Hello.
I have calculated that I can expect a 2.5mm2 separation of about 4W power on 1 meter of copper conductor when 20A current flows. For 30A it will already be about 9W of power.
Well, for such a 1 meter cable in the wall when it flows permanently around 22A (let's assume 5W power) can I expect cable insulation to burn out and damage? The cable is 5x2.5mm2.
I also wonder if the cable placed in the wall, stuck with plaster, gets much warmer compared to the cable loosely laid outside the wall.
I have calculated that I can expect a 2.5mm2 separation of about 4W power on 1 meter of copper conductor when 20A current flows. For 30A it will already be about 9W of power.
Well, for such a 1 meter cable in the wall when it flows permanently around 22A (let's assume 5W power) can I expect cable insulation to burn out and damage? The cable is 5x2.5mm2.
I also wonder if the cable placed in the wall, stuck with plaster, gets much warmer compared to the cable loosely laid outside the wall.