Power Assumptions for a 3-Phase Socket: Comparing 230V General Purpose Circuit (2kW) & Garage Usage

filu 45163 19
Best answers

What power should I assume for a 3-phase garage socket, and what socket/cable size should I choose?

There is no single fixed “installed power” for a 3-phase garage socket; it depends on the socket rating you choose, and a 3-phase outlet uses 400V, not 230V [#5741555] For a typical single-family house, one reply says the utility allocation is around 9kW, so you will likely end up with a 16A socket [#5747344] For a 16A socket, 5×2.5 mm² cable is enough [#5750252] If you want a 32A socket, use 5×4 mm²; 5×5 mm² is not a standard size [#5752911] One reply also notes that 4 mm² may be chosen as extra reserve if you expect heavier tools later, especially depending on cable length [#5750272]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 5741293
    filu
    Level 16  
    Posts: 276
    Rate: 15
    For the 230V general purpose socket circuit, the installed power is 2kW, and how much for a 3-phase socket? Specifically, it is about one 3-phase socket in the garage - of course, it is not known yet what will be connected there.
  • ADVERTISEMENT
  • Helpful post
    #2 5741555
    *paweł*

    Automation specialist
    Posts: 968
    Help: 60
    Rate: 95
    Buddy, it depends what 3-phase socket you put on. You have 16A, 32A, 63A and the rest is calculated from the formula. Just take into account that you have 400V there, not 230V ;)
    greetings
    Company Account:
    Automation-Systems
    Domatków 36, Kolbuszowa, 36-100 | Tel.: 17 XXXXXXX (Show) | Company Website: automatyka-sklep.eu
  • ADVERTISEMENT
  • #3 5747344
    noplis
    Level 21  
    Posts: 311
    Help: 36
    Rate: 48
    And one more thing, as far as I know, the energy company gives a power allocation for a single-family house about 9kW, so you will probably only have a 16A socket.
  • ADVERTISEMENT
  • #4 5749941
    Marsal20
    Level 13  
    Posts: 141
    Help: 4
    Rate: 43
    How can I connect this 16A 5x2.5 or 5x4 socket?
  • #5 5749988
    Arturo2005
    Level 33  
    Posts: 1892
    Help: 149
    Rate: 483
    5x2,5
  • #6 5750006
    filu
    Level 16  
    Posts: 276
    Rate: 15
    5 * 2.5 is enough because the long-term load capacity of such a cable is over 20A, but I wonder if for the 32A socket it is possible in practice to 5 * 4 because in the load capacity tables it is on the border of 4 and 6
  • Helpful post
    #7 5750028
    Jack14
    Level 38  
    Posts: 3515
    Help: 320
    Rate: 175
    This is what I "reworked" according to the new 5x4mm regulations
  • #8 5750046
    filu
    Level 16  
    Posts: 276
    Rate: 15
    If you are allowed to know, with what new regulations. As far as I know, in these new HD standards there are no changes in the way of calculating circuits or new tables of long-term load capacity of cables.
  • #9 5750071
    Jack14
    Level 38  
    Posts: 3515
    Help: 320
    Rate: 175
    I am also not an electrician, but I have a good advisor in whom I have 100% confidence (he is not a trickster).
    I installed the YDYP 5x4 cable

    ps

    He had in mind the possible connection of a saw, welder, small concrete mixer, etc.
    (do you want to provide specific recipes?).

    Greetings.
  • #10 5750090
    igabriel
    Level 20  
    Posts: 308
    Help: 35
    Rate: 60
    a 15kW / 400V motor can safely operate on a 5x4? cable ..........
  • #11 5750103
    Jack14
    Level 38  
    Posts: 3515
    Help: 320
    Rate: 175
    Deviating a bit from the problem, I had a 5x1 connected to the water heater and, surprisingly, the cable was soft like rubber and was lying loose on the wooden ceiling for probably 2 years (it did not bother anyone).
    ps

    It bothered me (although 998 is a toll-free number).
  • #12 5750121
    filu
    Level 16  
    Posts: 276
    Rate: 15
    Rather, it must be a 5X4mm2 cable for a 32A socket. I misread the long-term load capacity table of cables.
    The permissible current carrying capacity for a 5X4mm2 cable laid directly in the wall is 32A.
  • #13 5750140
    Jack14
    Level 38  
    Posts: 3515
    Help: 320
    Rate: 175
    Fortunately, you found your friend, because you could have misled the questioner.

    ps

    If you have the opportunity (and financial resources), it is better to use 5x5 (5x4 is the minimum acceptable cost of a meter, about PLN 7.5).
    I decided on the second option, the more that I do not know what to connect to this socket now, and I am also thinking about the future.
    (I did it once and well for years)

    :cry:
  • #14 5750163
    filu
    Level 16  
    Posts: 276
    Rate: 15
    Fortunately, he asked for socket 16A, and 32A is our consideration.
  • ADVERTISEMENT
  • #15 5750212
    Jack14
    Level 38  
    Posts: 3515
    Help: 320
    Rate: 175
    I agree with your opinion.
    So, in your opinion, what is the questioner supposed to do?
  • #16 5750252
    filu
    Level 16  
    Posts: 276
    Rate: 15
    A colleague asked about the 16A socket and we answered with Arturo2005 that 5X2.5 would be enough.
    As for the 32A socket, 5X4 should be enough.
    greetings
  • Helpful post
    #17 5750272
    igabriel
    Level 20  
    Posts: 308
    Help: 35
    Rate: 60
    :?: and where can you buy a 5x5? cable, unless it is the actual cross-section of a Chinese 5x6?, and seriously, cables laid permanently, multi-strand, laid directly on the plaster or in plaster with a number of wires 5-6 for copper belong to the V (fifth) class load capacity at the design temperature of 25 ° C and their permanent load capacity is: 31A for 4mm? and 24A for 2.5mm?, so I see no reason to use the 4mm? cross-section, for example because of the protection (I assume that it will not be greater than C25A), it is enough cross-section 2.5mm?, the only justification for a 4mm? cable would be its length, but please note what length it would have to be if the max. the resistance of a multi-core cable is for: 4mm? - 4.5 ? / km and for 2.5mm? - 7.15 ? / km.
  • #18 5750478
    Jack14
    Level 38  
    Posts: 3515
    Help: 320
    Rate: 175
    I decided on the second option, which the questioning colleague will decide, I don't know.
    Personally, I assumed that it is better to have something in reserve than to "scratch" the walls and plaster because the cable cross-section is too small.
    I don't know how my colleague will do it, but I just presented how I did it on my own example.

    ps

    I wrote that I am not an electrician, if there are other opinions, I agree with them, but I will do it "my way".
    (I do not know what to connect yet "and you already know what and how much" electricity "needs?)

    Greetings.
  • #19 5752812
    Marsal20
    Level 13  
    Posts: 141
    Help: 4
    Rate: 43
    Thanks for your comments.
    Summing up, for the 16A socket, 5x2.5 cable and 5x4 mm2 for the 32A socket.
    5x5 doesn't really exist ??
  • Helpful post
    #20 5752911
    jorgkrab
    Level 21  
    Posts: 294
    Help: 39
    Rate: 71
    5x5mm? does not exist according to the standards. For 32A socket - 5x4mm? as shown in the previous discussion. The socket is one degree higher, it is even better because it does not heat up so much when continuously loaded with the rated current.
    I saw sockets with 63A written on them, but with this current they got hot and on the larger 125A the load in the store was only limited to 5 hours of work.
    Stock will never hurt within reason. :D

Topic summary

✨ The discussion revolves around the power assumptions for a 3-phase socket in a garage, specifically comparing it to a 230V general-purpose circuit rated at 2kW. Participants highlight that the power capacity of a 3-phase socket depends on its amperage rating (16A, 32A, or 63A) and the voltage (400V). For a typical single-family home, a 16A socket is common, with a recommended cable size of 5x2.5mm². For a 32A socket, a 5x4mm² cable is suggested, as it can handle the necessary load without overheating. The conversation also touches on the importance of future-proofing installations by considering higher amperage sockets and appropriate cable sizes to avoid potential issues with load capacity and heating.