Star or triangle? Connection of the motor depending on the markings.

Witkacy8 73913 11
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 3511581
    Witkacy8
    Level 20  
    How to connect the engine.

    on the plate:
    triangle / star
    230 / 400V
    5.2 / 9.4 A

    How we connect the engine depending on the markings
  • ADVERTISEMENT
  • Helpful post
    #2 3511651
    kim
    Level 15  
    You have 2 rows of 2 pairs of clamps
    something like that

    * * *
    * * *

    And now the threesome is like this

    * * *
    | | |
    * * *
    L1 L2 L3

    And in the star yes

    * - * - *

    * * *
    L1 L2 L3

    These little lines are jumpers (most often of such a small flat bar
  • ADVERTISEMENT
  • #3 3511682
    Witkacy8
    Level 20  
    I know what this connection looks like, but I don't know if a given engine can work in a star or a triangle, and maybe in both ??
  • Helpful post
    #4 3511701
    kavma
    Level 21  
    Hello
    According to the markings you have given, this motor can work in a star connection in the network existing in our country (3 x 400V).
    greetings
    kavma
  • ADVERTISEMENT
  • Helpful post
    #5 3511708
    Aleksander_01
    Level 43  
    Hello.
    This motor can only run in a star - of course when powered directly from the 400 V mains.

    There are single-phase inverters, at the output of which we get a wire voltage of 230 V - and it is with such an inverter that you connect the motor in a triangle, and its power and torque will not change.
    greetings
  • Helpful post
    #6 3511754
    piter
    Level 15  
    Motor power will be maintained for delta and star connection.
    Direct switching of the motor under voltage in delta connection is not used due to the many times higher inrush currents
    than in the case of "star" operation. If the engine load is, for example, a fan or a turbine, a star-delta switch is used during start-up. This protects the motor itself as well as the mains. Of course, the other protection elements are in place.
  • #7 3511847
    Witkacy8
    Level 20  
    And what will the markings on the engine be when it can only work in a triangle or only in a star?
  • #8 3512006
    piter
    Level 15  
    Apart from the power supply from the inverter (attention - motors with a special design), the rating plate of the motor contains data about the speed, supply voltage and current. the engine can work with both connections, while maintaining the basic rules of control.
  • ADVERTISEMENT
  • Helpful post
    #9 3512067
    janhen
    Level 22  
    Hello
    3-phase winding motor. rated for operation in a network with a voltage of 400V 50Hz, the rating plate may have a delta connection and a voltage of 400V (or 380V) and, if it has 6 terminals, it may be connected via a star / delta switch, while the motor with a star connection on the plate and the voltage of 400V (or 380V) cannot be connected through such a switch
  • #10 3512133
    Aleksander_01
    Level 43  
    piter wrote:
    If the engine load is, for example, a fan or a turbine, a star-delta switch is used during start-up. This protects the motor itself as well as the mains. Of course, the other protection elements are in place.


    What are you typing?
    Well, this motor you want to switch from star to delta.
    People, learn to read the engine nameplate.
    If you power this motor in a star, you will get 230V on each of its phases, and the same applies to the triangle. The value of the currents on the rating plate is different because they are line currents, while the phase currents will be the same in both cases.

    If you connected this motor in a delta to the 400 V power grid, its power would triple, but not the shaft power, but heat loss, in other words, only gray smoke from this motor would go.

    Who taught you so, in which commune do they teach you like that?
    greetings
  • #11 3512232
    kavma
    Level 21  
    Hello
    Alexander_01
    I was about to stop speaking because my answer and your "just in the star" takes care of this topic.
    But you see what it's like when someone writes play for the sake of art.
    And a commune is like a commune.
    Mr. Witkacy8, I suggest you connect this engine, I advise you kavma with Aleksander_01 and close this topic.
    greetings
    kavma
  • Helpful post
    #12 3512236
    warbipower
    Level 18  
    Witkacy8 wrote:
    And what will the markings on the engine be when it can only work in a triangle or only in a star?


    Signs :
    230 / 400V - the engine can only work in a star,
    400V - the motor works in delta, star / delta starting can be used
    400 / 690V- the motor works in a delta at 400V or in a star at 690V. Can be used for star / delta starting.
    I recommend :

    http://www.elektroinstalacje.info/forum/viewthread.php?forum_id=9&thread_id=9

    http://www.elektroinstalacje.info/readarticle.php?article_id=4

Topic summary

The discussion revolves around the connection methods for a motor marked with "triangle/star" and voltage ratings of "230/400V" and current ratings of "5.2/9.4 A." It is clarified that the motor can operate in a star connection when powered by a 400V supply, while a delta connection is typically used with inverters providing 230V. The inrush currents during direct delta connection are significantly higher, which is why a star-delta switch is often employed for starting motors under load. The markings on the motor's nameplate indicate its connection capabilities: "230/400V" suggests it can only work in star, while "400V" indicates it can operate in delta or use a star/delta starting method. The importance of reading the motor's nameplate for proper connection is emphasized.