Choosing the Right Generator: 8kW vs 12kW for Putzmeister MP25 Plastering Unit with 40-50m Cord

tora302 34401 21
ADVERTISEMENT
Treść została przetłumaczona polish » english Zobacz oryginalną wersję tematu
  • #1 11709827
    tora302
    Level 2  
    Hello,

    I plan to connect the plastering unit to the power generator, but I'm not entirely sure what power the latter should provide.
    I need the generator to provide adequate power for start-up and continuous operation during plaster application.
    I will add that the power cord between the devices will be about 40-50m.
    I have 2 power generators to choose from: one with a power of 8kW (10kVa), the other with 12kW (15kVa).
    Which one will be suitable? Or is it still not enough power? I will be grateful for a hint.

    The plastering unit is Putzmeister MP25, which has the following specification:

    Pump - D6 Power
    Pumping pressure - 40 bar
    Compressor - 0.55 kW / 208 l / min
    Pump drive - 400V, 50Hz, 5.5 kW at 392 rpm
    Tank drive - 1.1 kW at 23 rpm
    Water pump - 0.78 kW at 3.4 m³/h
  • ADVERTISEMENT
  • #2 11709904
    12pawel
    Level 34  
    The first one is rather out, the second one should be fine if it really has 15kVA
    tora302 wrote:
    I will add that the power cord between the devices will be about 40-50m.

    I don't understand this at all. A power generator is a mobile device, so why use such long power cords?
  • #3 11709951
    kwantor
    Level 38  
    Why is the first one too small?
    Turns out it's just one time.
    The power supply distance has nothing to do with the power of the generator - it's a matter of voltage drop and proper cross-section selection.
  • #4 11709971
    12pawel
    Level 34  
    kwantor wrote:
    Why is the first one too small?

    The loads are themselves inductive, so high apparent power is needed. The first one is too weak.
  • ADVERTISEMENT
  • #5 11709987
    kwantor
    Level 38  
    It depends on what the launch conditions are - but it can indeed be a problem.
  • #6 11710004
    12pawel
    Level 34  
    The first is out of the question. With an inductive load (motors), the power of the generator is multiplied by two. The active power of the set is about 8kW, so the power of the aggregate is 16kVA then it will work efficiently. As you can see, even the second one is quite small, but once you have it, you can try with it.
  • #7 11710075
    tora302
    Level 2  
    12pawel wrote:
    The first one is rather out, the second one should be fine if it really has 15kVA
    tora302 wrote:
    I will add that the power cord between the devices will be about 40-50m.

    I don't understand this at all. A power generator is a mobile device, so why use such long power cords?


    An apartment in a block of flats on the 5th floor will be plastered. Unfortunately, there is no other way to connect the plastering unit (there is no power socket available in the block), but I guess that the power generator produces too much noise to stand on the balcony or in the apartment. Hence, this aggregate will be placed under the block, and we will lead the electricity to the apartment via a cable.

    So I understand that the other 12kW may not be enough either?
  • ADVERTISEMENT
  • #8 11710078
    nuszek
    Level 30  
    have a look here link

    Instead of an inverter, you can use a soft-start /a little cheaper/ and then the power of the generator is enough if it is twice as large as the largest motor, i.e. 12 kVA is enough.

    We have done this for a 55 kW motor and a 100 kVA generator, it starts without any problems on soft-start..
  • ADVERTISEMENT
  • #10 11710599
    atlantel
    Automation specialist
    The manufacturer states:
    power nom. 13.5KVA / 5.0KW
    The request will not work.
  • #11 11710965
    tora302
    Level 2  
    OK, so I guess there's nothing left but hand plaster.
    Thank you for your help!
  • #12 11710990
    kwantor
    Level 38  
    The one from the last link has 15 kW so it will do.
  • #13 11832994
    manekinen
    Level 29  
    I do not know if the question is still valid, but I will write from experience that even the second 12kW is not suitable. In plastering, all engines start at the same time, which already gives food for thought. At 15kW, if it starts smoothly "dry", then the start of a loaded plastering unit (loaded 5.5kW motoreducer) will look like an epileptic attack - and neither the unit nor the plasterers will be satisfied.
  • #14 12195889
    Maciek2808
    Level 10  
    hello. I admit that the topic interests me. I have the same problem as my colleague tora302. I have another machine. Pft Ritmo xl. with motor 5.5kw + compressor, etc. total about 7.5kw. I start the 5.5 kw motor separately and later I can turn on the rest. the machine works on 400 and 230. I called a few manufacturers of similar machines and they all talk about 15 or 16 kW. You also write about 15 kW. the matter is clear.
    Question: what brand? I want (it would be nice) to spend about PLN 10,000
    I can't afford a Honda. I know there are fake hondas. and I haven't heard about others, they are NONAME for me. do you have any opinions? what brand does the job?? I was thinking about a liquid-cooled diesel. Regards
  • #15 12201524
    manekinen
    Level 29  
    In each aggregate, you can manually turn on the engines separately, but you won't do it when you release the mortar - they must start together, well at least the water pump with the mortar - then you can attach the compressor and basket if it has a separate engine. And I think you know very well what eggs are like, when the glass dries up and the motoreducer cannot move it, then even after a short downtime, these 15kW may not be enough (as with a long power cord). For comfortable work, it is really worth looking for a more powerful aggregate, because these 15kW is such a minimum, and more combinations will be at the machine itself, like robots.
  • #16 12201620
    Maciek2808
    Level 10  
    hmm. You know, if you're right, I'll listen to you. It sounds sesownie. How much would you propose. 18 is enough? It's probably not worth $10,000 then. What brand do you suggest?
  • #18 12204005
    vanobro
    Level 11  
    when the water pressure is adequate, the pump is not needed. Always 0.7kV in "pocket" :)
  • #19 12204042
    Maciek2808
    Level 10  
    it so happens that I do not have a water pump in this model. But at some point, she'd rather have to be attached. otherwise, I'd rather not recommend a self-leveling screed. To be honest, I haven't used Ritmo yet. Still in PL. will be picked up in early May.
  • #20 12205155
    eljarkos
    Level 21  
    tora302 wrote:
    An apartment in a block of flats on the 5th floor will be plastered. Unfortunately, there is no other way to connect the plastering unit (there is no power socket available in the block)

    There are never power sockets in the block, but there are 3-phase power strips in floor switchgears. You apply to the power company for a power supply permit for the duration of the work and connect the extension cord and that's it. That's what I did and that's what, for example, scrapers do.
  • #21 12209507
    190_Wojciech
    Level 20  
    The friend's solution makes the most sense eljarkos

    For comfortable operation, a generator of about 20kVA
    Petrol prices of this capacity oscillate around PLN 20,000
    22kVA in the open version without housing costs about PLN 15,000 net
    Diesel 20 kVA is about PLN 20,000 net
  • #22 12477563
    Maciek2808
    Level 10  
    Thanks a lot for the info. So far, I can do it on 230. I only worked with clients who had 400. I bought a car and I don't have money for investments this year. I hope that in January the pradotworczy will appear. Regards

Topic summary

The discussion revolves around selecting an appropriate generator for the Putzmeister MP25 plastering unit, specifically whether to choose an 8kW or a 12kW generator. Key considerations include the power requirements for start-up and continuous operation, especially given the 40-50m power cord length. Responses indicate that the 8kW generator is insufficient due to the inductive nature of the loads, which require higher apparent power. The consensus suggests that a generator with at least 15kVA is necessary, with some recommending even higher capacities (around 20kVA) for optimal performance. Concerns about noise levels and the practicality of using a generator in a residential setting were also discussed, leading to suggestions for alternative power supply solutions.