  • #1 4561176
    fido
    Level 26  
    Hello
    A friend of mine has a problem with the selection of a cable, he has to run a 3-phase cable with a length of 230 m, with approximately 40-50 A going through it, and the problem is that I don`t know which cable to lay, can anyone advise or tell me how to calculate it, with the drop the voltage cannot be large
    many thanks in advance for your help
  • ADVERTISEMENT
  • #2 4561451
    HeSz
    Electrician specialist
    Hello.
    What is the way of laying this cable (in the ground, on ladders, on the plaster)?
    Regards
  • ADVERTISEMENT
  • #3 4561463
    Jerzy Węglorz
    Level 39  
    Hello!
    The calculation can be done in 2 ways:
    - according to thermal conditions (so that the cable can withstand...);
    - according to permissible losses.

    If we want to install a "free-lying" installation, the current density in the copper wires should not exceed 15A/mm2 in a 1-phase, 2-wire installation, or 10A/mm2 in a 3-phase, 4-wire installation. This condition shows that for currents of approximately 40 - 50A, a cable with wire cross-sections larger than 5mm2 each should be used (because thinner wires will melt the insulation...).

    Calculation for the second condition: we assume that the allowable losses on this installation are 5%. The load resistance (in the phase-earth system) is 230/50 = 4.6 ohms, so the resistance of a 230 m long transmission line can be at most 5% of it, i.e. 0.23 ohms. The resistance of copper is 17.5 milliohms with a cross-section of 1 mm2 and a length of 1 m. The calculation shows that the condition of losses <5% is met if the cable core has a cross-section of 17.5 mm2. We can choose from two similar standardized cross-sections: 16mm2 and 25mm2. Using the former will result in losses being exceeded and amounting to 5.46% (I guess this can still be accepted...), and in the latter case the losses will be lower (only 3.5%), but the cost of the cable will be higher by over 50%.

    Now you have a choice.
  • ADVERTISEMENT
  • #4 4561552
    fido
    Level 26  
    HeSz wrote:
    Hello.
    What is the way of laying this cable (in the ground, on ladders, on the plaster)?
    Regards


    As far as I know, this will only be a temporary solution and the cable will run on the surface, attached to a fence somewhere
  • #5 4561590
    lesrog
    Level 11  
    With such a long section and such a load, the cross-section is 50 mm². It is calculated like this:
    Voltage drop on 1 phase not more than 4%; ΔU=230V*4%=9.2V.
    Let`s calculate the cable selection according to the formula:
    - for uneven loading of phases:
    S=(wire length * 2 * copper current/conductivity * ΔU) * cosφ
    - for uniform loading of phases
    S=√3*(wire length*current/copper conductivity*ΔU)*cosφ
    In this arrangement, the cross-section will be 35 mm².

    copper conductivity = 57 m/Ωmm²
  • ADVERTISEMENT
  • #6 4561725
    Jerzy Węglorz
    Level 39  
    lesrog!
    The copper cable you propose with a cross-section of 35 mm2 has a resistance of 0.115 ohm over a length of 230 m. A phase current of 50A in such a cable causes a voltage drop of 5.75V, which is much less than the 9.2V you assumed.
    A 230m cable with a cross-section of 25mm2 has a resistance of 0.161 ohms and a current of 50A gives a drop of 8.05V, which is better than the assumed 9.2V.
    So maybe it`s not worth giving as much as 35mm2?
  • #7 4561829
    lesrog
    Level 11  
    With uneven load, I calculated as for phase 1. In such a case, the length should be counted * 2, which gives a resistance of 0.23Ω for a cross-section of 35 mm². For a uniform load, I agree with my colleague Węgloż. ΔU=16V. Sorry for the miscalculation.
    In sum:
    For an even load on the phases, 25mm² is enough, while for uneven load on the phases it must be 50mm² (I assume that there may be a situation in which only one 50A phase will be loaded).

Topic summary

The discussion revolves around selecting an appropriate 3-phase cable for a distance of 230 meters with a load of 40-50A, emphasizing the importance of minimizing voltage drop. Key considerations include the method of installation (surface-mounted), thermal conditions, and permissible losses. Calculations indicate that for a uniform load, a cable with a cross-section of 25 mm² is sufficient, while for uneven loading, a cross-section of 50 mm² is recommended. The resistance and voltage drop calculations suggest that a 35 mm² cable may be excessive, as a 25 mm² cable provides an acceptable voltage drop within the specified limits.