Set the meter to AC voltage and measure each conductor against a known grounded point such as a water or heating pipe; the conductor that gives the highest reading, around 230 V, is the phase [#18845283] Do not rely on a single low or unstable reading, because a high-impedance multimeter can show induced voltages and the smaller value alone does not prove a wire is neutral [#18845497] The safer recommendation from the thread is to use a neon tester or, better, a bipolar voltage tester such as a Duspol/UT18C, which directly indicates the phase wire [#18846630][#18848220] Also make sure the meter is set to voltage measurement, not current, because selecting the wrong mode is dangerous [#18845952][#18846270] If you are not confident, call an electrician [#18846630]
AI summary based on the discussion. May contain errors.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 18845251
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    Hi,
    I have a UNIT-T UT 33C meter and I would like to check which wire is phase and which is 0.
    Could someone instruct me on how to do this?

    Here is my meter.
    How to check with a meter which cable is 0 and which is phase
  • ADVERTISEMENT
  • Helpful post
    #2 18845268
    kaz69
    Level 37  
    Posts: 3357
    Help: 393
    Rate: 543
    Preferably a neon indicator.

    Added after 36 [seconds]:

    And in what installation?
  • ADVERTISEMENT
  • #3 18845281
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    kaz69 wrote:
    Preferably a neon indicator.

    Added after 36 [seconds]:

    And in what installation?


    Installation in an apartment. There is a fuse box in the apartment. I want to connect the meter cables to two of the 3 inputs, how to set the meter to what position and how to measure it.
  • Helpful post
    #4 18845283
    Sniezynka
    Level 33  
    Posts: 1508
    Help: 199
    Rate: 841
    Make a measurement between a grounded point (e.g. a water or central heating pipe) and the tested conductors in the range of 500V alternating voltage. The highest value of the indication applies to the phase wire, ie approx. 230V.
  • Helpful post
    #5 18845301
    Anonymous
    Level 1  
  • Helpful post
    #6 18845325
    H3nry
    Level 32  
    Posts: 1714
    Help: 165
    Rate: 289
    Sniezynka wrote:
    Make a measurement between a grounded point (e.g. water or central heating pipe) and the tested conductors in the 500V AC range. The highest value of the indication applies to the phase wire, ie approx. 230V.

    Exactly so, take a measurement and report the results :)
  • Helpful post
    #7 18845357
    kaz69
    Level 37  
    Posts: 3357
    Help: 393
    Rate: 543
    Give me a photo of this mailbox
  • #8 18845424
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    Below, there is a box and ... a socket that the builders connected to the refrigerator - I just have to check here which two cables are 0 to disconnect and connect to the pin because it is incorrectly installed.

    How to check with a meter which cable is 0 and which is phase How to check with a meter which cable is 0 and which is phase How to check with a meter which cable is 0 and which is phase


    So if I understood correctly:
    1. I take out each of the wires - I take one and one probe from the meter (red) to it, and the other probe (black) to some pipes, e.g. from water
    2. I repeat the operation for each cable

    If it shows> ~ 220 V, it means it's a phase cable
    If it shows 0 V it means it's cable 0

    In my case, there will be two cables with 0 and two cables with ~ 220V

    Do I understand correctly?
  • #9 18845444
    xury
    Automation specialist
    Posts: 7083
    Help: 878
    Rate: 1497
    And you can write why there is no RCD and three-core cables?
  • #10 18845449
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    xury wrote:
    And you can write why there is no RCD and three-core cables?


    I have no idea. What is the RCD and those cables you mentioned? From what I remember, builders made sockets and cables, and then an electrician set up a box. It was like that somehow.
  • #11 18845464
    xury
    Automation specialist
    Posts: 7083
    Help: 878
    Rate: 1497
    This has not been done for 25 years. Installation is not in accordance with the regulations. This is how builders do their job.
  • ADVERTISEMENT
  • #12 18845470
    karolark
    Level 43  
    Posts: 14407
    Help: 702
    Rate: 2516
    JohhnyCage11 wrote:
    xury wrote:
    And you can write why there is no RCD and three-core cables?


    I have no idea. What is the RCD and those cables you mentioned? From what I remember, builders made sockets and cables, and then an electrician set up a box. Somehow it was like that.


    The main thing is that the tiles are ?
    What is not important under plaster - electricians for organs on a hook
    Unless it's a multimedia builder
  • #13 18845474
    elpapiotr
    Electrician specialist
    Posts: 12210
    Help: 1015
    Rate: 3530
    JohhnyCage11 wrote:
    xury wrote:
    And you can write why there is no RCD and three-core cables?


    I have no idea. What is the RCD and those cables you mentioned? From what I remember, builders made sockets and cables, and then an electrician set up a box. Somehow it was like that.
    Good. somehow ... they did.
    But why the wrong values of security (the absence of a differential / differential has already been mentioned by my colleagues)
    If you were kind enough to post a photo of this box without a cover / mask (?)
  • #14 18845475
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    xury wrote:
    This has not been done for 25 years. Installation is not in accordance with the regulations. This is how builders do their job.


    As I mentioned, the construction company that did construction work pulled cables and sockets, and at the end an electrician who had permissions came and set up the box.
  • #15 18845481
    kkkamil
    Level 13  
    Posts: 223
    Rate: 23
    Heh, the peasant asked a specific question and, as usual, electricians turned out to be philosophers.

    Answer:

    You set the range to alternating voltage (NOT CURRENT!) And take one wire in the paw (yes, the metal one in your hand) and the other pole to the contact. On phase you will have an indication of around 50V, on zero you should read 0V. Of course, this is not professional and "do not do it at home", but if there is no way out ...

    The method is a bit dangerous because if you connect the wires for measuring the current by mistake, you will find out for yourself that you have found the phase. So if you are not familiar with the meter, maybe it's better to call an electrician or buy a neon lamp (a few zlotys is enough).

    greetings. Kamil

    Moderated By kozi966:

    You get warnings for such advice in this forum, and that is also how it ends in this case.
    This is a highly DANGEROUS tip.
    3.1.11. Posting non-substantive posts with harmful advice, non-troubleshooting advice, and posting identical posts that replicate or repeat information from discussions.

  • #16 18845485
    Łukasz.K
    Level 28  
    Posts: 989
    Help: 84
    Rate: 152
    If the meter shows between one wire and a grounded 160V pipe and between the other and 230V pipe. Which is phased and which is not? After all, the phase cannot be 160V with respect to the ground. Is it not? Unless someone has 160V in the socket, then maybe yes.
  • #17 18845490
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    elpapiotr wrote:
    JohhnyCage11 wrote:
    xury wrote:
    And you can write why there is no RCD and three-core cables?


    I have no idea. What is the RCD and those cables you mentioned? From what I remember, builders made sockets and cables, and then an electrician set up a box. Somehow it was like that.
    Good. somehow ... they did.
    But why the wrong values of security (the absence of a differential / differential has already been mentioned by my colleagues)
    If you were kind enough to post a photo of this box without a cover / mask (?)


    Sure please

    PS If something is wrongly done (done about 5 years ago), do I have the right to call him and tell him? All in all, it was paid to the construction company, and she hired an electrician.

    How to check with a meter which cable is 0 and which is phase
  • Helpful post
    #18 18845497
    Łukasz.K
    Level 28  
    Posts: 989
    Help: 84
    Rate: 152
    The meter must show exactly the same value between phase and pipe as it shows between the two wires in the socket. From the value of the smaller and the larger it is impossible to judge it. Because how will it be on one 120V and 180V on the other. And between the wires in the socket is 230V, which is phase and which is neutral 120V or 180V?
  • Helpful post
    #19 18845498
    elpapiotr
    Electrician specialist
    Posts: 12210
    Help: 1015
    Rate: 3530
    kkkamil wrote:
    Heh, the peasant asked a specific question and, as usual, electricians turned out to be philosophers. ...
    Yeah? How to react to the content # 8 of the author's post? When we learn about such babes?
    And the box and "elepstryk" are a failure, unfortunately, as a colleague wrote xury -
    Quote:
    This is how builders do their job
    Of course, the guarantee / warranty period has already expired and the author of the topic may ... jump on them :D
  • Helpful post
    #20 18845500
    Łukasz.K
    Level 28  
    Posts: 989
    Help: 84
    Rate: 152
    In addition, on one of these wires there must be less to the pipe than on the other because it may turn out that both are in phase. :cry:

    Added after 3 [minutes]:

    And in general, it is probably better to check it with neon lights.
  • Helpful post
    #21 18845515
    kaz69
    Level 37  
    Posts: 3357
    Help: 393
    Rate: 543
    And no one will be tied to the walls. And this socket, you have to replace it with a socket with a pin and make a substitute for "anti-shock protection" to "safely" use the refrigerator. If this is the way installation is done throughout the house, you still need to think about securing the washing machine and other devices that require a grounding pin.
  • Helpful post
    #22 18845516
    elpapiotr
    Electrician specialist
    Posts: 12210
    Help: 1015
    Rate: 3530
    Łukasz.K wrote:
    ...
    And in general, it is probably better to check it with neon lights.
    Sure, because it may turn out that blue is in phase. The builders never thought that they were not allowed to lay 2-core cables, by the way.
  • #23 18845552
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    Colleagues, unfortunately I do not know anything about it, I ordered a team that had an electrician and we did not even think that they could do something wrong. So what minimum should I do?

    1. Buy a socket with a pin for a refrigerator, washing machine, microwave?
    2. Take an electrician and he should connect it properly and ground it to the prongs right?
    3. What's wrong with the box itself? Is it about the lack of an RCD? Is it possible to install it somehow?

    What would you do in the present situation?
  • #24 18845569
    elpapiotr
    Electrician specialist
    Posts: 12210
    Help: 1015
    Rate: 3530
    Not very popular advice, criticized on the forum by users (who expect applause of their own ideas) but ...
    Get an electrician, save what he can.

    PS. Among your friends, do not recommend (or even advise against) this team of peppers, because they bring shame to professionals.
    And that it wasn't - the team didn't have an electrician, but someone who "licked two wires"
  • ADVERTISEMENT
  • #25 18845576
    kaz69
    Level 37  
    Posts: 3357
    Help: 393
    Rate: 543
    Without a 3-wire installation, you don't reel too much here. Connect the sockets with the pin and the pin to "0". And as for the box, you can't see much here. It is not known how the power goes, 1 or more phases. And what is the eti of 230 doing here?
  • #26 18845583
    elpapiotr
    Electrician specialist
    Posts: 12210
    Help: 1015
    Rate: 3530
    kaz69 wrote:
    Without a 3-wire installation, you don't reel too much here. Connect the sockets with the pin and the pin to "0" . And as for the box, you can't see much here. It is not known how the power goes, 1 or more phases. And what is the eti of 230 doing here?
    According to the principle "we protect first, then we supply"
    But in fact - even Solomon out of vain ... nothing can do, although there are veins of life, which do not know what role they play.
  • #27 18845589
    kaz69
    Level 37  
    Posts: 3357
    Help: 393
    Rate: 543
    Just like XX years ago :( .
  • #28 18845593
    JohhnyCage11
    Level 5  
    Posts: 19
    Rate: 28
    kaz69 wrote:
    Without a 3-wire installation, you don't reel too much here. Connect the sockets with the pin and the pin to "0". And as for the box, you can't see much here. It is not known how the power goes, 1 or more phases. And what is the eti of 230 doing here?


    Generally, it is done in such a way that you can turn off the electricity by sectors, such as the kitchen, children's room, bathroom or large room.

    PS The refrigerator socket has a pin
    PS 2 What is eti ze 230 and why are you surprised?
  • #29 18845608
    elpapiotr
    Electrician specialist
    Posts: 12210
    Help: 1015
    Rate: 3530
    Because a colleague of the previous speaker does not know that it is ... a bell.
  • #30 18845630
    kaz69
    Level 37  
    Posts: 3357
    Help: 393
    Rate: 543
    I was a bit surprised that such an "extended" system was equipped with a cabinet bell and no other security measures.

Topic summary

LABEL_AI_GENERATED
The discussion revolves around using a UNIT-T UT 33C multimeter to identify phase and neutral wires in an apartment's electrical installation. Users suggest measuring voltage between the wires and a grounded point, such as a water pipe, with the expectation that the phase wire will show approximately 230V while the neutral wire will show 0V. Concerns are raised about the safety and accuracy of this method, with recommendations to use a neon indicator for safer measurements. The conversation also highlights issues with the existing electrical installation, including the absence of RCDs and proper grounding, and the need for professional electrical work to ensure safety and compliance with regulations.
AI summary based on the discussion. May contain errors.

FAQ LABEL_AI_GENERATED

TL;DR: 230 V AC can stop a heart in under 0.2 s [HSE, 2018]; "Use a neon probe, not your body" [kaz69, #18845268]. Set the UT33C to 500 V AC, probe each conductor to a verified earth—≈230 V tags the phase. Why it matters: mis-identifying wires risks lethal shock and appliance damage.

Quick Facts

• Polish mains: 230 V ±10 % at 50 Hz [PSE, 2023] • Recommended meter range: ≥500 V AC, CAT II for socket checks “UT33C Manual” • Neon phase tester price: 3–10 PLN [RNIC, #18846630] • RCD trip current for socket circuits: ≤30 mA [PN-HD 60364-4-41] • Wire colours: brown = L, blue = N, yellow/green = PE [IEC 60446]

How do I find phase and neutral with a multimeter?

  1. Switch UT33C to the 500 V AC range. 2. Touch the black probe to a known earth (pipe or PE bar). 3. Touch the red probe to each conductor. ≈230 V identifies phase; ≤5 V shows neutral [Sniezynka, #18845283].

Which meter jacks should I use on the UT33C?

Insert the black lead into “COM” and the red lead into “VΩ” as pictograms on the meter indicate; never use the “10 A” jack for voltage tests to avoid fuse rupture or arc flash “UT33C Manual”.

Why is testing against earth safer than between two unknown wires?

Measuring to earth limits fault current through the meter and keeps one probe on a stable potential, reducing short-circuit risk [Łukasz.K, #18845497].

What if both wires show 120–180 V to earth?

Digital meters have high input impedance, so induced or phantom voltages can appear on open neutrals. Confirm by using a low-impedance tester or neon probe [Anonymous, #18845301].

How accurate is a neon tester compared with a multimeter?

A neon probe draws 0.5–2 mA; it lights only when true phase is present, filtering phantom voltages. Multimeters resolve ±1 V but show misleading readings on floating conductors [RNIC, #18846630].

What setting mistakes can damage the meter?

Selecting the current (A) range and touching the probes across 230 V creates a dead short that can explode the fuse and shock the user [kkkamil, #18845481].

Why do regulations now demand an RCD?

RCDs trip within 40 ms at 30 mA, reducing fatal shock probability by 97 % [HSE, 2018] and are mandatory for household socket circuits since 2009 [PN-HD 60364-4-41].

What breaker size should protect standard sockets?

Use 16 A type B breakers with 2.5 mm² wiring; oversized 20 A devices overload cables and violate Polish standard [ta­ki­ja­siu, #18845702].

How can I retrofit earthing in a two-wire outlet?

Option 1: Pull new 3-core cable. Option 2: Convert the circuit to TN-C (S) by bonding the PEN conductor to the socket earth pin, then distributing PE separately—allowed only where network PEN continuity is verified by a qualified electrician [H3nry, #18845325].

What colour wires should I expect?

Brown (or black) = phase (L); blue = neutral (N); yellow/green = protective earth (PE). Older Polish flats may have two grey wires without PE [IEC 60446].

Could the meter show 0 V yet the wire be live?

Yes. A broken neutral can sit near 0 V to earth until a load operates, suddenly rising to 230 V—an edge-case that causes surprise shocks [Łukasz.K, #18845490].

3-step quick labelling procedure?

  1. Kill power, separate conductors. 2. Re-energise, test each to earth with neon probe; mark the lit one “L”. 3. De-energise, verify continuity of blue wires back to neutral bar before final connection.