Can I convert an old 4-wire TN-C supply to a TN-S apartment installation by splitting PEN into PE and N in the board, and if I cannot run an earth electrode, will grounding the connector/N point be necessary for the RCD to work?

Yes: if the supply is TN-C, split the PEN conductor in the main switchboard into PE and N by landing it on the PE bar and bridging to the N bar, and the RCD will work either way even if that split point is not earthed [#9337370][#9358244] Grounding the split point is good practice and improves safety, but it is not required for the differential to trip [#9369007][#9368346] If you do ground it, remember that the connector likely does not belong to you, so you need permission from the administration/utility side [#9337370] Also make sure the PEN conductor has the appropriate cross-section, because one reply points out that an undersized PEN is a problem [#9337474]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 9337256
    Maroo_s
    Level 11  
    Posts: 31
    Help: 1
    Rate: 3
    Hello dear friends!

    Please analyze the two drawings below.
    Briefly about the topic. There is an old house and a connector on the wall. Power supply from the pole with a 4-wire cable. Power supply to the apartment on the first floor via a 4-wire cable.

    A new TN-S installation and switchgear prepared for TN-S have been installed in the apartment.

    I understand that the most optimistic solution is to ground the PEN distribution point, i.e. connect PE from the ground electrode to the board.

    So this is the arrangement:

    Rules for pasting photos are here: https://www.elektroda.pl/rtvforum/topic1491634.html
    [retrofood]

    What if it is not possible to conduct the EP? Will grounding the N point in the connector do the trick?

    What I mean, of course, is whether the differential will work, because that`s what the problem comes down to.

    I will be grateful for factual answers, because there are various versions on the forum - extremely different from each other.

    Thanks for the help in advance.

    EDIT: there is an error in the drawing: the N wire in the switchgear is disconnected with a 4-pole disconnector.

    EDIT2: Sorry, I`m pasting the pictures correctly

    layout 1:
    TN-C to TN-S Conversion in an Old House: Grounding at Distribution Point?

    layout 2:
    TN-C to TN-S Conversion in an Old House: Grounding at Distribution Point?
  • ADVERTISEMENT
  • #2 9337305
    Maroo_s
    Level 11  
    Posts: 31
    Help: 1
    Rate: 3
    The power supply to the building and the entire installation is TN-C. Only the apartment being renovated was constructed with 3- and 5-wire cables, with the planned power supply being connected to the connector with a 5-wire cable.
    Unfortunately, for some reasons, the 4-wire power supply had to remain.

    The question is whether the 4th wire of the power cable from the pole can be called PEN, but since it is grounded in the transformer station, it probably is.

    Is it possible to ground PEN in a connector? Ew. without interfering with the connector, make grounding along the way (between the connector and the board there is a box with protection which I have not drawn).
  • #3 9337370
    Miniax
    Electrician specialist
    Posts: 1438
    Help: 173
    Rate: 290
    The first thing you should do is call ZE and ask about the network layout.
    If it turns out that it is TN-C, then you divide the PEN wire in the RG into PE and N by inserting this wire into the PE strip and then bridging it to the N strip. Grounding the distribution point is not required. Additionally, a 4-pole disconnector is also unnecessary - a 3-pole one will be sufficient. As for the PEN grounding in the connector, you can do it, but the connector probably does not belong to you, so you need to contact the administration in this matter.

    Moreover, in the drawing, if you separate the PEN cable in front of the FR, where do the four wires come from to the FR?
  • #4 9337474
    remik_l
    Level 29  
    Posts: 1151
    Help: 144
    Rate: 325
    PEN conductor cross-section too small.
  • #5 9339896
    Anonymous
    Anonymous  
  • #6 9357955
    Maroo_s
    Level 11  
    Posts: 31
    Help: 1
    Rate: 3
    Bronek22 wrote:

    To the author of the topic.
    How can you perform an installation if you don`t understand how an RCD works?
    You won`t be able to check robots if you don`t know how it works.

    I don`t do it, did I write about it somewhere? If I were doing this installation, I probably wouldn`t ask such a question.

    Bronek22 wrote:

    Does the RCD have a terminal for grounding or protective conductor?
    Does the RCD manual say anything about grounding or protective conductor?
    A thinking person will understand that this is irrelevant to the operation of the RCD.
    Because the producer would write about it.
    Bronek


    Indeed, there is nothing about PE grounding. I know the principle of operation of the differential (I think so).
    My only concern is the case when there is a breakdown inside the device from the N wire to the metal casing, which is made of PE. In a "correct" installation, this will be a breakdown to ground and before anyone can touch the housing, the differential switch will turn off the voltage. If PE only appears in the table (no grounding of the distribution point) and is actually a duplicate neutral wire - will the differential switch turn off? Theoretically, a differential current will flow through PE from the receiver to the board, so... it will turn off
  • ADVERTISEMENT
  • #7 9358244
    neo_dc
    Level 32  
    Posts: 2206
    Help: 178
    Rate: 211
    The differential will work either way, the division point does not need to be grounded. Remember about the appropriate cross-section of the PE cable. You cannot use grounding in ZK without ZK`s consent.
  • #8 9358245
    Anonymous
    Anonymous  
  • #9 9367208
    Maroo_s
    Level 11  
    Posts: 31
    Help: 1
    Rate: 3
    I would like to thank my colleagues for their substantive tips.

    Bronek22 wrote:

    A thinking person will understand that this is irrelevant to the operation of the RCD.


    Bronek22 wrote:

    As you can see, you don`t know anything and you don`t know what a protective conductor is.
    What do the letters "PE" and possibly "PEN" mean?



    Buddy Bronek, you clearly have extensive knowledge on this subject, there is no doubt about it. It`s a pity that you can`t share it properly, suggesting the low level of intelligence of your interlocutors. And that`s rude


    Bronek22 wrote:

    It is not possible to give broad lectures on how security works on a forum. That`s what books are for. And school.
    Bronek

    Look at the title of the section "Electricians for beginners", bite your lip and please answer a little more broadly.

    Maybe in diffrent way. The differential detects the residual current and turns it off if it exceeds (probably) 0.5 IΔn, i.e. above 15mA, a typical RCD can turn off, but at 30mA it must.
    When, for example, a person touches a phase wire directly, current flows through it to the ground. This is basic knowledge that every user of this forum, thinking or not, should have.
    If a breakdown occurs from the phase or N conductor to the PE conductor (or to the metal casing connected to the protective conductor), current will also flow to earth and the RCD will also trip. Of course, when PE is connected to earth.


    Bronek22 wrote:

    The 30mA RCD is not intended to detect leaks to the housing.


    I agree that it`s not for that purpose, but it will work in the event of a puncture to the housing, right?

    Are you suggesting that S-ka (i.e. overcurrent switch, to be precise) is used to detect leakages?
    If I decipher SWZ correctly - Automatic Power Off is a concept that applies to automatic switches, including RCDs.
    So what`s it like?
  • #10 9367803
    Krawiecow
    Level 12  
    Posts: 30
    Rate: 9
    An overcurrent switch will not protect the circuit against leakages :) It will continue to work as if nothing had happened and will not turn off. This is why RCDs are used. ;)

    Added after 2 [minutes]:

    Maroo_s wrote:

    I agree that it`s not for that purpose, but it will work in case of a puncture on the housing, right?

    Are you suggesting that S-ka (i.e. overcurrent switch, to be precise) is used to detect leakages?
    If I decipher SWZ correctly - Automatic Power Off is a concept that applies to automatic switches, including RCDs.
    So what`s it like?


    And, of course, there are overcurrent circuit breakers with a differential element :)
  • ADVERTISEMENT
  • #11 9367868
    Miniax
    Electrician specialist
    Posts: 1438
    Help: 173
    Rate: 290
    And I still haven`t received an answer to the question: how come 4 wires enter the FR and three come out? Additionally, what is this 4th vein, since PEN has already been isolated?

    Instead of asking whether the differential switch will work, you should ask whether the circuit breaker will work and this should be the most important question - checking the IPZ.
    When current flows through the housing, "es" is supposed to act and this should be checked. The differential serves as SUPPLEMENTARY protection. Moreover, it is unlikely that in ordinary home conditions, when touching a phase wire, the RCD will trip.
  • #12 9367913
    Krawiecow
    Level 12  
    Posts: 30
    Rate: 9
    Miniax wrote:
    And I still haven`t received an answer to the question: how come 4 wires enter the FR and three come out? Additionally, what is this 4th vein, since PEN has already been isolated?

    Instead of asking whether the differential switch will work, you should ask whether the circuit breaker will work and this should be the most important question - checking the IPZ.
    When current flows through the housing, "es" is supposed to act and this should be checked. The differential serves as SUPPLEMENTARY protection. Moreover, it is unlikely that in ordinary home conditions when touching a phase wire, the RCD will trip.


    "Es" It will only operate when a current flows through it equal to or higher than the "switching on" current to which it has been adapted at a specific time. So I don`t agree that "es" has to work when the housing expires. The leakage can be of the order of mA. However, checking the short-circuit loop shows whether "ES" will operate in the REQUIRED time in the event of a short-circuit :) regards
  • #13 9368071
    Miniax
    Electrician specialist
    Posts: 1438
    Help: 173
    Rate: 290
    Krawiecow wrote:


    "Es" It will operate only when a current flows through it equal to or higher than the "switching on" current to which it has been adapted at a specific time. So I don`t agree that "es" has to work when the housing expires. The leakage can be of the order of mA. However, checking the short-circuit loop shows whether "ES" will operate in the REQUIRED time in the event of a short-circuit :) regards


    See how the circuit closes when a breakdown occurs on the device housing in the first protection class in the TN-S network system. And then say "es" won`t work.
  • #14 9368232
    Kuba_jb
    Level 15  
    Posts: 203
    Help: 10
    Rate: 14
    Don`t write nonsense! The point of division of the PEN cable into PE + N must MUST be grounded! This is the basis.
  • #15 9368243
    Miniax
    Electrician specialist
    Posts: 1438
    Help: 173
    Rate: 290
    Kuba_jb wrote:
    Don`t write nonsense! The point of division of the PEN cable into PE + N must MUST be grounded! This is the basis.


    Then I`m waiting for a recipe (quote + source) that REQUIRES grounding the chapter point. I`d love to read it ;)
    Until your friend finds such a provision, he better not spread heresy further.
  • #16 9368302
    Krawiecow
    Level 12  
    Posts: 30
    Rate: 9
    Miniax wrote:
    Krawiecow wrote:


    "Es" It will operate only when a current flows through it equal to or higher than the "switching on" current to which it has been adapted at a specific time. So I don`t agree that "es" is supposed to work when the casing expires. The leakage can be of the order of mA. However, checking the short-circuit loop shows whether "ES" will operate in the REQUIRED time in the event of a short-circuit :) regards


    See how the circuit closes when a breakdown occurs on the device housing in the first protection class in the TN-S network system. And then say "es" won`t work.


    In the case of a breakout - I agree, but not in case of a breakout after :)
  • ADVERTISEMENT
  • #17 9368331
    kkas12
    Level 43  
    Posts: 17397
    Help: 1076
    Rate: 4308
    Hello!

    And now we have other gentlemen suggesting the lack of protection against electric shock without a residual current device. Highly sensitive, of course.

    What danger (apart from an imaginary one) does a leakage of several milliamps between the phase and the housing of a stationary receiver made in protection class I pose to the user?
  • #18 9368346
    Krawiecow
    Level 12  
    Posts: 30
    Rate: 9
    Miniax wrote:
    Kuba_jb wrote:
    Don`t write nonsense! The point of division of the PEN cable into PE + N must MUST be grounded! This is the basis.


    Then I`m waiting for a recipe (quote + source) that REQUIRES grounding the chapter point. I`d love to read it ;)
    Until your friend finds such a provision, he better not spread heresy further.


    I agree, to this day I have not come across an act requiring the use of grounding of the PE N chapter point.

    Added after 17 [minutes]:

    PN-IEC 60364-3
    ELECTRICAL INSTALLATIONS IN BUILDINGS
    Part 3: Establishing general characteristics
    312.2 Types of grounding system

    I suggest you read that`s all I found.

    Added after 22 [minutes]:

    On a certain forum, I found the answer to a question asked by a forum member, by the well-known Dr. Edward Musiał. Since the Doctor agreed to make it public on that forum, I think he won`t blame me for making it public on this forum.

    "Good morning,
    The more grounding of the PEN or PE cable in the TN system, the better. Of course, the more, the higher the cost, so you should not overdo it. Moreover, multiplying grounds close together has little or no effect. After dividing the PEN conductor into PE and N conductors, it is advisable to ground the PE conductor in one place or in many places, depending on the installation configuration. In which place or places, the designer should decide, taking into account local conditions. No standard that I know of (IEC, EN or national: D, F, GB, I, A, CH, etc.) requires that a particular distribution point be grounded PEN cable, because there is no substantive justification, and such a rigid requirement would sometimes lead (I gave examples) to absurd solutions. It is allowed to ground the distribution point if it does not cause any problems, but there is no requirement to do so. In many situations it makes much more sense to ground a completely different point (or points). ....."
  • #19 9368946
    Kuba_jb
    Level 15  
    Posts: 203
    Help: 10
    Rate: 14
    TN-C to TN-S Conversion in an Old House: Grounding at Distribution Point?


    If a TN-CS network system is used, the protective-neutral conductor PEN is separated into a protective conductor PE and a neutral conductor N should take place in the connector or main switchboard of the building, and the separation point should be earthed. This ensures that the earth potential is maintained on the PE protective conductor connected to the conductive parts of accessible electrical equipment.

    If the PE wire is not grounded, it poses a risk of electric shock in the event of a receiver failure! Electrical voltage may then occur on accessible conductive parts. Therefore, the division point (or PE conductor) must be grounded.
  • #20 9369007
    neo_dc
    Level 32  
    Posts: 2206
    Help: 178
    Rate: 211
    Kuba_jb wrote:
    TN-C to TN-S Conversion in an Old House: Grounding at Distribution Point?


    If a TN-CS network system is used, the protective-neutral conductor PEN is separated into a protective conductor PE and a neutral conductor N should take place in the connector or main switchboard of the building, and the separation point should be earthed.


    Not necessarily in the main one, although it is a recommended practice that sometimes does not work, especially during renovations and expansions of installations.

    Quote:

    This ensures that the earth potential is maintained on the PE protective conductor connected to the conductive parts of accessible electrical equipment.


    With a functional PEN cable, the earth potential is also maintained. Remember that the PEN should have the appropriate cross-section.
    Quote:

    If the PE wire is not grounded, it poses a risk of electric shock in the event of a receiver failure! Electrical voltage may then occur on accessible conductive parts. Therefore, the division point (or PE conductor) must be grounded.


    If it is not connected to the distribution point at all, otherwise the RCD will always work in my opinion.


    Grounding the split point is good practice and improves safety, but is not required.
  • #21 9369156
    Akrzy74
    Rest in Peace
    Posts: 7910
    Help: 363
    Rate: 1504
    This is what happens when "theoreticians" interpret standards and regulations and transfer the requirements regarding professional energy to installations and individual consumers.

    The author received an answer to the question regarding grounding of the distribution point, and instead of guides that interpret the standards, Col. Kuba_jb refers to the source. Here you can clearly see the point of the chapter...
    TN-C to TN-S Conversion in an Old House: Grounding at Distribution Point?


    In my opinion, the topic is exhausted. I`m closing before more theorists appear.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around the conversion of a TN-C electrical system to a TN-S system in an old house, specifically addressing grounding practices at the distribution point. The main concern is whether grounding the PEN (Protective Earth and Neutral) conductor at the connector is necessary and how it affects the operation of residual current devices (RCDs). Various responses highlight that while grounding the PEN at the distribution point is advisable for safety, it may not be strictly required. The importance of proper conductor sizing and the functionality of RCDs in detecting leakage currents are emphasized. Additionally, the necessity of consulting local electrical regulations and utility providers is mentioned to ensure compliance and safety.
AI summary based on the discussion. May contain errors.
ADVERTISEMENT