TL;DR: A 75 m run carrying 26 A per phase shows just 0.009 % voltage drop with 4×10 mm² copper cable [Elektroda, jorgkrab, post #5535290] “10 mm² is easily enough” [Elektroda, Łukasz-O, #5530353]. Why it matters: picking the right cross-section avoids > 1000 zł overspend and keeps protection devices within spec. This FAQ helps homeowners and electricians choose the correct underground supply cable for a 18 kW / 32 A connection.
Quick Facts
• Recommended cable: 4 × 10 mm² Cu or 4 × 16 mm² Al for 18 kW, 75 m, 32 A [Elektroda, multiple posts].
• Price jump: 16 mm² Cu costs ≈ 1000 zł more than 10 mm² on 75 m [Elektroda, Krzysztof W., #5533954].
• Voltage-drop limit: ≤ 3 % for low-voltage feeders (PN-HD 60364-5-52:2011).
• Calculated drop: 0.009 % with 4 × 10 mm² Cu at 26 A phase [Elektroda, jorgkrab, post #5535290]
• Burial-grade cable: Use YKY, not YDY, for direct earth installation [Elektroda, jorgkrab & ekaand, #5537805; #5536898].
What cable size is best for a 75 m underground feed at 18 kW and 32 A?
4 × 10 mm² copper meets current-carrying and voltage-drop limits, giving only 0.009 % drop at 26 A [Elektroda, jorgkrab, post #5535290]
Why not just use 4 × 16 mm² for a bigger safety margin?
16 mm² works, yet adds > 1000 zł in material with no performance gain for this load [Elektroda, Krzysztof W., #5533954].
How do I calculate the required cross-section myself?
- Find phase current: I = P / (√3 × U) → 18 kW → 26 A. 2. Pick allowable voltage drop (≤ 3 %). 3. Use ΔU = √3 × I × R × L; solve for area. This gives ≈ 5.6 mm², rounded to 10 mm² [Elektroda, flaber007, post #5530294]
Copper or aluminium—what’s smarter for this run?
Aluminium (e.g., YAKY 4 × 16 mm²) costs less but needs larger size; copper 4 × 10 mm² is easier to terminate and still affordable at this length [Elektroda, ekaand, post #5536111]
Does 10 mm² fit standard utility meters?
Yes. Many utilities cap customer conductors at 10 mm²; larger wires may be refused [Elektroda, flaber007, post #5530504]
What happens if I bury indoor cable like YDY?
YDY lacks UV and moisture protection; soil chemicals can degrade PVC, leading to insulation failure within years [Elektroda, ekaand, post #5536898]
Which burial-grade cable should I specify?
Use YKY (Cu) or YAKY (Al). Both have PE sheath rated for direct burial and mechanical protection [Elektroda, jorgkrab, post #5537805]
Do I need a fifth conductor for PE?
In TN-C systems the PEN splits at the house, so a 4-core cable plus local ground electrode suffices [Elektroda, Krzysztof W., #5530680].
What standard limits voltage drop in domestic feeders?
PN-HD 60364-5-52:2011 sets a 3 % limit for final circuits and 5 % overall; keeping to 0.009 % is well inside “Electrical Installations” standard.
Edge case: future load increase to 25 kW—will 10 mm² still cope?
25 kW raises phase current to 36 A. Voltage drop stays < 1 % and current rating of 10 mm² Cu in soil is 57 A, so it remains compliant “ETIM Load Tables”. Failure only if protection exceeds 50 A.
Can I rely on ZE to connect the cable?
Utilities in Poland often leave cable termination to the investor’s electrician; ZE installs meter and seals only [Elektroda, Łukasz-O, #5533350].
Any brand recommendations for YKY?
Prysmian and Tele-Fonika offer YKY 0.6/1 kV rated for −40 °C to +70 °C; both comply with PN-EN 50525.