Compatibility of 1.5 kg/h Gas Reducer with 4 kg/h Burner for Heating Roofing Felt
MM2X 45465 29
Will a 1.5 kg/h gas regulator handle a roofing-felt burner that consumes 4 kg/h?
It will work, but a 1.5 kg/h regulator is too small for a burner that needs 4 kg/h, so you will not get full power; the proper regulator capacity should be 4000 g/h [#17973829] A propane-butane reducer is still recommended on an 11 kg cylinder for pressure reduction and safety, especially if the hose is damaged [#17975370] Some replies note that roofing burners often screw directly onto the cylinder and the torch head has its own air intake, so flashback into the hose is not considered the usual problem [#17975102][#17975734]
  • #1 17973000
    MM2X
    Rate: 619
    Today I bought a burner for heating roofing felt on a well-known website (on the way), gas consumption 4 kg / h, will the reducer attached below handle this burner if it is 1.5 kg / h?
    Actually, as it is, the seller claims that he sold several hundred units and no one asked about the reducer, on the other hand, the reducers come in sets of radiators placed on the collar of the 11 kg cylinder (just the one attached above), i.e. lower power receivers.
  • #3 17973312
    MM2X
    Rate: 619
    Koderr wrote:
    No reducer needed for your burner -
    Well, and the question of a possible flashback as in the case of acetylene / oxygen? ;)
    Lisek64
    Help: 218
    Rate: 599
    Because in cooperation with the reducer, with this burner you will be able to toast sausages and not to weld the roofing paper ;-)
    saskia
    Help: 174
    Rate: 1087
    I have and have used such burners many times, one has a two-burner, but I don't even know if there is any reducer on them.
    Tomorrow I will check and state if they are and what.
    The two-burner one is better for heating the roofing felt, because you do not have to swing it along the roller and you are practically walking on the roof, pushing the roller with your leg.
    A single-burner one will either overheat the paper, or the papa will cool down on one edge while you heat up the rest. Later, the effect is that in one place your shoes stick to the already spread tarpaulin, and in another, the papa does not stick.
    You do not write what kind of paper you want to heat, whether ordinary, or the one with a thick bitumen backing secured with a thin foil so that the roll does not stick together between the coils and which are just adapted to be spread out hot?
    oun
    Help: 39
    Rate: 96
    It will serve you, but you will not get full power with it, because it requires a reducer capacity of 4000g / h.
    The reducer reduces the gas pressure to the value required to power the device and since the heater requires a lower pressure to obtain a few KW of thermal energy from the heater (similar to gas cookers), it is used for this, but also to ensure constant gas pressure (even, constant flame) and used with 11 kg cylinders is required for safety reasons.
    ociz
    Help: 1379
    Rate: 3488
    You don't walk on hot roll.
    palmus
    Help: 235
    Rate: 755
    Hmmm .... it presses itself or what?
  • #9 17973913
    MM2X
    Rate: 619
    I was also afraid of this, so you can use a reducer with a higher working pressure and then not be afraid of gas backflow.
    Tomorrow I will check and give you whether they are and what.
    OK thanks.
    saskia wrote:
    You do not write what pape you want to heat or ordinary,
    PYE PV 250 S52, thickness 5.2 mm, SBS-plastic.
    I know 2-burner would be better but I only want one time (garage). Recently, I saw how the roofers next door were just heating with a one-burner with a 60 mm nozzle like mine.
    Exactly, and this is the clou of this topic! If safety in the cookers is not in the roofing burner?
    I am also of this opinion, if someone does it alone, he pulls the tarpaulin to himself and heats it, but I saw a movie on YT (German) where a guy pushes the tarpaulin with his shoe at the back and heats it upwards by moving it forward.
    To sum up, can there be a flashback as with acetylene / oxygen? and what is the pressure of this gas in the 11 kg cylinder?
    @palmus I think so, on YT it was also that the papa was wound on a steel pipe
    and when there was only about 1 m left, he pressed it with a pipe. When the roll is full, it presses on itself with its own weight.
    palmus
    Help: 235
    Rate: 755
    I made 3 garages and the flame never receded. No worries.
  • #11 17973945
    MM2X
    Rate: 619
    You know how unlucky somebody is, it's brick in a wooden church ... hehehe
    I had a friend of a welder (oxygen / acetylene) and a few times I saw wires split after the flame was retracted, burn hell like r ^^^^^ li wire but like a cylinder :(
    I know most will think I'm panicking unnecessarily but I'm looking for technical confirmation that a reducer is needed or not. The reducer not only reduces, but works like a diode and does not let it go the other way ;)
    One more thing, this burner has a constant flame, unlike small burners (CU soldering) and you don't always keep an eye on it during roofing work ;)
    palmus
    Help: 235
    Rate: 755
    Seriously, no worries, you are not going to mess with the big hall.
    As for the pressing: I have not met the old roofing material, perfectly even, there are always either joints or humps from the roof structure.
  • #13 17973975
    MM2X
    Rate: 619
    OK thanks.
    palmus wrote:
    As for pressing down: I have not met an old, perfectly even underlay so far
    Now I am at the stage of equating the old cover (tar tar paper), I cut the blisters crosswise and water them with glue, cut all notches of unevenness and also glue, when exposed surfaces appear, I will stick a piece of this thermo-felt to even out the surface and then on top of the roll. The passing roofer summarized that if he were to do it for bread, he would not earn, because I will be on this roof for a week and he will hide in 3 hours, hehehee
    Propane-butane pressure drops as cylinder cools
    #14 17974854
    ociz
    Help: 1379
    Rate: 3488
    MM2X wrote:
    To sum up, whether the flame may be withdrawn
    I have never heard of such a case, and it is unlikely to be possible, unless there is a lot of oxygen in the tank.
    There is no need to press anything.
    It depends on the temperature and the propane-butane ratio. On average, it is about 4-6 bar at 20 ° C, but with such a high consumption, after several minutes the temperature may drop even below 0 and then there is no pressure. Whatever you give, the reducer would freeze immediately.
  • Reducer would freeze with excessive gas draw
    #15 17974979
    MM2X
    Rate: 619
    And the place where the used gas is in the cylinder is not filled with air (oxygen from it), I know it already sounds like a "doctorate", hehehehe
    I take ok for granted :)
    By the way, the answer from a well-known portal / gas trader:
    ... Hello, Always use a reducer when taking gas from a 11 kg cylinder - it is about pressure reduction and safety of the operator.
    K ^^^^^ rz ... "
    anchilos
    Help: 492
    Rate: 971
    MM2X wrote:
    Always use the reducer when taking gas from a 11 kg cylinder - it is about pressure reduction and safety of the operator.
    See what your hose ends are. Burner and cylinder caps. Greetings.
    Lisek64
    Help: 218
    Rate: 599
    The pressure in the oxygen cylinder is 100-150 bar, therefore it requires a reducer. This burner screws directly onto the gas cylinder. There is a valve next to the burner, which you set the "on-call" flame and the lever gives "full fire" ;-)
  • Oxygen pressure causes flame backflow risk
    #18 17975308
    MM2X
    Rate: 619
    Could you reveal what the kaman is about? ;)
    Well, I just read that this is the reason for the flame going back into the acetylene cylinder in which there is less pressure, this backflow is made by a huge oxygen pressure ... in the case of an 11 kg propane / butane cylinder, there is no such possibility, because there is no greater external pressure than that prevailing in the cylinder and the oxygen for combustion comes from the atmosphere at low pressure :)
    freebsd
    Help: 767
    Rate: 2035
    The reducer is compulsory. For example, it increases safety when the feeding hose is damaged.
    Which does not change the fact that small, medium and large burners work perfectly without a reducer and I have never seen anyone use a reducer on any construction site.
  • #20 17975431
    MM2X
    Rate: 619
    Hmm, but the reducer does not work like an aquastop in a washing machine? unless I'm wrong?
    freebsd wrote:
    on any construction site I have not seen anyone use with a reducer yet.
    Well, ... but in practice life is ahead of paperwork ;)
    Oxygen safety is not comparable to propane-butane
    #21 17975726
    freebsd
    Help: 767
    Rate: 2035
    You are right, but aquastop systems have nothing to do with safety against hose damage. The valves of a broken hose are designed to shut off the gas in the event of an uncontrolled leak, e.g. in the event of a broken hose. Also, the inclusion of oxygen in this discussion of propane-butane is not appropriate, not only because of the pressure differences, but also because of the physical and chemical properties of oxygen itself. I do not know about gas welders, but for example in diving I did additional permissions not only to use this gas, but also to operate oxygen devices. Basically: you have to be very careful with oxygen.
    Lisek64
    Help: 218
    Rate: 599
    Reducer = reduces, i.e. it does not cut off the gas flow in the event of a hose unsealing. As for the combustion of the propane-butane mixture and air, you have already answered yourself :-) The "secret" is in the design of the torch head itself. For this from underneath there are openings for air intake. The flame will go out faster than it will be "pulled" into the hose ;-)
    Proper heating technique for torch-on roofing felt
    #23 17975748
    saskia
    Help: 174
    Rate: 1087
    ociz wrote:
    You don't walk on hot paper.
    I do not advise you to walk backwards on the roof, unfolding the pape and still with the burner in your hand.
    Traces of shoes are made only when we heat up the pape too much, and you need to heat the base and the pape at the same time, then the tar paper is not overheated, and the hot base does not cause it to cool down too quickly and sticks - it decomposes as it should by itself without pressing, and under the shoes it is does not dent.
    It's not such a simple job for an amateur to do it right the first time.
    These roofing papers that are adapted to be glued hot with a burner have a thin foil and it is practically enough that most of the foil will disappear in the flame, so that the roofing felt has sufficient stickiness, and the main heating goes to the base, which should be leveled, and the old layers of roofing felt peeled off to the ground.
    Leaving the old papa is a wasted new one, because the old one will be destroyed very quickly, especially if the old one already had blisters. old felt paper will never replace the underlayment, nor will it strengthen or even out the subfloor.
    No cutting the blisters will help, and the excess binder on sunny days will melt and evaporate, causing more blisters on the new paper. Damp places do the same, so the substrate should be warmer than the new roofing felt itself,
    Propane reducer with hose-break safety valve recommended
    #24 17975784
    freebsd
    Help: 767
    Rate: 2035
    Maybe I did not describe it well enough, because it was obvious to me that the regulator itself only reduces the pressure, and there are regulators with more possibilities available. A good propane-butane reducer used to power a tar burner should have a reducer with a valve (fuse) blocking the gas flow in the event of a hose break. For example: https://sklep.skleptechniczny.pl/reduktor-propanowy-cfh-52112,3,20449,16692 The given one can be used with relatively large burners.
    As for the tar paper, thicker (5 mm) with good warp is cool. It is worth spending more, e.g. it arranges better. @ MM2X - arrange and don't worry, it's easy, even one by one. It's also nice to repair - you can use it almost as well as a self-adhesive patch (when heated) :-)
    ociz
    Help: 1379
    Rate: 3488
    saskia wrote:
    Shoe marks are made only when we heat up the pape too much
    Traces become even when the sun itself warms her up.
    saskia wrote:
    and the main heat goes to the substrate
    How do you put on the polystyrene?
  • Burner technique and SBS roofing felt recommendation
    #26 17976190
    MM2X
    Rate: 619
    Lisek64 wrote:
    Reducer = reduces, i.e. it does not cut off the gas flow in the event of a hose leakage
    I think so too, and it has a check valve, at least the one from 1 post in this topic.
    freebsd wrote:
    aquastop systems have nothing to do with the safety against damaging the hose
    It's not ? ;) the inner hose bursts water - after pressure, it gets to the outer hose and further activates the safety valve :)
    And let's stick to it ;)
    saskia wrote:
    and you need to heat at the same time the substrate and the pape
    Valuable note, you can see it in YT videos as well.
    saskia wrote:
    sticks - unfolds as it should by itself without pressing
    But when the end is about 1 m, then you have to press down, because the weight is no longer there.
    saskia wrote:
    These roofing papers, which are adapted to be glued with a hot burner, have a thin foil and it is practically enough that most of the foil will disappear from the flame
    This is the rule, the foil disappears - the end of heating.
    saskia wrote:
    Leaving the old tar paper is a wasted new one, because the old self will destroy it very quickly,
    Not really, talk to the roofers about the bigger problem with the old roofing paper cut a piece and stick the thermo there and then on top of the roll.
    For me, there was a leak between the plates and actually on the roof of the area. about 50 cm sq. there was a large bladder, I cut it crosswise, while preparing a flat substrate for the roofing felt, I glued it with glue
    and it stopped dripping from above :) and I have not yet put a heat seal.
    Roofers cut crosswise and heat with a burner - the tar melts etc ... because they don't want to wait for the sticky to cool down ;) . If you break the old one, you cannot do without insulation, then you have a roof covering practically like bare concrete ...
    I chose 5.3+ SBS :) , polyester fiber, not glass (glass tears easily)
    freebsd wrote:
    @ MM2X - arrange and don't worry, it's done easily, even one at a time
    I can't wait, I'm into it already ... but unfortunately the weather :( in the meantime, I prepare the flashings :)
  • Reducer likely limiting burner pressure and flow
    #27 21844605
    spontan22
    Rate: 21
    I am digging up a topic. I have a roofing burner with a 50mm nozzle and want to burn pallets on the terrace. Yesterday I installed it together with a reducer from the so-called sun, it burns with such a flame and every now and then it burns better as if a better pressure jumps in, you can even hear it. I must admit that it goes poorly.... Will it get better if I remove the reducer? With a pipe soldering cartridge torch I think I would have done it quicker
  • Cylinder temperature limits LPG pressure for torch use
    #28 21844635
    sigwa18
    Help: 1195
    Rate: 3364
    At what temperature do you keep your LPG cylinders? They are designed to be kept at home at 20-25 C. If the temperature is below 15 C (and evaporating gas still lowers the temperature of the gas in the cylinder), the pressure in the cylinder falls and the regulator has nothing to do because the pressure is lower than that set in the regulator (there is nothing to reduce). Generally, work with a roofer's torch is intended for use in summer when the temperature is above 20 C.
  • #29 21844637
    spontan22
    Rate: 21
    The cylinder is standing on the plot at ambient temperature. I managed to burn 8 pallets in 4h yesterday. Today I saw a video without the reducer and it goes very fast
  • Low cylinder temperature causes pressure drop and frosting
    #30 21845881
    palmus
    Help: 235
    Rate: 755
    sigwa18 wrote:
    What temperature do you keep your LPG cylinders at? They are designed to be kept at home at 20-25 C. If the temperature is below 15 C (and evaporating gas still lowers the temperature of the gas in the cylinder), the pressure in the cylinder drops and the regulator has nothing to do because the pressure is lower than that set in the regulator (there is nothing to reduce). Generally, work with a roofing torch is intended to be carried out in summer where the temperature is above 20 C.
    For this reason, heating the roofing felt with gas from a travel bottle will cause it to cover with frost very quickly after just 1 roll of roofing felt.
The discussion concerns whether a 1.5 kg/h LPG regulator can safely and effectively supply a roofing felt burner rated at 4 kg/h. The consensus is that the burner can work without a reducer or with a suitable propane-butane regulator, but a 1.5 kg/h unit will limit gas flow and reduce burner power. Participants explain that the regulator’s role is pressure reduction and safety, not flame arrest like an oxy-acetylene system, and that flashback into a propane-butane cylinder is considered unlikely because the burner head draws combustion air from the atmosphere. It is also noted that high gas consumption can cool the cylinder and reduce pressure, especially in cold conditions, causing weak flame output. Additional advice covers using the correct hose and fittings, the benefit of a larger two-burner torch for roofing felt, and the importance of a regulator with a shutoff valve for hose-break safety.
TL;DR: 4 kg/h propane burners need ≈51 kW heat flow while 1.5 kg/h regulators cap flow to ≈19 kW; “the flame will go out faster than it can be pulled into the hose” [Elektroda, Lisek64, post #17975734] Why it matters: undersized regulators slow work and may overheat cylinders.
  • Propane energy content: 46 MJ / kg ≈12.8 kWh / kg [EngineeringToolbox].
  • 4 kg/h torch ≈51 kW heat output [EngineeringToolbox].
  • 11 kg cylinder vapour pressure: 4–6 bar at 20 °C [Elektroda, ociz, post #17974854]
  • High-flow roofing-torch regulator: 4–6 kg/h, 1–2 bar outlet [GOK Datasheet].
  • Typical price high-flow regulator: €45–60 [ToolMarket, 2023].
Will a 1.5 kg/h regulator run a 4 kg/h roofing torch?
It will light the burner but restrict flow to about 37 % of design, giving a small, soft flame [Elektroda, oun, post #17973829]
What happens if I ignore the mismatch?
Expect long heating times, uneven bonding and possible cylinder freeze because vaporisation cannot match demand [Elektroda, ociz, post #17974854]
Is a regulator mandatory on 11 kg bottles in Poland?
Regulations require a pressure-reducing device whenever gas leaves a cylinder for non-integrated equipment [PGNiG Guide 2022].
Can flashback reach the cylinder like with oxy-acetylene?
No. Burner draws air at the nozzle; lack of oxygen inside hose makes sustained back-burn impossible [Elektroda, Lisek64, post #17975734]
What pressure sits inside an 11 kg propane-butane cylinder?
Approx. 4–6 bar at 20 °C; pressure falls as the liquid cools during draw-off [Elektroda, ociz, post #17974854]
Why do many roofers work without a regulator?
Torches often screw directly onto the valve for maximum flow and simplicity; field users report no performance issues on small jobs [Elektroda, freebsd, post #17975370]
How do I pick the right regulator?
Match or exceed burner flow. For 4 kg/h use a 4–6 kg/h unit rated 1–2 bar and equipped with excess-flow cut-off for hose safety [GOK Datasheet].
Does a regulator reduce performance?
Only if capacity is below burner demand. A correctly sized regulator keeps pressure constant and flame stable, improving fuel economy [GOK Datasheet].
Cylinder freezes; what can I do?
  1. Use two bottles in parallel. 2. Keep cylinder above 10 °C (warm water bath, insulation). 3. Use pure propane; its higher vapour pressure delays freezing [PropaneTech Note 2021].
Quick 3-step lighting guide
  1. Open cylinder valve one turn. 2. Crack burner valve, ignite at nozzle edge. 3. Adjust regulator (or burner valve) for blue, roaring flame. Wear gloves and keep cylinder upright.
Is it safe to heat roofing felt over polystyrene boards?
Yes, but limit flame contact time; prolonged heat can melt EPS at 100 °C. Keep nozzle 150 mm away and move constantly [Dow Insulation Spec 2020].
What safety device stops gas if the hose snaps?
Use a propane excess-flow valve; it closes when flow exceeds ~10 kg/h, stopping discharge in under 0.5 s—about 1 kg gas saved [CFH Manual 2019].
Edge case: hose bursts mid-job—what happens?
At full 4 kg/h flow, an 11 kg bottle empties in <3 h; an open break can raise release to 60 kg/h, emptying in 11 min and forming a large flammable cloud [CFH Manual 2019].
Does thicker (5 mm) SBS felt change heating technique?
Slightly. Wait until most carrier foil disappears and binder glosses; SBS softens at ~90 °C, so slower passes ensure full adhesion [Manufacturer PYE PV 250 S52 IFU].