Can I run a 3.65 kW built-in oven together with a microwave and kettle on a single-phase 4 kW connection without tripping the fuse?
No — on a single-phase 4 kW connection, a 3.65 kW oven leaves very little margin, so you should not expect to use the oven, microwave and kettle at the same time without tripping protection [#15394896][#15394965] If the pre-meter fuse is 20A, that is about 4.6 kW continuous; 25A gives about 5.75 kW and is a more practical upgrade, while 32A was also suggested as even better if the installation and utility/building manager allow it [#15394965][#15395045] Choosing a weaker oven was considered a worse solution than increasing the connection power [#15395045] Before increasing the fuse/power, make sure the apartment wiring can safely handle the higher load, especially if parts of the installation are older aluminum [#15395174] The safest next step is to have an electrician check the installation on site and decide what can be changed [#15407066]
  • Can a 3.65 kW oven run with other appliances?
    #1 15394874
    krzysztof130390
    I have a question.
    I bought a flat in a block of flats with a single-phase installation and a connection power of 4kW.
    I want to buy a built-in oven with a capacity of approx. 3.65kW.
    My question is will the oven use all the power? I will be able to use the oven, microwave and kettle at the same time without crashes fuses?
    Here's something about "kicking" fuses: https://www.elektroda.pl/rtvforum/topic2979092.html //kozi966
  • #2 15394896
    elpapiotr
    Electrician specialist
    Help: 1015
    Rate: 3530
    There can be only one answer - no!
  • Upgrade the pre-meter fuse to 25A for 5.75kW capacity
    #3 15394965
    CYRUS2
    Help: 1241
    Rate: 3530
    krzysztof130390 wrote:
    I bought a flat in a block with a single-phase installation and a connection power of 4kW.
    The question is what is the pre-meter fuse.
    I suppose 20A t0 4.6kW. There is not much power left after the oven.
    The oven + kettle will handle it. But not much else.
    Apply for more power on 1-phase so that the pre-meter fuse is 25A.
    25A is 5750W, short-term 30A is 6900W.
    Changing the power allocation - it's just a replacement of the metering protection.
    Provided, of course, that your installation is in good condition.
  • #4 15395017
    krzysztof130390
    And such a power change is enough for me to use several. devices or maybe look for an oven with less power?
  • #5 15395045
  • #6 15395174
    Krzysztof Reszka
    Help: 609
    Rate: 1551
    I wouldn't be so quick to increase the value of the counter protection. Because the author of the topic may misunderstand that perhaps his aluminum installation in the apartment will withstand his new devices. Our topic author should provide data on his installation in the apartment.
  • #7 15397817
  • #8 15397884
    mawerix123
    Help: 482
    Rate: 951
    jaszto wrote:
    The oven can take full power only when heating up. To maintain the temperature during baking, the power will be reduced by at least half.
    Is it some kind of smart oven or heater itself :?: It's the same with the washing machine, if we pour hot water, it will also heat less or maybe heat it up with full power for a shorter time :?:
  • Pre-meter breaker rating determines actual available power
    #9 15397995
    lenio3
    1. the value of the connection power is basically not a measure of the real power that can be taken from the network (you have 4 kW in your papers and in order to continuously achieve this power value, you need to use pre-meter protection with a value of at least 20 A, which in fact results in the possibility of consumption of calculated mathematically a power of 4.6 kW, but in fact, for utility reasons, you probably have a protection installed with a value of 25 A (5750 kW).
    therefore, the value of the pre-meter protection, which can be used when calculating the available power, is important
    2. temporarily, it is possible to physically consume more power than it results from the mathematical product of the current value of the pre-meter protection and the voltage value, and it is possible to operate a microwave oven (700W), kettle (2200W) and dishwasher (2200W) powered from one circuit protected by a B16 overcurrent circuit breaker for a limited time that will not trip the overcurrent protection
  • Temporary overloads can exceed B16’s calculated power limit
    #10 15398205
  • #11 15406825
    krzysztof130390
    The case looks like this. The apartment has a copper installation with a cross-section of 1.5 cm. The wire from the fuses in the apartment to the fuses in the cage in the block is quite thick but aluminum. There are three b16 fuses in the house. Maybe add one and run the cable only under the oven?
  • #12 15407066
    elpapiotr
    Help: 1015
    Rate: 3530
    Or maybe finally call an electrician, let him decide on the spot?
The discussion revolves around the adequacy of a 4kW power allocation in a flat with a single-phase installation, particularly concerning the simultaneous use of a built-in oven (3.65kW), microwave, and kettle. Responses indicate that while the oven can draw full power during heating, it will reduce power consumption during operation. Users suggest that increasing the pre-meter fuse to 25A or 32A would allow for safer simultaneous use of multiple devices. Concerns about the existing electrical installation's capacity, particularly with aluminum wiring, are raised, emphasizing the need for an electrician's assessment. The consensus leans towards increasing power allocation rather than seeking lower-powered appliances.