Where can I buy small 3-wire PT100 sensors for a PLC system?

student_Wojtek 5373 4
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11391276
    student_Wojtek
    Level 16  
    Posts: 238
    Help: 2
    Rate: 32
    Hello,
    I’m building a smart home system based on a PLC controller, and I have an RTD6 module that supports PT100/PT1000 temperature sensors. I’d like to use this to measure the temperature in five rooms and outdoors.
    Unfortunately, the distance from the RTD module will be quite long – often more than 10 metres – so I’d like to use 3-wire sensors (the third wire being for distance compensation).
    Unfortunately, I can’t find any tiny 3-wire sensors anywhere… everywhere I look, there are only 2-wire ones… does anyone have access to them, or know where I can buy such sensors? Alternatively, how can I compensate for long distances with 2-wire sensors?
    Best regards
    V.
  • ADVERTISEMENT
  • #2 11414366
    Maly
    Level 33  
    Posts: 2609
    Help: 195
    Rate: 336
    Hmm, I connected the extra wires directly to the sensor. It’s an SMD PT100 sensor, with two wires on each side, connected to the temperature control module.
  • ADVERTISEMENT
  • Three-wire PT100 wiring and lead-resistance compensation

    #3 11758369
    Steryd3
    Level 33  
    Posts: 1641
    Help: 241
    Rate: 301
    What do you mean by ‘tiny’? Have a look at the ranges offered by companies such as Czah, Czaki and Limatherm. They have quite a wide selection. However, the sensors they offer are quite expensive (you should expect to pay around 150 zł for a Pt100). The previous speaker gave some sensible advice about soldering 3 or even 4 wires close to the sensor. With a 3-wire system, you should also ensure that the wires are of equal length, identical diameter and made of the same material. It is also possible to take measurements using a 2-wire system with cables of a known length, taking into account the temperature offset resulting from the resistance of the wires used. The problem is estimating this offset without a calibrator. You can try measuring the resistance of the wires and, using appropriate tables relating sensor resistance to temperature, estimate the corresponding temperature offset and factor this into the PLC.
  • ADVERTISEMENT
  • #4 11857448
    Anonymous
    Level 1  
  • #5 11862861
    Szymon Tarnowski
    Level 27  
    Posts: 1292
    Help: 61
    Rate: 181
    In my humble opinion, the P100s won’t work in this application – it’s like using a sledgehammer to crack a nut, with far too much wiring involved.

    Rethink the design: consider using 1-Wire or your own 485 modules. Alternatively, you could try ‘emulating’ the PT100 from the controller side and using digital communication with the sensors.