What does the bypass function do in a UPS emergency power supply system?
poter13 39750 5
  • #1 7108430
    poter13
    Hello, I have a question about the BYPASS in UPS, what is it for. Please explain it to the peasant reason
  • #2 7108444
    mareeczek
    The bypass is the primary power supply (from the power grid) located in the upkeep, but after the power grid has been cut off, the connected ups supply all the circuits connected to it, except for its own bypass outputs ...
  • #3 7108463
    poter13
    that is, the bypass is such a socket without holding the voltage, connected straight from the network.
  • #4 7108832
    Darrieus
    Help: 406
    Rate: 289
    You understand well. Most often this is used to connect the next UPS when there are more than one.
  • #5 7122569
    dcserwis.pl
    There are 2 types of BYPASS in larger UPSs:
    - internal in the UPS, it is used to protect the UPS against overload, the internal circuits of the UPS are live
    - external - bypassing the entire UPS, after manually turning it on, UPS maintenance can be performed
    In both cases of BYPASS, the receivers are connected directly to the "city", so they are not protected against loss.
  • #6 7127462
    SLAL
    Help: 45
    Rate: 76
    The name itself suggests that bypass is "bypass".
    In guaranteed power supply systems, BYPASS occurs
    internal and external - service option.
    The internal BYPASS is a kind of protection of the UPS against
    overload and "dropping" of power supply to receivers - in case of overload
    switches the network directly to the output - apart from the UPS processing path, it is most common in on-line technology, less often in line-interactive,
    and secures the power supply of devices in the event of a UPS failure - supplies power
    directly from the network. Changeover is automatic and controlled
    by UPS.
    The external BYPASS is most often used to "bypass" the UPS and disconnect it
    from power supply during service works - manual BYPASS, service BYPASS.
    An output socket not "protected" is not a BYPASS!
    SLAL