Outlet Voltage Fluctuation: Flickering Lights, 170V-230V Range, Heated/Unscrewing Plugs

Fircyk81 21345 14
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11962813
    Fircyk81
    Level 10  
    Hello and welcome.
    I hope it's the right section.
    My problem started when the light bulbs in my room started flickering. I had to turn on the light in the kitchen to stop them blinking. In some sockets, my microwave oven, printer do not work .... I measured 210V in one, 170V in the other. 228-230 in others.
    I am the first from the transformer, one plug in the board is heating up, also 2 plugs unscrew themselves.

    What could be the cause? Thanks for your answers.
  • ADVERTISEMENT
  • #2 11962909
    Juras28
    Level 12  
    Is there an overvoltage on that fuse? Maybe the socket is burned out, or the wires to the socket? Regards
  • #3 11962925
    .Jack
    Electrician specialist
    Fircyk81 wrote:
    What could be the reason

    It's like fortune-telling. Not enough details.
    Probably an old aluminum installation with fuses.
    There can be many reasons: poor contact of the cable in sockets, junction boxes, switchgear. Loose neutral contact, etc.
    Solution:
    Inspect the installation, from the socket through the junction boxes to the switchgear, and check the condition of the connections.
  • #4 11962934
    Fircyk81
    Level 10  
    surges? Does it mean it burns? Once in a while yes, but rarely. Just tighten. I'll check the socket tomorrow. But would it affect 170 volts in the socket?

    jack2com wrote:
    Solution:
    Inspect the installation, from the socket through the junction boxes to the switchgear, and check the condition of the connections.

    a job for an electrician. The installation is 20 years old.
  • ADVERTISEMENT
  • #5 11962980
    bartekfigura
    Level 29  
    First of all, we have fuses in the installation, not plugs as in the bathtub. Well, now to the point. Is it a 3 phase installation? because if so, it may be that one of the phases is too heavily loaded and there are voltage drops. Also check if the fault is not on the ZE side, i.e. invite an electrician to check the voltage values right behind the meter. It may also be that the transformer is overloaded too much, but that's more of a ZE problem. Voltage deviations may be a maximum of 10% of the rated voltage. If it is less, you have the right to advertise poor quality energy. So you can see for yourself that there can be many reasons. It's best if you invite an electrician and he will measure and check everything on site.
  • ADVERTISEMENT
  • #6 11962990
    .Jack
    Electrician specialist
    Fircyk81 wrote:
    a job for an electrician. The installation is 20 years old.

    Well, here you need an older, good electrician who gained experience on such installations.
    The fuse and the fuse socket in the switchgear are probably quite warm, the foot of the socket under the fuse may be burnt out.
    In fact, it is necessary to perform a technical inspection of the receiving installation by an electrician. And as soon as possible, because most fires are caused by the poor condition of the electrical system.
  • #7 11963021
    lukaszcafe
    Level 14  
    Of course it can have an impact.
    As a colleague wrote above - the entire installation from the fuse board to the sockets themselves - for review.
    Loose neutral, lack of contact on the fuse socket, burnt wires (especially if they are aluminum), possibly loose wires in the socket-socket lead.
    For now, these are just guesses.
    Check each point of the installation well and write what disturbing you noticed.
  • #8 11963256
    Anonymous
    Anonymous  
  • #9 11963291
    .Jack
    Electrician specialist
    Bronek22 wrote:
    There is no zero and asymmetry.

    This is not the way how the complete lack of zero can be. It would be immediately noticeable. You probably wanted to write that a poor contact on the neutral wire, or PEN if you prefer.
  • #10 11963700
    Anonymous
    Anonymous  
  • #11 11964446
    Fircyk81
    Level 10  
    Yes, 3 phase installation. I'll try to look myself.
  • #12 11965006
    kkas12
    Level 43  
    You, my friend, do not look, but look for a good electrician, because such a condition is a serious threat.
  • ADVERTISEMENT
  • #13 11965091
    Anonymous
    Anonymous  
  • #14 11974624
    przeme
    Level 20  
    Measuring the short-circuit loop impedance will help solve the problem, but that's an electrician's job.
  • #15 11975962
    Akrzy74
    Rest in Peace
    Earlier, I wrote to a colleague: "You have not written what you have already checked, and you can make a rational decision only when you have a sufficient amount of information." Unfortunately, you didn't draw any conclusions. At the moment, colleagues have provided enough information to diagnose the fault, so I close the topic.
    This is how it is when you forget about the early art of detecting damage - inspections / inspection, or maybe tinkering yourself without sufficient professional training ...

Topic summary

The discussion revolves around issues of voltage fluctuation in a three-phase electrical installation, characterized by flickering lights and varying outlet voltages (170V-230V). Users suggest potential causes including poor connections, overloaded phases, and aging wiring, particularly aluminum installations. Recommendations emphasize the need for a thorough inspection of the electrical system, including fuses, sockets, and junction boxes, to identify loose contacts or burnt components. The consensus is that a qualified electrician should be consulted to address these electrical safety concerns and perform necessary measurements.