Use a room thermostat with dry contacts and wire it to COM and NC, because those are the terminals that are closed when the set temperature is reached [#11593717][#11594614] The thread also notes that a model with three terminals (NC, NO, COM) does not need its own power supply, which fits your requirement [#11592929] As a practical choice, the thread starter bought an Auraton 1300 [#11593486] They later reported that an Auraton 2005 also worked well [#11595720]
Generated by the language model.
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11590338
    galusxx
    Level 12  
    Posts: 124
    Help: 3
    Rate: 15
    Hello,

    I have a 25 kW eco-coal stove with an IRYD RTZ PID fuzzy logic controller. I’d like to buy a thermostat for it (normally open), preferably with a bimetal control mechanism, without the need for a separate power supply. In other words, the contacts are open before the set temperature is reached, and once the temperature is reached, the contacts close and the stove (controller) switches to the maintenance mode. I found something like this on Allegro: ‘Bimetal Room Temperature Controller, Room Thermostat, model: MT-2’. The problem is that it seems to work the other way round, i.e. the contacts are normally closed. Can you recommend anything?
  • ADVERTISEMENT
  • #2 11591649
    Anonymous
    Anonymous  
  • ADVERTISEMENT
  • #3 11591849
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 806
    Here you go Link
  • #4 11592899
    galusxx
    Level 12  
    Posts: 124
    Help: 3
    Rate: 15
    Exactly, but first of all, you need to connect a separate power supply to it, which I’d like to avoid, and the sensor has to be clipped onto a pipe. What I’m after is a room thermostat that measures the air temperature.
  • ADVERTISEMENT
  • #5 11592929
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 806
    It doesn’t need a power supply, but if you want a room-temperature one, get one like this . It has 3 terminals: NC, NO and COM; you’ll need the NO and COM terminals.
  • #6 11593234
    galusxx
    Level 12  
    Posts: 124
    Help: 3
    Rate: 15
    The manual says I need COM and NC.

    Which bimetallic thermostat should I use for a 25kW eco-coal stove with IRYD RTZ?

    Which bimetallic thermostat should I use for a 25kW eco-coal stove with IRYD RTZ?
  • #7 11593245
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 806
    galusxx wrote:
    So the contacts are open before the set temperature is reached

    Sorry, but you wrote that yourself.
  • #8 11593284
    galusxx
    Level 12  
    Posts: 124
    Help: 3
    Rate: 15
    Yes, that’s right, and I can see there’s a mistake in the instructions :O . Take a look at the first image :P
  • #9 11593314
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 806
    Well, there you go – the contacts must be NO.
  • ADVERTISEMENT
  • #10 11593486
    galusxx
    Level 12  
    Posts: 124
    Help: 3
    Rate: 15
    OK, I’ve bought an Auraton 1300; I’ll let you know how it performs once I’ve installed it.
  • #11 11593717
    AdamMat
    Level 11  
    Posts: 15
    Rate: 1
    Room thermostats refer to contacts that are either open or closed when the set temperature in the room is reached.
    If COM and NC are marked, you need to connect to the terminals that will be closed when the temperature is reached.
    So the instructions are correct.
  • #12 11593743
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 806
    You’re wrong.
  • #13 11594614
    pafciowaw
    Automation specialist
    Posts: 2439
    Help: 480
    Rate: 364
    AdamMat is right – you just need to read the description carefully (the two sentences preceding the first diagram) – it’s very simple and to the point.
  • #14 11594793
    andrefff
    Level 36  
    Posts: 2719
    Help: 321
    Rate: 806
    You’re right.
  • #15 11595720
    galusxx
    Level 12  
    Posts: 124
    Help: 3
    Rate: 15
    Right, we’ve finally reached a consensus :)

    Perhaps a bit off-topic :)

    There’s a bit of a mess in the village :P
    Which bimetallic thermostat should I use for a 25kW eco-coal stove with IRYD RTZ?
    And here’s the mess my installer has left me with:
    Which bimetallic thermostat should I use for a 25kW eco-coal stove with IRYD RTZ?
    And then there’s the stove from Profil:
    Which bimetallic thermostat should I use for a 25kW eco-coal stove with IRYD RTZ?

    I paid a bit extra and bought an Auraton 2005; I splashed out on the day and night programmes. Everything’s working well.