How to add a DAFI instant water heater with pipe thermostat to a gas boiler system?

szumi3cit 3174 7
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11458887
    szumi3cit
    Level 11  
    Posts: 19
    Rate: 1
    Hello,

    I live in an old detached house with central heating, and the bathroom is heated by a gas boiler (condensing).
    Unfortunately, the kitchen is quite a distance from the boiler (which is in the loft), so it takes over a minute for hot water to come out of the tap; for short uses, the hot water doesn’t even reach the tap.
    I would like to install an electric instantaneous water heater (e.g. DAFI) on the hot water pipe from the gas boiler. I would like to install a THERMOSTATIC SWITCH on the hot water pipe before the electric water heater (at a suitable distance) so that a relay automatically switches off the heater when the hot water from the boiler ‘reaches’ the kitchen plumbing (i.e. the inlet to the heater). I’ve looked for such a switch but without success (preferably one that can be fitted onto the pipe without the need for ‘penetration’ – please could you offer some suggestions? (Apologies for the lack of Polish characters – I’m using the English version of Windows)

    Best regards!

    Polish letters are on the left-hand side, under the engineering symbols. Please correct the spelling in your posts! [retrofood]
  • ADVERTISEMENT
  • ADVERTISEMENT
  • #3 11458954
    szumi3cit
    Level 11  
    Posts: 19
    Rate: 1
    Thanks, Pletwa, but I’m looking for something more specifically designed for installation on a pipe, or with a block so I can connect it to the pipes ‘in-line’.
  • ADVERTISEMENT
  • #4 11459000
    płetwa
    Level 33  
    Posts: 1972
    Help: 164
    Rate: 547
    Is the tube made of metal? So what’s the problem? You attach the capillary tube to the pipe, tuck the rest away into an airtight casing, install it somewhere convenient and out of sight, set it to 40°C and don’t look at it again.

    But if that’s what you want.
  • #5 11459070
    szumi3cit
    Level 11  
    Posts: 19
    Rate: 1
    All in all, it’s a good idea. Do you know what sort of load I can put on this switch? I’m thinking of using a 3.7 kW heater.
  • #6 11459172
    płetwa
    Level 33  
    Posts: 1972
    Help: 164
    Rate: 547
    Unfortunately, the maximum contact rating isn’t specified anywhere. I use two of these to control my central heating boiler and, as far as I can remember, the maximum is 10A. You need at least 16A, so, as you mentioned above, you’ll need to use a suitable contactor.
  • ADVERTISEMENT
  • #7 11459273
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 806
    Here’s a 16 A terminal block Link It’s just that the load is almost at its limit. 3680 W.
  • #8 11513870
    bartek_p
    Level 31  
    Posts: 1812
    Help: 128
    Rate: 195
    Unless you’re thinking of a tap-mounted heater, all those with water temperature control have a built-in sensor. In other words, if you supply hot water from the boiler to the heater, it simply won’t switch on.
    It’s a question of choosing the right heater.