TL;DR: For an 11 kW three-phase motor (~23 A rated) [Elektroda, SZYMKA10, post #5387486], “4 × 2.5 mm² works only up to 50 m” [Elektroda, Luklukowaty, post #5380129]; most installers choose 4 × 4 mm² copper in star with PE. Use correct protection and match nameplate voltage.
Why it matters: Correct sizing prevents stalled starts, nuisance trips, and burnt windings for workshop or farm machinery.
Quick Facts
• Rated current: 17–23 A depending on 500 V or 400 V supply [Elektroda, HeSz, #5388688; SZYMKA10, #5387486]
• Long-term ampacity: 2.5 mm² Cu, 25 A in free air at 30 °C [Elektroda, HeSz, post #5388688]
• Typical cable pick: 4 × 4 mm² Cu ≤ 60 m run [Elektroda, Marian_em, post #5390567]
• Starting current: up to 10 × In (≈230 A) [Elektroda, Madrik, post #5380323]
• Rewind or derate 290/500 V motors on 400 V grids [Elektroda, Daj, post #5401880]
What cable cross-section is best for an 11 kW motor under 60 m?
Use 4 × 4 mm² copper. It carries 23 A with margin, keeps voltage drop reasonable, and meets installers’ experience [Elektroda, JK60, #5388241; Marian_em, #5390567].
Is 4 × 2.5 mm² ever acceptable?
Do I need a neutral wire for three-phase motors?
Why did my motor stall on light timber even though fuses stayed intact?
Thin mixed wiring (20 m of 4 × 1.5 Al + 30 m of 4 × 2.5 Cu) caused voltage drop, cutting torque. Flux drops with voltage, so torque falls (M = Ψ·I) [Elektroda, kiecio, #5407966; 00marian00, #5417606].
How large should the circuit breaker be?
Can I start an 11 kW motor directly across the line?
Should I use a star-delta (Y/Δ) starter on a 290/500 V nameplate?
No. The motor is designed for 500 V in star; switching to delta on 400 V would over-voltage the windings (400 V per phase) and burn them
[Elektroda, Daj, post #5401880]
What happens if I undersize the cable further, say 1.5 mm²?
Three-step checklist to size cable and protection quickly?
- Read nameplate voltage and full-load current.
- Select cable with ampacity ≥ 1.25 × In and ≤ 3 % voltage drop for run length.
- Choose breaker: C-curve at 1.1–1.25 × In and ensure upstream selectivity.
Tools like Moeller Suwak PKZ automate this [Elektroda, JK60, post #5387686]
Which software helps with motor sizing?
What standard tables back these numbers?
Edge case: private transformer vs public grid—does it matter?
A private substation tolerates direct starts better because voltage sag stays local. Public networks may flicker lights or trip upstream fuses
[Elektroda, Akrzy74, post #5389002]