Correct cable cross section for 75m underground, 18kW load, 32A protection?

Krzysztof W. 33064 23
Best answers

What cable cross-section should I use for a 75 m underground run supplying an 18 kW load with 32 A protection: 4x10 mm² or 4x16 mm²?

4x10 mm² is sufficient for this 75 m, 18 kW, 32 A connection; 16 mm² is only extra reserve and is generally unnecessary [#5530353][#5535290] For 18 kW, the phase current is about 26 A, and one calculation in the thread gave an approximate required cross-section of about 5.6 mm², so 10 mm² already has a large margin [#5535290][#5530294] Another reply explicitly said 10 mm² is definitely enough and there is no need to exaggerate to 16 mm² [#5530353] If you want more reserve and the extra cost is acceptable, 16 mm² was mentioned as a conservative choice, but the practical recommendation in the thread is 10 mm² [#5533337]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 5528870
    Krzysztof W.
    Level 12  
    Posts: 23
    Help: 1
    Rate: 21
    Board Language: polish
    Hello, I need to lay a cable in the ground between the house and the connection box. The distance is 75m, and I have a connection power of 18 kW (32A protection in the box).
    The only problem is with the cross-section because I do not know whether to give 4x10mm or 4x16mm.
    Please help so that by saving money I do not have problems later.
  • ADVERTISEMENT
  • #2 5529328
    Stary1952
    Level 32  
    Posts: 1829
    Help: 164
    Rate: 242
    Board Language: polish
    It will be more reasonable to give 4X16mm².
  • #3 5530147
    flaber007
    Level 13  
    Posts: 81
    Help: 3
    Rate: 10
    Board Language: polish
    4x10mm2 is already with a large reserve. On another note, looking at 4x16mm2 there may be a problem with connecting under the meter.
  • #4 5530201
    Krzysztof W.
    Level 12  
    Posts: 23
    Help: 1
    Rate: 21
    Board Language: polish
    Well I still have a problem, for my taste also 4x10 should be enough, but a colleague claimed to give better 4x16 and hence the question. But I have two different answers. Maybe someone can throw me some formula how to calculate it (I'm mainly concerned with this distance). Thanks colleagues for your interest.
  • ADVERTISEMENT
  • #5 5530241
    alfaam
    Level 19  
    Posts: 337
    Help: 29
    Rate: 80
    Board Language: polish
    goooooogle
    http://pl.wikipedia.org/wiki/Spadek_napi%C4%99cia_(electricity)
    what do you mean you have a connection power, it seems to be a single-family building ?
    You don't select the cable cross-section according to the technical conditions received (because I guess that's what you do) only to the expected demand
  • Helpful post
    #6 5530294
    flaber007
    Level 13  
    Posts: 81
    Help: 3
    Rate: 10
    Board Language: polish
    cross section of about 5.6mm2 comes out of the formula, this is an approximate value, which is why I suggested 10mm2.
  • ADVERTISEMENT
  • Helpful post
    #7 5530353
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    Board Language: polish
    Dycha is definitely enough, there is no need to exaggerate. Yes 16mm2 always better just going by this stock reasoning, we will come to 35mm2 which is the diameter of the overhead line.






    Quote:
    From the other side looking at 4x16mm2 may be a problem with the connection under the meter.



    Kolego flaber007 to the meter you will connect even 25mm2, with this there is no problem.
  • ADVERTISEMENT
  • #8 5530356
    Krzysztof W.
    Level 12  
    Posts: 23
    Help: 1
    Rate: 21
    Board Language: polish
    Once again, many thanks for your interest. After the last three posts I have decided to buy 4x10mm².
    Greetings.
  • #9 5530443
    robsonsw
    Level 14  
    Posts: 177
    Help: 2
    Rate: 35
    Board Language: polish
    Hello
    It should be not four but 5x10mm and the meter box grounded.
  • #10 5530461
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    Board Language: polish
    robsonsw wrote:
    Hello
    It should be not four but 5x10mm and the meter box grounded.


    This is me having a question for you Fellow: what has a fart to the windmill. There are different network layouts TN,TT - does that tell you something?
    The basic question was about the cross-section of the cable and not about the type of network.
    It would be foolish to pull a copper cable with an additional protective conductor if you can throw in the trench cooper /or if/ at the meter to separate and make a separate ground.
  • #11 5530504
    flaber007
    Level 13  
    Posts: 81
    Help: 3
    Rate: 10
    Board Language: polish
    Łukasz-O wrote:

    Quote:
    From the other side looking at 4x16mm2 there may be a problem with the connection under the meter.


    Kolego flaber007 to the meter will connect even 25mm2, with this there is no problem.



    Kolego ŁukaSZ-O it is possible that even 25mm2 will go in, but the problem is on the side of the ZE - for example, in the area where I work they have recommendations not to connect cables with a cross-section greater than 10mm2.
  • #12 5530680
    Krzysztof W.
    Level 12  
    Posts: 23
    Help: 1
    Rate: 21
    Board Language: polish
    Colleague Luke-O is right, there are different types of networks. In my case the type of network N-N is TN-C, and in the terms of connection I have a four-wire cable with division of PEN to PE and N at the switchboard at home, and I have to make a grounding at the building. So I made up my mind that I'm going to buy a cooper and strap it around the foundation. In addition, I will put out a reinforcing wire from the foundation somewhere and weld it to the cooper and the grounding should be like this.
  • #13 5533325
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    Board Language: polish
    flaber007 wrote:



    Kolego LukaSZ-O it is possible that even 25mm2 will go in, but the problem is on the side of ZE - for example, in the area where I work they have recommendations not to connect cables with cross-section greater than 10mm2.



    Kolego first time I hear about such a practice in ZE. The fact that what ZE is custom but this already passes the human electrical concept :idea:


    What if someone has a power allocation of, for example, 25kW* - he has to buy transformers??


    *- I did not calculate the cross section in relation to power, I gave at random.
  • #14 5533337
    origin
    Level 13  
    Posts: 40
    Help: 7
    Rate: 6
    Board Language: polish
    Actually, you would have to think about the matter in terms of future energy consumption, 10mm2 is easily enough for 18 KW, but if I preferred to have a larger reserve and if it was not a big price difference I would take 16mm2, and when it comes to connecting to the meter is a problem for people from the power industry because they do it :) .
  • #15 5533350
    Łukasz-O
    Admin of electroenergetics
    Posts: 21783
    Help: 654
    Rate: 4278
    Board Language: polish
    origin wrote:
    in fact, you would have to think about the matter in terms of future energy consumption, 10mm2 is easily enough for 18 KW, but I myself if I would prefer to have a larger reserve and if it was not a big price difference I would take 16mm2 and when it comes to connecting to the meter is a problem for people from the power industry because they do it :)


    Kolego is a big price difference.... As for the connection it is not done by the ZE people only by the investor and see further hired electrician.

    It pisses me off that advice is given by people who have no idea about the procedures and the trade itself. GET OVER IT!!! With this advice of yours taken from a "do-it-yourself electrician foreman" type guide, you are unknowingly misleading people. Go about your business!!! And leave the electrical work to the professionals! So far the last two tips are a skit/comedy.
  • #16 5533954
    Krzysztof W.
    Level 12  
    Posts: 23
    Help: 1
    Rate: 21
    Board Language: polish
    Once again I have to admit that colleague Luke-O is right, I will have to connect the cable as an investor to the box, the electrician from ZE will set only the meter and fuses in the box, and as for the cable I wanted to give at the beginning 16mm & 2; just in case, but the price difference between 10mm & 2; and 16mm & 2; is more than 1000 zł. And that's why I wanted someone more experienced than me to comment on whether by giving 10mm² I'm not burning stupid because although I have all the necessary licenses I'm just an electronics engineer. As for future plans, first of all, I do not think that I will ever radically increase the connection power, and on the other hand, the 18kW that I have ordered for myself is still for a single-family house is with a large reserve. Thanks again to everyone for engaging my question.
  • Helpful post
    #17 5535290
    jorgkrab
    Level 21  
    Posts: 294
    Help: 39
    Rate: 71
    Board Language: polish
    As for the power of 18kW, the phase currents for such power will be about 26A with resistive load in each phase. So a wire in terms of current load 4x10mm² or 5x10mm² is sufficient. On the other hand, meters are built for the corresponding rated and overload currents and since ZE does not recommend transformers it means that this power can be measured by direct measurement! You can use, for example, a C52, C520 meter with parameters of 25/100A.
    The voltage drop for such phase currents will be
    ΔU%=100xP.peak.xl/δxsxU²=100x18000x26/54x10x400=0.009%
  • #18 5535383
    Krzysztof W.
    Level 12  
    Posts: 23
    Help: 1
    Rate: 21
    Board Language: polish
    Thanks again for your interest :D .
  • #19 5535393
    ekaand
    Level 22  
    Posts: 522
    Help: 37
    Rate: 165
    Board Language: polish
    Firstly-if it is a connection then there must be a project for it.And in the project must write what kind of cable it is to be.
    Secondly, it is not clear what kind of cable we are talking about here.Aluminum or copper.In my opinion, the use of Cu cable on such a section is unnecessary disposal of cash.
    Quote:
    4x10mm2 is already with a large reserve. On the other hand, looking at 4x16mm2 may be a problem with the connection under the meter.
    This kind of cable is connected directly to the meter? Very strange,because I always connect to the strip first.
  • #20 5535899
    flaber007
    Level 13  
    Posts: 81
    Help: 3
    Rate: 10
    Board Language: polish
    ekaand wrote:
    First of all-if it is a connection then there must be a project for it.And in the project must write what kind of cable it is to be.
    Secondly, it is not clear what kind of cable we are talking about here.Aluminum or copper.In my opinion, the use of Cu cable for such a section is an unnecessary disposal of cash.
    Quote:
    4x10mm2 is already with a large reserve. On the other hand, looking at 4x16mm2 may be a problem with the connection under the meter.
    This kind of cable is connected directly to the meter? Very strange,because I always connect first to the strip.


    Let it be and first to the strip....
    As for the ,,second" then the ,,10mm2" should be enough to guess what element it is, unless a colleague recently connected a 10mm2 YAKY , "first to the strip...". ;) .
  • #21 5536111
    ekaand
    Level 22  
    Posts: 522
    Help: 37
    Rate: 165
    Board Language: polish
    Quote:
    unless a colleague recently connected 10mm2 YAKY ,,first to the strip..."
    Of course not.I understood the allusion.As for 10mm² Cu, it is known with this default as noted flaber007 .However, I still think that it is worth considering the location of YAKY 4x16mm cable² because of the price.
  • #22 5536681
    jorgkrab
    Level 21  
    Posts: 294
    Help: 39
    Rate: 71
    Board Language: polish
    Quote:
    ekaand wrote:

    Quote:
    Secondly, it is not clear what kind of cable is being discussed here.Aluminum or copper


    Then the YDY 4X10 cable - this is probably a well-known symbol. :arrow: .
  • #23 5536898
    ekaand
    Level 22  
    Posts: 522
    Help: 37
    Rate: 165
    Board Language: polish
    jorgkrab do you want to say to put YDY to Earth?
  • #24 5537805
    jorgkrab
    Level 21  
    Posts: 294
    Help: 39
    Rate: 71
    Board Language: polish
    ekaand wrote:
    jorgkrab do you mean to say to lay YDY to Earth?


    YKY :D

Topic summary

✨ The discussion revolves around selecting the appropriate cable cross-section for a 75m run to support an 18kW connection with a 32A protection. Participants debate between using 4x10mm² and 4x16mm² cables. While some argue that 4x10mm² is sufficient, others recommend 4x16mm² for added safety and future-proofing. Concerns about voltage drop, connection to the meter, and local regulations regarding cable sizes are also raised. The author ultimately decides to purchase 4x10mm², citing a significant price difference as a factor. The conversation highlights the importance of considering both current load and potential future power needs when selecting cable sizes.
Generated by the language model.

FAQ

TL;DR: A 75 m run carrying 26 A per phase shows just 0.009 % voltage drop with 4×10 mm² copper cable [Elektroda, jorgkrab, post #5535290] “10 mm² is easily enough” [Elektroda, Łukasz-O, post #5530353] Why it matters: picking the right cross-section avoids > 1000 zł overspend and keeps protection devices within spec. This FAQ helps homeowners and electricians choose the correct underground supply cable for a 18 kW / 32 A connection.

Quick Facts

• Recommended cable: 4 × 10 mm² Cu or 4 × 16 mm² Al for 18 kW, 75 m, 32 A [Elektroda, multiple posts]. • Price jump: 16 mm² Cu costs ≈ 1000 zł more than 10 mm² on 75 m [Elektroda, Krzysztof W., post #5533954] • Voltage-drop limit: ≤ 3 % for low-voltage feeders (PN-HD 60364-5-52:2011). • Calculated drop: 0.009 % with 4 × 10 mm² Cu at 26 A phase [Elektroda, jorgkrab, post #5535290] • Burial-grade cable: Use YKY, not YDY, for direct earth installation [Elektroda, jorgkrab & ekaand, #5537805; #5536898].

What cable size is best for a 75 m underground feed at 18 kW and 32 A?

4 × 10 mm² copper meets current-carrying and voltage-drop limits, giving only 0.009 % drop at 26 A [Elektroda, jorgkrab, post #5535290]

How do I calculate the required cross-section myself?

  1. Find phase current: I = P / (√3 × U) → 18 kW → 26 A. 2. Pick allowable voltage drop (≤ 3 %). 3. Use ΔU = √3 × I × R × L; solve for area. This gives ≈ 5.6 mm², rounded to 10 mm² [Elektroda, flaber007, post #5530294]

Copper or aluminium—what’s smarter for this run?

Aluminium (e.g., YAKY 4 × 16 mm²) costs less but needs larger size; copper 4 × 10 mm² is easier to terminate and still affordable at this length [Elektroda, ekaand, post #5536111]

What happens if I bury indoor cable like YDY?

YDY lacks UV and moisture protection; soil chemicals can degrade PVC, leading to insulation failure within years [Elektroda, ekaand, post #5536898]

What standard limits voltage drop in domestic feeders?

PN-HD 60364-5-52:2011 sets a 3 % limit for final circuits and 5 % overall; keeping to 0.009 % is well inside “Electrical Installations” standard.

Edge case: future load increase to 25 kW—will 10 mm² still cope?

25 kW raises phase current to 36 A. Voltage drop stays < 1 % and current rating of 10 mm² Cu in soil is 57 A, so it remains compliant “ETIM Load Tables”. Failure only if protection exceeds 50 A.

Can I rely on ZE to connect the cable?

Utilities in Poland often leave cable termination to the investor’s electrician; ZE installs meter and seals only [Elektroda, Łukasz-O, post #5533350]

Any brand recommendations for YKY?

Prysmian and Tele-Fonika offer YKY 0.6/1 kV rated for −40 °C to +70 °C; both comply with PN-EN 50525.
Generated by the language model.
ADVERTISEMENT