Best Cable Type for 20-30m Distance Garage/Workshop with 2.8kW Compressor, Fan & Lights

tetrusmorderca 70476 34
Best answers

What cable type and cross-section should I use to power a garage/workshop 20–30 m away with a 2.8 kW compressor, fans, lights, and possibly a heater?

You cannot choose a safe cable size from the posted data alone; the thread says it depends on whether the supply is single- or three-phase, the total load and future power increase, and the installation conditions, including mechanical strength, current capacity, voltage drop, short-circuit protection, and earthing [#15798260] [#15798266] For a cable buried between buildings, one reply says to use YKY if the earth cable is not exposed to damage, and another gives a rough estimate of YKY 5x6 mm², but only as a guess and with an electrician choosing the protections properly [#15798389] [#15798485] Several replies stress that the final sizing and protection should be done by a qualified electrician, not just the cable connection [#15800662]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 15798222
    tetrusmorderca
    Level 8  
    Posts: 37
    Rate: 20
    Hello.
    I am building a garage and I need information on which cable to use for electric power.
    The distance between the garage and the house is about 20-30 meters.
    A compressor will work in the garage - Power: 2.8kW, fan 145 [W] 0.62 [A], a dozen or so fluorescent lamps and maybe some electric heater in winter.
  • ADVERTISEMENT
  • #2 15798260
    kokapetyl
    Level 43  
    Posts: 13444
    Help: 1787
    Rate: 2089
    Some information is missing.
    Single-phase or three-phase power supply.
    Installation as it will be located between buildings.
    Are you planning to increase the power by 6kW, will the connection conditions allow it, what will be the total balance of power consumption.
  • #3 15798266
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    tetrusmorderca wrote:
    I need information on which cable to use for electrical power

    Quote:
    The selection of cables requires checking the following conditions:
    - mechanical strength,
    - long-term current carrying capacity and overload capacity,
    - selection for short-circuit conditions,
    - selection due to voltage drop,
    - selection due to protection against electric shock,
    - selection based on the requirements of the minimum cross-section of the PEN conductor or the conductor made of aluminum.


    Quote:
    The operation of the electrical installation (including the implementation of assembly works) may only be performed by persons who have a valid Qualification Certificate for the operation of electrical devices.
  • #4 15798283
    tetrusmorderca
    Level 8  
    Posts: 37
    Rate: 20
    kokapetyl wrote:
    Some information is missing.
    Single-phase or three-phase power supply.
    Installation as it will be located between buildings.
    Are you planning to increase the power by 6kW, will the connection conditions allow it, what will be the total balance of power consumption.

    Electricity is black magic to me.
    I'll bury the cable.
    I don't know if one or three-phase ... And what should it be?
    I do not know what the total balance of power consumption will be. I only know what will work in the garage.
  • ADVERTISEMENT
  • #5 15798301
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    tetrusmorderca wrote:
    Electricity is black magic to me.

    Rather, surgery or dentistry is also black magic.
    But somehow you don't cut yourself with a pocket knife and tear your teeth out with pliers.

    So get an electrician.
  • #6 15798342
    tetrusmorderca
    Level 8  
    Posts: 37
    Rate: 20
    zbich70 wrote:
    tetrusmorderca wrote:
    Electricity is black magic to me.

    Rather, surgery or dentistry is also black magic.
    But somehow you don't cut yourself with a pocket knife and tear your teeth out with pliers.

    So get an electrician.


    I was counting on someone who would know what cable to do it without spending money on an electrician. I can connect myself. I just don't know what cable to use.
  • #7 15798389
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    Buddy, how are we going to help you if you don't want to help us. It is impossible to advise without the basic data asked by colleagues. If the earth cable is not exposed to damage, then YKy ...
  • #8 15798392
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    tetrusmorderca wrote:
    I was counting on someone who would know what cable to do it without spending money on an electrician.

    Read post # 3. Provide the conditions that this cable is to meet.
    You can't go without it.

    Unless you want a glass ball. Here you go, my bullet tells you - YAKY 4x70mm?.
    It suits? Does it seem too fat?
    If too thick, please tell me why my glass ball is wrong. ;)
  • #9 15798485
    maziar1000
    Level 15  
    Posts: 280
    Help: 4
    Rate: 45
    Bury YKY 5x6 mm?, it should be enough for you, but then call an electrician to secure everything properly
    Moderated By Krzysztof Reszka:

    3.1.11. Publishing posts that do not contain substantive content with harmful advice.

  • #10 15798528
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    maziar1000 wrote:
    Bury YKY 5x6 mm?, it should be enough for you, but then call an electrician to secure everything properly

    Buddy, justify why 5 x and why 6mm2.
    We are waiting for an answer because you are misleading our friend.
  • #11 15798566
    Akrzy74
    Rest in Peace
    Posts: 7910
    Help: 363
    Rate: 1497
    tetrusmorderca wrote:
    Electricity is black magic to me.
    I'll bury the cable.
    tetrusmorderca wrote:
    I am building a garage and I need information on which cable to use for electric power.
    The distance between the garage and the house is about 20-30 meters.
    A compressor will work in the garage - Power: 2.8kW, fan 145 [W] 0.62 [A], a dozen or so fluorescent lamps and maybe some electric heater in winter.

    In my opinion, our colleague should only answer at what depth this cable should be buried, and therefore what groove it should dig. The selection of the cable and possible earthing should be performed by a qualified person.
  • #12 15798670
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    maziar1000 wrote:
    Bury YKY 5x6 mm?, it should be enough for you, but then call an electrician to secure everything properly

    What extreme bullshit advice !!!
    After the fact, you can "secure" yourself - but a lawyer, when the layman works miracles for you. Unless you do all the same and you do it for a bottle ... there is no topic.

    The layman can at most:
    - make the excavation to a certain depth along the route designated by the electrician,
    - make forging in walls and grooves in places designated by an electrician,
    - deliver sand for the slope to the excavation and help the electrician distribute it evenly,
    - unwind the cable and lay it in a trench, in culverts and furrows - but under the supervision of an electrician, so as not to injure the cable from time to time,
    - deliver sand to the mound and help the electrician to distribute it evenly,
    - cover with native soil about 25 centimeters, and compact it,
    - lay a warning foil and cover the trench with native soil to the end, compact it in layers and finally level the area, as well as sow grass or rebuild the surface,
    - fill the losses in culverts and furrows with gypsum or other building compound.

    Only a layman can do if he wants to save on costs when making cable routes ...
  • #13 15798868
    maziar1000
    Level 15  
    Posts: 280
    Help: 4
    Rate: 45
    Krzysztof Reszka wrote:
    maziar1000 wrote:
    Bury YKY 5x6 mm?, it should be enough for you, but then call an electrician to secure everything properly

    Buddy, justify why 5 x and why 6mm2.
    We are waiting for an answer because you are misleading our friend.

    Do you think it's not enough? Loosely estimating the energy consumption and the distance given by the author, this section is sufficient. On the other hand, a larger cross-section would have to mean even greater consumption, but I do not think that the connection capacity would be sufficient. I added that he would then call an electrician to choose the security measures for him in the garage itself. I don't believe anyone came and said that in this case this cross-section is too small.

    Moderated By retrofood:

    Instead of justification, go on. A colleague has no knowledge of the principles of installation, does not know the criteria for selecting cables and misleads others. Warning. Point 3.1.11 of the forum regulations.

  • #14 15799099
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    maziar1000 wrote:
    Do you think it's not enough?

    I do not think so.
    But the colleague did not answer the questions.
    Why 5 wires and not 4, why 6 mm2 from what calculation did it come up?
    maziar1000 wrote:
    On the other hand, a larger cross-section would have to mean even more wear

    What, buddy, use electricity, maybe copper in the cable. Dude, hold back on writing on a topic you don't master.
  • #15 15800102
    CYRUS2
    Level 43  
    Posts: 17639
    Help: 1221
    Rate: 3448
    Krzysztof Reszka wrote:
    Buddy, justify why 5 x
    I already wrote it.
    Because it will be possible to install in 3 phases. In the future.
    Without digging up and laying a new earth cable.

    Distinguish between working for yourself and a project according to your requirements.
    This is not a final project.

    A colleague of maziar1000 would write how he would do it.
  • ADVERTISEMENT
  • #16 15800112
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4781
    CYRUS2 wrote:
    Krzysztof Reszka wrote:
    Buddy, justify why 5 x
    Because it will be possible to install in 3 phases.
    Quote:
    and why 6mm2.
    Little 5 x 6?
    This is enough for home use in the garage.
    This is not a machine shop.
    House - it can be expected to have a 3-phase installation.


    So now you explain to me what 5 wires are for and answer the question why not YAKY 4 x 16, since it is a much cheaper variant.
  • #17 15800124
    CYRUS2
    Level 43  
    Posts: 17639
    Help: 1221
    Rate: 3448
    tetrusmorderca wrote:
    I can connect myself.
    You are lying. Why ?
    tetrusmorderca wrote:
    Electricity is black magic to me.
    tetrusmorderca wrote:
    I was counting on someone who would know what cable to do it without spending money on an electrician.

    This is an attempt to kill garage users.
  • #18 15800177
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4781
    CYRUS2 wrote:
    Krzysztof Reszka wrote:
    Why 5 wires and not 4, why 6 mm2 from what calculation did it come up?
    Would a colleague assume 4 veins instead of five?


    I would not put it on, and it would drive! The fifth wire is completely redundant, because at this distance, both PE or PEN must be earthed in the garage! And if so, what the hell is the fifth person in the world?

    CYRUS2 wrote:

    retrofood wrote:
    So now you explain to me what 5 wires are for and answer the question why not YAKY 4 x 16, since it is a much cheaper variant.

    Are you sure the switchboard at home has TN-C?

    What does it matter what's in the house? What comes to the house is important, let's leave the house alone.
  • #19 15800190
    CYRUS2
    Level 43  
    Posts: 17639
    Help: 1221
    Rate: 3448
    retrofood wrote:
    What does it matter what's in the house? What comes home is important.
    If TN-S is connected to the switchgear, then you will not make PEN from N.
  • #20 15800267
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4781
    CYRUS2 wrote:
    retrofood wrote:
    What does it matter what's in the house? What comes home is important.
    If TN-S is connected to the switchgear, then you will not make PEN from N.


    Krzysiek, who brings the TN-S switchgear to and from where? You theorize strongly now.
  • #21 15800367
    serwisor
    Level 29  
    Posts: 1397
    Help: 96
    Rate: 164
    @ CYRUS2 How can you be sure that the installation will be connected to TN-S and not to TN-C?
    If it will be TN-S or TN-C, what's the difference, since the 5th wire will not be needed, unless, hoping for a stroke of luck, we think about the activation of the RCD, but how can you know about it, since the author did not provide any details data, and in fact, I would not like to have a garage and a house under a common RCD, because if it is to protect it, it often causes unnecessary problems, especially with a long cable buried in the ground.

    In my opinion, the lack of an entry by the author of the topic means that it should be closed until he answers the questions asked, which, by the way, does not mean that he should do it himself, because at best he will hurt himself and not others, then yes he will have a lot of problems.

    By the way, clarifying the demands would also be useful.
    tetrusmorderca wrote:
    a dozen or so fluorescent lamps and maybe some electric heater in winter.

    It turns out that these several fluorescent lamps will be faster and cheaper to buy 6 halogen fittings, 500W each, and this heater is not a 2kW farelka, but a three-phase storage heater ...

    So, Dear author, be more specific and answer ALL the questions that have been raised in the topic, and we will try to advise you on what to choose, which does not mean that you should connect it yourself, since as you suggested yourself:
    tetrusmorderca wrote:
    Electricity is black magic to me.

    greetings
    Matthew
  • #22 15800395
    Brivido
    Level 34  
    Posts: 2845
    Help: 224
    Rate: 425
    I often see 5x taken from boxes in the border, even from projects, so it's not even theorizing. How do you know that from the switchgear and not some "boxes / sockets"? How do you know there's TN-S there? Nothing is known at all.
  • #23 15800546
    tetrusmorderca
    Level 8  
    Posts: 37
    Rate: 20
    serwisor wrote:

    In my opinion, the lack of an entry by the author of the topic means that it should be closed until he answers the questions asked, which, by the way, does not mean that he should do it himself, because at best he will hurt himself and not others, then yes he will have a lot of problems.

    By the way, clarifying the demands would also be useful.

    I will try to find answers because I don't know them at the moment. So again ... What exactly do you need to know to advise me well?
    After your answers, I decided to take an electrician, but only to connect the installation. I'll run the cable myself.
  • #24 15800638
    djlukas
    Level 27  
    Posts: 1606
    Help: 94
    Rate: 266
    Gentlemen, all of you theorize. After all, it limits it within the house, so let it be placed at this distance, because a larger cross-section is unnecessary in this case.

    Ps. On Saturday, in my warehouse, a guy picked up almost 200m of 5x4mm2 yky to power the horse stables and the same amount of utp for cameras. When I asked him out of curiosity who advised him like that, he said that the electrician who was doing this installation for him.
  • #25 15800662
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    tetrusmorderca wrote:
    After your answers, I decided to take an electrician, but only to connect the installation. I'll run the cable myself.

    Mistake.
    Get an electrician now and not just to connect.
    There is nothing worse for an electrician than a customer who "carved" something on his own and calls only to be connected.
    Such clients are deleted twice or three times, because you have to exercise three times in order to comprehend what the customer has done.

    See post # 12 - invite an electrician now, agree what he does and what you can do yourself.
  • ADVERTISEMENT
  • #26 15800750
    CYRUS2
    Level 43  
    Posts: 17639
    Help: 1221
    Rate: 3448
    serwisor wrote:
    @ CYRUS2 How can you be sure that the installation will be connected to TN-S and not to TN-C?
    I am not sure, therefore I am writing about 5 veins.
    Quote:
    How will TN-S or TN-C be, what's the difference,
    A big difference because there is no PEN in a switchgear powered from TN-S.
    You can't make TN-C with TN-S.
    Quote:
    since the 5th wire will not be needed, unless we are hoping for a stroke of luck that the RCD will trip,
    5th is always needed in 3f. And it's not about the RCD at all.
    I omit the symmetrical 3-phase receiver.
    Why 3 phases and not one phase?
    tetrusmorderca wrote:
    A compressor will work in the garage - Power: 2.8kW, fan 145 [W] 0.62 [A], a dozen or so fluorescent lamps and maybe some electric heater in winter.
    If one phase is additionally loaded with a welder and a heater, it will not supply anything more from this phase.
  • #27 15800824
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    CYRUS2 wrote:
    I'm not sure

    Exactly. So why a discussion when you don't know anything?
  • #28 15801028
    maziar1000
    Level 15  
    Posts: 280
    Help: 4
    Rate: 45
    The fifth wire is spare if someone has a problem with it :D
    If someone asks what for? And what does it matter is the stock and that's it.
    By the way, since the author decided to bury the cable himself, let him write what, because I'm curious what he chose himself
  • #29 15801214
    Krzysztof Reszka
    VIP Meritorious for electroda.pl
    Posts: 10574
    Help: 609
    Rate: 1545
    Unfortunately, I missed a lot of time. Bronek, in fact, the answer fell from the hands of a friend.
    retrofood wrote:
    The fifth wire is completely redundant, because at this distance, both PE or PEN must be earthed in the garage! And if so, what the hell is the fifth person in the world?

    Remember that our author does not mention anything about the type of network, so where to make such optimistic assumptions that you should give 5 x cable. As for the cross-section, probably with the mentioned lack of the network type, its minimum cross-section can be easily selected as the cross-section for the TN-C network.
    And here I asked our friend to explain to us his misconceptions.
  • #30 16084863
    tetrusmorderca
    Level 8  
    Posts: 37
    Rate: 20
    Hello.
    It took a while, but it worked. I had to learn a bit and do a lot of research on the Internet. I put the YKY 3x4mm cable in a gray conduit at a depth of 60cm. Before I buried the cable, I consulted three electricians what cable to use. I ran the entire institution on my own, except for connecting to the switching station at home - this was done by an electrician. I had a 25A security in the box on the street, which was far too little. After applying for an increase in power, the protection was exchanged for 40A without any problems.

    I would like to add that only the compressor and lamps work in the garage at the same time, which together gives less than 4.8 KW, and usually 4.5 KW, because some of the lamps are turned off. When I use other devices, the compressor is not working. I heat the garage with a gas heater.

Topic summary

✨ The discussion revolves around selecting the appropriate cable type for a garage installation located 20-30 meters from a house, powering a 2.8kW compressor, a fan, fluorescent lamps, and potentially an electric heater. Participants emphasize the importance of knowing whether the power supply is single-phase or three-phase, as well as the total power consumption. Various cable options are suggested, including YKY 4x70mm² and YKY 5x6mm², with recommendations to consult an electrician for proper installation and safety measures. The author ultimately decided to use YKY 3x4mm² cable buried at a depth of 60cm, after consulting multiple electricians. The discussion highlights the risks of DIY electrical work without proper knowledge and the necessity of professional oversight.
Generated by the language model.

FAQ

TL;DR: For a 20–30 m garage run, a 5 × 6 mm² copper YKY cable keeps voltage-drop under 3 % at 25 A [IEC 60364-5-52]. “So get an electrician.” [Elektroda, zbich70, post #15798301]

Why it matters: Oversized once, undersized forever—wrong cable overheats and voids insurance.

Quick Facts

• Typical burial depth: 0.6-0.7 m with 10 cm sand bed + warning tape [IEC 60364-5-52]. • Current-carrying capacity 6 mm² Cu in soil: ≈34 A (90 °C XLPE) [IEC 60364-5-52]. • Voltage-drop limits: 3 % lighting, 5 % other loads [PN-HD 60364-5-52]. • Retail price YKY 5×6 mm²: €7-9 per metre (Q1 2024 EU web-stores). • Minimum bend radius multi-core 6 mm²: 6 × OD ≈ 60 mm [Prysmian Cable Guide, 2023].

Which cable size safely supplies a 2.8 kW compressor, lights and a fan over 30 m?

A 230 V single-phase load of 4.5 kW draws about 20 A. A 5 × 6 mm² Cu YKY limits voltage-drop to ≈2.7 % and stays below its 34 A rating, meeting IEC limits [IEC 60364-5-52]. Forum electricians proposed the same section for future three-phase use [Elektroda, Krzysztof Reszka, post #15798528]

Why choose a 5-core instead of a 3- or 4-core cable?

Five cores give L1-L2-L3-N-PE. You can run single-phase now and upgrade to three-phase later without digging again [Elektroda, CYRUS2, post #15800102] PE also lets each building have its own earth while keeping the neutral separate, improving RCD reliability.

Should I request single-phase or three-phase power for a workshop?

Ask the DSO for three-phase if you plan welders, EV chargers, or >5 kW heaters. Balanced three-phase halves current per core and reduces voltage sag. The application is free in many EU countries when load exceeds 6 kW [ENEA DSO Guide, 2022].

What happens if the cable is undersized?

Undersized conductors run hotter. A 3 × 4 mm² buried under 40 A protection reaches ≈70 °C in summer soil, exceeding PVC limits and risking insulation failure [Prysmian Thermal Chart, 2023]. Breakers may not trip because overcurrent is continuous, not short-circuit [Elektroda, retrofood, post #16085652]

How deep must I bury the supply cable and what layers are required?

  1. Dig 60–70 cm deep trench.
  2. Lay 10 cm sifted sand, place cable, cover with 10 cm sand.
  3. Add PVC warning tape 25 cm above cable, backfill and compact [IEC 60364-5-52].

Do I need conduit if I already use YKY?

YKY is rated for direct burial. Rigid conduit only protects against spades and rodents but traps moisture. Many electricians prefer no conduit plus sand sleeve [Elektroda, Akrzy74, post #15798566]

How do TN-C and TN-S earthing schemes change conductor count?

TN-C needs a combined PEN, so 4-core suffices. TN-S separates N and PE, hence 5 cores. If supply is TN-S you cannot recreate PEN downstream [Elektroda, CYRUS2, post #15800190] Always ask the DSO which system reaches your house.

What voltage-drop is allowed and how do I calculate it?

IEC allows 3 % for lighting circuits and 5 % otherwise. ΔV = (2 × L × I × ρ) / S. For 30 m, 20 A, Cu resistivity 0.0175 Ω mm²/m, and 6 mm² section, drop is 2.1 V (0.9 %) [IEC 60364-5-52].

Can I trench the cable myself and hire an electrician only for terminations?

Yes, but agree scope first. Electricians charge double when they must diagnose DIY errors [Elektroda, zbich70, post #15800662] Let the electrician mark the route, specify sand, and inspect before back-fill.

What test documents must the electrician leave?

He must issue continuity, insulation-resistance, and earth-fault loop impedance (IPZ) reports proving disconnection times meet SWZ requirements [Elektroda, kortyleski, post #16257425] Keep them for insurance claims.

Edge case: Is upgrading the breaker to 40 A on 3×4 mm² safe?

No. 3×4 mm² buried with 40 A can exceed its 26 A soil rating, leading to hidden overheating and fire risk [IEC 60364-5-52]. The forum called this “extreme bullshit advice” [Elektroda, zbich70, post #15798670]

How-to: three-step checklist before the electrician arrives

  1. Confirm supply earthing type (TN-C, TN-S) with DSO.
  2. Dig trench to 0.7 m, lay sand bed, route cable without sharp bends.
  3. Photograph installation, leave ends 1 m spare above ground for termination.

Is YAKY 4×16 mm² aluminium a cheaper alternative?

Yes; price is ≈€4 /m, 45 % cheaper than Cu. Its 55 A capacity equals 5×6 mm² Cu, but larger diameter needs bigger glands and terminations [Prysmian Catalogue, 2023]. Aluminium requires bi-metal lugs and antioxidant paste, adding labour cost [Elektroda, retrofood, post #15800112]

Can I add a 3 kW electric heater or welder later?

With 5×6 mm² you can raise breaker to 32 A and still keep voltage-drop under 4 %. Total continuous load should stay below 7 kW single-phase or 10 kW three-phase to avoid DSO upgrade fees [DSO Prosumer Rules, 2022].

Does an outdoor RCD need its own neutral core?

Yes. RCD measures imbalance between live and neutral. Shared neutrals upstream cause nuisance trips. A dedicated N in a 5-core solves this [IEE Wiring Regulations 18th Ed., 2018].
Generated by the language model.
ADVERTISEMENT