Nie, dziękuję Przekieruj mnie tam2P wrote:Cube 6A for the oven is asking to short circuit. I had such a case myself, but it was caused by changing the oven from gas to electric - nobody looked into the socket until one day the fuses blown - the cube was melted and the wires were shorted.
When it comes to extending cables, please look here: https://www.elektroda.pl/rtvforum/topic3356395.html
Hardly any electrician wants to do this, but it is a failure-free solution for the entire life of the installation.
The cables themselves should be checked in advance if they have at least 2.5 mm2. If it is 1.5 mm - to the oven itself, however, I encourage you to replace the wires. You can rather let go of the refrigerator and dishwasher, but I would verify the power of the dishwasher - a 1.5 mm cable should have a 10A fuse, i.e. up to 2.2 kW in practice.
jalop wrote:He did it poorly. It all depends on the total power of household appliances
Adula1 wrote:Amber
Adula1 wrote:supports
Adula1 wrote:sq
Adula1 wrote:I mean, he used a six terminal block, but its load capacity is 10 Amber the oven supports 3.6 kw, will it stand?
kSmuk wrote:Adula1 wrote:Amber
Ampere
Adula1 wrote:supports
gets
Adula1 wrote:sq
kW
Adula1 wrote:I mean, he used a six terminal block, but its load capacity is 10 Amber the oven supports 3.6 kw, will it stand?
No, he won't. The current carrying capacity of this strip should not be less than 16 A.
Adula1 wrote:what can happen if it stays like this?
Adula1 wrote:So I have a question because I used a 400V terminal block, six amps but a 10 amp load. Will this cube burn? Shouldn't there be a higher load capacity? Please reply.
andrzej lukaszewicz wrote:Adula1 wrote:So I have a question because I used a 400V terminal block, six amps but a 10 amp load. Will this cube burn? Shouldn't there be a higher load capacity? Please reply.
I wonder, where did you read the load capacity of this strip? And everyone thoughtlessly picked up the topic and are discussing.
Upload a photo, I will believe it, but I bet that the strip is 400V and has an acceptable cross-section of 6mm2, not a current of 6A.
The smallest strip, e.g. a 2.5mm2 simet, has a load capacity of 24A! And 6mm2 has a load capacity of 41A, so each of them is theoretically suitable for an oven, but I personally link in such strips always "overlap", i.e. two wires overlap each other so as to were always tightened by 2 screws. And this forces the use of larger listers 6, 10 or 16mm2, depending on the cross-section of the conductor.
andrzej lukaszewicz wrote:
The smallest strip, e.g. a 2.5mm2 simet, has a load capacity of 24A! And 6mm2 has a load capacity of 41A,
andrzej lukaszewicz wrote:I ask again: where did you read the 10A? If this is the "cube" of the simet I wrote about, then 6mm2 has a rated current of 41A.
https://www.elektrykasklep.pl/towar/21412108-...MIivDbtr712gIVUEkZCh2-2w0nEAQYASABEgL8JfD_BwE
Adula1 wrote:andrzej lukaszewicz wrote:I ask again: where did you read the 10A? If this is the simet "cube" I wrote about, then 6mm2 has a rated current of 41A.
https://www.elektrykasklep.pl/towar/21412108-...MIivDbtr712gIVUEkZCh2-2w0nEAQYASABEgL8JfD_BwE
This is not a Simet cube. I have the last one here, but on the back of the back it has 10A written on it.
Borutka wrote:Adula1 wrote:andrzej lukaszewicz wrote:I ask again: where did you read the 10A? If this is the simet "cube" I wrote about, then 6mm2 has a rated current of 41A.
https://www.elektrykasklep.pl/towar/21412108-...MIivDbtr712gIVUEkZCh2-2w0nEAQYASABEgL8JfD_BwE
This is not a Simet cube. I have the last one here, but on the back of the back it has 10A written on it.
It is not so much about the amps, but about the surface of the guaranteed contact of the connected wires and the fact that such a connection can "release" on the thread. The bigger cube has only a bigger opening and is made of the same material, so it won't significantly improve the surface. If the wires were twisted and insulated together, it could be without a cube at all.
I ignore other issues, i.e. the quality of the ankle itself and the possibility of damaging the cord during forceful tightening. If the wires were not twisted together, or at least threaded through the ankle for the passage, I would not sleep well.
Adula1 wrote:
If something in this cube is released, will the security work then?
andrzej lukaszewicz wrote:I ask again: where did you read the 10A? If this is the simet "cube" I wrote about, then 6mm2 has a rated current of 41A.
https://www.elektrykasklep.pl/towar/21412108-...MIivDbtr712gIVUEkZCh2-2w0nEAQYASABEgL8JfD_BwE
conrad9210 wrote:Hi.
You saved, and now you will be fixing tiles and improving installations. It's a pity you only ask after the fact. He will write from experience and observation that some electricians from the previous state system are not easy to find in today's standards and norms.
BTW. There is no need to discuss now, just put the installations correctly.
greetings
mawerix123 wrote:andrzej lukaszewicz wrote:I ask again: where did you read the 10A? If this is the simet "cube" I wrote about, then 6mm2 has a rated current of 41A.
https://www.elektrykasklep.pl/towar/21412108-...MIivDbtr712gIVUEkZCh2-2w0nEAQYASABEgL8JfD_BwE
I took the 10 'strip, 15A current from the anlux manufacturer, so 6' can have 10A
http://www.anlux.pl/a_zdp-10.0.html
![]()
andrzej lukaszewicz wrote:.These strips are useless, easily break the thread with light pressure, the screws fall out when they are completely unscrewed, the body deforms when the screw is slightly tightened.
And where is the meaning of 6mm2 cable connections, but with a permissible current of 16 or 10A?
And this connection is probably no longer available, under the tiles?
TL;DR: A 3.6 kW oven pulls about 15.7 A at 230 V (IEC 60038). “The current carrying capacity of this strip should not be less than 16 A” [Elektroda, kSmuk, post #17208424] Use connectors, cables and fuses rated ≥16 A or risk melting and arcs.
Why it matters: undersized joints hidden behind tiles can overheat, ignite and kill appliances before breakers react.
• 3.6 kW single-phase load ≈ 15.7 A (P / U = I) [IEC 60038]. • 2.5 mm² Cu conductor: 24 A admissible current in walls [PN-HD 60364-5-52]. • Screw terminal for ovens should carry ≥16 A [Elektroda, kSmuk, post #17208424] • Wago 221-412 lever block: 32 A, 4 mm² max [WAGO Datasheet, 2023]. • 1.5 mm² branch cable must be protected by 10 A fuse, ≤2.2 kW [Elektroda, 2P, post #17208188]