Fuses for Mid-70s House: Amp Ratings & Protection for Old, Emergency Installations
cnd 79983 11
What fuse ratings should I use in a mid-1970s apartment installation, and do higher-amp fuses trip sooner or later on overloads and short circuits?
For this kind of old installation, use graded protection: with a 16 A fuse before the meter, the branch fuses are typically 10 A for lighting and 16 A for sockets, with higher-power outlets like a washing machine on 16 A [#836521][#838659][#6350979] A higher-amp fuse is less sensitive to overloads, so it will let more current pass before tripping [#836549] In a properly graded installation, a short circuit should trip the fuse regardless of its value [#836549] Selectivity also depends on the characteristic: if the fuse before the meter is gG, the downstream ones can be B or C; if the upstream protection is S B16A, there is little room for selectivity and a 16 A and 10 A device may trip together on short circuit [#837241] You also need to limit the simultaneous use of high-power appliances in this old wiring [#836521]
  • #1 836463
    cnd
    Rate: 15
    I live in a block from the mid-70s, what should be the fuses (what should be written on them), how many amps should be to protect the old, emergency installation? how is it ?, which gives more amps - ie the fuses will knock out already at a slight short-circuit or overload ??
    Thank you for your help
  • #2 836480
    piórko
    Level 30  
    Help: 176
    Rate: 90
    How is the installation done? Is the main fuse on the cage?, Aluminum wires? How many circuits in the apartment?
  • #3 836519
    cnd
    Rate: 15
    the main fuse is on the cage, aluminum wires, three circuits
  • #4 836521
    axxx
    Home appliances specialist
    Help: 376
    Rate: 1720
    Hello!!!
    In old installations from those years, the fuses are graded and on
    the main fuse is e.g. 32 A and goes down to the fuse up to 16 A
    in front of your meter and then on your meter there is only 10 A because there will be no washing machines, automatic cordless kettles etc. fuse and it is now only PLN 120. You have to limit the use of high-power receivers at the same time.
  • #5 836535
    cnd
    Rate: 15
    Oh, and on the cage there is already a "modern" fuse, such a switch is switched up and down, it writes 16A on it
    Thanks in advance for your help
  • #6 836549
    adamjur1
    Help: 772
    Rate: 1003
    There is not much you can do about it, if there are more circuits to the safety point then you can break them down into the maximum number of fuses.
    Oh, the more Amps on the fuse, the less sensitive it is to overloads. (due to a short circuit, a functional fuse in a well-graded installation should trip regardless of its value). I would like to remind you about the anti-shock protection function - in the event of voltage breakdown on the zeroed housing element, the fuse must work (or burn out if it is fusible). parameter scatter.
    Greetings J.
  • #7 836622
    cnd
    Rate: 15
    I understand that if I have 16 A in front of the meter, then these three fuses for the box behind the meter I have to buy 10 A ??
  • #8 837241
    adamjur1
    Help: 772
    Rate: 1003
    This is the result of the principle of selectivity of protections, it is also important what is the characteristic, if the one in front of the meter is a gG fuse, then these can be C or (recommended) B. If you have a S B16A in front of the meter, you do not have much room for maneuver, 16 in the same group as 10 will switch off together with 10 in the case of a short circuit. Such grading is only useful for overloads, and a slight difference does not guarantee selectivity.
    Greetings J.
  • #9 838640
    cnd
    Rate: 15
    one more question, I found out that I have to install fuses 10 and 16A in my installation, I just forgot to ask which ones should be for the circuit with lighting and which for the circuit with sockets.
  • #10 838659
  • #11 6350925
    lukaspl101
    I have a similar problem, I do not know what power to give the fuses in a residential building where I supplied the power from the house next to the 3rd phase, from the power connection
  • #12 6350979
    ROBSON33
    Admin of household appliances group
    Help: 465
    Rate: 1714
    In general, S191C16 is used for sockets, for S191B10 lighting circuits, but you do not write what security are "house next door"
The discussion revolves around selecting appropriate fuse ratings for a mid-70s residential electrical installation. The main fuse is rated at 32 A, with downstream fuses ranging from 10 A to 16 A. It is emphasized that higher amp fuses are less sensitive to overloads, while a well-graded installation should trip during short circuits regardless of fuse value. For lighting circuits, a 10 A fuse is recommended, while 16 A fuses should be used for circuits with high-power appliances like washing machines. The importance of selectivity in fuse ratings is also highlighted, suggesting that if a 16 A fuse is present before the meter, the downstream fuses should ideally be 10 A to ensure proper protection and functionality.