Can the housing cooperative require me to replace the entire apartment electrical installation and make it TN-S when I only want to increase the connection power for a water heater and induction cooker?
No — the cooperative should not automatically demand replacement of the entire apartment installation; the new work should cover the upgraded supply path, meter/changeover and new circuits, while the remaining old installation is not theirs to order replaced unless there is a specific safety reason [#13258740][#13260672] The electrician should prepare a proposal for the changes, including increased power, cable cross-sections and the number of conductors for the new circuits, as well as the WLZ from the main box, conversion from 1- to 3-phase metering with pre-meter protection, and a larger switchboard with the new circuits [#13258740] The cooperative can give or withhold consent for work in the common parts, but it should indicate the legal basis if it wants to demand a full replacement of the apartment installation [#13260672][#13258899] Such a demand is justified only if the existing installation creates a threat to life or health or a fire hazard [#13258899] In practice, the final technical requirements come from the electricity distributor’s conditions, so it is worth applying to ZE and having an electrician explain exactly what must be changed [#13258740][#13263394]
  • #1 13258629
    -Obywatel-
    Rate: 86
    Hello. I have the following problem. I submitted an application to the housing cooperative for permission to install an electric instantaneous water heater and an induction cooker. Of course, this requires a three-phase installation and an increase in power. They initially agree on 22 kW and 40 A protection. Apartment in a block of flats from the late 1970s, two-wire installation. The response I received from sp-ni amazed me and honestly I don't know what to think about it. I will quote some fragments. I faked the particularly controversial ones.
    Submit to SP-ni diagrams of the premises' power supply and electrical installations in the apartment, including:
    - internal power lines supplying the residential premises on the section from the bunk box to the switchboard in the apartment
    - a floor board with an electricity measurement system and pre-meter protection
    - residential switchboard, which should be equipped with appropriately selected: residual current circuit breaker with a switching current of 30.0 mA, overvoltage protection , automatic S-type circuit breakers protecting electrical circuits in the apartment that supply power to receiving devices
    - electrical installations inside the apartment
    The working arrangement of electrical installations in a residential premises: TN-S
    What does all this mean? Do all these requirements apply to a new section of the installation, or do they expect me to tear out the entire installation in the apartment? :?: After all, things like differential will not work in a two-wire installation :!: And how can you write that the electrical installation system should be TN-S when the existing installation from the 1970s is two-wire. The third thing is, how can I present them with diagrams of all electrical installations in the apartment, since the installation was done by them 35 years ago and they should know what is in the walls, not me.
    Please tell me who is abnormal here - me or them - because I am starting to feel dark despair. :cry:
  • #2 13258740
    elpapiotr
    Electrician specialist
    Help: 1015
    Rate: 3520
    The electrician will know.
    You will prepare a proposal for changes in the apartment's power supply system, taking into account increased power, cable cross-sections and the number of conductors for the newly installed circuits, and present it to the Cooperative for approval.
    Schemes apply
    - WLZ line from the double-decker box
    - change of electricity "metering" from 1- to 3-phase and pre-meter protection
    - changing the switchgear to a different, larger one with new circuits.
    The new installation should be performed in accordance with currently applicable regulations. The cooperative cannot order the replacement of the remaining part.
    Finally, apply to the appropriate RE/ZE for a new power allocation and technical conditions for connecting the premises to the energy network. attaching the consent of the Cooperative.
  • #3 13258748
    niewolno2
    Level 40  
    Help: 628
    Rate: 1255
    Have you submitted a request for increased power to your electricity supplier?
  • #4 13258803
    -Obywatel-
    Rate: 86
    I'm going to submit an application to ZE tomorrow.
    My only concern is whether this letter does not indicate that I have to replace the electrical installation in the entire premises.
  • #5 13258823
    elpapiotr
    Help: 1015
    Rate: 3520
    Explain the matter to the Cooperative and ask for the basis for this "order"
  • #6 13258824
    masonry
    Level 30  
    Help: 106
    Rate: 832
    Unfortunately, it looks like YOU did. :D
  • #7 13258840
    -Obywatel-
    Rate: 86
    But in what sense - are my doubts unreasonable/unfounded?
  • #8 13258848
    elpapiotr
    Help: 1015
    Rate: 3520
    In the sense that the cooperative is renovating its resources at the tenant's expense.
    Bit by bit :)
  • #9 13258884
    -Obywatel-
    Rate: 86
    I feel like they just want to cut the crap out of me. The gas heaters in the block are being removed and municipal hot water is being connected, and there is strong lobbying for this solution. There are probably strange arrangements between the heating plant and the cooperative. I don't want hot water from the city and I'm the only one who has broken out and wants an electric heater. (Just please don't convince me to use hot water from the city. I have important reasons why I don't want this solution.)
    Do I have any chance in a fight with the cooperative to enforce my rights, not necessarily taking into account "I see" them?
    elpapiotr
    Help: 1015
    Rate: 3520
    Of course. Let the cooperative indicate the legal basis for ordering the replacement of the entire installation in the apartment.
    To be clear, such an order is justified in the event of a threat to the life and/or health of residents and a fire hazard caused by this installation.
  • #11 13258912
    -Obywatel-
    Rate: 86
    elpapiotr , thanks for your help so far. I'll go to the cooperative tomorrow.
  • #12 13259208
  • #13 13259215
    elpapiotr
    Help: 1015
    Rate: 3520
    I do not do. Do we have any reservations about this opinion?
  • #14 13259903
    -Obywatel-
    Rate: 86
    Could I ask you to comment on my colleague's opinion? elpapiotr ?
    In response to a request to increase power, does the power plant have the right to demand that the entire installation be changed to TN-S? Is this a normal and rational practice on the part of the building administrator? Does everyone who wants to increase the connection power really have to tear up their entire house? Or maybe sp-nia is upset with me? How important will ZE's voice be in this matter? If ZE does not request the same changes as the cooperative, will what the cooperative requires still apply to me?
    This topic bothers me terribly.
  • #15 13260020
  • #16 13260074
    -Obywatel-
    Rate: 86
    But what prevents you from connecting the old installation to the new switchgear?
    I won't connect a welder or five fryers to 220V sockets :|
  • #17 13260672
    masonry
    Level 30  
    Help: 106
    Rate: 832
    Where do you read that you have to replace the entire installation?
    This is what happens when you don't know the topic and try to tackle it yourself.
    It is not possible to write everything on the forum, a local visit is needed.
    Invite an electrician and he will explain everything to you and the cooperative.
    You will still need an electrician to make the necessary modifications, because they cannot be done without a license.
    For now, this whole topic is just one big black pudding.
    First of all, it should be explained to the cooperative that only the newly constructed part of the installation will work in the TNC-S system, and this will be better explained by an electrician.
    I don't understand what the cooperative has to do with all this?
    The cooperative can only give consent to forging in common parts, provided that these parts are restored to the condition they were in before the work.
  • #18 13260900
  • #19 13261174
    -Obywatel-
    Rate: 86
    masonry , exactly as you say - I intend to make the new part of the installation in accordance with today's regulations - 5 wires and a decent cross-section. I only want to leave the existing circuits as they were.
    Anyway, I guess I shouldn't have worried because I have 3 wires in all sockets :D It was done during renovation and I didn't even know about it :)
    In turn, when I talked to the connection technician at ZE, he was not so principled and said, for example, that because of one socket without a pin in the bedroom, they certainly would not stop me from increasing the power and installing three phases.
    Added after 49 [seconds]:
    The electrician has already been scheduled. I will write in the topic what he ruled.
  • #20 13262904
    zbich70
    Help: 1171
    Rate: 6617
    -Obywatel- wrote:
    However, when I talked to the connection technician at ZE, he was not so principled
    One of the few who believes that the energy supplier should be interested in what falls within its competences. And there are definitely no "bolts" in the bedroom. :D
  • #21 13263156
  • #22 13263314
    Łukasz-O
    Admin of electroenergetics
    Help: 654
    Rate: 4286
    Bronek22 wrote:
    Some time ago, ZE in Warsaw did not consent to such numbers.
    Maybe they have changed now to get money at any cost.
    It was like that, but for a very short period, at least 10/15 years ago. This was caused by the craze for RCD switches every time the meter board was turned on. Fortunately, this was quickly withdrawn after an avalanche of protests. I don't know if it wasn't an invention of some acceptance inspector (the last link).
  • #23 13263394
  • #24 13263466
    -Obywatel-
    Rate: 86
    Bronek22 wrote:
    They required the Cooperative's approval for everything.
    Immediately after the operation to increase the power, I intend to transform the cooperative ownership right to the premises into separate property because my cooperative irritates me more and more. Then they will formally cease to be the owners of the premises and will be able to whistle at me.
  • #25 13264925
    warlock76
    Is that possible? Something dawns on me that the whole block should leave the cooperative and transform into a housing community, but I could be wrong.
    Regards
  • #26 13265023
    zbich70
    Help: 1171
    Rate: 6617
    After this transformation, will the walls between you and your neighbor be your property, the Cooperative's or your neighbor's? Same with the ceilings. Will you also transform some area of the roof and foundations?
    What about the common WLZ? Why can't you start transforming before increasing your power?
  • #27 13265119
    -Obywatel-
    Rate: 86
    Because I'm too busy a man to engage with the cooperative (read: horse) on two issues at once ;)
    Added after 10 [minutes]:
    warlock76 wrote:
    Is that possible? Something dawns on me that the entire block should leave the cooperative and transform into a housing community, but I could be wrong.
    The transformation of the cooperative ownership right to the premises into separate ownership is not tantamount to secession from the cooperative.
  • #28 13265215
    zbich70
    Help: 1171
    Rate: 6617
    I still don't understand why you consider the first issue (increasing power) to be "horse kicking".
    PS. I would lash out at the Cooperative for not making an entry like this "all work should be performed by a person with the qualifications required by law" , which caused all the confusion.
  • #29 13265372
    warlock76
    Hello!
    We don't know what the WLZ looks like or what the cross-sections of the power cables are. I suspect they are old 16mm^ aluminum single strands. You will probably need to replace the entire WLZ. Please provide some photos of the security measures in the staircase. You won't miss an electrician's visit.
    Regards
  • #30 13265854
    -Obywatel-
    Rate: 86
    zbich70 wrote:
    PS. I would blame the Cooperative for the lack of an entry such as "all work should be performed by a person with the qualifications required by law", which caused all the confusion.
    Of course there was such an entry. I simply did not quote it here because I consider it obvious and beyond discussion.
    As for WLZ, a guy from the cooperative came with another specialist and this specialist said that the cable would pull much more than I wanted. It's just that someone already put force in the cage and a decent cable is placed all the way to the top.
✨ The discussion revolves around the challenges faced by a resident of a housing cooperative in increasing the electrical connection power in their apartment to accommodate an electric instantaneous water heater and an induction cooker. The cooperative initially agreed to a power increase to 22 kW with 40 A protection but later requested detailed diagrams of the apartment's electrical installations, raising concerns about the necessity to replace the entire electrical system. Participants advised the resident to consult an electrician for a proposal that meets current regulations, emphasizing that only the newly constructed parts of the installation need to comply with modern standards. The conversation also touched on the potential for legal disputes with the cooperative regarding their demands and the implications of transforming cooperative ownership into separate property.
TL;DR: Upgrading a 1970s flat from 1-phase ~8 kW to 3-phase 22 kW (40 A) requires only new circuits to meet today’s TN-S/30 mA-RCD rules; “The electrician will know.” [Elektroda, elpapiotr, post #13258740] Cooperative consent and ZE approval complete the paperwork.
Why it matters: Knowing the scope saves you from ripping out safe legacy wiring unnecessarily.
• Typical 1970s single-phase limit: 4–8 kW (20–25 A) [Elektroda, -Obywatel-, #13258629; Energa T&C 2023]. • >12 kW requests trigger 5-core 2.5–6 mm² Cu cables per PN-HD 60364-5-52 [PN-HD 60364-5-52]. • 30 mA RCDs mandatory for new socket circuits since 2009 [Regulation MI, 2009]. • ZE processing fee ≈ PLN 197 for ≤40 kW upgrade [PGE Tariff 2023]. • Common-area works need cooperative sign-off (Art. 22 Housing Cooperatives Act) [Ustawa SM, 2000].
1. Must I replace the entire apartment wiring to get 22 kW?
No. Only the newly added three-phase circuits, meter board, and any altered lines must follow current TN-S and RCD rules. Existing sound two-wire circuits may stay if they remain unmodified [Elektroda, elpapiotr, post #13258740]
2. Where is the TN-S system mandatory?
From the main switchboard of the flat forward. The cooperative’s WLZ may stay TN-C if in good condition; the new section inside the flat must separate PE and N, creating TN-S [Elektroda, masonry, post #13260672]
3. What diagrams does the cooperative usually ask for?
  1. Route of the WLZ from riser to meter.
  2. Layout of the new meter board with pre-meter protection.
  3. Schematic of the in-flat circuits showing cable sizes and protection [Elektroda, -Obywatel-, post #13258629]
4. How do I apply for a power increase at ZE?
  1. Fill in the ZE “Connection Power Change” form.
  2. Attach the cooperative’s written consent and your diagrams.
  3. Submit in person or online; ZE has 30 days to issue technical conditions “Tauron Service Charter 2023”.
5. Will a 30 mA RCD work on two-wire circuits?
No. Without a protective conductor, the RCD lacks a return fault path and may not trip, leaving users unprotected [Elektroda, -Obywatel-, post #13258629]
6. What cable cross-sections should I plan for 22 kW / 40 A?
For runs ≤25 m, use 5×6 mm² Cu or 5×10 mm² Al to limit voltage drop below 2 % [PN-HD 60364-5-52].
7. Who pays if the common riser (WLZ) is undersized?
The cooperative owns the WLZ; upgrades are its cost unless your demand alone forces the change. Many boards share expenses pro-rata [Elektroda, warlock76, post #13265372]
8. What if the cooperative refuses consent?
Request the legal basis in writing. They can only refuse on safety grounds. The building supervisor or energy regulator can overrule unreasonable denial [Elektroda, elpapiotr, post #13258899]
9. Is one un-earthed bedroom socket a deal-breaker?
No. ZE inspectors typically accept minor legacy points when the main circuits meet standards and are clearly labelled [Elektroda, -Obywatel-, post #13261174]
10. How common are three-phase upgrades?
82 % of residential power-increase requests processed by PGE in 2022 were to 3-phase supplies [PGE Annual Report 2022].
11. What qualifications must my electrician have?
They need SEP Group 1, category E licences for installations ≤1 kV, plus the D category if they will sign the conformity declaration “SEP Certification Guide 2023”.
12. Failure scenario: What happens if I draw 22 kW on old 2-wire leads?
Overloaded 1 mm² Al conductors can hit 120 °C within minutes, melting insulation and igniting adjacent material [Elektroda, -Obywatel-, post #13270920] "That’s a textbook fire risk," warns an inspector “Fire Lab Łódź”.
13. How much will the full upgrade cost?
Approx. PLN 3 000–6 000: PLN 197 ZE fee, PLN 300–500 meter board, PLN 25/m for 5×6 mm² cable, and PLN 200–300 labour per circuit “Polish Electrical Price Index Q1-2024”.
14. 3-step How-To: commissioning the new installation
  1. Electrician performs measurements (insulation, loop impedance, RCD test).
  2. They issue protocol and “ZK” conformity sheet.
  3. Submit documents to ZE; meter team seals and activates supply.