How to Calculate 3-Phase Power Using P=U*I for 400V and 32A—Is It Correct?
besiu83 24305 2
  • #1 4723920
    besiu83
    I have a problem, is this formula P=U*I to calculate single-phase voltage 230V, or is this formula also used to calculate 3-phase voltage 400V and the result is multiplied by the number of phases or nothing is multiplied.
    e.g. I=32A, U=400V, it will be 12.8kW ??
    Hello, please reply
  • #2 4724615
    K.J.
    Power in single-phase systems
    P = U × I × cosφ = Uf × If × cosφ
    Power in three-phase systems
    P = U × I × cosφ = √3 × Uf × If × cosφ
    where: Uf= 230V U=√3 × 230V ≈ 400V
  • #3 4724856
    Quarz
    Help: 1646
    Rate: 629
    Although the markings are unambiguous here, the repetition of the notation implies that:
    U•I = U f •AND f , but this equality does not necessarily imply a double equality that;
    U = U f , and;
    I = I f .
    It's some new Theoretical Electrical Engineering Is... :cry:
    In three-phase systems, the measurement (calculation) of active power should be clearly differentiated P for the layout symmetrical three-phase and active power for the system unbalanced three-phase ...
    The parameters on the terminals of a three-phase and three-wire receiver (with an unknown connection inside this three-port) are:
    - line voltages AT p - between the next three pairs of wires,
    - conductor currents AND p - flowing in each of the three conduits.
    Only in the case of a three-phase and symmetrical receiver (but then in the neutral - neutral - no current flows and it does not matter whether it is a three- or four-wire system) you can use the following formula:
    P = √3•U p •AND p , while in the case of asymmetry, the powers in the individual phases of the receiver should be measured (counted) and summed up, or (but only for three-wire receivers) used to measure the sum of active power Arona system (two wattmeters respectively connected to the circuit).