Appropriate Cable Selection for 6kW 400V Storage Furnaces & Heaters

Grzegorz_n 44736 28
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 6274432
    Grzegorz_n
    Level 15  
    Hello :)


    I am asking for urgent help and advice from everyone who knows the subject :)

    I need to connect (I have sufficient power allocation):
    1.5 storage furnaces, each 6kWh / 400V
    2. 3 storage heaters, each 6kWh / 400V

    I would like to ask for advice, what cables and security should I use to connect the stoves ???

    I would like to ask for the cable cross-section, but also for the name (symbol) of the cable. following the example of cables available in Castorama. And here I especially mean that a cable with thick insulation is terribly expensive compared to the same cable in thinner insulation, so I would not like to overpay and ask someone of you who knows about it, to calculate it in such a way that it was very exaggerated, just so that it would be calm enough.

    I give (for convenience) which cables are available in Catrorama:

    YDYpżo 450/750
    YDYżo 450/750
    YKYżo 0.6 / 1 kV
    OWY (H05W-F) 300 / 500V
    OWY (H05W-F) 300 / 500V
    OPDżo (H07RN-F) 450 / 750V

    Thanks in advance for any help :)


    Kind regards :)
    Gregory
  • ADVERTISEMENT
  • #2 6274660
    msgow
    Level 27  
    Hello
    If you have stoves with a power of 6kW 3-phase, each current will be about 9A per phase, so all you need is a YDYżo 5x1.5mm2 cable and a S303 B10 protection.There is a separate circuit from the switchgear to each stove and, of course, securing it with this protection.
    For correct calculations, it is also necessary to know the lengths of individual circuits in order to check the protection and slopes.
    Regards
  • #3 6274725
    abrzuzek
    Level 15  
    Hello

    Contrary to appearances, the selection of cables is not easy. From what you wrote, it's a bit too little, but let's try to come up with something.

    He understands that there will be two stove circuits, one 5 pcs and the other 3 pcs.
    These furnaces will be powered by a network voltage of 3 x 400V ~ connected in a delta.
    Appropriate Cable Selection for 6kW 400V Storage Furnaces & Heaters
    as it results from the calculations for each phase, the current of one furnace is about 9A.
    For five furnaces, the current of one phase is 45A. in such a case, I would suggest a cable with a cross-section of 10mm2 (of course, it all depends on the method of installation and other factors such as e.g. length, etc.), of course, the protection is selected according to the cable used, in this case B50, and the type of cable is e.g. YDYżo 4x10 450/750 .

    For the second circuit (three furnaces), the current is 27A / phase, for example, 4 mm2 wire has a B35 protection. YDYżo 4x4 450/750.
    The above data should be taken as an example and, to be sure, it is better to consult an electrician who will check the existing conditions on the site.
    Regards
  • #4 6274763
    Łukasz-O
    Admin of electroenergetics
    My friend abdominals , each furnace must have its own circuit, not as you propose all furnaces on one or two.
    Second, why are you suggesting four-wire cables?
  • ADVERTISEMENT
  • #5 6275049
    Grzegorz_n
    Level 15  
    welcome back :)

    Thanks for the answers :)

    msgow wrote:
    Hello
    If you have stoves with a power of 6kW 3-phase, each current will be about 9A per phase, so all you need is a YDYżo 5x1.5mm2 cable and a S303 B10 protection.There is a separate circuit from the switchgear to each stove and, of course, securing it with this protection.
    And can I find out:
    1. How many maximum loads and what protection for such a load can be given for the above-mentioned cable???
    2. How much maximum load and what protection for such a load can be given for the YDYżo 5x2.5mm2 cable ???

    Now I am satisfied with the parameters based on theoretical calculations, and in the evening I will write what are the cable lengths for individual furnaces.


    Once again THANK YOU VERY MUCH :)

    Regards :)
    Gregory
  • ADVERTISEMENT
  • #6 6275311
    kubai
    Level 14  
    Grzegorz_n wrote:
    And can I find out:
    1. How many maximum loads and what protection for such a load can be given for the above-mentioned cable???
    2. How much maximum load and what protection for such a load can be given for the YDYżo 5x2.5mm2 cable ???

    For half-conductor according to table 16A, and for 2.5mm2 it will be 20A with a load of 3 phases in pipes and installation channels on the wall. For flush-mounted installation in pipes and installation ducts, respectively 13A poltorowka and 16A 2.5mm2. When installed on a 16A half-conductor wall, 2.5 mm2 25A cable.

    Only that I would treat these values as approximate, because I really do not know what it looks like on the site.

    As for the selection of cables and protection, I would personally choose the same as my colleague msgow: half-hole and B10 protection.

    Regards
  • #7 6276368
    abrzuzek
    Level 15  
    Grzegorz_n wrote:

    I need to connect (I have sufficient power allocation):
    1.5 storage furnaces, each 6kWh / 400V
    2. 3 storage heaters, each 6kWh / 400V


    Hello
    As the above quote from my friend shows Luke-O I'm not proposing two circuits, only the author of this topic and I don't know why each furnace must have its own circuit? If certain conditions are met, you can do more.
    As for the cable, why use a five-wire cable for this system. As you can see in the diagram, the system is powered from three phases and of course the PE protective conductor must be yellow and green, but I did not draw it because it is "A, B, C" of an electrician and everyone who has a license of at least 1kV must know about it.
    Of course, I cannot imagine that the entire installation will be designed and made by a person without preparation and authorization based on a few statements from the Internet of people who think that they know about "electricity"

    I cheer you
  • #8 6276801
    Grzegorz_n
    Level 15  
    kubai wrote:
    When installed on a 16A half-conductor wall, 2.5 mm2 25A cable.
    This is an installation placed under the KG slabs, so it can be considered as an installation on the wall ???

    The length of the cable to the farthest furnace is about 20 meters, the remaining ones are 15, 10, 5 meters.

    As for the division into 2 circuits, I wrote this because I have 2 different rooms to heat and I thought to divide them according to the number of stoves installed, but if I have to make a separate circuit for each stove, it does not matter in this system.

    Now another question ... colleague abdominals he wrote that there is no need to use 5 wires, so does this mean that I can buy a 4x1.5 mm2 cable ???

    And one more question ... I heard that for the lighting installation, according to some new regulations, give you an extra vein. Is it true and what's going on? Until now, you could have 2 wires for a single switch, and 3 wires for a double switch. Is it necessary to give +1 here and here now ???


    Thanks in advance for all the advice and suggestions :)


    Gregory
  • #9 6276830
    michcio
    Electrician specialist
    For 15 years, i.e. since three-wire installations are made (in Poland, after the war), single lighting fixtures have always been connected to 3 wires, and for double fixtures (chandeliers etc.) 4 wires (PE, N, L, L). The big mistake is pulling 2 and 3 wires, respectively.
    For circuit breakers unchanged - 2 or 3 wires. Only for the switch you cannot use yellow-green and blue wires, only black, brown, red, gray etc.
  • #10 6276943
    Łukasz-O
    Admin of electroenergetics
    My friend abdominals
    Grzegorz_n wrote:

    I need to connect (I have sufficient power allocation):
    1.5 storage furnaces, each 6kWh / 400V
    2. 3 storage heaters, each 6kWh / 400V

    It does not follow from the above quote that the author suggests two circuits.

    For a long time, in accordance with the art of installation, all permanently connected receivers (especially high-power ones) should be connected on separate circuits. The stoves were always connected separately, electrically, I don't think I need to explain it.
    In addition, any short circuit or fault in the circuit causes "coldness" throughout the house. Another thing, it is much easier to control the heating from one place, e.g. from a switching station, than with each of the furnaces separately. At the stove, you can at most set the temperature, but this solution will replace the "smart home" over time.

    As for the cable, L1, L2, L3 and PE are enough for the heaters themselves, but what if there is electronics with local control in the furnace? Not to mention the usual work indicator lamp.

    5x 1.5mm2 from the calculations is enough, but we do not know the length of the individual circuits yet. I would suggest 5x2.5mm2 for each furnace. It will be a solution with a margin and much cheaper than dragging one 4x10mm2 circuit all over the object.
  • ADVERTISEMENT
  • #11 6276959
    Akrzy74
    Rest in Peace
    Grzegorz_n wrote
    Quote:
    I need to connect (I have sufficient power allocation):
    1.5 storage furnaces, each 6kWh / 400V
    2. 3 storage heaters, each 6kWh / 400V


    A separate 5x2.5 cable and B16 protection for each furnace

    The cable itself - depending on how it will be laid, but certainly YDYp ... If they will be laid in pipes or cable ducts - then it can be YDY-round.
    450V is enough.
  • #12 6278458
    abrzuzek
    Level 15  
    Hello
    Before I wrote my own topic and wrote back on the first topic, I read a lot. I have always been hurt by such mutual attacks.
    I will not pull on these personal threads because it makes no sense.
    I believe that all my speakers are experts who know their stuff, but they look at this matter differently - and that's good because the author of the topic gave us too little information and we started to guess instead of asking him additional questions.
    This is how I read his information, and since we know from the author of the topic that it may be different than it was described in the first post, I will ask my colleagues what the costs will look like? (because I think that the author of the topic is most interested in this) 8 x B16 and 8 x YDY 5x 2.5, maybe it's better to focus on it than jump down your throat?

    I greet everyone and I suggest you relax
  • #13 6278556
    Akrzy74
    Rest in Peace
    The author wrote-
    Quote:
    I would like to ask for advice, what cables and security should I use to connect the stoves ???

    On my part, the answer was.

    abrzuzek wrote
    Quote:
    This is how I read his information, and since we know from the author of the topic that it may be different than it was described in the first post, I will ask my colleagues what the costs will look like? (because I think that the author of the topic is most interested in this) 8 x B16 and 8 x YDY 5x 2.5,


    The costs are the costs, and common sense is yours. If your colleague is so economical, he will probably start to suggest making installations in the entire two-story house on two circuits / or maybe on one /. Because costs ... Such an investor is unfortunately the worst.

    Where you chop - there the chips fly ...
  • #14 6278675
    Łukasz-O
    Admin of electroenergetics
    :arrow: abdominals
    Nobody jumps at their throat.
    As for prices, B16 costs about PLN 9, the number of wire / circuit length / - no data. What are we talking about?
    Installation must be carried out in accordance with the standards, regulations and technical knowledge, and not cheaply and on one circuit.
    This forum is for the questioner to get to know the opinion of many people, and it is up to him to make decisions.

    PS. Remember that theory doesn't go along with practice.
  • #15 6278803
    abrzuzek
    Level 15  
    Hello
    Dear Colleagues, I don't think we understand each other, I don't want to cut costs. Please read carefully all the statements without emotions and answer the author of the topic about the cheapest way to connect 8 stoves with a power of 6 kW each and why it must cost so much, taking into account your knowledge and experience. The unnecessary costs can then be verified.

    Added after 21 [minutes]:

    Hello
    I don't know why you don't advise the author of the topic but focus on other matters.
    The author of the topic still does not know what to install and for what.
    (there was already about art and rights)
  • #16 6279117
    retrofood
    VIP Meritorious for electroda.pl
    abrzuzek wrote:

    I don't know why you don't advise the author of the topic but focus on other matters.
    The author of the topic still does not know what to install and for what.
    (there was already about art and rights)


    the author is to commission an authorized person to design the electrical installation.
    And all the posts are telling yourself and the muses. There is no information here for a correct answer to be given. if someone says otherwise, please provide voltage drops, please specify SWZ conditions ... etc. etc.
  • #17 6279526
    Akrzy74
    Rest in Peace
    Grzegorz_n wrote-
    Quote:
    which cable for 6 kWh accumulation furnaces?

    Quote:
    I need to connect ( I have enough power allocation) :
    1.5 storage furnaces, each 6kWh / 400V
    2. 3 storage heaters, each 6kWh / 400V

    Quote:
    I would like to ask for advice, what cables and security should I use to connect the stoves ???


    Quote:
    I especially mean that a cable with thick insulation is terribly expensive compared to the same cable with thinner insulation,

    And
    Quote:
    that it would not be too exaggerated, just so that it would be quiet enough.


    Quote:
    This is an installation placed under the KG slabs

    Quote:
    The length of the cable to the farthest furnace is about 20 meters, the remaining ones are 15, 10, 5 meters.


    Quote:
    As for the division into 2 circuits, I wrote this because I have 2 different rooms to heat and I thought to divide them according to the number of stoves installed, but if I have to make a separate circuit for each stove, it does not matter in this system.


    Answers-
    Łukasz-O wrote-
    Quote:
    5x 1.5mm2 from the calculations is enough, but we do not know the length of the individual circuits yet. I would suggest 5x2.5mm2 for each furnace. It will be a solution with a margin and much cheaper than dragging one 4x10mm2 circuit all over the object.


    Akrzy74 wrote-
    Quote:
    A separate 5x2.5 cable and B16 protection for each furnace

    The cable itself - depending on how it will be laid, but certainly YDYp ... If they will be laid in pipes or cable ducts - then it can be YDY-round.
    450V is enough.


    retrofood wrote-
    Quote:
    the author is to commission an authorized person to design the electrical installation.
    And all the posts are for oneself and for the muses. There is no information here for a correct answer to be given. if someone says otherwise, please provide voltage drops, please specify SWZ conditions ... etc. etc.
    I agree if the protections of the order C25, B50 are concerned ... Small cross-sections of wires, distances. The author clearly wrote-
    Quote:
    I have enough power allocation


    Ps- Grzegorz_n- You wrote that the stove has 6 KWh- This is how the storage capacity of the stove is given. Enter the exact type of furnace, or the power in KW / Kilowatts /
    First, you hire an electrician, and then you buy a cable / one that the electrician recommends /.
  • #18 6280652
    Grzegorz_n
    Level 15  
    Hello again and thank you so much to ALL who got involved in installing my stoves.


    Akrzy74 wrote:
    Ps- Grzegorz_n- You wrote that the stove has 6 KWh- This is how the storage capacity of the stove is given. Enter the exact type of furnace, or the power in KW / Kilowatts /
    First, you hire an electrician, and then you buy a cable / one that the electrician recommends /.
    Of course, I meant 6kW - the power of the device.

    I want to connect these ovens myself because I have some practical knowledge and I think I should be able to handle it without any problem. I know how to route cables, I know how to connect it in a switchboard, but I lack theoretical knowledge and that's why I'm here.

    As for the costs, my calculations show that I will have to run about 90 meters of cable (a separate circuit for each furnace) + fuses (3 pieces for one furnace) and that's probably all costs. The fact is that the cables are expensive, so I don't want to overpay unnecessarily, especially for one cable with a cross-section of, for example, 10 mm2.

    By the way, I will ask what cable from the switching station to the meter. The switchboard also includes:
    lighting = 1000W
    water heater = 4.5 kW (3 phases)
    2 heaters for 2 radiators - 3000W (1 phase)
    6.4 kW induction hob (3 phases)
    several sockets for standard use = let it be around 1000W

    I can answer any question if asked.


    Regards :)
    Gregory
  • #19 6281394
    michcio
    Electrician specialist
    Is this an ordinary house?
    If so, the power of general sockets will probably be 2.5 kW.
    Plus other household appliances - they also have a lot of power.
  • #20 6282012
    Akrzy74
    Rest in Peace
    I will ask out of curiosity-
    What is your main protection, what is your power allocation, distance between the switchgear and the meter, ground or overhead connection, and whether you intend to do WLZ yourself ...
  • #21 6283889
    rysiu46
    Level 12  
    Hello
    Wouldn't it be better and certainly safer to invite a licensed electrician who, after completing the installation, will sign the acceptance report. You will sleep more peacefully.
  • #22 6283921
    retrofood
    VIP Meritorious for electroda.pl
    rysiu46 wrote:
    Hello
    Wouldn't it be better and certainly safer to invite a licensed electrician who, after completing the installation, will sign the acceptance report. You will sleep more peacefully.


    I have already written:
    Here you have to do the normal electrical installation project . Of course, after inspection and consultation with the Investor.
    Any hints in absentia are dangerous !!! Colleagues, look at what powers we meet here. This is not a bell installation, where the size of the current, the selection and method of cable routing, as well as the type and size of protections do not matter much. Here mistakes threaten with serious consequences! Do you want to have it on your conscience?
  • #23 6284362
    Anonymous
    Anonymous  
  • #24 6285056
    Akrzy74
    Rest in Peace
    Quote:
    The fact is that on the forum (in general, I do not write that in this topic), there are often such advice that the hair is on the head with fear,


    Button report to the moderator + 5 points does not bite :wink:
    This makes it easier for me to "work", and for others to get the correct answer - it applies to legitimate rapporteurs ... :wink:
  • #25 6292445
    Grzegorz_n
    Level 15  
    Hello everyone :)


    Thank you again for all your suggestions :)

    I made my decision (I already had to) and purchased 100 meters of YDYp 5x2.5 mm2. A separate circuit + protection for each furnace. A little, or maybe even more than a little exaggerated, but it is better to always have a spare than not to run out when it turns out that one day such an installation will be used for something else.

    However, I have a few other problems that I would like to attach to this topic, and they are related to my renovation, so if you want to continue the discussion, I invite you HORRIBLY, because I need your help just as badly.



    Problem # 1.

    I have to connect (temporary connection - in the old switchgear) the wires: 4x4 mm2 Al on one side, and 4x4 mm2 Cu on the other. After connection, the switchgear will be covered with KG plates and will not be accessible. Not only that, this connection is in the bathroom, where (while showering), a lot of steam will probably float.

    Questions:
    1. What kind of connection should be used so that it is durable and does not corrode, because, as we know, Cu cannot be combined with Al?
    2. How to effectively and safely secure the above-mentioned connection against moisture?
    3. After the connection is made, should it be bricked up / plastered over, should it be left in the free space of the switchgear, or else something else should be done?



    Problem # 2.

    For halogen lighting (bathroom, hall, dressing room) 2x1.5 mm2 cables were placed, and from what a colleague wrote michcio , it should be 3x1.5 mm2, i.e. additionally yellow-green to 2x1.5 mm2. We all know that theoretically (for it to work) 2x1.5 mm2 is enough, but I wonder if when you come from the power industry to connect a new installation, it won't cause problems for this?

    Questions:
    1. Do those from the power industry check such things before connecting a new installation?
    2. Record on the design that there is a third strand, in fact only leave two ???
    3. Should you leave two veins, apply the same number to the project and not worry about anything ???
    4. Or maybe the third core should be used only for the bathroom (where there is moisture), and the other rooms should be left on two cores ???


    Thanks a lot for everything :)
  • #26 6292536
    retrofood
    VIP Meritorious for electroda.pl
    Grzegorz_n wrote:

    I have to connect (temporary connection - in the old switchgear) the wires: 4x4 mm2 Al on one side, and 4x4 mm2 Cu on the other. After connection, the switchgear will be covered with KG plates and will not be accessible.

    Under no circumstances should this be done

    Grzegorz_n wrote:

    Questions:
    1. What kind of connection should be used so that it is durable and does not corrode, because, as we know, Cu cannot be combined with Al?
    2. How to effectively and safely secure the above-mentioned connection against moisture?
    3. After the connection is made, should it be bricked up / plastered over, should it be left in the free space of the switchgear, or else something else should be done?

    1. Special tips are available for purchase. details - in the electric wholesaler
    2. Make the other side of the bathroom wall.
    3. Make a normal switchboard with doors. Can be hidden in the wall.

    Grzegorz_n wrote:

    For halogen lighting (bathroom, hall, dressing room) 2x1.5 mm2 cables were placed, and from what a colleague wrote michcio , it should be 3x1.5 mm2, i.e. additionally yellow-green to 2x1.5 mm2. We all know that theoretically (for it to work) 2x1.5 mm2 is enough, but I wonder if when you come from the power industry to connect a new installation, it won't cause problems for this?

    Questions:
    1. Do those from the power industry check such things before connecting a new installation?
    2. Record on the design that there is a third wire, and in fact only leave two ???
    3. Should you leave two veins, apply the same number to the project and not worry about anything ???
    4. Or maybe the third core should be used only for the bathroom (where there is moisture), and the other rooms should be left on two cores ???

    1. No.
    2. No.
    3. Halogens I would advise to convert to 12V. Safer, more durable and no need for a third cord
    4. I would give it to everyone, but in the bathroom it is necessary (and the difference)
  • #27 6295699
    Akrzy74
    Rest in Peace
    Grzegorz-n, among other things, wrote-
    Quote:
    Questions:
    1. Do those from the power industry check such things before connecting a new installation?
    2. Record on the design that there is a third wire, and in fact only leave two ???
    3. Should you leave two veins, apply the same number to the project and not worry about anything ???
    4. Or maybe the third core should be used only for the bathroom (where there is moisture), and the other rooms should be left on two cores ???


    Buddy, this is some mistake! The third lived / as you call her / is to save your life, not for the men with ED! It is high time to call an electrician for this installation.

    I consider the topic closed.
  • #28 6297110
    zubel
    Conditionally unlocked
    If you have soooo power allocation, then by the meter, if it is a single-family house without economic activity. One lighting and one socket are enough to receive.
    What will you do after the receipt is yours and, possibly, the prosecutor's case. Are you looking for savings on a few meters of cable? 2x1.5 or3x1.5? That's laugh! You won't connect these furnaces directly from the installation because they are not built-in permanently. You have to install something indirect! A socket and a plug or a box and a Ly cable between them. Better ask an electrician!
  • #29 6335289
    Al-masudi
    Level 11  
    I work in the industry that assembles AEG, Inproel and Dimplex accumulation stoves. You did the right thing by giving a 5x 2.5mm cable
    The furnaces are powered by defacto 230, not 400 V. Each heater gets 230V.
    Can you know what kind of stoves do you have?
    With this number of stoves, I would install a weather controller.

Topic summary

The discussion revolves around the appropriate cable selection for connecting 6kW storage furnaces and heaters operating at 400V. Users provide various recommendations for cable types and cross-sections, emphasizing the need for separate circuits for each furnace. Suggested cables include YDYżo 5x1.5mm² and YDYżo 5x2.5mm², with protection ratings such as B10 and B16. The importance of installation methods, lengths of circuits, and compliance with electrical standards is highlighted. The conversation also touches on the necessity of consulting a licensed electrician for safety and regulatory compliance, especially given the high power requirements of the devices involved.