Induction Hob 230V: Comparing 4.5kV vs 7.2kV & 4.0kV Models for Apartment Installation
kodam 36642 10
Can I install a 7 kW induction hob on a 230 V apartment supply limited to 4.5 kW, or should I choose a 3.7–4.0 kW model instead?
A 3.68 kW/230 V induction hob should work in your apartment, while a 7 kW model will likely exceed your 4.5 kW allocation and may trip the 20 A protection if other appliances are running [#12414337][#12416312][#12416678] A hob with four zones rated 2x1.4 kW and 2x1.8 kW was specifically mentioned as having a connected load of 3.68 kW/230 V [#12415570] Users said this level of power gives reasonable cooking times, and even a 1.8 kW zone was described as enough for normal cooking; full power is mainly needed to bring food to the boil quickly [#12415490][#12415750]
  • #1 12414018
    kodam
    Rate: 29
    I am dealing with the purchase of an induction hob. I have a dilemma which to choose.
    Installation in an apartment 230V max. 4.5 kV.
    Can I mount a 7.2 kV board and use it carefully?
    Should I mount a 4.0 kV hob, only or will it not be too slow to cook?
  • #2 12414078
    Nereida4
    Help: 32
    Rate: 75
    Enter what other electricity receivers you have installed in the apartment.
    ps. power is measured in kW, not kV
  • #3 12414337
    Rysiek_XL
    Help: 9
    Rate: 31
    Hi.
    If you have a power allocation of 4.5 [kW], you probably have a protection of 20 [A].
    If you do not request a larger power allocation, the use of the 7 [kW] plate may not be possible, unless you write reasonably. It will only probably happen that someone will turn on the washing machine, something else and will, unfortunately, throw off the security.
    Regards.
  • #4 12414512
    vodiczka
    Help: 1185
    Rate: 4310
    How many half plates and what power of individual segments? I have a tourist one-field ALASKA with a power of 1800 W and I cook great at 20% of the power. You need full power to bring the contents to the boil QUICKLY, and you use some of the power for cooking.
  • #5 12414530
    kodam
    Rate: 29
    Washing machine, oven, TV, fridge, kettle.
    I know that when I turn everything on to the maximum, I know. I'm more interested in whether the 3.7 kW hob has any reasonable cooking time
  • #6 12415490
    vodiczka
    Help: 1185
    Rate: 4310
    This is the answer, finally, how many half of this disc is and what is the power of individual discs. As I wrote above, 1800 W / field gives more than reasonable cooking time and 1200W / field is also enough.
    Added after 53 [seconds]:
    A small part :D
  • #7 12415570
    kodam
    Rate: 29
    The board has four Bosch PIA611T66E fields
    2X1.4kW
    2X1.8kW
    Connected load 3.68kW / 230V
  • #8 12415750
    Rysiek_XL
    Help: 9
    Rate: 31
    Hi.
    I have a board with four fields 2x1.8 [kW] and 2x1.0 [kW]. I am satisfied and I do not miss anything when cooking.
    Regards.
  • #9 12416312
    kodam
    Rate: 29
    I conclude from your statements that the hob with four poles with a connection power of 3.68kW / 230V will work in my apartment. With installation 230v 4.5 kW
    Rysiek_XL
    Help: 9
    Rate: 31
    Yes of course.
  • #11 12417591
    kodam
    Rate: 29
    I ordered the CD.
    Thank you very much for all your help
The discussion revolves around the selection of an induction hob for a 230V apartment installation, specifically comparing models with power ratings of 4.0 kW, 4.5 kW, and 7.2 kW. Users emphasize the importance of existing electrical load, noting that a 4.5 kW allocation typically corresponds to a 20 A protection, which may not support a 7.2 kW hob without risking circuit overload. Participants share experiences with various hob configurations, highlighting that a 3.68 kW model with four cooking zones (two at 1.8 kW and two at 1.4 kW) provides satisfactory cooking performance. The consensus suggests that a 4.0 kW hob is adequate for reasonable cooking times, while a 7.2 kW model may be impractical unless the electrical system is upgraded.