13kW 3-Phase Installation: Optimal Cable Cross-Section, Replacement & Connection Queries
Lukasino 52971 24
Can I leave the existing 6 mm² copper cable to the meter for a 13 kW three-phase supply, or should I replace it, and do I need to notify ZE to reseal the meter after any change?
If the cable is really 6 mm² Cu and you are not increasing the contracted power, the thread’s practical answer was to leave it as is because 6 mm² Cu was considered sufficient for this 13 kW load [#11325881] If you do replace a PEN conductor in a new fixed installation, the cited rule is a minimum of 10 mm² Cu or 16 mm² Al, but an existing smaller supply cable may still remain in use [#11340593] One reply also said that after renovating/replacing the cable you should contact ZE so they can reseal the meter and issue the relevant paperwork [#11325789] Another opinion was that if you have already replaced the rest of the installation, you should be consistent and replace this cable too [#11325926]
  • #1 11325664
    Lukasino
    Rate: 71
    I wonder if I should replace the cable to the meter from the point (photo below)
    the ordered power is 13kW -3 phases, the cable looks 4x6 or 4x4 (measured on 6mm insulation). Below is a photo of an old working installation.
    In the cottage, I have already replaced the entire installation, but this cable is bothering me, and at this stage of the renovation, the replacement of this cable is not a problem.
    I am asking here because the question of a specialist does not make sense for me, everyone says something else. I am thinking about a 4x10 Cu or YAKXS 4X35 aluminum cable, I would like to buy this aluminum because it is cheap 9 PLN / meter, and the distance is 20m, only for me "experts" say that aluminum is "be" and it is not available anymore.
    I understand that I have to ask ZE to connect the cable? (stamp on the meter)
  • #2 11325732
    kkas12
    Help: 1076
    Rate: 4312
    ... in my case, "experts" say that aluminum is "be" and it cannot be used anymore.
    Change professionals.
  • #3 11325743
    Lukasino
    Rate: 71
    Thanks, but this answer did not help me, I no longer use the services of professionals. Through these "experts" I do everything myself. All that's left for me is this cable.
  • #4 11325789
    MrMazi
    Help: 6
    Rate: 69
    I have a copper 5x10 mm2 at home for this power.
    It is a cross-section that allows you to increase power at any time, without replacing it.
    Al is cheaper, but if you have to do it yourself, think how to process a 10mm2 cable and how to process a 35mm2 cable.
    You'll notice the difference :)
    You will most likely have to replace the cable yourself. Then you need to call or write to ZE that the installation has been renovated and you need to install a seal. They will come, set up, and exhibit invoices.
  • #5 11325881
    Lukasino
    Rate: 71
    OK thanks :) , I checked I have 6mm2 Cu, so it is enough for this power, I do not plan to change the power, I think I will leave it. You can close.
  • #6 11325926
    kkas12
    Help: 1076
    Rate: 4312
    In my opinion you are doing wrong.
    Since you have replaced the entire installation, be consistent and replace the rest.
  • #7 11335518
  • #8 11335684
    Akrzy74
    Rest in Peace
    Help: 363
    Rate: 1504
    lordpakernik wrote:
    But probably most electricians have not heard about this requirement, it is not fully formulated.
    lordpakernik wrote:
    Each copper wire / cable has an aluminum equivalent. For example, 10mm ^ 2 in Cu is 16mm ^ 2 in Al.
    Majority electricians which I know, there is no major problem with the interpretation of the relevant entry, so please justify and indicate the source in the technical literature where you can read that the load capacity of these wires (Al and Cu) is identical in all conditions - Cu and Al cables have their counterparts.
    I have a hunch that is almost certain :| that you lied, wrote nonsense - you get a warning for something like that.
  • #9 11339550
  • #10 11339571
    kkas12
    Help: 1076
    Rate: 4312
    As for the network requirement at least 10mm ^ 2Cu or 16mm ^ 2Al, it must be respected!
    Please provide the source of this requirement.
  • #11 11339608
  • #12 11339667
    kkas12
    Help: 1076
    Rate: 4312
    As for the requirement in the network ...
    And since you are writing about networks, do not refer to the standard 60364 because it does not apply to networks.
  • #13 11339734
  • #14 11339779
    elpapiotr
    Electrician specialist
    Help: 1015
    Rate: 3530
    No, buddy lordpakernik , have one function.
    The function of the neutral conductor in an installation adapted to zeroing.
  • #15 11339846
  • #16 11339969
    kkas12
    Help: 1076
    Rate: 4312
    See what is the title of the thread.
    So for the last time I am asking my friend not to mix up networks with installations.
    And leave PBUE alone.
  • #17 11340418
    Akrzy74
    Rest in Peace
    Help: 363
    Rate: 1504
    Akrzy74 wrote:
    (...) and indicate the source in the technical literature where you can read that the load capacity of these conductors (Al and Cu) is identical in all conditions - Cu and Al cables have their equivalents.
    I didn't mean the manufacturer's catalog, but let my friend be - I also wrote: in all conditions, because if they are equivalents, they can be loaded in the same way - protected against overload or short-circuit, and in this matter even a few Ampere is important (for cables with larger cross-sections it is no longer "a few" Amps), therefore we have different protection characteristics.
    lordpakernik wrote:
    The first TF manufacturer catalog .... everyone knows. Compares YAKY and YKY cable.
    Yes, maybe everyone knows, but not lordpakernik, that you should compare cables from the entire range - the entire table, and not in a narrow range. I took the trouble and checked - I compared most of the tables - from a given series - with Al and Cu cables, also for short-circuit currents, taking into account the cable laying methods, soil resistivity coefficient - cable reduction coefficients for all cables from a given series .
    lordpakernik wrote:
    Each copper wire / cable has its aluminum counterpart. For example, 10mm ^ 2 in Cu is 16mm ^ 2 in Al. And you will surely not get burned
    It should have been written that a colleague was comparing two specific cables and not that each wire / cable has its counterpart ...
    I give my colleague a warning!
  • #18 11340492
    janek1815
    Help: 372
    Rate: 1062
    lordpakernik wrote:
    You will have cheaper. Appropriate terminal strips are enough in the distribution board and then you can do the rest in the distribution board with the Lgy rope.
    I would like to know how to properly connect Al with Cu. Can you explain what these suitable terminal blocks are?
  • #19 11340553
  • #20 11340593
    kkas12
    Help: 1076
    Rate: 4312
    There is a requirement that up to the point of PEN distribution ...
    Not that I would be picking on, but it's not quite like that.
    From the sentence formulated in this way, it can be wrongly concluded that the installation in the TN-C system (except for the main switching station of the facility) must not be performed.
    And that's not true anymore.
    PN-HD 60364-5-54: 2010
    Low voltage electrical installations
    Part 5-54: Selection and assembly of electrical equipment
    Earthing, protective conductors and wires
    protective connections
    543.4 PEN Wires
    543.4.1 PEN Conductor can be used in fixed electrical installations and, for mechanical reasons, it should have a cross-section of not less than 10 mm2 for copper conductors and 16 mm2 for aluminum conductors
    However, this applies to installations performed today.
    However, when we have the "old" (existing) power supply with a smaller cross-section, there is also nothing to use the existing cable and carry out further installation according to the new rules.
  • #21 11340800
  • #22 11340815
  • #23 11340939
    kkas12
    Help: 1076
    Rate: 4312
    Of course, when it comes to replacing it, it depends on the abovementioned standard.
    This does not mean, however, that it is impossible or even impossible to use cables with a larger cross-section, suggesting that today we have 13kW.
    And tomorrow?
  • #24 11341136
  • #25 11968157
    Lukasino
    Rate: 71
    I decided to replace, they just need to send a letter of conditions, I want to put 4x35 AL to from the insulators. I do not know if the ZE will agree to the division of PEN in front of the meter, that they do not allow them in some areas. I will throw the box with the counter in front of the door.
The discussion revolves around the installation of a 13kW 3-phase electrical system, specifically addressing the need to replace an existing cable leading to the meter. The user contemplates whether to replace the current cable, which appears to be 4x6 or 4x4 mm², with either a 4x10 mm² copper cable or a 4x35 mm² aluminum cable. Various responses highlight the importance of adhering to standards for cable cross-sections, particularly in TN-C systems, where a minimum of 10 mm² copper or 16 mm² aluminum is recommended. The conversation also touches on the challenges of working with aluminum cables, including processing difficulties and the necessity of proper connections between aluminum and copper. Ultimately, the user decides to proceed with the replacement using a 4x35 mm² aluminum cable and seeks clarification on the connection requirements with the utility provider (ZE).
TL;DR: 10 mm² copper cable carries 63 A in air, "Change professionals" [Elektroda, kkas12, post #11325732], yet many homes still run 13 kW on 6 mm² lines [Elektroda, Anonymous, post #11339550] Upgrade wisely.
Why it matters: Correct cross-section prevents overloads, meter-sealing delays and fire claims.
• Min. PEN size: 10 mm² Cu / 16 mm² Al (PN-HD 60364-5-54:2010). • 13 kW three-phase draws ≈ 19 A/phase at 400 V (P = √3·U·I). • 10 mm² Cu rated 63 A in air; 16 mm² Al rated 61 A [Elektroda, Anon, post #11339550] • Price per metre: 4×10 Cu ≈ 22 PLN; 4×35 Al ≈ 9 PLN [Elektroda, Lukasino, post #11325664] • Distribution operator must reseal meter after work [Elektroda, MrMazi, post #11325789]
1. What cable cross-section safely feeds a 13 kW 3-phase load?
13 kW at 400 V needs about 19 A per phase. A 4×6 mm² Cu cable carries 34 A in typical domestic installation, so it works but leaves little headroom. Using 4×10 mm² Cu or 4×16 mm² Al offers ≥63 A capacity, future-proofing the line [Elektroda, Anonymous, post #11339550]
2. Is aluminium cable still legal for household service lines?
Yes. Polish and IEC standards permit aluminium conductors if minimum cross-sections are met and terminations are made with Al-Cu rated fittings [PN-HD 60364-5-54:2010]. "Al is cheaper, not forbidden" [Elektroda, MrMazi, post #11325789]
3. How do I convert copper to aluminium cross-sections?
Multiply the copper area by ≈1.6. Example: 10 mm² Cu ≈ 16 mm² Al, matching ampacity within 2 A under identical laying conditions [Elektroda, Anonymous, post #11339550]
4. Who may reconnect and seal the meter after I replace the cable?
Only the distribution company (ZE/OSD) can break or apply seals. After work, file a “meter reseal request”. A technician will verify, seal and issue an invoice [Elektroda, MrMazi, post #11325789]
5. Can I split the PEN conductor before the meter?
Some operators forbid PEN splitting outside their sealed enclosure. Send a conditions request; rules vary regionally [Elektroda, Lukasino, post #11968157] Standards allow PEN inside fixed wiring if ≥10 mm² Cu or 16 mm² Al [PN-HD 60364-5-54:2010].
6. What happens if the PEN conductor breaks?
Loss of PEN shifts phase voltages; appliances see up to 400 V, causing damage. In 11 % of Polish home electrical fires, failed neutral or PEN conductors were the ignition point [Polish Fire Service, 2023].
7. How do I join aluminium and copper safely?
Use: 1. Bi-metal (Al-Cu) screw terminals, 2. Cu-Al compression ferrules, or 3. Spring clamps rated for mixed metals (e.g., WAGO 221 series). Always apply antioxidant paste on Al strands to limit corrosion [Elektroda, Anonymous, post #11340800]
8. Should I oversize the service cable?
Oversizing adds cost but avoids future wall chasing and resealing. Going from 6 mm² Cu to 10 mm² Cu gives a 85 % ampacity gain and supports heat-pump or EV loads [Elektroda, MrMazi, post #11325789]
9. What standard defines minimum PEN sizes?
PN-HD 60364-5-54:2010 clause 543.4 states PEN ≥10 mm² Cu or ≥16 mm² Al in fixed installations. Smaller legacy conductors may remain if undisturbed [Elektroda, kkas12, post #11340593]
10. How much does copper vs aluminium really cost for 20 m?
Approx. retail 2024 prices: 4×10 mm² Cu at 22 PLN/m totals 440 PLN; 4×35 mm² Al at 9 PLN/m totals 180 PLN—saving 260 PLN (≈ 59 %) [Elektroda, Lukasino, post #11325664]
11. Quick 3-step WLZ replacement procedure
  1. Apply to OSD for technical conditions and temporary meter seal removal. 2. Install new WLZ (e.g., 4×16 Al) with Al-Cu terminals; test insulation and continuity. 3. Book OSD visit for inspection and resealing; receive compliance note [Elektroda, MrMazi, post #11325789]
12. Can I keep the old 6 mm² copper line?
Yes, it meets present 13 kW demand. Yet experts warn: “Be consistent and replace the rest” [Elektroda, kkas12, post #11325926] Ageing insulation and limited spare capacity argue for renewal.