logo elektroda
logo elektroda
X
logo elektroda

3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP

szympans123 23544 12
Best answers LABEL_AI_GENERATED

How do I connect a 3 kW 220/380 V three-phase motor to a star-delta switch, and can it run in delta on a standard network?

You should not use a classic star-delta starter for this motor on a normal 3×380 V network, because delta operation would require a 3×220 V network; on your network the motor can work only in star [#16207962][#16208107][#16208162] If you want to use that switch at all, use it only as a 0-1 switch: connect L1 to 1, L2 to 4, L3 to 9, and the motor U1 to 2, V1 to 8, W1 to 10 [#16210343] The third position must be mechanically blocked, because it would short-circuit the supply [#16210343] The simplest recommendation from the thread is to forget the star-delta switch and buy a normal motor 0-I switch instead [#16216336]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • Wiring a 3 kW 220/380 V motor with star-delta switch

    #1 16207932
    szympans123
    Level 9  
    Posts: 6
    Rate: 1
    Hello,
    I am a lucky buyer of 3-phase 3-phase motor.
    I also have a star triangle switch.

    Now I have a problem how to put it all together. Unfortunately, I can not find the diagrams for this engine or the circuit breaker. It looks like someone has already bridged the star on the engine. Is there any less power then?

    Paramters 3kW, 4HP 220/380, Y / ?

    I am enclosing one by one.
    Engine nameplate 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170117_1..627.jpg (3.58 MB)You must be logged in to download this attachment.
    Connector on the engine - looks like bridging under the star 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170117_1..728.jpg (7.24 MB)You must be logged in to download this attachment.

    Switch with 4 pages
    1. 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170117_1..117.jpg (1.47 MB)You must be logged in to download this attachment.
    2. 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170117_1..127.jpg (1.66 MB)You must be logged in to download this attachment.
    3. 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170117_2..333.jpg (1.1 MB)You must be logged in to download this attachment.
    4. 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170117_2..344.jpg (1.06 MB)You must be logged in to download this attachment.
    5. 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170119_0..140.jpg (1.25 MB)You must be logged in to download this attachment.
    and a plate 3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP20170117_2..448.jpg (453.66 kB)You must be logged in to download this attachment.
  • ADVERTISEMENT
  • #2 16207938
    Andrzej42
    Level 32  
    Posts: 1534
    Help: 178
    Rate: 322
    This motor is not suitable for operation with the Y / ? switch.
    As you have noticed, the order of switching on is Y and ?, and on the motor plate you have the opposite, i.e. ? / Y.
    Do you have such a poor installation that you can start the 3KW engine with start up?
  • ADVERTISEMENT
  • Questioning direct starting and 220/380 V motor connections

    #3 16207949
    szympans123
    Level 9  
    Posts: 6
    Rate: 1
    Andrzej42 wrote:
    Do you have such a poor installation that you can start the 3KW engine with start up?


    The installation should be easy to manage, but I have a switch like that. Is it possible to connect it so that it works without a boot?

    Added after 2 [minutes]:

    Andrzej42 wrote:
    (...) Y and ? are on, and you have the opposite on the motor plate, ie ? / Y.

    If I can ask for an explanation of what does ? / Y mean on the plate? (Of course, in this case - 220/380)

    Thanks
  • ADVERTISEMENT
  • #4 16207962
    niewolno2
    Level 40  
    Posts: 4694
    Help: 630
    Rate: 1260
    Buddy, this engine can not work in delta connection because you get it.
    In connecting to a triangle, the network layout would have to be 3 X 220V and you probably do not have one.
  • #5 16207963
    Andrzej42
    Level 32  
    Posts: 1534
    Help: 178
    Rate: 322
    There is a good chance that it will. But you would need to test this switch a bit - the description and appearance does not say anything.
  • Clarifying direct-start feasibility and 220/380 V star-delta notation

    #6 16207965
    Topolski Mirosław
    Moderator of Electrical engineering
    Posts: 7163
    Help: 355
    Rate: 1624
    szympans123 wrote:
    Andrzej42 wrote:
    Do you have such a poor installation that you can start the 3KW engine with start up?


    The installation should be easy to manage, but I have a switch like that. Is it possible to connect it so that it works without a boot?

    Added after 2 [minutes]:

    Andrzej42 wrote:
    (...) Y and ? are on, and you have the opposite on the motor plate, ie ? / Y.

    If I can ask for an explanation of what does ? / Y mean on the plate? (Of course, in this case - 220/380)

    Thanks

    Read here: https://www.elektroda.pl/rtvforum/topic1298087.html
  • #7 16207968
    szympans123
    Level 9  
    Posts: 6
    Rate: 1
    Andrzej42 wrote:
    There is a good chance that it will. But you would need to test this switch a bit - the description and appearance does not say anything.


    Ok, tomorrow I'll stick with the meter and see what it's there :)

    Thanks again!
  • ADVERTISEMENT
  • Motor must run in star on the Polish network

    #8 16208107
    Anonymous
    Anonymous  
  • #9 16208129
    szympans123
    Level 9  
    Posts: 6
    Rate: 1
    Kurtka na wacia wrote:
    Just an ohmmeter or a battery with a bulb, and an analysis of which contacts are closed.

    I have a meter with a pipe ;) and I just measured the switch.
    On Y
    1 contains 2
    4 -> 8.12
    9 -> 10
    Na ?
    1-> 2.4
    5-> 8
    9-> 10.12
    I do not know where to connect L1, L2 and L3 now and where the engine ...
  • 220/380 V motor must run in star on Polish mains

    #10 16208162
    Krzysztof Kamienski
    Level 43  
    Posts: 21895
    Help: 2033
    Rate: 5167
    szympans123 wrote:
    Paramters 3kW, 4HP 220/380, Y / ?

    I am enclosing one by one.

    Good night. Only ? (star :D ) Do you live in the US? As colleagues wrote, there is no possibility of this type of start-up (? / ?) in the classic European network (except perhaps Norway)

    Kurtka na wacia wrote:
    The switching order is determined by the star / delta switch and not the motor nameplate. I have never seen the triangle / star switch. This engine can not work in our Polish network connected in a triangle. It can work only on a star. The switch probably can be connected so that it serves as an on / off switch. Just an ohmmeter or a battery with a bulb, and an analysis of which contacts are closed.
    Answering and right.
  • #11 16210343
    Andrzej42
    Level 32  
    Posts: 1534
    Help: 178
    Rate: 322
    It's best if you take down all the bridges and measure again.
    Put a photo of the switch's top, please, because I'm still not telling me anything.
    If you want to use this switch only as 0-1 then I suggest: L1 to 1, L2 to 4, L3 to 9; and the motor: U1 to 2, V1 to 8, W1 to 10. It is necessary to block the possibility of switching to the third position because it will be short-circuited.
  • Preventing dangerous third-position short circuit

    #12 16213703
    szympans123
    Level 9  
    Posts: 6
    Rate: 1
    Andrzej42 wrote:
    Put a photo of the switch's top, please

    Added - number 5 in the original post.

    Andrzej42 wrote:
    It is necessary to block the possibility of switching to the third position because it will be a short circuit.

    This is probably the biggest problem I see.
    I found it separately in the barn and there's a 0-1 switch on it, so I'll start with it.
    If everything works well, maybe it will invest in something like:
    3kW 3-Phase Motor Connection: Star-Delta Switch, Wiring Diagram, 220/380 Voltage, 4HP6d382cc54f...a3249c.jpg (51.78 kB)You must be logged in to download this attachment.
  • #13 16216336
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4798
    szympans123 wrote:
    Hello,
    I am a lucky buyer of 3-phase 3-phase motor.
    I also have a star triangle switch.


    Just as the Colleagues wrote. This is not a switch to such an engine and you should not make any combinations, but buy a normal 0-I motor switch
    I close the subject.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the connection of a 3kW, 4HP, 3-phase motor using a star-delta switch. The user is seeking guidance on wiring the motor correctly, as the motor's nameplate indicates a different switching order than the switch they possess. Responses indicate that the motor cannot operate in a delta configuration due to the voltage supply limitations (220/380V) and that it should only be connected in a star configuration. Suggestions include measuring the switch contacts and using it solely as an on/off switch, with specific wiring recommendations provided. The consensus is that the current switch is unsuitable for the motor, and a standard 0-I motor switch is recommended for proper operation.
AI summary based on the discussion. May contain errors.
ADVERTISEMENT