Biawar Kaskada 2 Heater: Intermittent Heating, Fuse Blowing & Water Flow LED Diagnostics
buffalo222 15876 15
Why does a Biawar Kaskada 2 heater heat only for a few seconds, sometimes blow the fuse, and then stop heating even though the flow LEDs come on?
Check the safety thermostat first, then inspect the pressure switch assembly because a damaged membrane or sticky piston can stop the microswitches from engaging even when the flow LEDs light up. [#16587127] [#16742960] [#16743036] Verify that the heater elements and thermostats are electrically OK, and clean the inlet strainer plus any tap aerators/filters so the pressure switch gets the needed pressure difference. [#16594831] [#16742960] The pressure switch should close its contacts progressively as flow increases; if it only works manually or remains misadjusted, set it only with the power fully disconnected, or replace the switch if adjustment does not help. [#16742960] [#16743036] In the thread, the actual fault turned out to be a perforated membrane and a dirty piston; after cleaning the piston and replacing/cleaning the membrane, the heater worked normally with all four LEDs on. [#16745103] [#18734121] [#18741007]
  • Intermittent heating with flow LEDs and fuse trips
    #1 16587069
    buffalo222
    Rate: 8
    Over half a year ago I bought a house in which the Biawar Kaskada 2 heater is mounted. In fact, throughout the whole winter-spring period, it heated and worked well, apart from the fact that sometimes it happened to blow the main fuse. Unfortunately, it has not heated water for several days. The red LEDs light up as the water flow increases and the water heats up for a few seconds you can feel it under the tap, but it is cold again in a moment, sometimes even very much.
    At the maximum opening of the draw-off valve (in taps or shower) all 4 diodes indicating flow flow light up. After closing the draw-off valves, you can hear a characteristic 2 or 3 times tick in the heater. The heater is currently set on the first level dial according to the manufacturer's recommendation. I tried at level two - no changes.
    Where to start searching for a problem?
    jdubowski
    Tube devices specialist
    Help: 2511
    Rate: 2804
    From checking whether you do not need to reset the safety thermostat (on the heating unit).
  • #3 16587486
    buffalo222
    Rate: 8
    I unfolded the cascade and at first glance everything is ok. "S" fuses are raised. When setting the hot water, these springs in the picture rise up (only the middle one stands still)
    Biawar Kaskada 2 Heater: Intermittent Heating, Fuse Blowing & Water Flow LED Diagnostics Biawar Kaskada 2 Heater: Intermittent Heating, Fuse Blowing & Water Flow LED Diagnostics Biawar Kaskada 2 Heater: Intermittent Heating, Fuse Blowing & Water Flow LED Diagnostics
  • #4 16587523
    jdubowski
    Help: 2511
    Rate: 2804
    Do you have a diagram inside the cover?
  • #5 16594760
    buffalo222
    Rate: 8
    I don't have a schematic. Could someone suggest me where to start looking for a problem?
    teskot
    Rest in Peace
    Help: 420
    Rate: 957
    From disconnecting the power supply, checking the heater resistance, switching on the thermostats.
  • #7 16601062
    buffalo222
    Rate: 8
    A friend who is currently taking care of our home said today that she set the heater to 3rd degree and very hot water in the shower is running. When she opened the cabin, the couple broke down. At that time, a friend observed that while hot water was set to the maximum flow, only 2 red LEDs lit on the heater. Before something broke down, boiling water flew in the 2nd stage and all 4 LEDs were on. I don't understand why. Level 3 heats the water, maybe not like boiling water, but it heats and for 2 flies very cold. Maybe you have something in mind that can be damaged?
  • #8 16742788
    buffalo222
    Rate: 8
    Some time has passed, unfortunately winter is coming, could use hot water. The situation is that I live in the countryside and it's hard for a "specialist" here. There was an electrician who did the measurements and all the electronics are fully functional, i.e. the 3rd phase is, heaters, thermostats OK, passages are correct everywhere. The electrician decided that something was happening that after unscrewing the water (taps or shower), these switches on the springs do not rise, i.e. they do not work, so the signal diodes do not turn on and the heating does not work. Regulated the spring tension unfortunately without effect. 100% of all these switches on the springs (there are 5 of them) work because by pressing each of them separately with a screwdriver they all tick and the next LEDs turn on and from what I felt at hand it began to heat which would be logical, the switch with the spring rises so the heating turns on . In any case, it came to the fact that the Lord does not know what next causes these switches not to turn on, i.e. they do not turn on and do not tick only manually.
    However, he solved the problem of the heater switching off automatically, i.e. the main "S" fuses from the heater in the switchboard were 16A and were to be 24A.
    You haven't arrived yet, what can you do with this heater?
    Pressure switch likely causing heater cutoff
    #9 16742960
    teskot
    Rest in Peace
    Help: 420
    Rate: 957
    Since the heaters and thermostats are functional and the micro switches on the power change knob are working, the reasons should be sought in the pressure switch assembly. First of all, check if there are correct flows, i.e. clean all strainers (aerators) in the taps, the same applies to any filters in the water system, if any. The pressure switch turns on all heaters only at a certain pressure difference between the water inlet and outlet. Of course, you can adjust the sensitivity of this switch, but you have to do it with a great deal of caution, because incorrect setting may cause the heater to not turn off after turning off the water and / or overheating the water with a minimum flow.
  • #10 16742983
    buffalo222
    Rate: 8
    All strainers in the taps were replaced less than a week ago, but to no avail. Apparently, there is a strainer between the heater and the water entrance to the house? After the strainer, there is probably something like a "membrane"
    Check and clean the inlet strainer and pressure switch
    #11 16743036
    teskot
    Rest in Peace
    Help: 420
    Rate: 957
    The membrane is just part of the pressure switch. And the filter (strainer) should be on the heater supply - check and clean. The pressure switch contacts should switch in turn as the tap is unscrewed (increasing the flow). If one of them remains open and the water temperature at the maximum flow is insufficient, it should be adjusted on it. Make adjustments with the power supply completely disconnected! If this does not help, replace the pressure switch.
  • #12 16745103
    buffalo222
    Rate: 8
    Thanks for the help. I couldn't count on an electrician or plumber here (no response to the phone), so I had to count on myself. Once a goat's death. Heater removed on the table and unfolded. The piston is cleaned and greased. The replaced membrane (it was full of holes) was cleaned, blown and greased. Folded and flashes, all LEDs work (4 on 4) heats richly without any interruptions. Regards
  • #13 18734103
    buffalo222
    Rate: 8
    Hello. I come back like a boomerang with a cascade theme. The previous cascade fell after short circuits on the heaters, at which a nearby electrician was buried. I bought a briefly used Cascade 2. Everything was fine (six months) until yesterday. The heater does not heat, I exclude a set of heaters because the pressure switches do not turn on and, despite the spout being ajar to the maximum, the warning lights do not turn on, which for peasant reason means that the heaters do not turn on and ultimately the water does not heat. Entrance strainer cleaned. Can I consider a damaged (perforated membrane)?
  • #14 18734121
    teskot
    Rest in Peace
    Help: 420
    Rate: 957
    Of course. Damage to the membrane will result in the heater not switching on.
  • #15 18741007
    buffalo222
    Rate: 8
    With thanks for your help. The diaphragm was damaged and the piston was dirty
  • #16 18751285
    Miraskortes
    Rate: 24
    Hello. I have the same problem (the stove does not fire) where is the membrane in question? How do I replace it?
The Biawar Kaskada 2 heater has been experiencing intermittent heating issues, with the main fuse blowing occasionally and the water not heating consistently. Users have reported that while the red LEDs indicate water flow, the water quickly turns cold after a brief heating period. Suggestions for troubleshooting include resetting the safety thermostat, checking the heater's resistance, and ensuring the pressure switch assembly is functioning correctly. Cleaning strainers and filters in the water system is also recommended, as blockages can prevent proper operation. A damaged membrane in the pressure switch has been identified as a common cause of failure, and users have successfully resolved issues by cleaning or replacing the membrane and ensuring all components are functioning properly.