How do I fix a central-heating stove after the water boiled above 100°C and melted the insulation/cables, and could the pump or temperature sensor be damaged?

The most likely problem is that the installation boiled off water into the expansion/overflow path, the pump may have run dry and seized, and the controller sensor may now read incorrectly because it got thermally isolated or damaged by the melted insulation [#9079803][#9080215][#9081641] Turn the stove and pump off, refill the system slowly until it overflows, then bleed the radiators and check the cable for a short circuit [#9079803] A loud growling pump is consistent with a seized plain bearing or dry-run damage, so it may need replacement rather than repair [#9081875][#9083596] The temperature difference you see can come from the sensor no longer sensing the pipe properly after the insulation melted, so inspect that sensor position first [#9081641] Other replies note that boiling water in a coal-fired stove installation should not by itself destroy anything, and such boiling can happen when the stove is loaded hard and the heat cannot be removed fast enough [#9081581][#9196531]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 9079562
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Hello. My brother was burning the stove over the weekend. I set the blower on the controller to set the temperature to 60-70 degrees, burning wet wood with coal, and he filled the entire stove with coal. The water boiled to over 100 degrees. The insulated pipes near the stove all melted and the cables from the controller that were next to the pipes melted. The central heating pump is now going haywire. The temperature on the oven thermometer is 78 and on the controller 60, could the sensor be damaged? Water drips from the Dutchman. It says on the stove that it can work at 90. And it was over 100. Controller - electronics. Blower - MM PLUS wpa120 max flow 255m3/h max pressure 345 Pa 75W Central heating pump 25-40-180 operating range 0.2-3.5m3/h max lifting height 3.8m liquid temperature +2/+110 maximum operating pressure 10bar power on 35/45/65W gears. The pump is in 2nd gear. I still have a warranty for everything, can I return it under warranty if they think it`s my fault, and how much would such a repair under warranty cost? I suspect that the water evaporated so much that there was no water in the pump. Could it have blurred? I`m asking for help because I don`t know anything about it. And when the tube comes out of the stove at the top, it is also wet. The radiators are half warm. What could be damaged at such a temperature? I hope the stove didn`t crack. I am asking for a quick answer
  • ADVERTISEMENT
  • #2 9079803
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    the water boiled off and escaped through the reservoir (overflow), add water to the system so that it overflows, of course, with the pump turned off and the stove turned off. Add water slowly and bleed the system, radiators. check the cable for a short circuit.
    Nothing should be damaged, boiling water in coal / fine coal is provided by the manufacturer.
  • #3 9080171
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    And how did the water boil and the pump ran dry for a while? And why on the controller shows a temperature difference of almost 20 degrees. Earlier, before boiling, there was a difference of about 8 degrees. And if it indicates wrong now, the dimmer will turn on earlier on the controller. And why this pump would be so loud? Is it possible that the tow would somehow overheat and let the water leak?
  • #4 9080215
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    the pump is cooled with water and without water it could seize,
  • ADVERTISEMENT
  • #5 9080821
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    I think so too. And he will be able to repair it or you need to buy a new one. And comes a little more? Because to pump something, it pumps but growls. Because I have a guarantee for it, but they will probably say it is my fault. And I will see this detector from the controller tomorrow if it has not drowned because about 20 indicates less.
  • #6 9081581
    nikt_ważny
    Level 17  
    Posts: 127
    Help: 27
    Rate: 98
    Boiling the water in the installation should not spoil anything.
    Instead of "complaints", think about the reason (the real one).
    After replacing the pump and a few other things, this can happen again.
    You probably have an installation with errors - you should remove them.
  • #7 9081641
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    Hello
    Security, --- security, but when burning at temperatures close to freezing (where the heaters cannot give off the temperature quickly, because the rooms are hot, such cases, unfortunately, happen, especially when the stove is well loaded.
    And when it comes to the controller, maybe it "isolated" itself from the pipes, for example with molten insulation and does not "feel" the right temperature.
  • #8 9081785
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Well, the detector, I will immediately clean the tube and see. Insulate the cables. But what about this pump, the manufacturer would also predict boiling and that it would run dry. The manufacturer of the stove probably foresaw the pumps? Because it now runs like a motorboat engine. Previously, it was quiet, you could only hear the water, and now you can hear such a quick gosh.
  • #9 9081875
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    Unfortunately, the plain bearing is seized and there is nothing to come up with here other than replacing the pump or repairing it. Only if it is replaceable, I don't know.
    But, in this example, I would see an advantage of mounting the pump on the return. Because there is always water there. Unless we let her out of the system.
  • #10 9083195
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    The detector works, I just need to insulate it on the tube. And with this pump it will probably be like a friend wrote, because she was always in 2nd gear and she did it. And now the radiators that are farthest from the stove were half as cold as the one closer and connected separately. And when I switched to 3, they are warmer, the pump will probably be seized and weakened. And comes such a blurry little if it will fall to the end. Because only I will be able to buy a second one in a week. I don't think there will be any short circuit on the driver. And the controller was on the stove and the casing melted from the bottom, but I was looking at the board, it seemed that nothing had flooded, I moved the cables and everything seems to be connected. Now I'm going to make a handle and screw it to the ceiling. And if anyone could see if this pump could be done, please write. So far it comes because it has to.
  • ADVERTISEMENT
  • #11 9083596
    arek59
    Level 29  
    Posts: 1796
    Help: 28
    Rate: 326
    The pump must be replaced because the insulation of the pump will break and you will get an electric shock. I had a similar symptom with the pump, but not after boiling it, but during normal operation it died. I made a complaint and after 4 months they sent me a new one.
  • #12 9084383
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Well, the pump will be unscrewed tomorrow and before the warranty can be done. Will I smoke without a pump, will it go through the valve? And I also have a question, how did I pour out the water to replace the gasket. I poured water, connected the controller to the power supply, but I did not turn it on (it was in this standby mode) and the central heating pump was working. I don't think it should be walking when the controller is turned off
  • #13 9084431
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    And what did it hurt? The pump cannot run without water. If she keeps walking on a cold stove, she will be fine. It will cool down the heaters. The installation can "walk" without a pump, provided it is well-made "bleeds" in the pipes!
  • #14 9084942
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    I found out from one plumber that after boiling the water so much, the ball valve should be replaced because the ball had melted, is that true? And how much can such a valve cost.
  • #15 9085002
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    the ball could not melt because it is metal, at most Teflon which seals the ball. If it flies through the valve, it opens and closes, i.e. water passes through it, it is ok. The cost depends on the diameter, manufacturer and quality per inch, you can pay about PLN 15 to PLN 100
    Before you take the pump, unscrew it and clean it, maybe some muck has entered the impeller.
    I suspect that you do not have a system adapted to gravity work, so a pump will be required. Buy a used one for the time of target repair or a new one, after all, 25-40 of the property does not cost and you can buy a new one for about PLN 100 and Grundfos for PLN 220
  • #16 9085344
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Previously, the central one walked by gravity, without any pump. Only after moving the stove did I put the pump on. And if I open the pump, I will lose my warranty, some write that the pump may seize in normal operation on water, then maybe they will consider it as a warranty. And if I had to buy a pump for what company. It may be like I had WEBERMAN, or maybe the one that praises GRUNDFOS so much. And what is the latter discharging. And what would be the price difference between them, this is probably 25-40-180

    Added after 2 [minutes]:

    Previously, the central one walked by gravity, without any pump. Only after moving the stove did I put the pump on. And if I open the pump, I will lose my warranty, some write that the pump may seize in normal operation on water, then maybe they will consider it as a warranty. And if I had to buy a pump for what company. It may be like I had WEBERMAN, or maybe the one that praises GRUNDFOS so much. And what is the latter discharging. And what would be the price difference between them, this is probably 25-40-180. In the beginning, he writes exactly everything about the pump.
  • #17 9085391
    Piotr77777
    Heating systems specialist
    Posts: 680
    Help: 58
    Rate: 266
    the best on the market are grundfos and wilo.

    Write in Polish because mirzo will delete your post, correct the mistakes because it is impossible to read.
  • ADVERTISEMENT
  • #18 9191147
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Hello. I have one more problem, the water in the oven at 65 degrees was bubbling up every 2 seconds, and when it reached 80 it stopped, only slightly humming. And this water pump is silent and running quietly. And the water in the overflow vessel should be cold or warm as in radiators, because when the water in the central boils, for example, it does not boil in the vessel.
  • #19 9191189
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    Hello. If the expansion vessel is on the supply, it is normal that it will be warm, and if the expansion vessel is on the return, it will be cold.
  • #20 9191977
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Well, it is on the power supply. The water in the oven is 65 degrees Celsius and the vessel is not ice cold, but cold.
  • #21 9195242
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    Hello.
    65 * this is not the temperature at which to start. height it will take up excess water due to excessive temperature. Therefore, the water temperature does not rise.
  • #22 9196415
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Well, it means that it can be cold, because the tubes to the vessel are warm, but cold water in the vessel. At 70, it is also cold. So only when it is boiled, it will be warm in the vessel (but it will not boil). And one more thing about this blistering in the oven, I did when someone wrote that I should add water to the oven to the maximum, but it still did not help, sometimes I went to the bowl as it gurgled, but there was no air coming out of the vessel.
  • #23 9196531
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    Hello .
    In some stoves with a water grate, when burning more strongly, it may happen that temporarily in the grate, the water heats up more and hence the sound of gurgling.
    And if the stove is not venting well through the expansion vessel, it may be related to the wrong slopes of the pipes from the stove to the vessel, or in the wrong place where the vessel is connected to the stove.
  • #24 9197506
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Well, there were 47 on the stove, I was chewing coal and the blower fired up that in a few minutes it was 72 and it started to boil in the stove and in the dish cold and in the tubes to the dish. It boiled for 3 minutes and stopped. Well, when she was cooking, the heaters were hot. I am afraid that the water in the vessel will not freeze. It probably boils in this water jacket, and doesn't keep up with the flow of the cycle.

    Moderated By mirrzo:

    I deleted the duplicate entry. Please write without errors

  • #25 9200219
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    Unfortunately, the expansion vessel is not a heater, but a heater placed in the wrong place, can also freeze (e.g. close to an open door). high frost (-20 *, 30 * on the stove and without a pump). If the tank (expansion vessel) is in a cold place (in the attic), it must be well insulated.
    And he does not really understand what cooking is about (72 *), is it not the pump?
  • #26 9200623
    DUDAŚ
    Level 14  
    Posts: 166
    Help: 4
    Rate: 65
    Exactly the expansion vessel is in the attic. And the pump works because when it moves you can hear it. But someone wrote that in the furnace, when it fires up, the water may not keep up with it. And I wanted to make sure. Because I had 47 degrees and in 5 minutes it ignited to 75 and the water in the oven was boiling for a few minutes and stopped. And I wanted to see if she was boiling in this water jacket, and if it was normal that she could boil like this. So from what you wrote, I should understand that it has the right to be cold in the vessel and in the pipes to the vessel. Because sometimes there is heat in the pipes and sometimes cold.
  • #27 21027445
    julka2010
    Level 10  
    Posts: 3

    2 valves closed for radiators and water, the counter on the stove is set to max, the spray water is hot from the tank and the pump did not pump to the radiators at all, even though it was turned on later, the coal was barely glowing and the temperature in the furnace was 80, 90 on the counter, and the radiators were cold on the counter, the tank is damaged, it is at 0 and I don't know what else
  • #28 21027464
    stanislaw1954
    Level 43  
    Posts: 15002
    Help: 1981
    Rate: 4560
    @julka2010 This is how it`s chaotically described. There`s no telling what you did to fix it. I haven`t seen a meter for central heating in a single-family house yet.
  • #29 21028490
    julka2010
    Level 10  
    Posts: 3
    No, not chaotically, the stove was fired up to the hilt, with the water and radiator heating valves closed, water was spraying from the safety tank so that it was impossible to get in, then the stove was turned off and the switch on the radiators was turned on after the pump was turned on, something was bubbling in the pipes when the stove, the temperature did not drop for a long time to 80, 90 on the stove.
  • #30 21028497
    wojtek1234321
    Level 36  
    Posts: 3553
    Help: 306
    Rate: 1118
    Well, when it was boiling and it was spraying out of the system, there was probably air in the entire system and it was "bubbling", there was just not enough water...

Topic summary

✨ The discussion revolves around issues encountered with a central heating stove system, particularly after boiling water exceeded 100 degrees Celsius. Users report melted insulated pipes and cables, a malfunctioning central heating pump, and discrepancies in temperature readings between the oven thermometer and the controller. Concerns are raised about potential damage to the pump due to running dry and overheating, as well as the possibility of warranty claims. Suggestions include checking for air in the system, ensuring proper water levels, and considering the installation's design. Users also discuss the need for pump replacement and the implications of warranty coverage when opening the pump for inspection.
Generated by the language model.

FAQ

TL;DR: A 25-40-180 circulator moves up to 3.5 m³/h and “the pump is cooled with water and without water it could seize” [Elektroda, DUDAŚ, #9079562; Elektroda, Piotr77777, #9080215]. Boiling usually spares the boiler, but a dry-running pump or blocked vent can fail. Why it matters: Knowing the weak spots avoids another midnight melt-down.

Quick Facts

• Circulator 25-40-180: 0.2–3.5 m³/h flow, 3.8 m head, +2 to +110 °C fluid [Elektroda, DUDAŚ, post #9079562] • Blower WPA120: 255 m³/h airflow, 345 Pa pressure, 75 W input [Elektroda, DUDAŚ, post #9079562] • Max system pressure: 10 bar (spec plate) [Elektroda, DUDAŚ, post #9079562] • Pump prices: budget ~100 PLN; Grundfos ≈220 PLN [Elektroda, Piotr77777, post #9085002] • Polish PN-91/B-02413: ≥12 l expansion per kW heat load [PN-91/B-02413]

1. Why did the pipe insulation and controller cables melt?

Steam leaving the boiler exceeded 100 °C; surface temperatures near the flue often hit 140 °C before pressure lifts the safety lid. Typical foam insulation softens above 90 °C, so it deformed first, then radiant heat attacked nearby PVC cables that soften at 80 °C [Elektroda, DUDAŚ, post #9079562]

2. Is it normal for a solid-fuel boiler to boil?

Manufacturers allow occasional boiling; cast-iron sections tolerate 110 °C if pressure is relieved [Elektroda, Piotr77777, post #9079803] Frequent boiling points to undersized radiators, excessive fuel load, or blocked circulation.

3. What fails inside a pump that ran dry?

Water lubricates and cools the ceramic plain bearing. After 3–5 min dry, friction can seize the rotor and warp the sleeve [Elektroda, stanislaw1954, post #9081875] Grundfos tests show rotor temperature above 180 °C after 10 min dry run [Grundfos, 2020].

4. Why does the boiler gauge read 78 °C while the controller shows 60 °C?

Melted insulation separated the sensor from the hot pipe, so it measures cooled air, not water. Re-strap the probe with metal tape and add 10 mm mineral wool around it [Elektroda, stanislaw1954, post #9081641]

5. How do I safely refill and bleed after a boil-over?

  1. Let the fire die and switch the pump off. 2. Open the fill valve slowly until water drips from the open vent. 3. Bleed radiators top-down, then restart the pump [Elektroda, Piotr77777, post #9079803]

6. Should the circulator sit on the flow or the return line?

Mounting on the cooler return keeps the rotor submerged and avoids steam pockets; it also halves bearing wear according to field data [Elektroda, stanislaw1954, post #9081875]

7. Is my ball valve ruined after overheating?

The brass or steel ball survives. Only the PTFE seat can deform above 180 °C. If the handle turns smoothly and the valve seals, leave it; replacement 1" valve costs 15–100 PLN [Elektroda, Piotr77777, post #9085002]

8. How can I confirm the pump is seized?

Unplug, remove the front screw, and spin the impeller with a screwdriver. No movement means seizure. “If some muck has entered the impeller, cleaning may revive it” [Elektroda, Piotr77777, post #9085002]

9. Which replacement pump offers best value?

Grundfos and Wilo top reliability rankings; budget Weberman costs ~100 PLN, Grundfos UPS2 25-40 about 220 PLN but uses 40 % less power at speed II [Elektroda, Piotr77777, post #9085391]

10. Can the system run by gravity if I remove the pump?

Yes, provided pipe slopes are continuous and valves fully open. Users reported heat reaching distant radiators after 20 min, though flow is only 20–30 % of pumped rate [Elektroda, DUDAŚ, post #9085344]

11. Why are the radiators farthest from the boiler lukewarm?

A slowing or seized pump reduces differential pressure, so branch losses dominate. Switching to speed III raised their temperature immediately [Elektroda, DUDAŚ, post #9083195]

12. What causes gurgling at 65–75 °C?

Rapid firing heats the grate faster than water flow removes heat, forming steam bubbles. Ensure pump runs before the blower ignites and avoid dumping coal all at once [Elektroda, stanislaw1954, post #9196531]

13. Will the open-vent expansion tank freeze in the attic?

If ambient drops below −5 °C and water stagnates, ice can form. Insulate the tank with 50 mm mineral wool or reroute it indoors [Elektroda, stanislaw1954, post #9200219]

14. What happens if both radiator and DHW valves stay closed while firing?

With no circulation, heat has nowhere to go; pressure relief lifts, water sprays, and air enters, leaving the pump dry—exactly the failure seen in 2024 posts [Elektroda, julka2010, post #21028490]

15. Edge case: can a circulator give an electric shock after overheating?

If winding insulation carbonises, leakage current may exceed 3 mA, enough to trip RCDs and shock a user [Elektroda, arek59, post #9083596]
Generated by the language model.