive electronic equipment and I wonder if it is not for this ...
    I will be grateful for your advice.
    Best regards.
  • #3 13261554
    aksel_pl
    Help: 8
    Rate: 76
    I understand +/- 10% from 240V? So if I note that there is 205 V on one phase, for example, can they say that it is temporary and ignore it?
    soadfan
    Help: 6
    Rate: 25
    Dude +/- 10% and yes, but in Poland the voltage is 230 volts.
  • #5 13261824
    aksel_pl
    Help: 8
    Rate: 76
    Well, that's how it is on the border.
  • #7 13261855
    aksel_pl
    Help: 8
    Rate: 76
    Well, if even -15% is acceptable, then I suspect that everything is normal. You have to get used to dimming lights, slowing fans etc ...
    I just hope that it does not destroy the led lighting under 230 V because it rains quite often and I have to replace it.
    I am surprised then that they even accepted the application.
  • #8 13261923
  • #10 13261961
    aksel_pl
    Help: 8
    Rate: 76
    Thank you, Maciej, for the information, I just wanted to point out that the measurement error can be excluded.
    I just recorded a quick jump from 205 to 195 and back again. Generally, I recorded a short film with tensions in case they said tomorrow that everything is ok because it is around 220.
  • #12 13262007
    aksel_pl
    Help: 8
    Rate: 76
    Can I pick it up with an oscilloscope?
  • #13 13262267
  • #14 13262394
    aksel_pl
    Help: 8
    Rate: 76
    We'll see what the gentlemen from Eneia will say. I bet that the transformer does not work through the new housing estate and hence such things.
  • #15 13262853
    zbich70
    Help: 1171
    Rate: 6664
    If I know life, they will measure it with an ordinary multimeter, see 208V and say that it is good, nothing for them. ;)
  • #16 13262870
    aksel_pl
    Help: 8
    Rate: 76
    Well, that's what I'm afraid of too ... any ideas ...?
  • #17 13262926
    masonry
    Level 30  
    Help: 106
    Rate: 832
    Request a network analyzer, because your equipment is damaged, you have epilepsy and you cannot stay in rooms where the light is blinking. In general, the more persistent and resolute you are, the more seriously they will take you.
  • #18 13262948
    aksel_pl
    Help: 8
    Rate: 76
    Thanks a lot, that's something :)
    Currently, I have a constant 204v also great ... I am curious if this quality corresponds to the losses in power transmission and energy consumption or are they too low values?
    PS
    Is it allowed to record a conversation with energy workers with a camera?
  • #19 13262969
    zbich70
    Help: 1171
    Rate: 6664
    Even the most annoying client who shows signs of a layman will be treated with bulldozer. Better results are obtained when neighbors are joined together and a "collective" complaint - although this is sometimes impossible, it is worth asking whether someone has similar symptoms (preferably from different places in the area supplied by a given transformer station).
  • #20 13262983
    aksel_pl
    Help: 8
    Rate: 76
    I am planning to visit two neighbors tomorrow and measure the tensions on the phases. The question is simply if there is any reason to do so. Is what I have described really should be "fixed"? Or is it such a small problem that it's not worth worrying about?
  • #21 13262995
    masonry
    Level 30  
    Help: 106
    Rate: 832
    I suppose that he will not agree to the recording and he has the right to do so.
    If it is only a temporary voltage drop and it doesn't happen all the time, you can get used to it and give it up. What you describe is not some wolf hello again. From your posts it appears that it is a multi-family building, so any damage does not have to be on the ZE side. Something may be happening at the building's WLZcie, and this already belongs to the owner, not to ZE.
  • #22 13263003
    michalekk1
    Help: 54
    Rate: 105
    [quote = "aksel_pl" I am allowed to record a conversation with energy workers with my camera? [/ quote]
    As far as I know, they are not office workers or public figures. They do not have to speak at all in front of the camera, that's why they have "spokesmen".
  • #23 13263032
    zbich70
    Help: 1171
    Rate: 6664
    First of all, you need to determine what is the cause. Voltage fluctuations and fired electronics may indicate a PEN burnout. It can be in the provider's network but also ... at your place. Voltage fluctuations in your neighbors are one thing, but reliable measurements of your installation from the boundary of ownership are another.
  • #24 13263052
    aksel_pl
    Help: 8
    Rate: 76
    I carried out the measurements at the meter output, so there are only the power plant cables in front of it. It seems to me that at this point I can not have too much influence on the voltage, especially if no welders are connected.
    Of course, I do not have enough knowledge here, so I can be wrong, or in the case of a month ago everything was ok, that is, before the commissioning on the estate began. I am not 100% sure that the estate has a connection with it, but I remember that a year ago no one was supposed to have an electricity permit because there was no transformer, and suddenly over 100 apartments were built, and the transformer will be put up ... hence my guesses.
    I would like to remind you that the problem occurs in all three phases, but it is not the same. I know that the house is definitely connected with two phases, but as I have a 3-phase control in the box, I suspect that all 3 are connected.
    I also made measurements in sockets and in the home section, and the voltages there are the same, because with fluctuations it is difficult to say whether they are exactly the same if one person does it :)
    Generally, this hesitation is more and more noticeable, it didn't bother me before, but now it's starting to irritate me. I have a fan that runs once as if it was in 1st speed and once as if it was in 2nd speed, although I do not change anything.
    However, the problem with incident led "bulbs" lasts longer.
    I remember that half a year ago I left the RGB strip turned on for the night, the alledrogo one and in the morning here and there the red chips did not glow anymore and the red ones are the most susceptible to fluctuations.
    Even now I remembered that very often I have to replace the usual small 12v bulbs that I have in the spider chandelier. There are still some burnouts. - Of course, it does not necessarily have to do with the quality of the electricity.
  • #25 13263117
  • #26 13263128
    aksel_pl
    Help: 8
    Rate: 76
    I'll stock up on this invention, but not right now :)
    In general, I am very grateful to everyone for their help, because people here are not always so willing to share their knowledge ;)
  • #27 13263192
  • #28 13263279
    aksel_pl
    Help: 8
    Rate: 76
    but if your devices burned down, the power plant would pay, wouldn't it?
  • #29 13263290
    michalekk1
    Help: 54
    Rate: 105
    He would have to prove it first. And how can you prove it without some kind of failure like a blown PEN?
  • #30 13263410
The discussion addresses voltage fluctuations observed in a 230/400V low-voltage network, with measured phase voltages ranging from approximately 195V to 225V, occasionally dropping to around 200V. According to applicable standards and EU regulations, voltage deviations of +10% to -15% from the nominal 230V are generally acceptable, meaning voltages between 195.5V and 253V fall within tolerance. Fluctuations can be caused by factors such as load changes, transformer aging, or network configuration, including new housing estate connections without completed transformer installations. Measurement accuracy and equipment limitations were considered, with suggestions to use devices like oscilloscopes with memory or network analyzers for detailed voltage quality monitoring. The importance of measuring at the ownership boundary to attribute responsibility was emphasized. Voltage dips may cause dimming of lighting and slower operation of appliances but typically do not damage CE-marked equipment designed to withstand short-term voltage variations up to 253V. Overvoltage protection devices and mains voltage controllers can mitigate transient spikes, though some impulses may still reach connected devices. Collective complaints and persistence in communication with energy suppliers are recommended for resolution. The discussion also touched on the impact of voltage levels on energy losses and consumption, noting that higher voltages reduce current and transmission losses, while low voltages may increase losses and affect device performance. Proving supplier fault for damages requires detailed, continuous voltage monitoring, often with specialized equipment such as the FLUKE VR1710 or Tektronix oscilloscopes. The overall consensus is that the observed voltage levels, while at the lower end of the acceptable range, are within regulatory limits, and that infrastructure upgrades like transformer replacement may be necessary for long-term improvement.