13kW 3-Phase Installation: Optimal Cable Cross-Section, Replacement & Connection Queries

Lukasino 48633 24
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11325664
    Lukasino
    Level 16  
    Hello,

    I wonder if I should replace the cable to the meter from the point (photo below)

     13kW 3-Phase Installation: Optimal Cable Cross-Section, Replacement & Connection Queries

    the ordered power is 13kW -3 phases, the cable looks 4x6 or 4x4 (measured on 6mm insulation). Below is a photo of an old working installation.
     13kW 3-Phase Installation: Optimal Cable Cross-Section, Replacement & Connection Queries

    In the cottage, I have already replaced the entire installation, but this cable is bothering me, and at this stage of the renovation, the replacement of this cable is not a problem.

    I am asking here because the question of a specialist does not make sense for me, everyone says something else. I am thinking about a 4x10 Cu or YAKXS 4X35 aluminum cable, I would like to buy this aluminum because it is cheap 9 PLN / meter, and the distance is 20m, only for me "experts" say that aluminum is "be" and it is not available anymore.

    I understand that I have to ask ZE to connect the cable? (stamp on the meter)
  • ADVERTISEMENT
  • #2 11325732
    kkas12
    Level 43  
    Quote:
    ... in my case, "experts" say that aluminum is "be" and it cannot be used anymore.
    Change professionals.
  • #3 11325743
    Lukasino
    Level 16  
    kkas12 wrote:
    Quote:
    ... in my case, "experts" say that aluminum is "be" and it cannot be used anymore.
    Change professionals.


    Thanks, but this answer did not help me, I no longer use the services of professionals. Through these "experts" I do everything myself. All that's left for me is this cable.
  • #4 11325789
    MrMazi
    Level 16  
    I have a copper 5x10 mm2 at home for this power.
    It is a cross-section that allows you to increase power at any time, without replacing it.
    Al is cheaper, but if you have to do it yourself, think how to process a 10mm2 cable and how to process a 35mm2 cable.
    You'll notice the difference :)

    You will most likely have to replace the cable yourself. Then you need to call or write to ZE that the installation has been renovated and you need to install a seal. They will come, set up, and exhibit invoices.
  • ADVERTISEMENT
  • #5 11325881
    Lukasino
    Level 16  
    OK thanks :) , I checked I have 6mm2 Cu, so it is enough for this power, I do not plan to change the power, I think I will leave it. You can close.
  • #6 11325926
    kkas12
    Level 43  
    In my opinion you are doing wrong.
    Since you have replaced the entire installation, be consistent and replace the rest.
  • #7 11335518
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #8 11335684
    Akrzy74
    Rest in Peace
    lordpakernik wrote:
    But probably most electricians have not heard about this requirement, it is not fully formulated.
    lordpakernik wrote:
    Each copper wire / cable has an aluminum equivalent. For example, 10mm ^ 2 in Cu is 16mm ^ 2 in Al.

    Majority electricians which I know, there is no major problem with the interpretation of the relevant entry, so please justify and indicate the source in the technical literature where you can read that the load capacity of these wires (Al and Cu) is identical in all conditions - Cu and Al cables have their counterparts.
    I have a hunch that is almost certain :| that you lied, wrote nonsense - you get a warning for something like that.
  • #9 11339550
    Anonymous
    Anonymous  
  • #10 11339571
    kkas12
    Level 43  
    Quote:
    As for the network requirement at least 10mm ^ 2Cu or 16mm ^ 2Al, it must be respected!
    Please provide the source of this requirement.
  • #11 11339608
    Anonymous
    Anonymous  
  • #12 11339667
    kkas12
    Level 43  
    Quote:
    As for the requirement in the network ...

    And since you are writing about networks, do not refer to the standard 60364 because it does not apply to networks.
  • #13 11339734
    Anonymous
    Anonymous  
  • #14 11339779
    elpapiotr
    Electrician specialist
    No, buddy lordpakernik , have one function.
    The function of the neutral conductor in an installation adapted to zeroing.
  • #15 11339846
    Anonymous
    Anonymous  
  • #16 11339969
    kkas12
    Level 43  
    See what is the title of the thread.
    So for the last time I am asking my friend not to mix up networks with installations.
    And leave PBUE alone.
  • #17 11340418
    Akrzy74
    Rest in Peace
    Akrzy74 wrote:
    (...) and indicate the source in the technical literature where you can read that the load capacity of these conductors (Al and Cu) is identical in all conditions - Cu and Al cables have their equivalents.

    I didn't mean the manufacturer's catalog, but let my friend be - I also wrote: in all conditions, because if they are equivalents, they can be loaded in the same way - protected against overload or short-circuit, and in this matter even a few Ampere is important (for cables with larger cross-sections it is no longer "a few" Amps), therefore we have different protection characteristics.
    lordpakernik wrote:
    The first TF manufacturer catalog .... everyone knows. Compares YAKY and YKY cable.


    Yes, maybe everyone knows, but not lordpakernik, that you should compare cables from the entire range - the entire table, and not in a narrow range. I took the trouble and checked - I compared most of the tables - from a given series - with Al and Cu cables, also for short-circuit currents, taking into account the cable laying methods, soil resistivity coefficient - cable reduction coefficients for all cables from a given series .
    lordpakernik wrote:
    Each copper wire / cable has its aluminum counterpart. For example, 10mm ^ 2 in Cu is 16mm ^ 2 in Al. And you will surely not get burned

    It should have been written that a colleague was comparing two specific cables and not that each wire / cable has its counterpart ...

    I give my colleague a warning!
  • ADVERTISEMENT
  • #18 11340492
    janek1815
    Level 38  
    lordpakernik wrote:
    You will have cheaper. Appropriate terminal strips are enough in the distribution board and then you can do the rest in the distribution board with the Lgy rope.



    I would like to know how to properly connect Al with Cu. Can you explain what these suitable terminal blocks are?
  • #19 11340553
    Anonymous
    Anonymous  
  • #20 11340593
    kkas12
    Level 43  
    Quote:
    There is a requirement that up to the point of PEN distribution ...

    Not that I would be picking on, but it's not quite like that.
    From the sentence formulated in this way, it can be wrongly concluded that the installation in the TN-C system (except for the main switching station of the facility) must not be performed.
    And that's not true anymore.
    PN-HD 60364-5-54: 2010
    Low voltage electrical installations
    Part 5-54: Selection and assembly of electrical equipment
    Earthing, protective conductors and wires
    protective connections

    Quote:
    543.4 PEN Wires
    543.4.1 PEN Conductor can be used in fixed electrical installations and, for mechanical reasons, it should have a cross-section of not less than 10 mm2 for copper conductors and 16 mm2 for aluminum conductors


    However, this applies to installations performed today.
    However, when we have the "old" (existing) power supply with a smaller cross-section, there is also nothing to use the existing cable and carry out further installation according to the new rules.
  • #21 11340800
    Anonymous
    Anonymous  
  • #22 11340815
    Anonymous
    Anonymous  
  • #23 11340939
    kkas12
    Level 43  
    Of course, when it comes to replacing it, it depends on the abovementioned standard.
    This does not mean, however, that it is impossible or even impossible to use cables with a larger cross-section, suggesting that today we have 13kW.
    And tomorrow?
  • #24 11341136
    Anonymous
    Anonymous  
  • #25 11968157
    Lukasino
    Level 16  
    I decided to replace, they just need to send a letter of conditions, I want to put 4x35 AL to from the insulators. I do not know if the ZE will agree to the division of PEN in front of the meter, that they do not allow them in some areas. I will throw the box with the counter in front of the door.

Topic summary

The discussion revolves around the installation of a 13kW 3-phase electrical system, specifically addressing the need to replace an existing cable leading to the meter. The user contemplates whether to replace the current cable, which appears to be 4x6 or 4x4 mm², with either a 4x10 mm² copper cable or a 4x35 mm² aluminum cable. Various responses highlight the importance of adhering to standards for cable cross-sections, particularly in TN-C systems, where a minimum of 10 mm² copper or 16 mm² aluminum is recommended. The conversation also touches on the challenges of working with aluminum cables, including processing difficulties and the necessity of proper connections between aluminum and copper. Ultimately, the user decides to proceed with the replacement using a 4x35 mm² aluminum cable and seeks clarification on the connection requirements with the utility provider (ZE).