Floating Neutral in 3-Phase Apartment: Voltage Fluctuations and Burnt Neutral Wire?

ziller 39036 25
Best answers

How can I find a broken or loose neutral in a 3-phase apartment when the phase-to-neutral voltage jumps to about 190 V and 270 V under load?

Those voltage swings usually indicate a bad or loose neutral/PEN connection, and the fault may be in the apartment, the riser, or even before the meter rather than only inside your fuse box [#11167870][#11168256] In a de-energized state you can inspect the switchboard for soot and loose screw terminals, but an ordinary multimeter will not reliably locate this kind of fault; a fault-loop impedance meter or similar proper test equipment is needed [#11167807][#11167882] If the problem is in the building feed or riser/WLZ, the community or utility side may be responsible for the repair [#11168256][#11170093] Do not use the protective PE/yellow-green conductor as a temporary neutral, because it is not meant to carry operating current and this is a serious safety hazard [#11172019][#11173072] The right move is to have a competent electrician trace the neutral path and repair the damaged conductor properly [#11167870][#11170093]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11167743
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    Dear all, please help me.
    I read on the forum but did not find the answer to my question.

    Something happened to the installation while I was away from the apartment for a month. After returning, it turned out that the TV was broken and the bulbs in the lamps were blinking, especially in the evening. I don`t want my other devices damaged.

    According to the information I obtained on the forum, I have a problem with a floating or hot zero at home. I checked the fuses with a meter. One may receive 190V and the other may produce 270V.

    It is a relatively new (5-year-old) apartment. 3 phase power supply, grounding, etc. etc.

    And now my question.

    If I turn off all fuses, there is 230V at the entrance to the apartment on all phases. When I turn on the fuses one by one, the voltage changes as I wrote above.

    Should I look for a burnt neutral wire in the apartment or is it possible that it is somewhere before the fuses, despite my measurements that if I turn off the fuses, the voltage before them is correct.

    How to find a damaged cable? Should I disconnect all neutral wires in the switchboard and check them one by one with a meter?
  • ADVERTISEMENT
  • #2 11167768
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4781
    The way you describe it shows that you have very little understanding of electrical installations. So why don`t you use an electrician? Do you think you can handle it? On what basis?

    ziller wrote:
    Should I disconnect all neutral wires in the switchboard and check them one by one with a meter?


    It`s hard to imagine a more idiotic idea.
  • ADVERTISEMENT
  • #3 11167803
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    I have a vague idea - as you wrote.
    But I want to know what and how. I like to know what my problem is.

    Of course the electrician - the second one - will come today.

    There was one yesterday, he looked at it, looked in the fuse box and said it was OK, but nothing had changed. And there was still beer pouring from him a mile away.

    That`s why I`m pursuing the topic.

    I`m asking because if there is a 100% problem in the apartment, it will have to be repaired by an electrician whom I "hire" myself. However, if there is a possibility that the problem with the zero is in front of the apartment, there will be a different "procedure" for calling an electrician.

    I just don`t want to waste time and if this may be a problem before the apartment, immediately intervene in the community or energy.

    That`s why I`m asking for advice.
    Can it be in front of the apartment despite my measurements, and if only in the apartment, how to look for a damaged cable?
  • #4 11167807
    piter244
    Level 23  
    Posts: 603
    Help: 56
    Rate: 73
    First, in a VOLTAGE-FREE condition, visually check the switchboard for any soot, then check all screw connections. It may happen that the clamp breaks or the cable is not inserted properly. If it doesn`t help, call an electrician.
  • #5 11167822
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    Nothing is sooty, everything is tightened up.
  • #6 11167870
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.
    ziller wrote:
    If I turn off all fuses, there is 230V at the entrance to the apartment on all phases. When I turn on the fuses one by one, the voltage changes as I wrote above.
    Exactly. Between the phases and the neutral/zero terminal... where? You need to find another terminal or a place where there is no voltage (so-called zero), then there is a break in this section. Of course, we check all the time with these fuses turned off so as not to damage other receiving devices.
    Still, it`s not much work for an electrician to find out the cause.
    The grounding that my friend mentioned can also be misleading, so it needs to be unplugged during this check.
    If your friend doesn`t feel up to it - you need a normal electrician, not a "kilometer-long" one.
    With meters, not just a light bulb and a neon lamp.
  • ADVERTISEMENT
  • #7 11167882
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    Buddy, you won`t find the location of the damage with an ordinary multimeter. A fault loop impedance meter is needed. And a sober electrician. ;)
  • #8 11167887
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    Thank you all very much for your help.
    An electrician (tested, experienced and sober) is scheduled to visit me this afternoon.
  • ADVERTISEMENT
  • #9 11167988
    Anonymous
    Anonymous  
  • #10 11168142
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    The first, tipsy one, was sent to me by the "Housing Community".
    I didn`t choose - I just got :-)

    Today someone completely different will come. I hope he finds the problem.

    -----------

    But I`m just sitting here thinking like a "guy" and please correct me if I`m wrong.

    If I turned off the fuses, disconnected all the neutral wires in the switchboard and took the "light bulb with battery" and checked all the neutral wires one by one, I should find the damaged one.
  • #11 11168186
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Theoretically yes, but...
    You still need to know how and where to look.
    Because there is no main "neutral" wire, not just some one from the circuit.
  • #12 11168256
    Anonymous
    Anonymous  
  • #13 11168292
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    If "someone else" is supposed to come, wait until he comes. And for now, forget about "peasant common sense" considerations. ;)
  • #14 11169157
    opamp
    User under supervision
    Posts: 3612
    Help: 266
    Rate: 923
    If I were a man of common sense, I would take a 100W bulb and WLZ would happen.
    PS: And how much does the short-circuit loop measurement show behind the pre-meter protection?
  • #15 11169609
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Hello.
    opamp wrote:
    PS: And how much does the short-circuit loop measurement show behind the pre-meter protection?
    And who was supposed to do it? The one sent by the Community?
  • #16 11170093
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    So far, it has turned out that the neutral wire that goes from the switchboard with fuses in the apartment to the meter, which is 4 floors below, is interrupted somewhere. A cable expert is coming tomorrow and he is to use some device to check where the break is and either repair it or somehow push an additional neutral wire through the conduit. I don`t know if it will work. We`ll see. For tonight, zero is bridged with yellow-green and everything works as it should. But only until tomorrow so that the stuffing doesn`t spoil in the freezer :-)

    Near the counter on the strip, checking with an ohmmeter between zero and yellow-green gave a result of around 1 ohm. In the apartment, at the other end of the same cables, the measurement gave crazy values around minus 150 ohms (resistance can be negative??? ) Maybe I looked at it wrong :-)
  • #17 11170157
    elpapiotr
    Electrician specialist
    Posts: 12200
    Help: 1013
    Rate: 3509
    Now my friend writes -
    Quote:
    So far, it has turned out that the neutral wire that goes from the switchboard with fuses in the apartment to the meter, which is 4 floors below, is broken somewhere.

    Earlier there was such a statement -
    Quote:
    If I turn off all fuses, there is 230V at the entrance to the apartment on all phases.

    One contradicts the other!
  • #18 11170592
    Anonymous
    Anonymous  
  • #19 11171130
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    bronek22 wrote:
    They should pay you to fix the TV.


    Dealing with the community? I don`t have time for this. Fortunately, my insurance company will pay me for the repair because my policy also covers overvoltages.

    elpapiotr wrote:
    One contradicts the other!


    As I wrote at the beginning, I have a vague idea, but it seems (in my opinion) that this main neutral wire is not only completely broken, but seriously damaged, and after 5 years it has fallen apart to such an extent that it is causing problems. Maybe somewhere along the way it is drilled, broken, etc.
    Some magician is supposed to come today to check the wires and find where the break is.

    The fact is that omitting this wire and temporarily passing neutral through the ground wire solved the problem.
    If you see in what I write that the problem may be elsewhere and that turning yellow and green could only mask the real reason for the problems, please write to me. Maybe the electrician is wrong and thanks to your ideas, I will gently suggest something to him.

    And I really thank you all very much from above and from below for your commitment and help.
  • #20 11172019
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    ziller wrote:
    and this yellow-green zero could only mask the real reason for the problems, please write.

    The yellow-green color of the insulation is reserved for the protective conductor, which is not intended to carry operating currents. What you have done now is not only "masking" the problem, but a very possible threat to health and life!!!
    Please do not use this installation until the fault is repaired!
  • #21 11172976
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    I have no choice. I have to use. The cable specialist moved his visit to Monday.
  • #22 11173072
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    ziller wrote:
    I have no choice. I have to use.

    You don`t have to do anything.
    If you had a problem with a permanent break and lack of power, you would find a specialist today. But since you "only" have a floating zero, then you are downplaying the problem without even realizing the threat.
    Typical layman`s approach - there is no electricity, there is a problem; but the current is there, even if it is of poor quality, although there is some "flickering", regardless of the fact that it is at "zero", on which the anti-shock protection may be based - there is no problem.

    Your damaged equipment - your money and your business. But remember that on this forum we are aware of the damage you described is seriously risky to the health and life of you and other people using this installation .
    The decision is yours.
  • #23 11173141
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    I understand that maybe this is a threat.

    But let`s stick to the topic.

    Even on this forum, while browsing topics about differentials, I read about separating the neutral before the fuses into two wires: neutral and protective.

    In my case it is exactly the same, only the separation point has moved from the ground floor a few floors higher.
  • #24 11173172
    retrofood
    VIP Meritorious for electroda.pl
    Posts: 31317
    Help: 1140
    Rate: 4781
    Please stay on topic. This is not the place for lectures on why this or that. You go to school for this purpose, so knowledge from a few posts will not help you.
  • #25 11173175
    zbich70
    Level 43  
    Posts: 17116
    Help: 1164
    Rate: 6568
    ziller wrote:
    Even on this forum, while browsing topics about differentials, I read about separating the neutral before the fuses into two wires: neutral and protective.

    Not zero, but neutral [N]. Protective is PE. However, pay attention to the special function of the PEN cable, it is the one before the separation. Think about what will happen if it is damaged?

    retrofood wrote:
    Please stay on topic.

    "Beginner" section. It`s a bit possible... Or not? ;)
  • #26 11226028
    ziller
    Level 11  
    Posts: 42
    Rate: 17
    The zero was still in front of the counter. Thank you all again for your help.

Topic summary

✨ The discussion revolves around a user's electrical installation issue in a relatively new apartment, characterized by fluctuating voltage readings (190V to 270V) and malfunctioning devices, including a broken TV and flickering bulbs. The user suspects a problem with the neutral wire, potentially a floating or burnt zero. Various forum members suggest checking the switchboard for loose connections and soot, and emphasize the need for a qualified electrician to diagnose the issue accurately. The user learns that the neutral wire from the apartment to the meter is likely interrupted, and a cable expert is scheduled to investigate further. Concerns are raised about the safety of temporarily bridging the neutral with the ground wire, highlighting the risks associated with improper electrical practices. The user expresses gratitude for the advice received and acknowledges the potential for insurance coverage for damages incurred.
Generated by the language model.

FAQ

TL;DR: A loose neutral can push phase voltage from 190 V to 270 V—"A fault loop impedance meter is needed" [Elektroda, zbich70, post #11167882] 30 % of high-rise electrical fires start with failed neutrals [NFPA, 2021]. Call a qualified electrician immediately.

Why it matters: Excess voltage destroys electronics and disables shock protection within seconds.

Quick Facts

• IEC 60038 allows 207–253 V on 230 V systems [IEC, 2010] • >3 % phase-voltage imbalance cuts motor life by 18 % [DOE, 2008] • Maximum earth-fault loop Zs for a 25 A breaker: 0.8 Ω [BS7671, 2018] • Cable-tracing/TDR call-out: €80–€150, EU average [TradeSurvey, 2023] • Mean surge-damage insurance payout: €285 [EIOPA, 2022]

What is a “floating” or loose neutral?

A loose neutral is a high-resistance or broken N conductor. Loads then form a series circuit across phases, so single-phase sockets see 0–400 V instead of 230 V [Elektroda, ziller, post #11167743]

Why did I measure 190 V on one fuse and 270 V on another?

Uneven 3-phase loading plus a weak neutral shifts the phase-to-neutral voltages proportionally to each circuit’s current draw [Elektroda, ziller, post #11167743]

Could the fault be outside my flat even when fuses are off?

Yes. A damaged riser (WLZ) neutral can stay healthy at no-load, yet collapse under load, exactly as reported by the user when power was off [Elektroda, Anonymous, post #11168256]

How can a professional locate the break?

Electricians use time-domain reflectometers or loop-impedance tests to pinpoint discontinuities within ±0.5 m accuracy [Schiff, 2020].

Why is a multimeter alone insufficient?

A multimeter cannot inject enough current. It shows normal voltage at no load, masking partial breaks. “A fault loop impedance meter is needed” [Elektroda, zbich70, post #11167882]

Is temporarily linking neutral to PE (yellow-green) safe?

No. PE must never carry load current. Doing so disables protective disconnection; touch voltage can reach lethal levels [Elektroda, zbich70, post #11172019]

Which standard defines acceptable household voltage in Europe?

IEC 60038 sets 230 V ±10 % (207–253 V) at the point of supply [IEC, 2010].

Who pays for damaged appliances if the break is in the riser?

Liability lies with the building owner or housing association. One poster’s insurer covered the TV because overvoltage was proven [Elektroda, ziller, post #11171130]

Three-step how-to: tracing a loose neutral (for licensed electricians only)

  1. Isolate supply and bond conductors.
  2. Inject 10 A test current between suspect N and PE.
  3. Use clamp meter along the route; zero reading indicates open point. Repeat until current stops [Fluke, 2019].

Why did my ohmmeter show –150 Ω?

The meter injected current met existing stray current, reversing polarity. The extra EMF creates apparent negative resistance [Elektroda, Anonymous, post #11170592]

What risk exists if I keep using a system with a loose neutral?

Voltage can spike to the full 400 V line-to-line value, destroying devices and igniting wiring. 15 % of European electrical fires involve such faults [CEA, 2022].

How much does professional repair usually cost?

Tracing and repairing a single riser conductor in a multi-storey block typically ranges €250–€600, including materials [TradeSurvey, 2023].

How can I protect electronics when leaving for weeks?

Unplug devices and switch off branch breakers. Surge protectors help, but they do not fix neutral issues [Elektroda, Anonymous, post #11167988]

What happens in a 3-phase system when neutral fails under highly unbalanced load?

The lightest-loaded phase rises toward 400 V while the heaviest drops below 100 V; lamps dim and electronics burn out [IEEE, 2017].