with the light switch off, there is still a phase on both wires
luk200p 24111 17
Why do both wires at my light fixture still seem live when the switch is off, and why do my LED bulbs glow faintly?
Your switch wiring is likely wrong or leaking: the break should be in the phase conductor, not the neutral, and a neon test screwdriver can show a false “phase” due to phantom voltage [#15270152][#15270155] A poor neutral contact or other leakage can also produce these symptoms, so the installation needs to be checked and measured properly [#15270145] In the thread, the faint LED glow was ultimately traced to the cable from the ceiling box to the switch: it was an antenna coaxial cable, possibly damaged, and disconnecting it fixed the problem [#15270661] The remedy is to have an electrician rewire it so phase goes to the switch and neutral goes directly to the lamp [#15270152]
  • #1 15270102
    luk200p
    Hello. I changed all the bulbs in the whole house to "LED", but in the kitchen I have a big problem because there the bulbs do not go out completely after switching off. I also noticed that after disconnecting the entire chandelier and turning off the switch, it slightly "kicks" the current on both cables, and when applying a test-tube screwdriver (with the switch off) on both cables, the bulb of this test-tube gently glows. Has anyone had a similar problem?
    I will add that on ordinary traditional bulbs with tungsten, the problem did not occur or was not visible..
  • #2 15270119
    marekhab
    Help: 251
    Rate: 267
    You don't accidentally have backlight switches that stay on if the light is off, when you turn the light on they go out.
    If so, you need to disconnect them because they are the cause of glowing.
  • #3 15270127
    luk200p
    Hello. No, I don't have such a backlight in any room..
  • #4 15270145
    000andrzej
    Level 37  
    Help: 302
    Rate: 238
    If you don't have a neon light in the switches, you need to review the installation, because you have something messed up. A slight leakage or poor contact of the N wire is enough and you will have such symptoms. You need to measure where the error lies.
    kozi966
    Help: 599
    Rate: 1288
    Typical problem with a circuit breaker located on the neutral conductor, not the phase conductor.
    Similar topics have already been: https://www.elektroda.pl/rtvforum/topic3124972.html
    You have to replace the wires "powering" the switch and the lamp in the box. Instead of neutral going to the light switch, it should be phase. Neutral should come to the lamp.
  • #6 15270155
    Piko
    Help: 47
    Rate: 110
    A test tube or neon indicator is not an authoritative instrument for this type of measurement. This is an indicator and it shows the potential difference between what you touch and the so-called earth (whatever that means). As for the light glow of the LEDs. This is probably due to the converter in the chandelier and the protective wire is looped, or some other electronic or suppressor circuit in the switch.
    Regards.
  • #7 15270317
    luk200p
    I checked. In the box in the wall, the double wire from the switch is connected to the one with the phase.. I also noticed that after turning off the fuses of the automatic ones next to the meter, the dial still rotates very slowly. It stops completely only after unscrewing the (older model - porcelain) main fuse 20A in the box outside.
  • #8 15270332
    retrofood
    Help: 1140
    Rate: 4800
    luk200p wrote:
    I also noticed that after turning off the automatic fuses next to the meter, the dial still rotates very slowly. It stops completely only after unscrewing the (older model - porcelain) main fuse 20A in the box outside.
    So it has to be.
  • #9 15270347
    000andrzej
    Level 37  
    Help: 302
    Rate: 238
    retrofood wrote:
    So it has to be.
    Why should the meter show the current consumption after the fuses are turned off?
  • #10 15270610
    retrofood
    Help: 1140
    Rate: 4800
    Do not indicate consumption, only the disc goes to the braked position. Such a black fragment of the edge of the shield is to be visible in the window. If he is not there, the shield has the right to turn to make him visible. Then it stops.
  • #11 15270661
    luk200p
    The problem with the LEDs not going out until the end was the cable going from the box under the ceiling to the switch. Somebody put an ANTENNA coax in here! which probably has a puncture in it, or it was because it's from the antenna. I disconnected it and made a temporary "on top" of the two-wire. I'm going to drill and put it under plaster tomorrow. The case with the rotating shield is still unresolved, because after disabling the safety automatic spins all the time and does not stop at the mark
  • #12 15270675
    000andrzej
    Level 37  
    Help: 302
    Rate: 238
    The colleague did not mention anything that it stops, but after disconnecting the power supply at the input, yes. For me, it stops in every position, but maybe there are different counters. Let the author of the post check that after turning off the fuses, the disc will stop in the "zero" position, as described by retrofood. If it spins on and on and keeps spinning - it may mean you have some kind of runaway download. Maybe a ringtone? It's just guesswork.
  • #13 15270799
    luk200p
    I will call an electrician because the fuses next to the meter do not disconnect the gas heater's electricity. Despite leaving everyone on off, the stove is getting power, the digital display is on and the ignition is working
  • #14 15270844
    retrofood
    Help: 1140
    Rate: 4800
    So you already know why the counter is spinning, right?
  • #15 15270875
    luk200p
    Yes, but for me it is strange because the stove is not protected in any way, and only removing the plug causes its electronics to stop working.
  • #16 15270879
    retrofood
    Help: 1140
    Rate: 4800
    Therefore, a visit to an electrician is highly recommended.
  • #17 15271199
    luk200p
    fuses without housing with the light switch off, there is still a phase on both wires with the light switch off, there is still a phase on both wires with the light switch off, there is still a phase on both wires
  • #18 15271676
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    If he connected it as in the picture, it cannot be turned off (black cable). I always wonder when I see such pictures and ask "who did this to you" shocking.
The discussion revolves around an issue where LED bulbs in a kitchen chandelier do not turn off completely when the light switch is off. The user observes a slight current on both wires even after disconnecting the chandelier, indicated by a test-tube screwdriver that glows. Responses suggest potential causes such as backlight switches, improper wiring, or a circuit breaker on the neutral conductor instead of the phase conductor. The user later identifies that a coaxial cable was incorrectly used in the wiring, which likely caused the issue. There are also concerns about a spinning electricity meter even when fuses are turned off, indicating possible electrical leakage or incorrect wiring. The user plans to consult an electrician for further assistance.