logo elektroda
logo elektroda
X
logo elektroda

Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions

zgorany 25746 13
Best answers LABEL_AI_GENERATED

How can I stop reverse draft and cold air from the kitchen and toilet ventilation grilles in my 62 m² apartment?

Reduce and balance the ventilation, because the apartment likely has too much total airflow and that is cooling the rooms. One reply estimates 4 grilles plus the hood at about 280 m³/h and recommends cutting the system down to around 100 m³/h total, using adjustable grilles and a hood backflow valve; the supply diffusers should be sized to match the needed intake, for example about 4×20 m³/h [#16952850] Do not choke the diffusers too aggressively, because limiting the inflow too much can cause reverse flow in another riser; instead, balance the grilles and let the ventilation stabilize [#16953457] In the kitchen, keep the grille adjustable and open it only when the hood is running, and if needed provide make-up air by briefly opening the apartment/corridor door or unsealing the entrance door slightly on the top floor [#16954288] If one chimney still back-drafts, a rotary chimney cowl/turbovent was reported to solve the problem in the bathroom [#16964297]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 16951550
    zgorany
    Level 10  
    Posts: 30
    Rate: 11
    I warmly welcome,
    I moved to a 3-room flat + bathroom + wc. Area 62 m2. The apartment has separate ventilation ducts, 3rd floor, in a 3-story block. The kitchen has two ventilation grilles next to each other. One hood is connected to one. There is one grid in the toilet next to the kitchen. The bathroom has two grilles. In the kitchen and in the large room, the windows are wooden with cut out gaskets at the top, and probably even in some places sealing with gaskets (approx. 15 years). In the other two rooms, plastic windows tight. Some time ago I noticed the phenomenon of reverse thrust in the kitchen and toilet. I studied internet resources and installed 1 pressure diffuser for each room and kitchen. The situation has not improved. Only opening the window stabilized the situation. I decided to experiment with covering the grilles. With foil covering one grille in the bathroom (where the draft is correct) and in the toilet. The kitchen stopped blowing, but somehow it did not pull out too. I continued reading and an employed chimney sweep lengthened the chimneys from one grille in the kitchen (the one without the eaves) and from the toilet. In wc the situation stabilized and the sequence is. In the kitchen, however, the wind blew even a little less. I covered one box in the bathroom again. To check if the draft in the kitchen returned, I accidentally touched the ventilation duct right next to the grille. It's very cold. In addition, I felt cold near the engine in the roof of the hood. As I mentioned, the kitchen is adjacent to the toilet and the wall with ventilation chimneys is very cold, the temperature in the morning is 17 degrees in the toilet. Very unpleasant feeling. Humidity in the apartment at 35 -45% is also normal. But for the apartment to reach 20 degrees, all radiators must be turned on for a minimum of 3.5, and it cools down quickly. My guess is that through the diffusers, so I set them to trial and error to the optimal position, but still feel the cold air above my head. I have a question what to do with this hood, which cools my kitchen and toilet. Can also extend the ventilation chimney? Bills for heating for a month are about PLN 230, and the average temperature is less than 20.3 degrees. The massacre, and the frosts so far have been -5 degrees. In a month the family will grow and I need to ensure optimal conditions for the child. And it seems to me that the ideas are over. Yes, I can heat and tilt the window, but instead of pampers I will spend a lot of money on heating, and eventually the fungus will come out, or some bacteria on the ever-cold wall ? I am asking for some constructive suggestions. Thank you in advance.
  • ADVERTISEMENT
  • #2 16952199
    p.obelix
    Refrigeration equipment specialist
    Posts: 1997
    Help: 215
    Rate: 563
    If he was a chimney sweep, why did he not take measurements of the lift? At that time, you would know if there is too much of it and it should be suppressed or not enough, and you panic that your windows are blowing. Now we can take or measure ventilation.
  • ADVERTISEMENT
  • #3 16952850
    Wlodek22
    Level 31  
    Posts: 1790
    Help: 78
    Rate: 526
    4 grilles + hood, together around 280m3 / h is too much. The humidity level also confirms this. Two in the bathroom, probably one for the boiler. If there is no boiler, stop it. On others. Fit the adjustable grilles. On 3 sheets, you need to limit the flow to around 100m3 / h, i.e. 30m3 / h. The hood must be with a flow stop valve when turned off. The diffusers must have a total capacity of 100m3 / h, e.g. 4 windows of 20m3 / h.
  • ADVERTISEMENT
  • #4 16953354
    zgorany
    Level 10  
    Posts: 30
    Rate: 11
    p.obelix wrote:
    If he was a chimney sweep, why did he not take measurements of the lift? At that time, you would know if there is too much of it and it should be suppressed or not enough, and you panic that your windows are blowing. Now we can take or measure ventilation.


    He is such a chimney sweep ... He stated that he is similar in winter and clogs the foil with foil, I did not even want to enter into the discussion.

    Added after 9 [minutes]:

    Wlodek22 wrote:
    4 grilles + hood, together around 280m3 / h is too much. The humidity level also confirms this. Two in the bathroom, probably one for the boiler. If there is no boiler, stop it. On others. Fit the adjustable grilles. On 3 sheets, you need to limit the flow to around 100m3 / h, i.e. 30m3 / h. The hood must be with a flow stop valve when turned off. The diffusers must have a total capacity of 100m3 / h, e.g. 4 windows of 20m3 / h.


    The block from 2002 boilers was not planned. In the kitchen I put on an adjustable grille as in the picture. In the bathroom all the time one grille is covered. Mounted diffusers are Ventair II Trdn with an air flow of 25m3 / h. The hood is Faber Synthesis x 90, I was looking for specifications in the network and I think it should have a blocking valve, but I'm not sure. I screwed the diffusers to a minimum gap, because they cool the room very much. I wonder to completely blind the eaves grille from the inside, because I do not use too often only in cooking, but then I still have to open the window. Also, I think I would just open the window while cooking.
    Attachments:
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions DB18FC5B-6306-4A34-97CF-763B55B435EE.jpeg (2.06 MB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions 6429D06B-E32E-4702-A461-2096FADAEB38.jpeg (1.85 MB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions F2DC2453-86BD-45C9-9596-1522F1963402.jpeg (653.11 KB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions 12F5F47F-B800-485B-9944-13168F2C39A5.jpeg (1.78 MB) You must be logged in to download this attachment.
  • #5 16953457
    Wlodek22
    Level 31  
    Posts: 1790
    Help: 78
    Rate: 526
    You must understand how gravitational ventilation works.
    It will always be accompanied by the phenomenon of "cooling" the rooms. You have to come to terms with it and simply adjust it.
    If you limit the inflow of air, on the other hand, already with two ventilation risers, vertical back draft with weaker draft may occur. So limit and align the flows on the sheets and do not limit the diffusers.
  • ADVERTISEMENT
  • #6 16953721
    zgorany
    Level 10  
    Posts: 30
    Rate: 11
    In your opinion, which grids should I restrict in the flow? Hood and toilet?

    I blocked the eaves duct. In the toilet I covered half the grille. In the bathroom, as you said, I blocked one box. Diffusers open for max. Blows from them sharply ...
  • #7 16954288
    BoguSO
    Level 12  
    Posts: 26
    Help: 8
    Rate: 13
    I agree with the opinion of Włodek22. Too high efficiency of ventilation ducts, it threatens to reverse the flow in at least one and suck air from the roof, and there you can do everything. Personally, I saw smoke in the bathroom and the rock sensor in the kitchen that works. My supplement to the suggestions given above for limiting the ventilation capacity is:
    1 you live on the top floor - unseal the door to the apartment you will provide warm ventilation air.
    2. as the drafts in the ventilation ducts reverse, open the eye briefly or better, corridor doors.
    3. in the kitchen, install an adjustable grille and open it only when the hood is working.
  • #8 16954453
    zgorany
    Level 10  
    Posts: 30
    Rate: 11
    The door can't break. I covered the boxes as in the pictures. The string may not be spectacular, but it is. Diffusers in the kitchen and in the large room (one side of the apartment) blows gently. However, in the bedroom and the smaller room (the other side of the apartment) the diffusers from the bathroom grille blow as if more air was still needed to be replaced, despite the fact that the bathroom grille was 3/4 grille. Please look at the pictures. According to me, with such a reduction in the area of grates, the supply of air to the apartment should be stabilized, and it looks like it would be best if I was in the bathroom probably sealed the grille, and I can not do it. I don't know what else to do ...
    Attachments:
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions 64CB4740-7621-479F-8E18-818A8F914ABE.jpeg (564.97 KB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions DCD227D8-0684-4448-BDBA-18D9A12AA401.jpeg (1.94 MB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions B6BA9A30-2F8E-42F0-BD1E-116403FB2CB6.jpeg (1.87 MB) You must be logged in to download this attachment.
  • #9 16954470
    p.obelix
    Refrigeration equipment specialist
    Posts: 1997
    Help: 215
    Rate: 563
    And why can't you break the front door?
  • #10 16954497
    zgorany
    Level 10  
    Posts: 30
    Rate: 11
    And how should I do it? Cut out the gasket?
  • #11 16954501
    p.obelix
    Refrigeration equipment specialist
    Posts: 1997
    Help: 215
    Rate: 563
    You can probably take it out to see what's going on.
  • #12 16954539
    Wlodek22
    Level 31  
    Posts: 1790
    Help: 78
    Rate: 526
    zgorany wrote:
    The door can't break. I covered the boxes as in the pictures. The string may not be spectacular, but it is. Diffusers in the kitchen and in the large room (one side of the apartment) blows gently. However, in the bedroom and the smaller room (the other side of the apartment) the diffusers from the bathroom grille blow as if more air was still needed to be replaced, despite the fact that the bathroom grille was 3/4 grille.

    Maybe the kitchen door and the large room are suppressed by the internal door.
    The second thing is that in the kitchen there was reverse thrust, then the riser is cooled down and it takes time to heat it. Similarly, with a reduction in cross-section, the plummet must "cool down" so that the vacuum decreases.
  • #13 16954601
    zgorany
    Level 10  
    Posts: 30
    Rate: 11
    The door in the apartment is locked only in the bathroom. Will these sealed grilles not cause insufficient ventilation in the apartment?

    I changed the grilles in the bathroom, set the flow in the kitchen, bathroom, toilet. I have inserted a backflow preventer valve into the hood duct. The entrance door in my opinion is very tight, I did not notice the possibility to remove the seal, unfortunately. Still, in my opinion, too little air gets into the apartment. This is demonstrated by the flows on the diffusers. Windows evaporate after bathing at the bottom seals.

    Unfortunately, the wall in which the ventilation chimneys run is icy 16 degrees, which translates into temp in the toilet. Gentlemen, what else can you do?
    Attachments:
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions 1550366B-F956-473C-A764-1DC488F3A426.jpeg (1.87 MB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions E21BC600-D3CD-486F-8B84-C9C2233AD069.jpeg (572.62 KB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions 04814677-7EA7-4E88-AB2D-CC8F8D8ADAED.jpeg (564.97 KB) You must be logged in to download this attachment.
    • Reverse Thrust Issue in 62m2 Apartment: Ventilation Grilles, Pressure Diffusers & Window Solutions A49F9F64-AB8C-4BF3-91D4-A8DFDAD575C5.jpeg (1.82 MB) You must be logged in to download this attachment.
  • #14 16964297
    zlotaraczka.
    Level 7  
    Posts: 132
    Rate: 63
    What I read here is according to this, I have no problem with ventilation in principle.
    Air supplied with diffusers should be sufficient as long as they are properly selected for the size of the rooms. The sealing of the grilles should also cause alignment of the draft in other grilles.
    Not an interesting situation.
    One thing I would advise is the installation of rotary chimney cowls, turbovent. For me, this solved the problem in the bathroom because there was a reverse thrust.
    As for heating, I have 47 sqm, 2 rooms. Heaters unscrewed to max 3.5 at a temperature of about -7 * outside and in the apartment 23.5 *. At night we screw to position 3 and in the morning it is around 22.6 *.
    In my kitchenette, I have 2 tiles next to each other. One sealed because I have no eaves, the other a full flight and sometimes it blows into the apartment a little. But this happens as the wind blows from the wrong side for the chimney. Unfortunately, the administration urges to install diffusers because they will not put on the second base. Explaining this lack of need because it could cause that in the bathroom, for example, there could be a reverse thrust or vice versa.

    On the other hand ... how to check that the capacity in the X box is e.g. 20m3 / h, and in the Y box is e.g. 100m3 / h?

    I check the string by putting a plastic breakfast bag on the grid. If it is attracted to the plaid, the string is. In addition, I have a hygrometer and observe the humidity in the apartment. this one is just low for me, from 20 to 40 to 50% max.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around a reverse thrust issue in a 62m2 apartment with separate ventilation ducts. The user has installed pressure diffusers in each room and kitchen but has not seen improvement, only stabilization when windows are opened. Various suggestions are made, including adjusting the flow of ventilation grilles, using adjustable grilles, and ensuring the kitchen hood has a flow stop valve. Concerns about excessive ventilation leading to reverse airflow are raised, with recommendations to limit airflow in certain ducts and to consider the installation of rotary chimney cowls to mitigate reverse thrust. The user also notes issues with humidity and temperature in the apartment, indicating a need for better air circulation and heating management.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: In a 62 m² flat, “4 grilles + hood ≈ 280 m³/h is too much,” so balance grilles, add a hood backdraft valve, and size window diffusers to ~100 m³/h total. [Elektroda, Wlodek22, post #16952850]

Why it matters: This FAQ helps apartment owners fix reverse thrust, cold drafts, and humidity issues in gravity ventilation systems.

Quick Facts

How do I fix reverse thrust in my kitchen or toilet?

Reduce total exhaust, not the inlets. Set adjustable grilles to about 30 m³/h each and keep diffusers open. Add a backdraft valve to the hood duct. If two bathroom grilles exist without a boiler, cap one. Recheck after the cold riser warms. [Elektroda, Wlodek22, post #16952850]

What is gravity (natural) ventilation, and why does it feel cold?

Gravity ventilation relies on warm indoor air rising in vertical shafts. Colder makeup air enters through diffusers, so rooms feel cooler. As one expert notes, “You must understand how gravitational ventilation works” and accept some cooling, then adjust flows. [Elektroda, Wlodek22, post #16953457]

What airflow should I aim for in a 3-room, 62 m² apartment?

Aim for roughly 100 m³/h total extract. Split about 30 m³/h per active grille across kitchen, bath, and WC. Keep window diffusers sized to supply that same total. This alignment limits backflow while maintaining air quality. [Elektroda, Wlodek22, post #16952850]

Do I need a backdraft (non-return) valve on the kitchen hood?

Yes. A flow-stop/backdraft valve prevents cold air ingress and reverse thrust when the hood is off. Many hoods support this, and retrofitting an inline damper is straightforward. It’s a first-line fix for cold ducts near the hood. [Elektroda, Wlodek22, post #16952850]

Should I throttle the diffusers or the exhaust grilles?

Do not choke diffusers; ensure enough fresh air supply. Throttle and align the exhaust grilles instead to hit the target extract rate. Keep diffusers totaling about 100 m³/h so supply matches extraction. [Elektroda, Wlodek22, post #16953457]

I have two bathroom grilles but no boiler. What should I do?

If a bathroom grille was dedicated to a boiler that doesn’t exist, cap that opening. Then balance the remaining grilles to about 30 m³/h each. This reduces over-extraction and stabilizes draft. [Elektroda, Wlodek22, post #16952850]

Top-floor flat: can the apartment door help air supply?

Yes. Slightly unsealing the entrance door can provide warm corridor air as make-up air. During a temporary reverse, briefly open the door or a transom to restore correct draft. [Elektroda, BoguSO, post #16954288]

How can I quickly test if the ventilation is pulling the right way?

Use a light plastic bag or tissue at the grille. If it’s drawn toward the grille, there’s extract. If it blows out, you have a reverse. Track humidity as a supporting indicator. [Elektroda, zlotaraczka., post #16964297]

Why are the walls around the shafts icy, and does it affect draft?

A past reverse cools the riser and adjacent wall. After you reduce cross-sections, the column must re-warm before draft stabilizes. Expect a lag before performance improves. [Elektroda, Wlodek22, post #16954539]

Could over-ventilation raise my heating bill and dry the air?

Yes. Excess extract (e.g., 280 m³/h) drives low indoor humidity and higher heating demand. One case showed ~PLN 230/month with <20.3°C average, indicating over-ventilation. [Elektroda, zgorany, post #16951550]

Is installing a rotary chimney cowl (turbovent) a good idea?

It can help where wind-driven reverse occurs. Users report resolving bathroom backflow with a rotary cowl. Treat it as a complement to balancing, not a substitute. [Elektroda, zlotaraczka., post #16964297]

What should I do during a sudden reverse flow event?

  1. Open the corridor door briefly to admit make-up air.
  2. Ensure the hood’s backdraft valve is shut.
  3. Verify bathroom and WC grilles are balanced near 30 m³/h. [Elektroda, BoguSO, post #16954288]

Edge case: Can reverse flow pull dangerous air from the roof?

Yes. A reversed duct can draw smoke or contaminants from the roof. One report noted smoke in the bathroom and a kitchen CO alarm activation. Treat reversals promptly. [Elektroda, BoguSO, post #16954288]

My windows fog after showers—do I need more supply or less exhaust?

Balance first. Keep diffusers open and set bath/WC grilles near 30 m³/h. If fogging persists, confirm the hood has a backdraft valve and that no unused bathroom grille is left open. [Elektroda, Wlodek22, post #16952850]

Can I just close the kitchen grille and open a window while cooking?

If you block a grille, you must provide equivalent make-up air while the hood runs. Opening a window works, but balance the system for normal operation to avoid chronic reversals. [Elektroda, zgorany, post #16953354]

Why does humidity stay low even after adding diffusers?

If total extract remains high, humidity stays low despite diffusers. Match diffuser capacity to about 100 m³/h and limit each exhaust grille to ~30 m³/h to reduce over-drying. [Elektroda, Wlodek22, post #16952850]