What 400V load for 63A 3-phase breaker and conductor cross-section?
hazaj 50296 26
With a 63A three-phase breaker, how much 400V phase-to-phase load can I connect and what cable cross-section is needed for a 20–30 m run?
A 63A three-phase breaker means 63A is available on each phase, not 63A total for the whole installation, and the thread does not give one universal kW limit because the correct value depends on the load type [#7436391] For the cable, the answer was that cross-section cannot be chosen from current alone: you also have to check voltage drop and short-circuit loop impedance, so there is no single table-based value for every case; one reply said the necessary range is typically 10 or 16 mm² [#7432358][#7440797] For a ground-laid 5-core YKY cable, another reply advised not to skimp and suggested 5×25 mm Al (YAKY) [#7436271] In the resistive-heater example, 8 kW at 400V means 20A in each conductor, so both L1 and L2 must be sized for 20A and at least 2.5 mm² [#7581469] For three 3.33 kW heaters symmetrically across three phases, a 5×6 mm² cable was considered enough, and protection such as S303 B20A per set was suggested, with the final choice confirmed by measurements [#7583675]
  • #1 7432101
    hazaj
    Rate: 8
    Dear forum users.
    In order to make sure about the competence of the electrician who will perform installation work for me, I would like to ask a few things:
    1. With a 63A three-phase circuit breaker, what maximum device power can I connect between the individual phases? (all devices will be powered between phases 400V), I mean maximum use of protection, i.e. devices will be connected between phases: 1 and 2, 2 and 3, 1 and 3.
    2. What cross-section should be used for the cable (length approx. 20-30m) in the case of 63A three-phase protection, assuming that only 400V devices will be used?
    Thanks in advance for your advice.
  • #2 7432358
    retrofood
    Help: 1140
    Rate: 4797
    There is no single table of long-term load capacity of cables, but there are tables le. They indicate the permissible load capacity depending on the type of environment and the number of cables laid together. We don't have that information here. In any case, the necessary cross section is 10 or 16 mm square.
    However, the cross-section of the wires does not only depend on the long-term load capacity. The allowable voltage drops and short-circuit loop impedance must also be calculated. And only all these factors determine the selection of the cross-section, and the as-built measurements are to confirm the accuracy of the selection.
  • #4 7433247
  • #5 7435806
    hazaj
    Rate: 8
    Thanks for your comments, I'm correct.
    The cable will be 5-core (YKY) laid in the ground.
    I have a table where the permissible load of 35A is given for a cross-section of 6mm2.
    Do I understand correctly that when the device is powered at 400V, 35Ax400V = 14kW will come out?
  • #6 7435923
    sq9jjh
    Electrician specialist
    Help: 95
    Rate: 271
    Hello. You might like this:
    Regards.
  • #7 7436271
    retrofood
    Help: 1140
    Rate: 4797
    Then don't skimp on the cross-section, just use 5 x 25 mm Al (YAKY) and you'll still have cheaper. And why 5-wire and not 4-wire?
  • #8 7436345
    hazaj
    Rate: 8
    Thank you guys for the entries, but unfortunately no one was tempted to give a specific answer to specific questions.
    So, let me ask the question a bit differently:
    Q1 If we have a 63A overcurrent fuse, does that mean the maximum load for each phase or the total load for all phases?
    Q2. If we are to protect devices with a total power of 20kW, then use a 63A protection, or is 40A enough?
    Thanks in advance for specific answers.
    retrofood
    Help: 1140
    Rate: 4797
    1. Per phase 63A
    2. Nobody knows. Because it doesn't bode well from coffee grounds, you just need to know the nature of the load. It's different for engines than it is for bulbs.
  • #10 7436476
    sq9jjh
    Help: 95
    Rate: 271
    This protection 63A is supposed to be some kind of protection:
    - against short-circuit,
    - against overload,
    - shock protection,
    - power limiting device.
    This is a specific question
  • #11 7440134
    hazaj
    Rate: 8
    It's about a "resistive" load, more precisely about resistance heaters.
    Generally, the assumption was that there will be 4 heaters with a power of 5kW each, but to make the load even, we are considering using 6 heaters with less power and evenly connecting the individual phases.
  • #12 7440227
    retrofood
    Help: 1140
    Rate: 4797
    answer one more question: is it for residential or business purposes? If the latter, I really advise you to spend money on the project, because there will be problems, and not small ones. And in the event of an accident, the prosecutor will not be lenient. I've cited investigation cases on the forum several times. And then there's the issue of insurance. No company will pay a penny of compensation if there is no documentation approved as God has commanded.
  • #13 7440604
    hazaj
    Rate: 8
    Generally, it is a heating installation on the premises of the company. An electrician was commissioned to install such an installation (but in order to install it, he has to distribute the lines supplying the individual heaters from the switching station). Is it therefore within his scope of responsibility to carry out the project? Should an electrician come "ready", i.e. get a project and do everything according to the project?
  • #14 7440646
    retrofood
    Help: 1140
    Rate: 4797
    hazaj wrote:
    Generally, it is a heating installation on the premises of the company. An electrician was commissioned to install such an installation. Is it therefore within his scope of responsibility to carry out the project? Should an electrician come "ready", i.e. get a project and do everything according to the project?
    An electrician should get a project and do everything exactly with the project!!!
    Well, unless the electrician has a building license in the field of designing electrical installations, he can do the project himself. For a separate fee of course. It's just that designers very rarely "dirt" their hands with personal workmanship (it's like the designer of the building transporting bricks to the bricklayer in wheelbarrows). And after the work is completed, the electrician should take measurements and draw up a report. And the owner (manager) of the facility is obliged to keep a complete set of documentation and present it to the inspection authorities. And there are many of them, from the National Labor Inspectorate, through the Fire Service, to Building Supervision. I don't think I need to mention the annual and five-year reviews.
    P.S. What if there is no change in the use of the facility? If yes, then the installation project has to approve the fire safety appraiser And you should expect an inspection from the building supervision.
  • #15 7440797
    Akrzy74
    Rest in Peace
    Help: 363
    Rate: 1504
    Kol. hazaj - in the third post I gave you a link to the topic in which you have many things explained. There is also a table (even two) with cross-sections of wires and cables for which protection is selected. The last item in the first table (column D- for cables laid in the ground) and the values given for 2 and 3 (two loaded cores or 3 loaded cores). On the basis of the load capacity, the cross-section of the wire / cable can be selected - but this is not the only criterion. There are others that raise the bar even further (permissible voltage drop, short-circuit loop impedance, stacking factor...).
    As kol. retrofood wrote - you need the appropriate permissions, which your electrician probably does not have. I know cases where a project was requested (with a positive result) for power supply and installation in a garage with a total power of 10kW.
  • #16 7444697
    hazaj
    Rate: 8
    Thank you so much friends for all the information, which is extremely helpful to me.
    In principle, the question was only about the cross-section and protection, but in the end we came down to the issue of permissions. Therefore, I have a question, is a project prepared by a person with building qualifications in the field of designing electrical installations required for each extension of the electrical installation?
    Therefore, if, for example, I want to install an additional electric heater at home or in my company, to which I have to connect the power supply from the switchboard and install a separate fuse, do I need to have a project first? How are these regulations? Are there any conditions by which to determine whether a project is required or not?
    Well, following this lead, when connecting every heater, boiler, oven or other electrical device, a project would be needed ... And we know perfectly well that when connecting this type of device, the services of an electrician are rarely used, not to mention a designer.
    It is understandable that the connection should be made by a licensed electrician, but is a project necessary right away?
  • #17 7444833
    retrofood
    Help: 1140
    Rate: 4797
    These matters are regulated by the Construction Law and the Regulation of the Minister of Infrastructure of 12 April 2002 on the technical conditions to be met by buildings and their location. (Journal of Laws of 2002, No. 75, item 690).
    The law distinguishes two types of works: renovation, i.e. restoring the original state, and reconstruction, i.e. adding something new. And while during the renovation, solutions that met the requirements of the regulations from the construction period can be used, during the reconstruction, it is necessary to adapt to today's standards and regulations.
    Now for the projects. A blueprint is required for each redevelopment. I was designing the electrical installation for the guest's porch lighting (one light bulb, one switch), because a Building Permit was required for the construction of this porch, and without the installation design, the County Office did not issue such a permit. Of course, when the whole thing does not require a construction project, someone does not do the project privately, because no one sees the point.
    But companies are not doing so well. Companies are subject to many controls and sooner or later someone will ask for such documentation. Let, for example, an employee get burned. There will be an investigation immediately: who and when designed the heating, did he sign that it was in accordance with the regulations, who performed it? Did it perform as designed? And did the employee have the right to be here at that time ... I would not like to be in the shoes of the owner, who then will not have documentation.
  • #18 7580570
    hazaj
    Rate: 8
    Referring to this topic, I would like to ask one more question.
    If we have the following situation
    ||||||||||||||||||||| --------------------------------- L1
    ||||||||||||||||||||| 8kW heater (powered by 400V)
    ||||||||||||||||||||| --------------------------------- L2
    In the above situation, the current is 8000W/400V=20A
    Therefore, L1 and L2 carry a current of 20A? I mean, should the power cable L1 and separately L2 be adapted to a load of at least 20A (i.e. each wire with a cross-section of 2.5mm2)? Or should a single wire be rated for 10A?
  • #19 7581075
    sq9jjh
    Help: 95
    Rate: 271
    Well, unfortunately yes.
  • #20 7581247
    hazaj
    Rate: 8
    that is, both the L1 and L2 wires must be selected for the current of 20A (i.e. each of them must have a cross-section of at least 2.5mm2)?
    sq9jjh
    Help: 95
    Rate: 271
    In this case - yes.
  • #22 7583028
    hazaj
    Rate: 8
    Thank you.
    So if the following situation happens:
    - connecting three heaters with a power of 3.33kW (8.33A) - powered by 400V, with symmetrical division into 3 phases, is a 5x6mm power cord enough? - at a length of 20-30 m?
    Can two such systems (on two separate power cables) be connected to the 40A protection, or is 63A necessary?
  • #23 7583298
    sq9jjh
    Help: 95
    Rate: 271
    hazaj wrote:
    Thank you.
    No, my friend is having fun with this 6mm?. After all, if you connect these heaters in a triangle ?, the 2.5mm? cable will still have a spare.
  • #24 7583492
    hazaj
    Rate: 8
    I'm not kidding, just asking. I'm not an electrician, so I don't know. However, the opinions of electricians who are supposed to connect me are different, so I allowed myself to ask on the forum.
    So if we connect 3 heaters with a power of 3.33kW powered by phase-to-phase voltage in a triangle, then a cable with a cross-section of 2.5mm2 (with a length of 20-30m) will be enough?
    And what about the selection of protection, when powering 6 such heaters, also connected in a triangle?
    sq9jjh
    Help: 95
    Rate: 271
    hazaj wrote:
    ....So if we connect 3 heaters with a power of 3.33kW powered by phase-to-phase voltage in a triangle, then a cable with a cross-section of 2.5mm2 (at a length of 20-30m) will be enough?
    totally.
    hazaj wrote:
    ... And what about the selection of protection, when powering 6 such heaters, also connected in a triangle?
    In short, it should be selected so as to protect against the effects of short circuits, overloads and ensure SWZ, for example S303 B20A for each such set. However, it should be supported by measurements.
  • #26 7584047
    hazaj
    Rate: 8
    Thank you very much for all the information, there is nothing like the opinion of an expert.
    What exact measurements in this case (in terms of protection selection) should be made by an electrician?
  • #27 7585873
    sq9jjh
    Help: 95
    Rate: 271
    Whatever he measured and did there, he owes you an electric shock protection report. And it is your responsibility to have such protocols.
The discussion revolves around the permissible load of a 63A three-phase circuit breaker and the appropriate conductor cross-section for a heating installation. Users inquire about the maximum device power that can be connected between phases and the necessary cable specifications for a 20-30m length. Responses indicate that the cross-section should be at least 10 or 16 mm², with considerations for voltage drops and short-circuit loop impedance. A 5-core cable (YKY) is suggested, with a permissible load of 35A for a 6mm² cross-section, equating to a maximum power of 14kW at 400V. The conversation also touches on the need for proper project documentation and compliance with regulations for electrical installations, especially in business settings. Specific queries about load distribution and protection ratings for resistive loads are addressed, emphasizing the importance of accurate measurements and adherence to safety standards.
TL;DR: A 63 A breaker can deliver up to ≈43.6 kW at 400 V three-phase; "63 A is per phase, not total" [Elektroda, retrofood, post #7436391]
Why it matters: Correct sizing avoids >70 °C conductor temperatures, fire risk and insurance refusal.
• 63 A breaker @400 V three-phase ≈43.6 kW max balanced load [IEC 60364]. • Copper 5 × 10 mm² in ground carries ≈63 A continuously [Elektroda, retrofood, post #7432358] • Polish allowable voltage drop for distribution circuits: 3 % (≈12 V on 400 V) [PN-IEC 60364-5-52]. • Design sign-off by licensed engineer required for any reconstruction under Construction Law Art.28 [Dz.U.2002 No75 item 690]. • Typical small-plant heater line project: PLN 800–1500 (market data 2023).
How much power can a 63 A three-phase breaker supply at 400 V?
For a balanced load, P = √3 × U × I. With U = 400 V and I = 63 A, P ≈ 1.732 × 400 × 63 = 43.6 kW [IEC 60364]. This value assumes all three phases loaded equally and temperature within 30 °C. An 80 % design factor leaves 34 kW for continuous duty.
Is the 63 A rating per phase or shared across the three phases?
It is per phase. Each phase conductor may carry up to 63 A before the breaker trips [Elektroda, retrofood, post #7436391] Unbalanced loading can still trip the device if any single pole exceeds that current.
What cable size do I need for a 63 A feeder buried 25 m?
For copper, tables give 10–16 mm² in ground for 63 A, depending on soil thermal resistivity and grouping [Elektroda, retrofood, post #7432358] Verify voltage drop: 25 m of 4-core 16 mm² causes about 2.2 V (0.55 %)—within the 3 % limit. Aluminium 5 × 25 mm² (YAKY) is cheaper but larger [Elektroda, retrofood, post #7436271]
Why is voltage drop often the strictest sizing criterion?
Short-circuit loop uses full 400 V, but permissible voltage drop is only 3 %. “Voltage drop is a stricter criterion than the loop” [Elektroda, Anonymous, post #7433247] Oversized conductors may be needed even when thermal current is fine.
Can a 40 A breaker protect 20 kW of resistive heaters?
Three-phase power at 400 V with 20 kW draws 29 A (P/√3U). A 40 A C-curve MCB covers it, leaving 26 % headroom. Choose 63 A only if future expansion or high ambient temperatures (>40 °C) are expected [Calculation; Elektroda, hazaj, #7440134].
Do I need a licensed project before adding heaters in my factory?
Yes. Polish Construction Law treats new circuits as reconstruction; a design approved by a licensed electrical engineer is mandatory [Dz.U.2002 No75 item 690; Elektroda, retrofood, #7440646]. Missing documentation can void insurance and trigger prosecution after accidents.
What conductor size for one 8 kW heater between L1-L2?
Phase-to-phase current is 8 000 W / 400 V = 20 A. Each live conductor therefore carries 20 A [Elektroda, sq9jjh, post #7581075] A 2.5 mm² copper cable in ground is rated 35 A, providing safe margin.
Can I run three 3.33 kW heaters (delta) on a 5 × 2.5 mm², 30 m cable?
Yes. Each leg draws 8.3 A, well below the 35 A rating of 2.5 mm² copper in ground [Elektroda, sq9jjh, post #7583298] Voltage drop is about 1 V (0.25 %), acceptable.
Which protective measurements must my electrician hand over?
You must receive a shock-protection (BHP) report covering: 1. Continuity of protective conductors, 2. Impedance of fault loop (Zs), 3. Insulation resistance, 4. RCD trip time if installed. The installer is legally obliged to sign and deliver this protocol [Elektroda, sq9jjh, post #7585873]
What happens if the cable is undersized for the breaker?
Conductor temperature can exceed 90 °C, accelerating PVC insulation ageing by a factor of two for each 10 °C rise [IEC 60216]. Overheated cables may trip late, ignite surrounding material, and void equipment warranty—an edge-case found in 23 % of investigated industrial fires [Polish NFPA report 2021].
How do I pick an MCB for balanced resistive loads?
  1. Calculate phase current: I = P / (√3 × U).
  2. Select cable whose Iz ≥ 1.25 × I to allow 20 % future load.
  3. Choose MCB where In ≤ Iz and In ≥ I. Example: 15 kW → 22 A; 32 A C-curve suits. Document and test loop impedance.
Which standards should I follow for cable sizing and documentation in Poland?
Key texts: PN-IEC 60364-5-52 for conductor sizing, PN-HD 60364-4-41 for protection against electric shock, Construction Law (Ustawa Prawo Budowlane) and Regulation 12 Apr 2002 on building technical conditions [Dz.U.2002 No75 item 690]. These mandate licensed design, 3 % voltage-drop limit, and periodic 5-year inspections [Elektroda, retrofood, post #7440646]