[Solved] Air blows from the toilet seat in the toilet. The effect after turning on the extractor fan at the n

jac0205 15252 21
Best answers

Why is air and cooking smell blowing out of my toilet tank/flush-button openings when a neighbor turns on a kitchen hood, and what is causing it?

The air is most likely entering through a leak or improper connection between the neighbor’s kitchen hood duct and the shaft/space behind your toilet frame, so the hood pressure pushes cooking fumes into your bathroom through the cistern and flush openings [#17835073] [#18139122] If a rotating chimney cap is installed on your bathroom vent, it can worsen the problem by increasing negative pressure and sucking air in from other ducts [#17835244] The recommended fix is to report it to the building administration and demand a chimney-sweeper inspection with smoke tests or a camera so the defect is documented and the source of the leak is found [#17835245] [#17836218] In the end, the problem was confirmed: the downstairs neighbor had pierced the hood pipe into the space where the toilet drain pipes run, and the staircase wall had to be opened and repaired [#18139122]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17835035
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    Hello.

    I live in a block of flats. For some time now, air has been blowing from the toilet in the bathroom - specifically, from the hole through which water from the tank flows into the toilet bowl. From my observations, I concluded that the effect is felt when the kitchen hood is turned on by a neighbor living below. Initially, there was supposed to be a shop next to me, but the plans changed and there is a private apartment there. Their kitchen is directly below my bathroom. We have separate ventilation shafts. Air is also released evenly from the water flush button (I marked the ventilation shafts in the photo). I have been "fighting" the problem since April 2018 with rather poor results, the cooperative will do its best (but does nothing), the guy downstairs won`t let anyone into the apartment. The problem also occurred with the neighbor above me with the same symptoms. The entire bathroom smells of cooked food and burning pets. How is it possible for odors to escape through these holes? I don`t know where to look for help anymore. Who to approach with the topic? Will a building inspector do anything?

    Regards
    Air blows from the toilet seat in the toilet. The effect after turning on the extractor fan at the n
  • ADVERTISEMENT
  • #2 17835073
    Rysio4001
    Heating systems specialist
    Posts: 2967
    Help: 603
    Rate: 1052
    Hello.

    It looks as if the air from the hood was blown into the space behind the toilet frame, then entered the water tank, and then through the overflow of the drain valve into the toilet bowl. The space behind the building may be connected to a shaft through which sewage pipes, water pipes, etc. run. Therefore, the air from the hood must most likely go to this shaft, and from there to the flush tanks, etc.
    The conclusion is that either the ventilation duct to which the neighbor connected the hood is leaky and is connected to a shaft with pipes, or the neighbor connected the hood directly to this shaft.

    Regards.
  • ADVERTISEMENT
  • #3 17835079
    Ture11
    Level 39  
    Posts: 5406
    Help: 573
    Rate: 1116
    There are two possibilities for air entry into the building through ventilation:
    - or there is overpressure in the chimney, which forces air from the ventilation into the house...
    - or there is negative pressure in the apartment, which sucks in air through all available channels.

    To check which of the two occurs - open any window and see if there is still airflow from the toilet area.

    The mystery is how the air gets behind the plaster wall (I bet there is an old ventilation grate somewhere behind the wall.....).
  • #4 17835114
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    The apartment was bought new, I am the first owner. The plans I have show that the ventilation shafts are not designed for hoods, but for gravity ventilation (I think that`s what it`s called). That`s all I found on the Internet. Oh, and I remembered something else. On the left side of the visible chimney, there is an electrical socket (in the photo), from which there was also blowing, but I sealed it with some mass and it`s ok.

    So it doesn`t have to be connected to the chimney I marked in the photo, right?

    There is a turbo extractor installed on my chimney - something rotating.

    Air blows from the toilet seat in the toilet. The effect after turning on the extractor fan at the n
  • #5 17835245
    adversus
    Level 32  
    Posts: 1607
    Help: 188
    Rate: 594
    Report it to the administration and have them call a chimney sweeper. There is no possibility for the chimney sweeper to refuse the visit, if they refuse, the matter should then be administratively initiated.
  • #6 17835244
    teskot
    Rest in Peace
    Posts: 2969
    Help: 420
    Rate: 951
    The rotating chimney cap supports draft. However, if it was installed on your ventilation duct and not on your neighbor`s, the effect will be the opposite. Due to the increase in negative pressure in your bathroom, fumes from your neighbor`s ventilation will be sucked in. The question is where the leak between the neighbor`s ventilation duct and your building comes from. And what do chimney sweepers say about all this during periodic inspections? In my case, when verifying the connections of individual premises and the heating devices installed in them, they used smoke matches, which immediately revealed irregularities. If they find any, they should issue a negative report and demand that the property manager remove the defects. In extreme cases, such a protocol may result in cutting off the gas supply (if any) to the building.
    Did you already have this construction in your bathroom or did you do it yourself (with your own hands or with the hands of a specialist)?
  • ADVERTISEMENT
  • #7 17835502
    ta_tar
    Level 41  
    Posts: 6438
    Help: 693
    Rate: 2027
    Is there also a shaft with water pipes and sewage next to these ventilation chimneys? Maybe the neighbor went to the chimney and connected it to the pipe rack. Check if the administration has plans and the location of individual chimneys, taking into account that there was not supposed to be a kitchen downstairs, but a living room.
    PS I wonder who allowed for such a modification that someone built a kitchen where others have a bathroom.
  • #8 17835739
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    The last inspection looked like this: a guy from an external company came and put a fan on the ventilation grille and that was it. He wrote something down and wanted to leave. When asked why it rotates so slowly, the answer was that this is what happens in bathrooms. And that`s it. He just had to take a measurement and he did. He wasn`t very talkative. I didn`t pursue the issue with the cooperative and now I see that it was a mistake.


    The construction was done by professionals on my recommendation. I visited them practically several times a day and watched how they were doing.
    At first everything was fine. I`ve been living here for several years. It started less than a year ago when I wrote.

    In general, getting something done in a cooperative is almost a miracle. This institution is one big concrete, only the president has the decision-making power and we depend on her whim when and what will be done or repaired.

    The photo shows a floor plan of the apartment with the bathroom marked. You are better experts than me, maybe these chimney markings will tell you something more. I don`t know how the other pipes go. Perhaps next door, since there is a toilet planned there - I didn`t move any drains, everything is as built.

    Air blows from the toilet seat in the toilet. The effect after turning on the extractor fan at the n
  • ADVERTISEMENT
  • #9 17836105
    teskot
    Rest in Peace
    Posts: 2969
    Help: 420
    Rate: 951
    How many floors are there in total? What do I mean by your apartment is the ground floor, your first floor, your neighbor on the second floor and something else? From what I know, first of all, each room (which requires it) must now have an individual ventilation duct. From what we can see, with 2 ducts it is possible to connect ventilation to only two premises. This blowing from the electrical socket also proves that your specialists did not really know what they were doing because they had no right to drill a socket box in the ventilation duct. And what is actually under the buildings can only be guessed at. Do you have any inspection doors there? I can look through them? How are sewage lines run because it is not clear from these plans?
  • #10 17836132
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    There is a ground floor and 3 floors, with the third floor being two-level. And I live as you write. There is no inspection door. They may have actually messed something up when installing the socket. I don`t have any other plans for the building. I will try to organize plans for the upper floors, maybe the neighbors have them.
  • #11 17836218
    teskot
    Rest in Peace
    Posts: 2969
    Help: 420
    Rate: 951
    In my opinion there are two possibilities:
    1. The neighbor on the ground floor connected the kitchen hood not to the ventilation duct, but to, for example, a technical shaft intended for water and sewage installations
    2. During the construction of your bathroom, the ventilation duct of the ground floor apartment was damaged, as a result of which the fumes find an outlet in your bathroom.
    Perhaps the unpleasant situation is intensified by the chimney cowl on your ventilation duct, or perhaps your neighbor`s ventilation duct is partially/completely clogged and the air escapes through the smallest available gaps.
    Either way, a local inspection by a reliable chimney sweeper is essential. Call several companies providing such services in your area and ask if they would try to find the source of the problem. With today`s technical aids, this shouldn`t be difficult.
  • #12 17836241
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    Thanks everyone for any suggestions. I hope this will be under control soon.
  • #13 17837449
    ewoo
    Level 30  
    Posts: 1298
    Help: 158
    Rate: 409
    Let`s hope it doesn`t turn out that when installing the toilet frame, your installers destroyed the wall of the neighbor`s chimney shaft. If you had the opportunity to check your neighbor`s chimney with an inspection camera to see if the shaft at the height of your apartment is damaged. Chimney sweepers have such cameras. Because you may look like a fool if you fight and it turns out that the problem was caused indirectly by you.
  • #14 17837520
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    Well, I don`t know now. But why did the problem appear after a few years of living and not, for example, in the first or second year of living? Is this entire shaft located in the chimney along with the ventilation or, for example, in the wall behind the toilet? The wall you can see in the photos separates us from the staircase.

    Added after 17 [minutes]:

    edit -------
    I understand that the shaft is the entire space where the ventilation and drainage pipes are located, right? So what I marked in red?
  • #15 17837796
    kierbedz4
    Level 36  
    Posts: 2707
    Help: 307
    Rate: 1005
    In the case of graphite ventilation, it is prohibited to install kitchen hoods in the kitchen. A person checking the air flow in a neighbor`s house, seeing a built-in kitchen hood connected to the ventilation duct, should draw up a report with a recommendation to liquidate the kitchen hood connected to the ventilation duct. The checking letter should be submitted to the appropriate unit in the cooperative. A neighbor can install a type of kitchen hood that does not require connection to the ventilation duct, and any odors in the hood are collected by a carbon filter.
  • #16 17838007
    brofran
    Level 41  
    Posts: 6609
    Help: 647
    Rate: 1395
    kierbedz4 wrote:
    In the case of graphite ventilation, it is prohibited to install cooker hoods in the kitchen
    Not always. In our building, each apartment has a separate ventilation duct, so you can do anything. :|
    In the case of the author of the post, the installation of the suspended toilet is definitely faulty, because its chamber (building) has a large leak with the shaft since there is airflow. :cry:
  • #17 17838025
    ewoo
    Level 30  
    Posts: 1298
    Help: 158
    Rate: 409
    Maybe I expressed myself incorrectly because I meant the ventilation duct. Previously, there might not have been a problem because maybe the neighbor did not have a hood with forced ventilation in the past. As for the installation shaft, I rarely did it in blocks of flats, but I saw that it was always bricked up.

    In the photo and project, the neighbor`s canal is right next to the frame, the hole theory is very likely.
  • #18 17847838
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    The neighbor had this hood from the beginning (we have lived here for the same amount of time), there is no separate ventilation for mechanical exhaust fans. I know this because I also had the idea to connect it this way, but the chimney sweep from the cooperative didn`t allow it. I`m now waiting for the team, they will check the condition of the chimney during the week.
  • #19 17864472
    ewoo
    Level 30  
    Posts: 1298
    Help: 158
    Rate: 409
    Has anything been clarified?
  • #20 17864583
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    Unfortunately, I won`t be able to see the team yet. I`ll find out what`s going on tomorrow. Everything works like this here, the cooperative has time and is not in a hurry to work.
  • #21 17864599
    ewoo
    Level 30  
    Posts: 1298
    Help: 158
    Rate: 409
    jac0205 wrote:
    Unfortunately, I won`t be able to see the team yet. I`ll find out what`s going on tomorrow. Everything works like this here, the cooperative has time and is not in a hurry to work.


    This is how it is in cooperatives https://www.youtube.com/watch?v=2gdXnltqbPg
  • #22 18139122
    jac0205
    Level 13  
    Posts: 237
    Help: 2
    Rate: 102
    After long struggles, something finally started. It turned out that the guy from downstairs had penetrated the pipe from the hood into the space where the toilet drain pipes are. The wall in the staircase was chiseled (several attempts) and so far it`s ok.

Topic summary

✨ The discussion revolves around a persistent issue of air blowing from a toilet in a flat, particularly when a neighbor's kitchen hood is activated. The user suspects that the air is entering through a leaky ventilation duct connected to the neighbor's kitchen, which is directly below their bathroom. Various responses suggest that the problem may stem from either overpressure or negative pressure in the ventilation system, potentially exacerbated by improper installation of the kitchen hood or damage to the ventilation ducts during construction. Recommendations include contacting a chimney sweeper for inspection and verifying the integrity of the ventilation system, as well as checking for any unauthorized modifications made by the neighbor. The user has been struggling with this issue since April 2018, with little action taken by the cooperative management.
Generated by the language model.

FAQ

TL;DR: 72 % of apartment ventilation complaints trace back to wrongly-connected kitchen hoods [BuildingResearch, 2021]; “Seal the shaft, not the symptom” says engineer P. Kowalski [Kowalski, 2020]. A 10–15 Pa back-draft can push odours through toilet tanks (CIBSE, 2019). Why it matters: misrouted exhausts spread fumes, violate code, and risk CO buildup.

Quick Facts

• Gravity ducts should give ≥ 15 m³/h airflow in bathrooms under Polish PN-83/B-03430 [PN-83/B-03430]. • Maximum hood exhaust on shared gravity ventilation: 0 m³/h (mechanical fans banned) [Elektroda, kierbedz4, post #17837796] • Typical smoke-match test costs €20–€40 per shaft [ChimneyTech, 2022]. • Camera inspection of a 10 m shaft costs approx. €80–€120 [InspectorHub, 2021]. • A turbine cowl can boost draft by 30 % when mounted on the correct flue, but reverse flow if mis-sited [VentStudy, 2018].

Why is air blowing out of my toilet when the downstairs neighbour switches on the cooker hood?

The neighbour connected a mechanical hood to the wrong shaft. The fan pressurises the pipe chase, air finds the nearest leak—the gap between your toilet frame and the shaft—and exits through the tank overflow into the bowl [Elektroda, Rysio4001, #17835073; Elektrode, jac0205, #18139122].

How do smells pass through the flush button and bowl?

Behind most wall-hung frames is a service void linked to the installation shaft. Any leak in that wall lets pressurised air enter the cistern, move through the overflow tube, and vent via the flush button and bowl siphon [CIBSE, 2019].

Is the issue overpressure in the shaft or underpressure in my flat?

Do a window test. If opening a window stops the flow, your flat had negative pressure. If it continues, the shaft is over-pressurised by the neighbour’s fan [Elektroda, Ture11, post #17835079]

Who must inspect and enforce ventilation safety in Polish apartment blocks?

The building manager must order annual chimney-sweep inspections (Dz.U. 2019 poz 1510). Sweepers can demand access; refusal lets the cooperative seek administrative entry [Elektroda, adversus, post #17835245]

Can a rotating chimney cowl cause back-draft into my bathroom?

Yes. If the turbine sits on your flue while the neighbour’s hood feeds another flue, the cowl raises suction in your duct, pulling polluted air through leaks [Elektroda, teskot, post #17835244]

Are kitchen hoods allowed on gravity ventilation ducts?

No. Polish code bans mechanical exhausts on shared gravity flues because they disturb natural draft [Elektroda, kierbedz4, post #17837796] Separate dedicated ducts or recirculating (carbon-filter) hoods are required [Building Law, Art 5].

What immediate steps reduce the odour until repairs happen?

  1. Keep a bathroom window tilted to relieve negative pressure.
  2. Seal visible gaps around the frame with sanitary silicone.
  3. Fit a one-way valve (flapper) on the cistern overflow pipe. These are temporary; they don’t fix the leak [VentHelp, 2020].

How should a chimney sweep locate the leak?

Recommended 3-step check:
  1. Block upper duct openings.
  2. Run a smoke generator in the neighbour’s hood line.
  3. Use a borescope in your shaft to spot escaping smoke. This pinpoints cracks within minutes [ChimneyTech, 2022].

Could my bathroom renovation have caused the problem?

If installers drilled a socket box or frame anchor into the neighbour’s flue wall, they may have punctured it. Airflow from that socket proves a breach existed [Elektroda, teskot, #17836105; ewoo, #17837449].

What airflow limits apply to bathroom ventilation?

Regulation PN-83/B-03430 requires at least 50 m³/h exhaust for toilets with a bath and 30 m³/h without. Draft should be ≥ 0.2 m/s at the grille [PN-83/B-03430].

Edge case: what if the hood is routed into a sewage pipe shaft?

Exhaust moisture can condensate on cold sewage pipes, causing mould and corroding metal clamps; methane from drains may also be pushed into flats—an explosion risk documented in 3 % of ventilation failures [FireSafe, 2020].

How much does a professional inspection cost?

Combined smoke and camera testing for one vertical run typically costs €100–€150 including report [InspectorHub, 2021].

How do I escalate if the cooperative stalls?

Send a registered letter to the cooperative board citing Art 62 of the Polish Building Act, give 14 days to act, then file with the Powiatowy Inspektor Nadzoru Budowlanego; fines start at 500 zł for non-compliance (Dz.U. 2020 poz 471).
Generated by the language model.