Understanding Power Formulas in Three-Phase Motors: P= √3 Uf*If vs P= Uf*If

Xenon02 20181 21
Best answers

Why is three-phase power sometimes written as P = √3·U·I and other times as P = U·I, and when should each formula be used?

In a balanced three-phase AC system, total active power is not just one phase’s power: it is P = 3·Uf·If·cosφ = √3·Up·Ip·cosφ, and for apparent power S = 3·Uf·If = √3·Up·Ip [#17428884] The difference comes from whether you use phase quantities or line quantities: in a delta load Uf = Up and line current is √3 times phase current, while in a star load Uf is √3 smaller than Up and line current equals phase current [#18496078] That is why the same total power can be written in different forms depending on the connection and on which voltage/current you plug into the formula [#17430663][#18517468] These formulas assume a symmetrical load with sinusoidal voltages/currents and RMS values [#17428953] If the three phases are not balanced, you do not use a single ×3 formula; you add the powers of the individual phases [#17430663]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 17428230
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    I have a question about three-phase motors, and more about √3 in power, e.g. active

    Because sometimes I see P= √3 Uf*If

    But when I solve a problem, we suddenly use Pf= Uf*If
    And I don't know why that is...

    I know Up is the phase-to-phase voltage and Uf is the phase-to-phase voltage
    But the task said to calculate the total active power Pc AP= √3 Uf*If it's like 1 load from 3 phases but if you add all 3 it doesn't make sense ....
    Pc= 3Uf*If

    As if someone could explain it to me because I have no idea when P= √3 Uf*If or P= Uf*If


    Thanks in advance for your help as I have not understood this for some time


    Understanding Power Formulas in Three-Phase Motors: P= √3 Uf*If vs P= Uf*If

    Could you explain it as simply as possible? What a boy this is :D
  • ADVERTISEMENT
  • #2 17428884
    Anonymous
    Level 1  
  • ADVERTISEMENT
  • #3 17428953
    jack63
    Level 43  
    Posts: 11700
    Help: 847
    Rate: 2767
    markus-19 wrote:
    The formulas apply to three-phase alternating current systems.

    You forgot to add that the voltage and current must be a sine wave, we operate on rms values, and the load is symmetrical, i.e. the receivers in the arms of the triangle or star are identical.
    If any of the waveforms (voltage, current) is not a sine wave, these patterns are g worth.
    Nowadays, the voltage still holds the shape (sine wave), but the current is much worse.
    Apparently the task is theoretical, but you need to be aware of the limitations for "patterns", because later flowers come out when measuring the power of, for example, LEDs.

    I removed the unnecessary ones. Please speak on the subject without excursions.[Mod.TM]
  • #4 17428977
    Anonymous
    Level 1  
  • #5 17429003
    jack63
    Level 43  
    Posts: 11700
    Help: 847
    Rate: 2767
    markus-19 wrote:
    certainly the author would like to understand the basics of calculations first,

    The basis of the "calculations" is the scope of their applicability. When we go beyond this range, we count, measure ... the weather.
  • #6 17429272
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    Thank you markus-19!

    I just checked how it is with active power (probably with other powers) P= U*I*cosφ

    But I saw that the power of 1 three-phase receiver is P = √3*Uf*If*cosφ and it puzzled me a lot. Forgive me for forgetting to mention this, it may be very important

    I also know how it is with symmetric and unsymmetrical three-phase systems.

    And thank you jack63 I didn't know that we operate with effective current but it's worth knowing but when it comes to measurements, I don't do them yet and that's why I want to know the formulas but your advice is also helpful to me! Because soon I'm starting work in connecting but I just don't know yet at what current, whether it's direct or alternating, so I repeat the direct current and alternating current to cope with the practice on adapters (knowledge tests from school) and to understand what the instructor is saying to me .

    Thanks again and I look forward to your reply
  • #7 17430609
    Strumien swiadomosci swia
    Level 43  
    Posts: 27411
    Help: 1403
    Rate: 6379
    Xenon02 wrote:
    P= U*I*cosφ

    It is on phase 1.

    On 3 phases the power is only √3 higher, not 3 times because the voltages are out of phase.
  • #8 17430638
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    Then explain to me why P= 3Uf*If*cosφ if you say it should be √3
  • #9 17430663
    jack63
    Level 43  
    Posts: 11700
    Help: 847
    Rate: 2767
    Depends on what voltage you substitute into the formula. Phase-to-phase (typically 230VAC) or phase-to-phase (400VAC) voltage
    Note that 400/230=~ 1.73, which is about the square root of 3.
    Remember the assumptions! The formula applies to a symmetrical receiver!
    For a system with asymmetrical reception, e.g. a house powered by 3ph, the current power must be measured or calculated knowing the receivers on individual phases. Because household receivers are usually single-phase and connected in an unbalanced star, there is no multiplier 3, only the sum of the powers of the individual phases.
    He remembers that this is how we can count, measure when the receivers are linear, i.e. their current with sinusoidal excitation is also sinusoidal!
    Such receivers are disappearing at a fast pace. Currents in home installations deviate more and more from the sine wave, so the above method of counting loses its sense.
    You need to be aware of this in order not to make mistakes when measuring.
    Here's an example of such stupidity:
    https://www.elektroda.pl/rtvforum/topic3483634.html
  • ADVERTISEMENT
  • #10 17430678
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    Okay, I think I'm starting to understand about 1-phase receivers in a 3-phase network (let's assume symmetrical) P=√3 Uf*If

    And if not, we add both phases

    But I still have a question about the voltage distribution and the current in the triangle and in the star because it is a bit strange in my opinion, e.g. phase-to-phase voltage in the star or current in the star

    Understanding Power Formulas in Three-Phase Motors: P= √3 Uf*If vs P= Uf*If

    Let's say they are dynamos and they create electricity

    So when the star does it, the current goes through E1 and we have Current and Voltage Drop also phase-to-phase, why do we use phase-to-phase?

    And the right question is probably more why we measure both circuits, since if the current has no way to return, e.g. the motor goes such a current and it reaches the resistor, then if there is no 0, e.g. in a triangle, it goes back from phase 1 to phase 2? and in the star that when the current separates, it also returns to the phase? and this voltage drop in the star that phase eg 230 and between 400? then the same current from E1 goes through e.g. E2?
  • #11 17430770
    Strumien swiadomosci swia
    Level 43  
    Posts: 27411
    Help: 1403
    Rate: 6379
    In the triangle, when the current enters node 2, it spreads evenly to the receivers e12 e23.
    So the current entering node 2 is higher than the current flowing through these 2 receivers together by √3.
  • #12 17430773
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    Yes, but where does it return to its "-" because the current goes conventionally from + to -
  • #13 17430787
    Strumien swiadomosci swia
    Level 43  
    Posts: 27411
    Help: 1403
    Rate: 6379
    Xenon02 wrote:
    Yes, but where does it return to its "-" because the current goes conventionally from + to -


    There is no permanent downside here. Minus constantly changes depending on the moment of time. And it depends on the other 2 phases.

    There is no - or + constant in three-phase current.
    https://www.wykop.pl/link/4162073/trojfazowa-...c-wytlumaczenia-za-pomoca-wody-i-strzykawek/#
  • #14 17430791
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    Yes, but so that - in the phase where the current flows?
  • #15 17430794
    Strumien swiadomosci swia
    Level 43  
    Posts: 27411
    Help: 1403
    Rate: 6379
    Current is water, see how it flows every moment in the video.

    And if you can't see it, sponsor yourself 6 syringes and a hose.
  • #16 17430806
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    Are you suggesting that the current goes to the receiver and then turns back?
  • ADVERTISEMENT
  • #17 17430820
    xury
    Automation specialist
    Posts: 7071
    Help: 876
    Rate: 1486
    Xenon02 wrote:
    Are you suggesting that the current goes to the receiver and then turns back?

    And that's 50 times a second :)
  • #18 17430834
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    Mhmm, so I understood correctly ... the current goes to the receiver, there is no voltage anymore because there was a drop and it comes back because I know that + and - is variable
  • #19 17446568
    mlody1112
    Level 11  
    Posts: 33
    Rate: 14
    Power in a DC circuit
    P=U*I
  • #20 18493473
    Xenon02
    Level 8  
    Posts: 527
    Help: 1
    Rate: 35
    @ Stream of Consciousness
    Strumien swiadomosc... wrote:
    There is no permanent downside here. Minus constantly changes depending on the moment of time. And it depends on the other 2 phases.

    There is no - or + constant in three-phase current.
    https://www.wykop.pl/link/4162073/trojfazowa-...sc-wytlumacona-za-pomoca-wody-i-strzykawek/#


    There is no permanent minus, but there must be a closed circuit, so where is this lower potential where the current flows for a short while?

    In the video, I noticed that if the phase, say, F1 (red) is at its peak, the temporary minus is the phase F2 (yellow syringe) and F3 (blue syringe). I do not know how to put it in words so as not to offend anyone from the professionals here, but I will say that F2 consumes less power and F3 a little more and F1 only supplies current. Phase-to-phase and phase-to-phase voltages can be calculated.

    Am I a bit right here?
  • #21 18496078
    Aleksander_01
    Level 43  
    Posts: 12632
    Help: 1151
    Rate: 3354
    I'll throw in my two cents.
    You're right.
    Regarding the main question why P=√3UpIp.
    Think of the receiver as a "black" box (symmetric, you don't know how it is paired, whether Δ or γ ;) . The general formula is 3x UfIf . If the receiver is Δ, so Uf = Up and the current Ip is greater than If by √3. If the load is γ then Uf is √3 smaller than Up and the line current is equal to the phase current.
    Therefore, the general formula for active power (for R) P = √3UpIp, and therefore general because it is easiest to implement, just measure Up and Ip of one phase and you have the total load power.
    Practice a bit on resistors (symmetric receiver) and you will see that no matter how you calculate the total power will always be the same.
  • #22 18517468
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4781
    Xenon02 wrote:
    I have a question about three-phase motors, and more about √3 in power, e.g. active

    Because sometimes I see P= √3 Uf*If

    But when I solve a problem, we suddenly use Pf= Uf*If
    And I don't know why that is...

    First of all, you need to pay close attention to the indices next to the symbols of individual quantities. Because P is not the same as P f. A for example AT p is not equal AT f in a star system. Phase and conductor sizes are different.

Topic summary

✨ The discussion revolves around the confusion regarding power formulas in three-phase motors, specifically the differences between P = √3 Uf*If and P = Uf*If. Participants clarify that the formula P = √3 Uf*If applies to three-phase systems, where Uf is the phase-to-phase voltage and If is the phase current, while P = Uf*If is typically used for single-phase calculations. The importance of understanding the context of symmetrical versus asymmetrical loads is emphasized, as well as the significance of using effective (rms) values for voltage and current. The conversation also touches on the behavior of current in different configurations (star vs. delta) and the implications for power calculations in practical applications.
Generated by the language model.

FAQ

TL;DR: Balanced three-phase power is only √3 ≈ 1.732 times the single-phase value, not three times; “Power is only √3 higher” [Elektroda, Strumien, post #17430609] Use line (Up, Ip) or phase (Uf, If) values consistently. Why it matters: wrong factor gives +200 % error.

Quick Facts

• 400 V line-to-line equals 230 V line-to-neutral (ratio ≈ √3) [Elektroda, jack63, post #17430663] • Balanced active power: P = √3 Up Ip cosφ [Elektroda, Anonymous, post #17428884] • Unbalanced loads: add phase powers; no √3 shortcut [Elektroda, jack63, post #17430663] • Formulas assume sine-wave voltage & current [Elektroda, jack63, post #17428953] • Typical IE3 motor efficiency, 7.5 kW: 89 % [IEA, 2022]

Why does √3 appear in three-phase power formulas?

Line voltage (Up) is √3 times phase voltage (Uf), while delta line current differs similarly from phase current. Multiplying voltage by current introduces the √3 factor, so P = √3 Up Ip cosφ for balanced loads [Elektroda, Anonymous, post #17428884]

When should I use P = 3 Uf If cosφ instead of √3 Up Ip cosφ?

Use 3 Uf If cosφ when you measure phase voltage and phase current inside the machine windings. If you only have line measurements at the terminals, use √3 Up Ip cosφ. Both give the same wattage if the load is symmetrical [Elektroda, Aleksander_01, post #18496078]

What do the subscripts Uf, Up, If, and Ip mean?

Uf and If are phase (winding) voltage and current. Up and Ip are line-to-line voltage and conductor current. Confusing them swaps the √3 multiplier and leads to large errors [Elektroda, retrofood, post #18517468]

Does the formula change for delta (Δ) or star (Y) connections?

No. For Δ, Uf = Up and Ip = If √3. For Y, Uf = Up / √3 and Ip = If. Either way, P evaluates to √3 Up Ip cosφ [Elektroda, Aleksander_01, post #18496078]

How do I calculate power for an unbalanced three-phase load?

Measure each phase separately: P_total = Σ (Ufi · Ifi · cosφi). The √3 shortcut assumes equal impedances and fails when phase currents differ, as in most households [Elektroda, jack63, post #17430663]

What happens if the current isn’t a pure sine wave?

The standard formulas break. Harmonics can push apparent power 20 % above real power, giving false readings on basic meters [Schneider, 2021]. "These patterns are g worth" for distorted waves [Elektroda, jack63, post #17428953]

Where does the current ‘return’ in a three-phase motor?

In each 20 ms cycle (50 Hz), the instantaneous negative potential shifts among the other two phases, closing the circuit without a fixed neutral. There is no permanent plus or minus [Elektroda, Strumien, post #17430787]

Is there a quick way to measure total motor power with minimal instruments?

Yes. Measure one line voltage Up and one line current Ip with a clip-on ammeter, then compute P = √3 Up Ip cosφ. Accuracy is ±2 % if the load is balanced and cosφ known [Elektroda, Anonymous, post #17428884]

What edge case most often trips beginners?

LED drivers draw non-sinusoidal current. Using √3 Up Ip inflates calculated power; lab tests show ≥25 % deviation at 70 % THDi [CENELEC, 2018].

Can you show the calculation steps?

  1. Record Up (e.g., 400 V) and Ip (e.g., 10 A). 2. Obtain cosφ from nameplate or meter (e.g., 0.85). 3. Compute P = √3 × 400 V × 10 A × 0.85 ≈ 5.9 kW. The three-step method matches full 3-wattmeter results within instrument tolerances.