Currents in 110kV, 220kV, & 440kV High Voltage Networks: Understanding Current Orders
jaroslawk 26202 12
What order of current typically flows in 110 kV, 220 kV, and 440 kV high-voltage networks?
There is no single fixed current value; in practice these high-voltage lines usually carry tens to hundreds of amperes, often around a few hundred amps. [#3598896] [#3600088] One example from 110 kV substations lists line currents of 60 A, 80 A, 100 A, and 160 A, and a 110/15 kV transformer lower-voltage side at 450 A. [#3598383] Another estimate says a medium-sized city drawing about 40 MW over one 110 kV line corresponds to roughly 210 A, which is still in the hundreds-of-amps range. [#3613303] The thread also notes that HV networks transmit large powers, so the currents are generally tens or hundreds of amps and can reach hundreds of MVA on heavily loaded lines. [#3596883]
  • #1 3596245
    jaroslawk
    Help: 30
    Rate: 13
    Which orders are the currents in high voltage networks (110 kV, 220 kV and 440 kV)
    Regards
  • #2 3596378
    Nstan
    Help: 309
    Rate: 158
    I would like to aim for 1A because the losses on the wires = I?xR. Losses increase to the square of the current and when we have 1A -> 1? = 1 they will be the lowest. Therefore, when transmitting energy over long distances, we raise the voltage to even several hundred thousand. Volt
  • #3 3596536
    jaroslawk
    Help: 30
    Rate: 13
    Thanks a lot for the theory.
    And from a practical point of view - what order of currents are there in these networks.
  • #4 3596883
    jiwaniuk
    Help: 142
    Rate: 145
    In the high-voltage networks (from 110kV up to 750kV in Poland), large currents flow, because they transmit large powers (they are tens and hundreds of amps and the powers are already tens or hundreds of MVA).
    I greet everyone
    jjanek
  • #5 3598383
    twardyboro
    Help: 11
    Rate: 32
    In RE where I work, the currents in the GPZ on 110kV lines in amperes: 160, 100, 60, 80. For the 110 / 15kV transformer on the lower voltage side of 450A, SN15kV lines take from a few to about 80A
    Regards.
    PS. What I gave are the instantaneous values but I hope they give a picture of the current values.
  • #6 3598606
    zielu_lodz
    Help: 5
    The current that flows depends on the network load. And this varies depending on the time of day or even the year of the year. The demand for energy in Poland is highest in January, in January 2000 it was on average over 21,000 MW. The problem of Electricity is that we do not lack it, so we manage its resources properly and determine the amount of energy needed in various ways ... it's not that one power plant works for itself and something is connected under it!
    As for the currents, different currents will flow on the same lines. Take, for example, a transformer that supplies a village with medium voltage, and the same transformer that is installed in a cinema :) and has to cope with a great load.
    Therefore, it is not possible to define unequivocally what current will flow. I am writing here about low and medium voltage lines! How it is on high voltage transmission lines, I do not know: /. but I guess you really try to keep the intensity as low as possible, because then the losses are as low as possible !!
  • #7 3598896
    stomat
    Help: 257
    Rate: 1982
    The question was "Which ROWS are the currents flowing ...". So I answer: in the order of hundreds of amps.
  • #8 3599805
    twardyboro
    Help: 11
    Rate: 32
    Welcome back.
    The values of the currents that I gave were taken from the Power Disposition of the Energy Region in which I work. The 750kV line that my colleagues mentioned has theoretically a transmission capacity of 2000MW, so please calculate what current should flow then - the wires on this line are 4 cables with a cross-section of 525mm? arranged in a square with a side of 40cm, if I remember correctly.
    Regards.
  • #9 3599862
    sp5wcx
    Help: 170
    Rate: 312
    twardyboro wrote:
    Welcome back.
    Regards.
    I will just add that this line, the only one in Poland with such a voltage, has not been sent a single kilowatt-hour for several years, because Ukraine does not work synchronously with UCTE. And on the other side, there is not much left of this line, we even make commas under it.
  • #10 3600088
    twardyboro
    Help: 11
    Rate: 32
    A colleague is right - the line has been without tension for several years, although on our side of the border it is ready for use and can be switched on at any time. However, the 750kV switchgear itself is energized from time to time. Coming back to the topic, currents of the order of several dozen to several hundred amperes flow in the HV lines.
    Regards
  • #11 3601765
    Enpro
    Help: 39
    Rate: 97
    It all depends on the number of GPZs on a given line and the load they consume, but they are certainly currents in the range of several amps to several hundred. The load on one GPZ in my area reaches 25MGW
  • #12 3613303
    Zbrozlo
    Active power supplied to a medium-sized city (up to 50,000 people) is in the order of 40MW. Of course, it depends on the time of day, season, and the specificity of the city and its surroundings (type and number of industrial plants). Assuming that such power is transmitted via one 110kV line, the current will be:
    I = P / (?3 * U * cos? ;) = 40000 / (?3 * 110 * 1) = 210 [A],
    so it is in the order of hundreds of amps . I assumed the power factor as 1, in fact it is close to one.
    The order of currents flowing through the HV line can also be assessed by analyzing the parameters of current transformers offered by various companies. You can find a lot of catalog cards on the web.
  • #13 3613557
    jaroslawk
    Help: 30
    Rate: 13
    Thank you for all your comments.
    The topic is considered closed.
    Regards
In high voltage networks, such as those operating at 110kV, 220kV, and 440kV, current levels can vary significantly based on the load and time of day. Typical current values range from several amps to several hundred amps, with specific examples indicating currents of 60A, 80A, 100A, and 160A on 110kV lines. For instance, a 110kV line supplying a medium-sized city may carry approximately 210A when delivering 40MW of power. The design of these networks aims to minimize losses by maintaining lower current levels, as losses increase with the square of the current. The discussion also highlights the importance of understanding the load characteristics and the impact of seasonal demand variations on current flow.